> Don't buy MR DIY Surge Protector powerstrip, The MOV is only protecting one socket.

views
     
TSJohnLai
post Aug 13 2018, 07:38 PM, updated 8y ago

Skeptical Cat
*******
Senior Member
3,669 posts

Joined: Apr 2006
Recently, uncle bought one cheap surge protector powerstrip from MR DIY store at RM24 something? dry.gif

But, to uncle dismay, the MOV is installed at wrong place. As the result, only one socket is protected from possible surge while the other three are not.

Some pictures below (large image):

» Click to show Spoiler - click again to hide... «


Searching around the net for the MOV model returned:
user posted image
https://www.sunrom.com/p/10d471k-varistor-mov-for-220v-ac


Data from https://www.sunrom.com/get/559199 seem to indicate:
user posted image
Aside from the wrong MOV placement in the powerstrip, the MOV itself is fine for its intended purpose.
How in the world this thing qualify as surge protector when it only protect one socket out of four sockets? sweat.gif

SIRIM tengah tidur ke? dry.gif


ListenToTheWind
post Aug 13 2018, 07:41 PM

Casual
***
Junior Member
453 posts

Joined: Feb 2014
Parking
zetshield21
post Aug 13 2018, 07:41 PM

New Member
*
Junior Member
28 posts

Joined: Jun 2011
Abang engineet bole tau bape gaji abang?
kamfoo
post Aug 13 2018, 07:45 PM

Enthusiast
*****
Junior Member
845 posts

Joined: Nov 2010


wat is mov
acbc
post Aug 13 2018, 07:45 PM

Look at all my stars!!
*******
Senior Member
9,035 posts

Joined: Jan 2003
SIRIM bayar only. No need test also pass.
urnicksux2
post Aug 13 2018, 07:45 PM

Getting Started
**
Junior Member
77 posts

Joined: Jul 2013


wow got sirim sticker
Satori 14118a
post Aug 13 2018, 07:46 PM

Regular
******
Senior Member
1,003 posts

Joined: Sep 2014


From eyeballing the innards seems like the singlr mov protects all sockets (when individual sockets switched on). Look at the common N and L rails.

Then again I'm not an electronic circuitry expert.
waterjunk
post Aug 13 2018, 07:46 PM

New Member
*
Newbie
0 posts

Joined: Oct 2005



The MOV is being installed across Line and Neutral which is correct. Since this is a single phase socket array, all the 3 (Line Neutral and Ground) are shorted together via the copper busbar. Therefore the potential differences between the sockets should be negligible.

More expensive surge arrestors will have MOV across line-line, line-neutral, neutral-ground and line-ground. Obviously this Mr DIY is just a extra precaution instead of full protection~ better than nothing i suppose haha
ar188
post Aug 13 2018, 07:49 PM

Look at all my stars!!
*******
Senior Member
9,206 posts

Joined: Jun 2006
QUOTE(kamfoo @ Aug 13 2018, 07:45 PM)
wat is mov
*
movie file format biggrin.gif
olman
post Aug 13 2018, 07:49 PM

Regular
******
Senior Member
1,998 posts

Joined: Jan 2003


Sirim keje diamond lekat sticker saja
zerorating
post Aug 13 2018, 07:50 PM

Miskin Adab
*****
Senior Member
970 posts

Joined: Aug 2007
From: Lokap Polis


for sensitive item, get AVR please.
acbc
post Aug 13 2018, 07:51 PM

Look at all my stars!!
*******
Senior Member
9,035 posts

Joined: Jan 2003
Mr DIY items are cheap because they don't last. I usually buy them for emergencies. They do stock branded ones but quite expensive.
Jag23sys
post Aug 13 2018, 07:54 PM

New Member
*
Junior Member
18 posts

Joined: Aug 2016
Wah, who pass the sirim cert??

Kena liao.
zerorating
post Aug 13 2018, 07:55 PM

Miskin Adab
*****
Senior Member
970 posts

Joined: Aug 2007
From: Lokap Polis


QUOTE(acbc @ Aug 13 2018, 07:51 PM)
Mr DIY items are cheap because they don't last. I usually buy them for emergencies. They do stock branded ones but quite expensive.
*
mr diy start selling branded items already, you can see philips and pentene there.
also hotak sets is good enough for my usage too. their single piece of screw driver oso good as well.
SUSslimey
post Aug 13 2018, 07:56 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
erm..................

ts bodo
TSJohnLai
post Aug 13 2018, 07:56 PM

Skeptical Cat
*******
Senior Member
3,669 posts

Joined: Apr 2006
QUOTE(Satori 14118a @ Aug 13 2018, 07:46 PM)
From eyeballing the innards seems like the singlr mov protects all sockets (when individual sockets switched on). Look at the common N and L rails.

Then again I'm not an electronic circuitry expert.
*
QUOTE(waterjunk @ Aug 13 2018, 07:46 PM)
The MOV is being installed across Line and Neutral which is correct. Since this is a single phase socket array, all the 3 (Line Neutral and Ground) are shorted together via the copper busbar. Therefore the potential differences between the sockets should be negligible.

More expensive surge arrestors will have MOV across line-line, line-neutral, neutral-ground and line-ground. Obviously this Mr DIY is just a extra precaution instead of full protection~ better than nothing i suppose haha
*
Yes, I know about those three lines protection.

In MR DIY powerstrip, if there is power surge and all four switches are turned on, only Green socket will be protected from surge while the Blue, Orange and Red sockets will be hit by surge.

In this case, the MOV should be installed as shown below in red line (Point of entry):
user posted image
This way, all four sockets will be protected from surge coming from Live wire by redirecting surge to Neutral wire out.
I have no idea why the MOV is installed that way protecting only one socket sweat.gif and still pass SIRIM.
Snoopycute98
post Aug 13 2018, 07:57 PM

Casual
***
Junior Member
402 posts

Joined: Oct 2016
U get what u paid la
SUSalteclp
post Aug 13 2018, 07:59 PM

New Member
*
Junior Member
27 posts

Joined: Feb 2010
Wadeyer expect from rm24 item, furthermore its mr diy
rwzf
post Aug 13 2018, 07:59 PM

New Member
*
Newbie
14 posts

Joined: Oct 2017


Report to SIRIM!
mazannor81
post Aug 13 2018, 07:59 PM

Getting Started
**
Junior Member
64 posts

Joined: May 2012
wanna beter protection, better buy Cal Lab
EarendurFefalas
post Aug 13 2018, 08:01 PM

Getting Started
**
Junior Member
155 posts

Joined: Sep 2012


ayam buruh nelayan dan juga petani

apa MOV MOV ni? ELI5 takda ka?
Satori 14118a
post Aug 13 2018, 08:02 PM

Regular
******
Senior Member
1,003 posts

Joined: Sep 2014


QUOTE(JohnLai @ Aug 13 2018, 07:56 PM)
Yes, I know about those three lines protection.

