 RCCB for Water Heater

views
     
SUSceo684
post Nov 7 2021, 12:33 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(hcmalaya @ Nov 6 2021, 02:55 AM)
Maybe ur house bungalow lo
Mine just normal terrace house
Add labour around 100?
*
Wah landed!
I stay in highrise.
Long time ago supply only 40A per phase due to wire size small. So not very useful, hence prev owner put in 3ph so can use up to 120A.

U supply the parts yourself will be cheaper than asking the electrician to buy for you..But to get the right part w/o pic of ur existing is hard..err on the side of 63A 30mA 2P RCD. then get an electrician or wireman to wire it up should cost around there. For plug and play replacement you can shop around FB..some are pretty cheap on labour. My usual sub con costs from 200 to show up. laugh.gif
SUSceo684
post Jan 12 2022, 07:13 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(esoo88 @ Jan 12 2022, 05:43 PM)
Hi All,
does anyone know if water pump require a RCBO protection as it also dealing with water ? my current water pump has a dedicated MCB without RCCB, it relies on main RCCB with sensitivity of 100ma.
*
Here in MY whilst the appliance is not in a wet floor area, it won't be covered by ST reg w.r.t water heater. But if its outdoors then should have at max 30mA RCD.

b) Regulation 36(2) of the Electricity Regulations 1994 states that for
a place where the floor is likely to be wet or where the wall or
enclosure is of low electrical resistance, protection against earth
leakage current must be provided by a residual current device of
sensitivity not exceeding 10 milliamperes;
c) Regulation 36(3) of the Electricity Regulations 1994 states that for
an installation where hand-held equipment, apparatus or
appliance is likely to be used, protection against earth leakage
current must be provided by a residual current device of
sensitivity not exceeding 30 milliamperes;


Over in UK - https://www.electricalsafetyfirst.org.uk//g.../garden-safety/ it is recommended to fit an RCD for water pump.

In your case..I would suggest to change the 100mA main RCD with a 30mA RCD in the event rainwater drip in onto the pump during thunderstorm. Then it would cover all bases including your 13A sockets. thumbup.gif

Modern RCD from ABB, Hager come with anti nuisance trip feature, it will not nuisance trip much compared to those sold before 2000, about 97% reduction.
SUSceo684
post Jan 13 2022, 02:15 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(esoo88 @ Jan 13 2022, 09:50 AM)
thanks for responding, my water pressure pump is located on ceiling and covered by roof, hence it is at dry area.

do you still see a need for a RCD for extra protection ?

many have talked and discussed that RCD is mandatory for WH, little is talking about water pump here in malaysia.

on your recommendation on changing the main RCD from 100ma to 30ma, would it be too sensitive with unnecessary trips ?

i see many electrician uses 300ma in main RCD.
*
What is the likelihood the roof leaks from thunderstorm/strong wind esp in older homes, and causes the pump to be flooded?

RCD has dual function to protect life, and protect against fire.
Assuming only a single unit (main RCD) is installed, 100mA you already breaking Electricity Regulations 1994 as all the 13A sockets can kill humans at 50mA.

Itu electrician qualified or not? You are not running a dodol machine at home that will trip a 30mA on normal startup.

Nobody in their right mind put 300mA in residential. In SG and UK, everybody put 30mA for residential. Maybe Malaysia got stronger human than them can sustain 230V currents lah.. laugh.gif

I personally use all 30mA.

As mentioned, modern RCD has anti nuisance trip so it does not trip on false alarm like those made before 2000.

This post has been edited by ceo684: Jan 13 2022, 02:24 PM
SUSceo684
post Mar 29 2022, 06:49 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(BL98 @ Mar 29 2022, 01:41 PM)
user posted image

Recently upgraded to 3 phase for my house reno.
The contractor say this device the higher the better.
True?

Edit: found out mine is 300mA
*
300mA better dun put la. Confirm six times killed, then only trip icon_idea.gif

The higher the better for them only because 1. Lowest price (lousy sensitivity is dirt cheap on 3phase) and 2. very hard to trip (no callbacks from owner). Which is ok for industrial use but at home, what good is human dying 6 times over ☠☠☠☠☠☠ before it decided oh ok..lets trip.🥱

All the expensive specification i.e. 63A max load, 30mA top tier sensitivity, 3phase supply and good brand like ABB/Hager using VI design (works regardless got voltage or not) will cost 290-300 bucks for RCD alone easily exclude installation.