In MR DIY powerstrip, if there is power surge and all four switches are turned on, only Green socket will be protected from surge while the Blue, Orange and Red sockets will be hit by surge.

In this case, the MOV should be installed as shown below in red line (Point of entry):
user posted image
This way, all four sockets will be protected from surge coming from Live wire by redirecting surge to Neutral wire out.
I have no idea why the MOV is installed that way protecting only one socket sweat.gif  and still pass SIRIM.
*
Look carefully. It's the same.
lawrencesha
post Aug 13 2018, 08:03 PM

Enthusiast
*****
Junior Member
882 posts

Joined: Nov 2004


Uncle must have failed electronics in college. The MOV is placed in the COMMON ground and neutral point - which is exactly the same as what you mentioned in the later post.
fabianz03
post Aug 13 2018, 08:05 PM

Look at all my stars!!
*******
Senior Member
4,649 posts

Joined: Aug 2008
From: Tāmaki Makaurau
Dude, English please ELI5
waterjunk
post Aug 13 2018, 08:07 PM

New Member
*
Newbie
0 posts

Joined: Oct 2005



QUOTE(JohnLai @ Aug 13 2018, 07:56 PM)
Yes, I know about those three lines protection.

In MR DIY powerstrip, if there is power surge and all four switches are turned on, only Green socket will be protected from surge while the Blue, Orange and Red sockets will be hit by surge.

In this case, the MOV should be installed as shown below in red line (Point of entry):
user posted image
This way, all four sockets will be protected from surge coming from Live wire by redirecting surge to Neutral wire out.
I have no idea why the MOV is installed that way protecting only one socket sweat.gif  and still pass SIRIM.
*
Except electricity doesn't work that way. It will always travel along the path of least resistance. What the MOV does is to give it an easy alternative so the MOV burns up instead of your load. So essentially electricity doesn't really care whether it is 'nearer' or 'further' UNLESS there is added impedance which I don't believe to be the case because your power switch is barely 1' long...

Try taking a multimeter and measure the resistance between your proposed location and the actual location. Probably u get less than 50ohms. When the surge comes in at 1,000 volt, it probably isn't going to care about the 50ohms haha.
SUStsunade
post Aug 13 2018, 08:08 PM

Look at all my stars!!
*******
Senior Member
2,063 posts

Joined: Jan 2003
From: Konoha
lol. TS oh TS
TSJohnLai
post Aug 13 2018, 08:15 PM

Skeptical Cat
*******
Senior Member
3,669 posts

Joined: Apr 2006
QUOTE(waterjunk @ Aug 13 2018, 08:07 PM)
Except electricity doesn't work that way. It will always travel along the path of least resistance. What the MOV does is to give it an easy alternative so the MOV burns up instead of your load. So essentially electricity doesn't really care whether it is 'nearer' or 'further' UNLESS there is added impedance which I don't believe to be the case because your power switch is barely 1' long...

Try taking a multimeter and measure the resistance between your proposed location and the actual location. Probably u get less than 50ohms. When the surge comes in at 1,000 volt, it probably isn't going to care about the 50ohms haha.
*
hmm.gif
Now that is something new......
If that the case, why do those high end surge protector MOVs normally located before the socket or load?

fireballs
post Aug 13 2018, 08:20 PM

10101
*******
Senior Member
5,646 posts

Joined: Mar 2012
Even the protection voltage also wrong.
Should be 275
lawrencesha
post Aug 13 2018, 08:24 PM

Enthusiast
*****
Junior Member
882 posts

Joined: Nov 2004


Anyway, when 1000V comes along, do you think that small MOV will help?

Industrial surge protection cost thousands of dollars. And most of all, they have good grounding (which also cost thousands to achieve).
Phoenix_KL
post Aug 13 2018, 08:26 PM

Getting Started
**
Junior Member
156 posts

Joined: Sep 2017
RM24 expect belkin RM90
waterjunk
post Aug 13 2018, 08:28 PM

New Member
*
Newbie
0 posts

Joined: Oct 2005



QUOTE(JohnLai @ Aug 13 2018, 08:15 PM)
hmm.gif
Now that is something new......
If that the case, why do those high end surge protector MOVs normally located before the socket or load?
*
Well the truth about surge protection is electrical surges are kinda unpredictable in terms of amplitude (peak to peak volt) or duration (surge time) so designing a perfect surge arrestor is close to impossible. Even industrial surge protector guys such as Emerson etc usually do not offer any sort of guarantee.

In fact some manufacturers put multiple MOVs across the same system in hopes that one of them 'catches' the strike. Theoretically installing a MOV at the 'entrance' is a good industry practice but there is no concrete proof that installing elsewhere along the PCC (Point of common coupling) affects the efficiency of the surge arrestor system.

If you have an expensive equipment, investing in a proper surge arrestor instead of Mr DIY is highly recommended biggrin.gif
SUSendau02
post Aug 13 2018, 08:30 PM

Look at all my stars!!
*******
Senior Member
3,180 posts

Joined: Jun 2009
From: Borlänge


QUOTE(JohnLai @ Aug 13 2018, 07:56 PM)
Yes, I know about those three lines protection.

In MR DIY powerstrip, if there is power surge and all four switches are turned on, only Green socket will be protected from surge while the Blue, Orange and Red sockets will be hit by surge.

In this case, the MOV should be installed as shown below in red line (Point of entry):
user posted image
This way, all four sockets will be protected from surge coming from Live wire by redirecting surge to Neutral wire out.
I have no idea why the MOV is installed that way protecting only one socket sweat.gif  and still pass SIRIM.
*
pls dont tell me u r an electrical engineer
SUSendau02
post Aug 13 2018, 08:33 PM

Look at all my stars!!
*******
Senior Member
3,180 posts

Joined: Jun 2009
From: Borlänge


QUOTE(fireballs @ Aug 13 2018, 08:20 PM)
Even the protection voltage also wrong.
Should be 275
*
we get single phase 220, 240v is rms value. peak is 220 X root(2).

275V hancur lor
deejay_krish
post Aug 13 2018, 08:33 PM

You're Just Another Part Of Me
******
Senior Member
1,015 posts

Joined: Jul 2005
From: Neverland
What do u expect? A few hundred ringgit quality when u just buy it for few bucks? Simple terms. U get what u pay for.
SUSendau02
post Aug 13 2018, 08:34 PM

Look at all my stars!!
*******
Senior Member
3,180 posts

Joined: Jun 2009
From: Borlänge


QUOTE(waterjunk @ Aug 13 2018, 08:28 PM)
Well the truth about surge protection is electrical surges are kinda unpredictable in terms of amplitude (peak to peak volt) or duration (surge time) so designing a perfect surge arrestor is close to impossible. Even industrial surge protector guys such as Emerson etc usually do not offer any sort of guarantee.

In fact some manufacturers put multiple MOVs across the same system in hopes that one of them 'catches' the strike. Theoretically installing a MOV at the 'entrance' is a good industry practice but there is no concrete proof that installing elsewhere along the PCC (Point of common coupling) affects the efficiency of the surge arrestor system.