At 300mA 🤦‍♀️, VD type (won't work if no voltage), non high end brand (Schneider and below) easily half the price but ZERO life protection. ☠☠☠☠☠☠ It only protect building for FIRE 🔥 protection. Not to mention, its illegal to use 300mA in residential...CHEAP mah! 😅

This post has been edited by ceo684: Mar 29 2022, 07:03 PM
SUSceo684
post Mar 29 2022, 07:02 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(Kiding @ Mar 29 2022, 06:42 PM)
The lower of the trip current, the higher sensitivity of detecting current leaking.
*
Yes, lower mA trip current is safer.

Humans die at 50mA current.

Pick your poison between 30mA, 100mA, 300mA.
Two of them can and will ☠. Just a matter of whether ☠☠ or ☠☠☠☠☠☠
SUSceo684
post Mar 29 2022, 10:22 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(BL98 @ Mar 29 2022, 09:23 PM)
Holy cow. Lucky I asked. kknccb contractor.

Spent 10k to upgrade to 3 phase thinking can get better safety. Manatau...

So this EPS brand ok? Saw they use EPS brand in the whole DB box.

Going to tell the contractor to change this RCBO...Which brand should I tell him to change to?

Should I call other electrician to double check or audit their work? Scare kena electrocuted.
*
3phase and 10k reno should use ABB or Hager for the mains RCD 30mA (0.03A)
EPS boleh pakai lah..local brand.. but I personally prefer ABB. Safety item really you get what u pay for biggrin.gif

⚠️ Also ensure you have individual 10mA (0.01A) per each water heater unit.
SUSceo684
post Mar 30 2022, 10:28 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(BL98 @ Mar 30 2022, 01:05 AM)
If MCB is EPS, can still mixed with Hager RCD?

So I just tell the electrician to change the 300mA to Hager/ABB RCD 30mA?

If I got 4 toilets with water heater, then have to use 4 individual 10mA RCD? Or just use 1 10mA RCD?

Suddenly feel like kena kencing by contractor... Damn sienzz... ranting.gif
*
If MCB is EPS, can still mixed with Hager RCD? Yes

So I just tell the electrician to change the 300mA to Hager/ABB RCD 30mA? Yes thumbup.gif

If I got 4 toilets with water heater, then have to use 4 individual 10mA RCD? Yes 4WH = 4x 10mA RCD's is best. If DB no space issue, can use Schneider 25A 10mA RCBO

SUSceo684
post Mar 30 2022, 06:18 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(BL98 @ Mar 30 2022, 01:26 PM)
Appreciate your reply.

The Hager/ABB RCD 30mA can support the whole house? Even with 3 phase wiring?
I only have 1 DB box for  story terrace house. Contractor say 1 DB box enough liao.
*
Can, I'm using single (whole house) 30mA RCD w 3ph supply to type this
SUSceo684
post Mar 30 2022, 11:59 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(BL98 @ Mar 30 2022, 07:03 PM)
So 1 number of 63A Hager 30mA RCB for whole house, replacing the EPS 300mA 63A.

And 1 25A Schenider 10mA RCB for water heater
*
thumbup.gif

QUOTE(maxguy @ Mar 30 2022, 07:20 PM)
hager 63A 30mA RCD for power socket and 40A 30mA RCD for lighting and fans, then 25A Schneider 10mA RCBO for water heater
*
no need lah, this is 2022
we are not in the business of selling RCDs
MS1979:2007 COP55 mentioned can put one single whole house RCD [at origin of installation]
Attached Image

the code in force is Electricity Regulations 1994
back then:
a. nobody use LED light. all use leaky fluorescent tube.
b. nobody use inverter at home for AC and fridge.
c. my Sony VCR also leak current, always kena zap from metal body. it came with 2 pin plug.
d. people use CRT TV

nowadays
appliances are made better with much lesser leakage current
meaning to say there's no actual need to use so many mains RCD's [this is in relation to some who propose one 30mA and one 100mA]
when one single whole house RCD 30mA can comply fully.
note its "maximum tolerance allowed" not "identical die-die must be exact"
Attached Image

----

as for your suggestion it is not wrong.. actually split load design is to have half the lights and half the sockets on each mains RCD (two mains RCDs), not split by lights vs sockets. Because again, 2022 everyone using much better made items with much lesser residual leakage current.

to expand on your suggestion, 3 phase supply CAN also be protected with 3x single phase RCDs.

split load pro: so in the case one RCD trips, you still have half the things running until user figure out what's wrong
split load con: cost of extra RCD whistling.gif sweat.gif

This post has been edited by ceo684: Mar 31 2022, 12:05 AM
SUSceo684
post Jun 11 2022, 05:25 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(zodiacyi @ Jun 11 2022, 03:25 AM)
Hi all, my current water heater is not connected to RCCB. I plan to install RCBO instead of RCCB due to limited space at my current DB box.