If you have an expensive equipment, investing in a proper surge arrestor instead of Mr DIY is highly recommended  biggrin.gif
*
you can say its electrical energy in Joule. its one of the specs.
SUSendau02
post Aug 13 2018, 08:35 PM

Look at all my stars!!
*******
Senior Member
3,180 posts

Joined: Jun 2009
From: Borlänge


QUOTE(lawrencesha @ Aug 13 2018, 08:24 PM)
Anyway, when 1000V comes along, do you think that small MOV will help?

Industrial surge protection cost thousands of dollars. And most of all, they have good grounding (which also cost thousands to achieve).
*
it can many-many volts.

it depends on how much electrical energy absorbed in Joule
SUSendau02
post Aug 13 2018, 08:36 PM

Look at all my stars!!
*******
Senior Member
3,180 posts

Joined: Jun 2009
From: Borlänge


QUOTE(lawrencesha @ Aug 13 2018, 08:03 PM)
Uncle must have failed electronics in college. The MOV is placed in the COMMON ground and neutral point - which is exactly the same as what you mentioned in the later post.
*
it will work

but not a good design
WaCKy-Angel
post Aug 13 2018, 08:37 PM

PeACe~~
*********
All Stars
21,961 posts

Joined: Dec 2004
From: KL



lel these cheapo thing got surge protector? jew so gullible to believe them?
ar188
post Aug 13 2018, 08:38 PM

Look at all my stars!!
*******
Senior Member
9,206 posts

Joined: Jun 2006
QUOTE(fireballs @ Aug 13 2018, 08:20 PM)
Even the protection voltage also wrong.
Should be 275
*
betul la use 471
SUSendau02
post Aug 13 2018, 08:39 PM

Look at all my stars!!
*******
Senior Member
3,180 posts

Joined: Jun 2009
From: Borlänge


QUOTE(WaCKy-Angel @ Aug 13 2018, 08:37 PM)
lel these cheapo thing got surge protector? jew so gullible to believe them?
*
if that MOV is not imitation, it can offer surge protection across Live n Neutral as per spec.
ozak
post Aug 13 2018, 08:39 PM

10k Club
********
All Stars
17,013 posts

Joined: Jan 2005


QUOTE(JohnLai @ Aug 13 2018, 07:56 PM)
Yes, I know about those three lines protection.

In MR DIY powerstrip, if there is power surge and all four switches are turned on, only Green socket will be protected from surge while the Blue, Orange and Red sockets will be hit by surge.

In this case, the MOV should be installed as shown below in red line (Point of entry):
user posted image
This way, all four sockets will be protected from surge coming from Live wire by redirecting surge to Neutral wire out.
I have no idea why the MOV is installed that way protecting only one socket sweat.gif  and still pass SIRIM.
*
There is nothing wrong with the varistor placing. It did connect to live common and neutral common.

If you said it just protect the green, than the varistor should connect to the copper plate after the green switch.
Revamperz
post Aug 13 2018, 08:39 PM

im freaking IN! ™
*******
Senior Member
5,163 posts

Joined: Jan 2003


so i bought expensif belkin wan for over hundred rm ok o not?


Drian
post Aug 13 2018, 08:41 PM

Look at all my stars!!
*******
Senior Member
4,999 posts

Joined: Jan 2003


QUOTE(JohnLai @ Aug 13 2018, 07:56 PM)
Yes, I know about those three lines protection.

In MR DIY powerstrip, if there is power surge and all four switches are turned on, only Green socket will be protected from surge while the Blue, Orange and Red sockets will be hit by surge.

In this case, the MOV should be installed as shown below in red line (Point of entry):
user posted image
This way, all four sockets will be protected from surge coming from Live wire by redirecting surge to Neutral wire out.
I have no idea why the MOV is installed that way protecting only one socket sweat.gif  and still pass SIRIM.
*
It’s the same, they are all connected at the same line.
I doubt the parasitic inductance has any effect on it.

This post has been edited by Drian: Aug 13 2018, 08:42 PM
TSJohnLai
post Aug 13 2018, 08:43 PM

Skeptical Cat
*******
Senior Member
3,669 posts

Joined: Apr 2006
QUOTE(waterjunk @ Aug 13 2018, 08:28 PM)
Well the truth about surge protection is electrical surges are kinda unpredictable in terms of amplitude (peak to peak volt) or duration (surge time) so designing a perfect surge arrestor is close to impossible. Even industrial surge protector guys such as Emerson etc usually do not offer any sort of guarantee.

In fact some manufacturers put multiple MOVs across the same system in hopes that one of them 'catches' the strike. Theoretically installing a MOV at the 'entrance' is a good industry practice but there is no concrete proof that installing elsewhere along the PCC (Point of common coupling) affects the efficiency of the surge arrestor system.

If you have an expensive equipment, investing in a proper surge arrestor instead of Mr DIY is highly recommended  biggrin.gif
*
sad.gif I just read what those manufacturers product training brochure mentioned about MOV placement......it recommends the MOV to be installed at 'entrance' of power input.

Wouldn't installing MOV at 'entrance' mean that location is path of least resistance once the varistor start to conduct after encountering a surge?

user posted image


QUOTE(endau02 @ Aug 13 2018, 08:30 PM)
pls dont tell me u r an electrical engineer
*
I am not. laugh.gif


But seriously, I am not planning to use it for 1000v or lightning strike protection, just day to day small surge from high powered motors/heaters (Neighbours car cleaning/washing business) sweat.gif
waterjunk
post Aug 13 2018, 08:43 PM

New Member
*
Newbie
0 posts

Joined: Oct 2005



Mr DIY surge arrestor also can spark discussion LOL

SUSendau02
post Aug 13 2018, 08:43 PM

Look at all my stars!!
*******
Senior Member
3,180 posts

Joined: Jun 2009
From: Borlänge


QUOTE(ar188 @ Aug 13 2018, 08:38 PM)
betul la use 471
*
u wrote 275... the 275 is part number or volt?
ar188
post Aug 13 2018, 08:45 PM

Look at all my stars!!
*******
Senior Member
9,206 posts

Joined: Jun 2006
QUOTE(endau02 @ Aug 13 2018, 08:43 PM)
u wrote 275... the 275 is part number or volt?
*
where did i write? hmm.gif

in anycase if got one behind the part number, usually is multiplier la.
slaveone
post Aug 13 2018, 08:46 PM

Regular
******
Senior Member
1,229 posts

Joined: Jan 2003
QUOTE(mazannor81 @ Aug 13 2018, 07:59 PM)
wanna beter protection, better buy Cal Lab
*
still selling aaa..? last time bought one from them way back then. seller like cheebai but product is good
kurangak
post Aug 13 2018, 08:46 PM

certified /k addict
******
Senior Member
1,170 posts

Joined: Apr 2011
From: Deus Vult



wow.. i learned something new and useful in /k

what a rarity
slaveone
post Aug 13 2018, 08:46 PM

Regular
******
Senior Member
1,229 posts

Joined: Jan 2003
QUOTE(waterjunk @ Aug 13 2018, 08:43 PM)
Mr DIY surge arrestor also can spark discussion LOL
*
it's a crappy dump site for china products. some are ok but a lot of crap sold there
SUSendau02
post Aug 13 2018, 08:46 PM