Question, since the neutral wire from double pole switch for water heater is connected directly to the neutral busbar in db box, how can I identify which is the neutral wire for it, so that I can divert it to the outgoing at the RCBO? Many thanks in advance for your reply.
*
By the process of elimination.
Obviously, it won't be the 1.5mm thin wires.
So out of the 2.5mm pile..
disconnect half and test continuity. (isolate the bunch u disconnected - make sure it doesnt contact elsewhere). if its not lighting up the double pole switch LED then u have isolated that "half" - its somewhere in that isolated pile.

Its not hard, but its annoying coz you don't know which is which at the neutral. But it is a necessary evil and salute you for installing a 10mA RCD/RCBO anyhow.
SUSceo684
post Jun 11 2022, 10:28 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(jchong @ Jun 11 2022, 06:42 PM)
I saw some RCCBs listed as 'High Immunity'. Is this HI the same as anti nuisance trip feature or it's something different?
*
HI is usually used to described advanced anti-nuisance trip (protect against switching transients and harmonics).
Those with anti nuisance trip (protect against switching transients) for residential use will suffice.
SUSceo684
post Jun 14 2022, 01:01 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(zodiacyi @ Jun 14 2022, 12:53 AM)
Thanks for the reply. On another note, I have one issue with my newly installed RCCB (brand EPS, 63A, 100mA). The RCCB will trip once the main power is switched on, even when all the MCB are switched off. Any idea why is this happening and how to troubleshoot? My electrician is telling me my RCCB is faulty and I'll need to get a new one.
*
Also by process of elimination, it should not be hard for the electrician to prove a component or the load is faulty by hooking up a test load like a lamp or something (ie disconnect everything else). Sometimes old wiring or old appliance can be leaky. A competent electrician can easily swap out your RCCB with another 100mA unit that he/she has in stock.
SUSceo684
post Jun 14 2022, 08:06 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(zodiacyi @ Jun 14 2022, 02:12 AM)
Thanks for the suggestion. Unfortunately, my electrician does not have a spare 100mA RCCB, instead he swapped it with his spare 300mA RCCB and it stops tripping. Therefore he is telling me that my newly bought RCCB is faulty and to get a new one. Just wondering, will it be possible it's due to earth leakage from a neutral wire?
*
That is where the process of elimination comes into play (if there is no load connected at all to the RCD you bought) then it should stay energised.
He can also slave the 100mA you bought into his 300mA onto a spare bulb as test circuit just to test the RCD functionality.

You should return it for more reputable brands if even a controlled test circuit refused to work.
SUSceo684
post Mar 18 2023, 01:23 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(RagingCandy @ Mar 17 2023, 05:14 AM)
Hi there, my house is a 3 stories terrace with 3 phase electric supply. Developer gave 0.3A RCCB. Is it safe?

user posted image
*
Completely useless for human life protection.
Its only good for fire protection.

0.3A RCD has NO PLACE in residential domestic use.

For single RCD (whole house RCD) your RCDs shall be a 30mA (0.03A) [one per house] to be code compliant; AND
a 10mA (0.01A) [one for each water heater circuit].


Attached thumbnail(s)
Attached Image
SUSceo684
post Mar 18 2023, 01:36 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(zodiacyi @ Jun 14 2022, 03:45 PM)
I think it's time for me to get a certified electrician to get the job done. He has no idea what I'm talking about when I asked him to perform a test circuit to confirm if the RCD is indeed faulty. He even suggested for me to buy a new RCD that is less sensitive (300mA) just like the spare RCD he has installed for me. I do not want to be killed 6 times over so I just brushed him off. Thanks again for your reply.
*
Most welcome. Sorry late reply.

QUOTE(davidlow7 @ Jun 14 2022, 11:15 PM)
I got headache with most electricians nowadays and I don't know where to find someone competent now to install ab RCD/RCBO 10mA for me.

The electrician that someone recommended does not know what is RCBO and tell me this is not for Malaysia one 🤦‍♂️. He further insisted that I'll need to rewiring everything when I install one.

Really headache and I don't know where to get someone competent. I've not used the water heater for months now.
*
Got one, but you need to dig in FB "Chargeman & Wireman" group.

QUOTE(judesh @ Jan 6 2023, 08:03 AM)
Hi Guys, after reading the comments here I decided to check what's in my house. It's a 2 storey  house in Melaka with 3 phase supply.  1 WH connected to dB downstairs which I will replace with 10mA RCCB. Will also replace the main 4P 100mA RCCB with 30mA from ABB.
Upstairs DB will also replace main 100mA RCCB  to 30mA.... But all slots full so can't change to RCCB for each WH so looking at options...
1. Change 14way to 18way DB?
2. Replace with 10mA RCBO for the 2 WH...is this PnP or need also to identify the N and connect accordingly?
3. Maxguard or any other Sirim approved 10mA RCBO ok or recommended Schneider only?
4. All the WH are connected by plug socket in wall above inside bathroom. Will also replace this with splash proof socket as recommended... Can I connect the 10mA RCCB above this socket instead ? Or above  switch outside bathroom?
Thanks
*
1) is always possible, I run 48 way for my small apartment; RCBO is space saving as it can replace existing MCB slot (1-to-1).
2) need to identify the return N for that specific circuit. bit mafan. but doable, and its a necessary step for proper installation.
3) Your life insurance provider. Personally if best-of-the-best, ABB or Hager has technical advantage being VI (voltage independent) in such that even if the voltage to RCD dips below certain V, the RCD still will operate even at 0 voltage. It is pure current imbalance detection. Whereas "for any other commonly available brand that is cheaper" they are highly likely to be the VD type RCD (voltage dependent). Nevertheless, understand that ABB/Hager 10mA costs upwards of RM150 each, I would recommend at least getting a Schneider 10mA.
4) Plug and socket is illegal because almost all WH already exceed 15A nominal. Change to splash proof centon connector.
4.1) The 10mA ideally should be at the DB box area for ease of maintenance but if there is no other better way, keep it OUTSIDE of the wet area (outside of bathroom) and before the 20A switch (i.e. RCD must always be powered).

QUOTE(lowyat101 @ Jan 6 2023, 10:50 AM)
» Click to show Spoiler - click again to hide... «


just curious, why you want to use the 30mA for the mains?

sorry ignore the questions above, just found out that my house also having the 30mA  sweat.gif
*
30mA offers a "seatbelt" to cut power before your heart goes out of order "ventricular fillibration" at 50mA.
Since 100mA or 300mA is gonna cut power AFTER your heart goes out of order "ventricular fillibration" at 50mA... in short, it means bye bye rclxs0.gif

There is no mention of 300mA for domestic installation in the MS1979 COP at all.
--Yes this is old version @ 2007 but the 2015 one didn't change much.


Attached thumbnail(s)
Attached Image
SUSceo684
post Mar 19 2023, 06:16 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(RagingCandy @ Mar 19 2023, 01:52 PM)
Shitty developer. There is one sub-db which using a 0.1A RCCB. Shall I change the main-DB to 0.1A or lower?
*
It’s for lighting only (does not control any sockets or any water heaters) then it’s ok-lah
SUSceo684
post Mar 19 2023, 06:17 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(RagingCandy @ Mar 19 2023, 01:53 PM)
Means using 300mA RCCB is okay? Noob here
*
Six times ded. Hexa kill 300mA is only used in commercial/industrial applications. You don’t run huge motors at home
SUSceo684
post Mar 20 2023, 12:20 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(RagingCandy @ Mar 19 2023, 09:07 PM)
Got it. will change it to 100mA then.
*
Use 30mA, no developed country use 100mA for homes one.
SUSceo684
post May 8 2023, 02:54 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(Pain4UrsinZ @ May 8 2023, 11:29 AM)
why many still using ELCB instead of RCD when RCD is better and cheaper cost ?
*
ELCB is cheaper because it is dinosaur tech.
https://electrical-engineering-portal.com/w...rent-device-rcd

10mA RCD one ketul good one (ABB/Hager) VI type already RM160 barang only.
It attract new problem like no space in DB box and a complete overhaul of new panel (new DB) is a lot of work and not every customer willing to pay for it.
Quote even RM10 more expensive you lost the job so there is no incentive to do things proper in MY.

This post has been edited by ceo684: May 8 2023, 02:55 PM
SUSceo684
post May 11 2023, 11:09 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(mushigen @ May 9 2023, 11:44 PM)
ST guidelines and electrical safety guidelines say max sensitivity is 100mA for both 1P and 3P supplies.
For 3P, you can choose to install one 100mA rccb (if any phase is defective, you lose power to whole house) or 3x100mA rccb for each phase.
*
https://www.clipsal.com/learn-and-discover/...ts-up-buzz-rcds
In Australia:
The main change is to the application of RCDs in domestic installations. All final sub-circuits in a residential installation, no matter the amperage or number of phases, are to be 30mA RCD protected. In general, the changes made now require fixed or stationary electrical equipment, such as a hot water service, an air conditioner, cook top, oven or range to be protected by a 30mA RCD.

Where a whole switchboard is being upgraded to replace existing protection then that switchboard is to be brought up to date with RCD protection.

In Msia:
Maybe humans in MY can tahan better than humans in AU.