Look at all my stars!!
*******
Senior Member
3,180 posts

Joined: Jun 2009
From: Borlänge


QUOTE(endau02 @ Aug 13 2018, 08:43 PM)
u wrote 275... the 275 is part number or volt?
*
OK

i saw the data sheet. it can be used.

the question here is can 275V damage ur load? if can, then hv to go 275V

sorry
QUOTE(ar188 @ Aug 13 2018, 08:45 PM)
where did i write? hmm.gif

in anycase if got one behind the part number, usually is multiplier la.
*
u did wrote 275 lol

This post has been edited by endau02: Aug 13 2018, 08:47 PM
KcX35
post Aug 13 2018, 08:52 PM

ㄨㄨ
*******
Senior Member
2,364 posts

Joined: Aug 2011
From: Between Heaven & Hell


want safety, want quality dont cheapskate, simple as that smile.gif
waterjunk
post Aug 13 2018, 08:52 PM

New Member
*
Newbie
0 posts

Joined: Oct 2005



QUOTE(JohnLai @ Aug 13 2018, 08:43 PM)
sad.gif  I just read what those manufacturers product training brochure mentioned about MOV placement......it recommends the MOV to be installed at 'entrance' of power input.

Wouldn't installing MOV at 'entrance' mean that location is path of least resistance once the varistor start to conduct after encountering a surge?

user posted image
I am not. laugh.gif
But seriously, I am not planning to use it for 1000v or lightning strike protection, just day to day small surge from high powered motors/heaters (Neighbours car cleaning/washing business) sweat.gif
*
Using back your diagram,

user posted image

If the impedance between the 2 points are negligible, then these 2 points are at the same electrical potential. I guess manufacturers don't know this value that's why they recommend putting at the 'entrance'? And Mr DIY probably installed it at whichever cheapest location
ar188
post Aug 13 2018, 08:54 PM

Look at all my stars!!
*******
Senior Member
9,206 posts

Joined: Jun 2006
QUOTE(endau02 @ Aug 13 2018, 08:46 PM)
OK

i saw the data sheet. it can be used.

the question here is can 275V damage ur load? if can, then hv to go 275V

sorry

u did wrote 275 lol
*
u got eye sight problem?

come i screen cap for you who wrote 275

Attached Image
nonnon
post Aug 13 2018, 08:57 PM

Getting Started
**
Junior Member
86 posts

Joined: Jul 2006
Must read fine print. How many sockets are protected.
TSJohnLai
post Aug 13 2018, 08:59 PM

Skeptical Cat
*******
Senior Member
3,669 posts

Joined: Apr 2006
QUOTE(waterjunk @ Aug 13 2018, 08:52 PM)
If the impedance between the 2 points are negligible, then these 2 points are at the same electrical potential. I guess manufacturers don't know this value that's why they recommend putting at the 'entrance'? And Mr DIY probably installed it at whichever cheapest location
*
Hmm, make sense. hmm.gif

So, sifu notworthy.gif ....Is it fine if I move current MOV location to entrance just to be safe? Or I just leave it as it is?
Since I don't even know the impedance between those two points and MR DIY probably installed it randomly.
SUSendau02
post Aug 13 2018, 09:00 PM

Look at all my stars!!
*******
Senior Member
3,180 posts

Joined: Jun 2009
From: Borlänge


QUOTE(ar188 @ Aug 13 2018, 08:54 PM)
u got eye sight problem?

come i screen cap for you who wrote 275

Attached Image
*
ok sorry

*okay.jpg*
ar188
post Aug 13 2018, 09:03 PM

Look at all my stars!!
*******
Senior Member
9,206 posts

Joined: Jun 2006
QUOTE(endau02 @ Aug 13 2018, 09:00 PM)
ok sorry

*okay.jpg*
*
sweat.gif alrite its all good.
waterjunk
post Aug 13 2018, 09:04 PM

New Member
*
Newbie
0 posts

Joined: Oct 2005



QUOTE(JohnLai @ Aug 13 2018, 08:59 PM)
Hmm, make sense. hmm.gif

So, sifu notworthy.gif  ....Is it fine if I move current MOV location to entrance just to be safe? Or I just leave it as it is?
Since I don't even know the impedance between those two points and MR DIY probably installed it randomly.
*
I not sifu la lol. If you paranoid then make a trip to Jln Pasar, buy another MOV with same part number and stick it to the entrance also can.

What makes u consider surge arrestors at the first place? If your lights dim while your neighbours wash their car it's better to check grounding instead icon_rolleyes.gif
TSJohnLai
post Aug 13 2018, 09:21 PM

Skeptical Cat
*******
Senior Member
3,669 posts

Joined: Apr 2006
QUOTE(waterjunk @ Aug 13 2018, 09:04 PM)
I not sifu la lol. If you paranoid then make a trip to Jln Pasar, buy another MOV with same part number and stick it to the entrance also can.

What makes u consider surge arrestors at the first place? If your lights dim while your neighbours wash their car it's better to check grounding instead  icon_rolleyes.gif
*
Aside from dimming, the light also become brighter suddenly for few seconds.

I can feel my table fan rotation suddenly speeds up a lot before returning to normal speed after my neighbours shut down their equipments.
sweat.gif
SUSendau02
post Aug 13 2018, 09:26 PM

Look at all my stars!!
*******
Senior Member
3,180 posts

Joined: Jun 2009
From: Borlänge


QUOTE(waterjunk @ Aug 13 2018, 09:04 PM)
I not sifu la lol. If you paranoid then make a trip to Jln Pasar, buy another MOV with same part number and stick it to the entrance also can.

What makes u consider surge arrestors at the first place? If your lights dim while your neighbours wash their car it's better to check grounding instead  icon_rolleyes.gif
*
stick
LN
LE
NE
TSJohnLai
post Aug 13 2018, 09:33 PM

Skeptical Cat
*******
Senior Member
3,669 posts

Joined: Apr 2006
QUOTE(endau02 @ Aug 13 2018, 09:26 PM)
stick
LN
LE
NE
*
Planning to do so.
It appears electrical shop nearby my housing area got sell this kind of stuff. Hope there are higher joule rating available for sale.
howszat
post Aug 13 2018, 09:35 PM

Look at all my stars!!
*******
Senior Member
2,932 posts

Joined: Sep 2007
QUOTE(waterjunk @ Aug 13 2018, 07:46 PM)
The MOV is being installed across Line and Neutral which is correct. Since this is a single phase socket array, all the 3 (Line Neutral and Ground) are shorted together via the copper busbar. Therefore the potential differences between the sockets should be negligible.

More expensive surge arrestors will have MOV across line-line, line-neutral, neutral-ground and line-ground. Obviously this Mr DIY is just a extra precaution instead of full protection~ better than nothing i suppose haha
*

This.

shirohamada
post Aug 13 2018, 09:40 PM

Enthusiast
*****
Senior Member
944 posts

Joined: Jan 2007
don't buy one of those flashlights that charge via plugging straight into the wall.
fire and shock hazard.
Satori 14118a
post Aug 13 2018, 09:41 PM

Regular
******
Senior Member
1,003 posts

Joined: Sep 2014


QUOTE(waterjunk @ Aug 13 2018, 09:04 PM)
I not sifu la lol. If you paranoid then make a trip to Jln Pasar, buy another MOV with same part number and stick it to the entrance also can.

What makes u consider surge arrestors at the first place? If your lights dim while your neighbours wash their car it's better to check grounding instead  icon_rolleyes.gif
*
Add "pls don't electrocute yourself in the process" disclaimer here.
SliparJepun
post Aug 13 2018, 09:44 PM

Getting Started
**
Junior Member
109 posts

Joined: Jun 2013
QUOTE(kamfoo @ Aug 13 2018, 07:45 PM)
wat is mov
*
Ministry of Virgin
Metal Oxide Varistor

Mr DIY shop tumbuh mcm cendawan.
In my area got 2-3. I never visit one.
Selling mediocre quality stuff?
mabaw
post Aug 13 2018, 09:48 PM

Getting Started
**
Junior Member
223 posts

Joined: Oct 2009
QUOTE(SliparJepun @ Aug 13 2018, 09:44 PM)
Ministry of Virgin
Metal Oxide Varistor

Mr DIY shop tumbuh mcm cendawan.
In my area got 2-3. I never visit one.
Selling mediocre quality stuff?
*
cheapo but for the price is good
dont expect big brand quality la
yeezai
post Aug 13 2018, 09:49 PM

-using no way as way-having no limitation as limitation-
*******
Senior Member
2,531 posts

Joined: Feb 2009
From: Land below the wind
Repot sirim ..i dont want my 10k laptop burn ..
zerorating
post Aug 13 2018, 10:05 PM

Miskin Adab
*****
Senior Member
970 posts

Joined: Aug 2007
From: Lokap Polis


QUOTE(yeezai @ Aug 13 2018, 09:49 PM)
Repot sirim ..i dont want my 10k laptop burn ..
*
if you own a 10k laptop, you should use cal-lab product + industrial grade AVR and original charger.

fireballs
post Aug 13 2018, 11:10 PM

10101
*******
Senior Member
5,646 posts

Joined: Mar 2012
in malaysia, our official voltage is
230V single phase, variation -6% +10%
meaning from 216 to 253

most appliance can withstand +/- 10% of 230, meaning 207 to 253

thus the need of mov at 275V

if you use a 400V mov... slightly higher voltage (non lightning) will burn your everything connected. equivalent to dont install.

btw, you must have a fuse to disconnect the MOV once it got hit by lightning. else will bbq your house.
joe_mamak
post Aug 14 2018, 12:31 AM

Casual
***
Junior Member
363 posts

Joined: Dec 2006


Trust me, I am an engineer. biggrin.gif

It should be ok.

Then again, I have been wrong before. laugh.gif
Baby1985
post Aug 14 2018, 12:46 AM

Getting Started
**
Junior Member
142 posts

Joined: May 2006
/k really have lots of expertise.. hmmmm... 😄
cikalakacikaci
post Aug 14 2018, 12:58 AM

Getting Started
**
Junior Member
107 posts

Joined: Jun 2013
From: kl.klang.



ayam guna belkin power surge only mia still strong after 7years
diy kaput

This post has been edited by cikalakacikaci: Aug 14 2018, 12:58 AM
simonblowais
post Aug 14 2018, 03:43 AM

New Member
*
Junior Member
25 posts

Joined: May 2009


QUOTE(joe_mamak @ Aug 14 2018, 12:31 AM)
Trust me, I am an engineer.  biggrin.gif 

It should be ok.

Then again, I have been wrong before.  laugh.gif
*
How many victims in yoUr wrong?
Doraku
post Aug 14 2018, 03:47 AM

Old threads digger
******
Senior Member
1,155 posts

Joined: Apr 2016


QUOTE(kamfoo @ Aug 13 2018, 07:45 PM)
wat is mov
*
Metal Oxide Varistor whistling.gif
joe_mamak
post Aug 14 2018, 03:56 AM

Casual
***
Junior Member
363 posts

Joined: Dec 2006


QUOTE(simonblowais @ Aug 14 2018, 03:43 AM)
How many victims in yoUr wrong?
*
No one died yet, to the best of my knowledge. biggrin.gif
kucingrimau
post Aug 14 2018, 06:08 AM

Getting Started
**
Junior Member
197 posts

Joined: Sep 2015


Sirim sticker is not guarantee a product (as a whole) is safe for use. For example, 3-core extension wire, roll type. The sticker is on the 3-pin plug receptacle and it is for certify the receptacle only. The body, wire and other components are not covered by the sticker. But when people buy it they thought the whole thing is certified safe.
fantasy1989
post Aug 14 2018, 07:46 AM

Look at all my stars!!
*******
Senior Member
4,705 posts

Joined: May 2008



QUOTE(waterjunk @ Aug 13 2018, 08:43 PM)
Mr DIY surge arrestor also can spark discussion LOL
*
but good discussion icon_rolleyes.gif
latipbogiba
post Aug 14 2018, 07:49 AM

Getting Started
**
Junior Member
102 posts

Joined: Dec 2015
From: kolumpo


Haha why buy mr diy surge protector? Go get belkin ke something like that.
fantasy1989
post Aug 14 2018, 07:50 AM

Look at all my stars!!
*******
Senior Member
4,705 posts

Joined: May 2008



still using this for 7 years for my pc with high load usage

the rest use cheapo socket

user posted image
hotjake
post Aug 14 2018, 07:50 AM

Getting Started
**
Junior Member
194 posts

Joined: Nov 2010
QUOTE(JohnLai @ Aug 13 2018, 07:38 PM)
Recently, uncle bought one cheap surge protector powerstrip from MR DIY store at RM24 something? dry.gif

But, to uncle dismay, the MOV is installed at wrong place. As the result, only one socket is protected from possible surge while the other three are not.

Some pictures below (large image):

» Click to show Spoiler - click again to hide... «


Searching around the net for the MOV model returned:
user posted image
https://www.sunrom.com/p/10d471k-varistor-mov-for-220v-ac
Data from https://www.sunrom.com/get/559199 seem to indicate:
user posted image
Aside from the wrong MOV placement in the powerstrip, the MOV itself is fine for its intended purpose.
How in the world this thing qualify as surge protector when it only protect one socket out of four sockets? sweat.gif

SIRIM tengah tidur ke? dry.gif
*
Thanks for info, uncle

jagged
post Aug 14 2018, 07:52 AM

Enthusiast
*****
Senior Member
757 posts

Joined: May 2005


Park dulu, masuk opis baru study...
SUSMarioKart
post Aug 14 2018, 07:54 AM

New Member
*
Newbie
22 posts

Joined: Dec 2017


QUOTE(urnicksux2 @ Aug 13 2018, 07:45 PM)
wow got sirim sticker
*
You oay money they stick lah. Just like halal logo.

Anyway, i cannot brain why people buy cheap eletrical product from Mr Diy and actually expect high quality protection?

This post has been edited by MarioKart: Aug 14 2018, 09:01 AM
arturo_bandini
post Aug 14 2018, 07:59 AM

Getting Started
**
Junior Member
136 posts

Joined: Aug 2005


QUOTE(JohnLai @ Aug 13 2018, 07:38 PM)
Recently, uncle bought one cheap surge protector powerstrip from MR DIY store at RM24 something? dry.gif

But, to uncle dismay, the MOV is installed at wrong place. As the result, only one socket is protected from possible surge while the other three are not.

Some pictures below (large image):

» Click to show Spoiler - click again to hide... «


Searching around the net for the MOV model returned:
user posted image
https://www.sunrom.com/p/10d471k-varistor-mov-for-220v-ac
Data from https://www.sunrom.com/get/559199 seem to indicate:
user posted image
Aside from the wrong MOV placement in the powerstrip, the MOV itself is fine for its intended purpose.
How in the world this thing qualify as surge protector when it only protect one socket out of four sockets? sweat.gif

SIRIM tengah tidur ke? dry.gif
*
lol uncle, look carefully la. you can say that it only protects green socket if one of the terminals is placed at the metal part below the green switch. at current state, the MOV terminals are between incoming live and neutral, exactly as they should be.
miromiro
post Aug 14 2018, 08:02 AM

On my way
****
Junior Member
560 posts

Joined: Mar 2008


Some diy stuff are not worth to buy...
calvin2003
post Aug 14 2018, 08:10 AM

New Member
*
Junior Member
7 posts

Joined: Mar 2010
It's from Mr DIY. So, if you think it is placed wrong, DIY it.
IamNOT
post Aug 14 2018, 08:10 AM

Getting Started
**
Junior Member
283 posts

Joined: Aug 2008
From: Malacca


QUOTE(lawrencesha @ Aug 13 2018, 08:03 PM)
Uncle must have failed electronics in college. The MOV is placed in the COMMON ground and neutral point - which is exactly the same as what you mentioned in the later post.
*
Anyway the thinny-tiny MOV wont help with a real surge...

This post has been edited by IamNOT: Aug 14 2018, 08:14 AM
Zot
post Aug 14 2018, 08:15 AM

Look at all my stars!!
*******
Senior Member
7,934 posts

Joined: Mar 2014
Nothing 's wrong for SIRIM to approve this product. It meets the spec on what it is intended for.

Varistor is small power and protect the basic L and N line. Probably cost no more than RM5. So, I consider the power strip is not worth that RM24
ciwi1166
post Aug 14 2018, 08:25 AM

~~~Prestissimo~~~
*******
Senior Member
2,263 posts

Joined: Dec 2006
From: In your head...
stuff is cheap china mari.. what you expect?
Skylinestar
post Aug 14 2018, 08:25 AM

Mega Duck
********
All Stars
10,467 posts

Joined: Jan 2003
From: Sarawak
Not a big fond of this surge regulator stuff on almost every damn power strips in the market. I connect power amp for audio on power strip. Depending on audio, current draw can go extremely high in a short time.
calvin2003
post Aug 14 2018, 08:26 AM

New Member
*
Junior Member
7 posts

Joined: Mar 2010
Speaking of SIRIM, the real certified Surge Protector/Extension cords get a sticker on the plug and on the extension body?
christ14
post Aug 14 2018, 08:36 AM

Regular
******
Senior Member
1,567 posts

Joined: Jul 2011
From: Grand Ol' Lady


if u xsuka, then buka tered and diy yoself the mov
bereev
post Aug 14 2018, 08:38 AM

Getting Started
**
Junior Member
257 posts

Joined: Dec 2011
QUOTE(JohnLai @ Aug 13 2018, 07:38 PM)
Recently, uncle bought one cheap surge protector powerstrip from MR DIY store at RM24 something? dry.gif

But, to uncle dismay, the MOV is installed at wrong place. As the result, only one socket is protected from possible surge while the other three are not.

Some pictures below (large image):

» Click to show Spoiler - click again to hide... «


Searching around the net for the MOV model returned:
user posted image
https://www.sunrom.com/p/10d471k-varistor-mov-for-220v-ac
Data from https://www.sunrom.com/get/559199 seem to indicate:
user posted image
Aside from the wrong MOV placement in the powerstrip, the MOV itself is fine for its intended purpose.
How in the world this thing qualify as surge protector when it only protect one socket out of four sockets? sweat.gif

SIRIM tengah tidur ke? dry.gif
*
doh.gif
it connected to the main line so entire socket is protected la , if u say the MOV connect after the switch yes it is only protect one socket
doh.gif doh.gif doh.gif

This post has been edited by bereev: Aug 14 2018, 08:39 AM
TheEvilMan
post Aug 14 2018, 08:43 AM

囧囧囧囧囧囧囧囧囧囧囧囧
****
Senior Member
674 posts

Joined: Nov 2011



sirim kata ok jer
bereev
post Aug 14 2018, 08:45 AM

Getting Started
**
Junior Member
257 posts

Joined: Dec 2011
QUOTE(JohnLai @ Aug 13 2018, 07:56 PM)
Yes, I know about those three lines protection.

In MR DIY powerstrip, if there is power surge and all four switches are turned on, only Green socket will be protected from surge while the Blue, Orange and Red sockets will be hit by surge.

In this case, the MOV should be installed as shown below in red line (Point of entry):
user posted image
This way, all four sockets will be protected from surge coming from Live wire by redirecting surge to Neutral wire out.
I have no idea why the MOV is installed that way protecting only one socket sweat.gif  and still pass SIRIM.
*
stop making accusation if i am the socket manufacturer i can send LOD to u, the 3 line straight connect to all socket the MOV put every where also same effect if it is connected after the switch then this MOV are only protect the particular socket , but this photo clearly show the MOV connected to the main line before the switch.

u try plug in and power on but dun switch on any of the socket use test pen to test the place of MOV connect it is live , means the MOV are protect the whole gang of socket. It is just place at the end of the main line

This post has been edited by bereev: Aug 14 2018, 08:46 AM
Stigonboard
post Aug 14 2018, 09:03 AM

Casual
***
Junior Member
335 posts

Joined: Aug 2014
Prepare to get sued by Mr DIY lol
iGamer
post Aug 14 2018, 09:08 AM

Toxic ktards probably losers irl
******
Senior Member
1,374 posts

Joined: Feb 2016
From: Milky Way
QUOTE(JohnLai @ Aug 13 2018, 09:21 PM)
Aside from dimming, the light also become brighter suddenly for few seconds.

I can feel my table fan rotation suddenly speeds up a lot before returning to normal speed after my neighbours shut down their equipments.
sweat.gif
*
Cannot complain to TNB and let them tackle this?
Drian
post Aug 14 2018, 09:22 AM

Look at all my stars!!
*******
Senior Member
4,999 posts

Joined: Jan 2003


QUOTE(Zot @ Aug 14 2018, 08:15 AM)
Nothing 's wrong for SIRIM to approve this product. It meets the spec on what it is intended for.

Varistor is small power and protect the basic L and N line. Probably cost no more than RM5. So, I consider the power strip is not worth that RM24
*
Labour, plastic, packaging , shipping, design is free.


jerm57
post Aug 14 2018, 09:51 AM

Casual
***
Junior Member
405 posts

Joined: Nov 2010
From: Penis ular Bolehland


Noted. But honestly, if I wanted to protect expensive appliance, I will got a proper branded power bar lorr.. Good job on checking this out tho. Props to you.
Zot
post Aug 14 2018, 09:55 AM

Look at all my stars!!
*******
Senior Member
7,934 posts

Joined: Mar 2014
QUOTE(Drian @ Aug 14 2018, 09:22 AM)
Labour, plastic, packaging , shipping, design is free.
*
If you look around, the parts to make one is very cheap. You can buy the raw extension socket (no wire) cheap. DIY probably around RM10 excluding vaistor
joe_mamak
post Aug 14 2018, 09:57 AM

Casual
***
Junior Member
363 posts

Joined: Dec 2006


QUOTE(Peiyantiu @ Aug 14 2018, 09:40 AM)
Who are the ones with B. Eng (E&E) here?
*
wave.gif
thunderbird
post Aug 14 2018, 09:58 AM

SO what?
******
Senior Member
1,811 posts

Joined: Jan 2003
From: KL



QUOTE(urnicksux2 @ Aug 13 2018, 07:45 PM)
wow got sirim sticker
*
so? what if i tell you is fairly easy to get sirim sticker, and in most cases you just need to submit some brochures and tech specs
thunderbird
post Aug 14 2018, 09:59 AM

SO what?
******
Senior Member
1,811 posts

Joined: Jan 2003
From: KL



QUOTE(bazarayamy @ Aug 14 2018, 09:31 AM)
how can pass sirim
*
why cant? you think sirim is NASA ?
Zot
post Aug 14 2018, 09:59 AM

Look at all my stars!!
*******
Senior Member
7,934 posts

Joined: Mar 2014
QUOTE(joe_mamak @ Aug 14 2018, 09:57 AM)
wave.gif
*
knock.gif
shinkawa
post Aug 14 2018, 10:03 AM

parttime otaku
*****
Senior Member
855 posts

Joined: Jun 2008
Biasalah, government hire those people who cant get job elsewhere.
or they bully new joiner buat kerja


reversependulum
post Aug 14 2018, 10:05 AM

New Member
*
Junior Member
27 posts

Joined: Jul 2016

QUOTE(JohnLai @ Aug 13 2018, 07:56 PM)
Yes, I know about those three lines protection.

In MR DIY powerstrip, if there is power surge and all four switches are turned on, only Green socket will be protected from surge while the Blue, Orange and Red sockets will be hit by surge.

In this case, the MOV should be installed as shown below in red line (Point of entry):
user posted image
This way, all four sockets will be protected from surge coming from Live wire by redirecting surge to Neutral wire out.
I have no idea why the MOV is installed that way protecting only one socket sweat.gif  and still pass SIRIM.
*
For components parallel with each other, theoretically install at the front or end the effect still the same.

But I doubt a SPD with rated power 0.4 W can protect you at all.
ar188
post Aug 14 2018, 10:06 AM

Look at all my stars!!
*******
Senior Member
9,206 posts

Joined: Jun 2006
QUOTE(Peiyantiu @ Aug 14 2018, 09:40 AM)
Who are the ones with B. Eng (E&E) here?
*
only work with those engineers on daily basis to spec components. biggrin.gif
0168257061
post Aug 14 2018, 10:06 AM

EimiFukada
********
All Stars
14,242 posts

Joined: Jul 2007
From: JAVABUS


RM 20 cheap plug stuff.
I see also avoid it.

You see Belkin why costs RM 100+ ?
That is the reason.


lulz
post Aug 14 2018, 10:07 AM

New Member
*
Junior Member
25 posts

Joined: Jul 2008


I think this one is false advertisement, since it does have surge protection but never mention on 1 socket only.
ar188
post Aug 14 2018, 10:07 AM

Look at all my stars!!
*******
Senior Member
9,206 posts

Joined: Jun 2006
QUOTE(reversependulum @ Aug 14 2018, 10:05 AM)
For components parallel with each other, theoretically install at the front or end the effect still the same.

But I doubt a SPD with rated power 0.4 W can protect you at all.
*
i think ts feels the physical location is priority! biggrin.gif between the entry of the strip and the last socket position, you know how much resistance drop or not? laugh.gif
SUSbig[1]
post Aug 14 2018, 10:09 AM

On my way
****
Senior Member
632 posts

Joined: Jun 2015
QUOTE(urnicksux2 @ Aug 13 2018, 07:45 PM)
wow got sirim sticker
*
0168257061
post Aug 14 2018, 10:10 AM

EimiFukada
********
All Stars
14,242 posts

Joined: Jul 2007
From: JAVABUS


QUOTE(fantasy1989 @ Aug 14 2018, 07:50 AM)
still using this for 7 years for my pc with high load usage

the rest use cheapo socket

user posted image
*
High load for half year whistling.gif

[attachmentid=9970907]

[attachmentid=9970906]

bereev
post Aug 14 2018, 10:10 AM

Getting Started
**
Junior Member
257 posts

Joined: Dec 2011
QUOTE(bazarayamy @ Aug 14 2018, 09:31 AM)
how can pass sirim
*
dun see every thing got sirim sticker means it is true , u need to see what is the sirim certify , if just only the plug socket of cause it pass sirim test,

but is the test include the surge arresting test ? brows.gif


Jasonist
post Aug 14 2018, 10:11 AM

Oldfag
******
Senior Member
1,176 posts

Joined: May 2006
From: Memesia



pay peanut get monkeys?
joe_mamak
post Aug 14 2018, 10:12 AM

Casual
***
Junior Member
363 posts

Joined: Dec 2006


TS should edit the subject title. His claim is wrong.
bereev
post Aug 14 2018, 10:12 AM

Getting Started
**
Junior Member
257 posts

Joined: Dec 2011
QUOTE(joe_mamak @ Aug 14 2018, 09:57 AM)
wave.gif
*
what is ur comment on this
joe_mamak
post Aug 14 2018, 10:13 AM

Casual
***
Junior Member
363 posts

Joined: Dec 2006


QUOTE(bereev @ Aug 14 2018, 10:12 AM)
what is ur comment on this
*
All four sockets are protected.
bereev
post Aug 14 2018, 10:15 AM

Getting Started
**
Junior Member
257 posts

Joined: Dec 2011
QUOTE(joe_mamak @ Aug 14 2018, 10:13 AM)
All four sockets are protected.
*
yes , we dun say about the efficinacy of the protection fisrt , but
it is all protected
TS can prepare lawyer
lol

This post has been edited by bereev: Aug 14 2018, 10:15 AM
ozak
post Aug 14 2018, 10:17 AM

10k Club
********
All Stars
17,013 posts

Joined: Jan 2005


QUOTE(0168257061 @ Aug 14 2018, 10:10 AM)
High load for half year  whistling.gif

[attachmentid=9970907]

[attachmentid=9970906]
*
How high is the load ?


feekle
post Aug 14 2018, 10:20 AM

Bibo ergo sum!
******
Senior Member
1,922 posts

Joined: Apr 2009
From: Constellation Cygnus
just buy socket type RCD for better peace of mind
barcabodo
post Aug 14 2018, 10:22 AM

Getting Started
**
Junior Member
129 posts

Joined: Feb 2012
From: Pipipidi City


ts can show the picture how it suppose to looks like?
didn't know how to read the diagram
my spm physics dulu only got 6c je
feekle
post Aug 14 2018, 10:24 AM

Bibo ergo sum!
******
Senior Member
1,922 posts

Joined: Apr 2009
From: Constellation Cygnus
QUOTE(lawrencesha @ Aug 13 2018, 08:24 PM)
Anyway, when 1000V comes along, do you think that small MOV will help?

Industrial surge protection cost thousands of dollars. And most of all, they have good grounding (which also cost thousands to achieve).
*
lol before that 1000V can reach, the main breaker already trip.
fantasy1989
post Aug 14 2018, 10:31 AM

Look at all my stars!!
*******
Senior Member
4,705 posts

Joined: May 2008



QUOTE(0168257061 @ Aug 14 2018, 10:10 AM)
High load for half year  whistling.gif

[attachmentid=9970907]

[attachmentid=9970906]
*
indeed highly loaded rclxms.gif
0168257061
post Aug 14 2018, 10:48 AM

EimiFukada
********
All Stars
14,242 posts

Joined: Jul 2007
From: JAVABUS


QUOTE(ozak @ Aug 14 2018, 10:17 AM)
How high is the load ?
*
Bake cake


Drian
post Aug 14 2018, 10:52 AM

Look at all my stars!!
*******
Senior Member
4,999 posts

Joined: Jan 2003


QUOTE(Zot @ Aug 14 2018, 09:55 AM)
If you look around, the parts to make one is very cheap. You can buy the raw extension socket (no wire) cheap. DIY probably around RM10 excluding vaistor
*
So you are making your own labour free and then claim that other people are doing it expensive?
glorykeeper
post Aug 14 2018, 10:55 AM

Getting Started
**
Junior Member
119 posts

Joined: Feb 2013
if someone die, sirim are to be blame? shop to be blame?
alanyuppie
post Aug 14 2018, 10:57 AM

Look at all my stars!!
*******
Senior Member
2,833 posts

Joined: Jul 2006
From: here


dear TS. You know what DIY means right?

move along now.

amir.asyraf
post Aug 14 2018, 11:26 AM

On my way
****
Junior Member
504 posts

Joined: Oct 2012
From: It's all relative


Someone should make a Youtube channel reviewing electric products found in Malaysia
ZeneticX
post Aug 14 2018, 11:29 AM

stars for what
********
All Stars
12,410 posts

Joined: Jan 2008
From: KL - Cardiff - Subang - Sydney



i rather buy branded from lazada/11street/shopee than buy those unbranded surge protectors from mr diy
RallyNight
post Aug 14 2018, 11:32 AM

Regular
******
Senior Member
1,119 posts

Joined: Nov 2015
QUOTE(JohnLai @ Aug 13 2018, 07:56 PM)
Yes, I know about those three lines protection.

In MR DIY powerstrip, if there is power surge and all four switches are turned on, only Green socket will be protected from surge while the Blue, Orange and Red sockets will be hit by surge.

In this case, the MOV should be installed as shown below in red line (Point of entry):
user posted image
This way, all four sockets will be protected from surge coming from Live wire by redirecting surge to Neutral wire out.
I have no idea why the MOV is installed that way protecting only one socket sweat.gif  and still pass SIRIM.
*
Maybe demo set pass so they no kesah but curi ayam in production.

I buy 1 extention cable in aeon. I just pull out the power cord already patah. If u long hours i doubt it wont melt
Zot
post Aug 14 2018, 12:57 PM

Look at all my stars!!
*******
Senior Member
7,934 posts

Joined: Mar 2014
QUOTE(Drian @ Aug 14 2018, 10:52 AM)
So you are making your own labour free and then claim that other people are doing it expensive?
*
It is simple job. Labor in factory is dirt cheap. The company makes profit, not much left on operator. China labor more probably more expensive than Malaysia.
stupiak07
post Aug 14 2018, 01:04 PM

Casual
***
Junior Member
396 posts

Joined: Oct 2007
From: broken heart land, single forever~
Lol, TS is so wrong
bamkai
post Aug 14 2018, 01:07 PM

Getting Started
**
Junior Member
167 posts

Joined: Jan 2010
Park at unker engineer thread
TSJohnLai
post Aug 14 2018, 01:13 PM

Skeptical Cat
*******
Senior Member
3,669 posts

Joined: Apr 2006
QUOTE(stupiak07 @ Aug 14 2018, 01:04 PM)
Lol, TS is so wrong
*
I know I wrong lah..... sweat.gif

Didn't you guys read the rest of the post from first page till last page? blink.gif
COOLPINK
post Aug 14 2018, 01:31 PM

Look at all my stars!!
*******
Senior Member
3,652 posts

Joined: Oct 2010
QUOTE(JohnLai @ Aug 14 2018, 01:13 PM)
I know I wrong lah..... sweat.gif

Didn't you guys read the rest of the post from first page till last page? blink.gif
*
well maybe it is not providing the surge protection you were expecting icon_rolleyes.gif
Justin.Loong
post Aug 14 2018, 02:46 PM

Look at all my stars!!
*******
Senior Member
8,293 posts

Joined: Feb 2014


QUOTE(shirohamada @ Aug 13 2018, 09:40 PM)
don't buy one of those flashlights that charge via plugging straight into the wall.
fire and shock hazard.
*
Do you mean flashlights using the magnetic charging method?
user posted image
Or the one that's using the USB plug in method?
user posted image
I'm curious to know. hmm.gif
stupiak07
post Aug 14 2018, 02:47 PM

Casual
***
Junior Member
396 posts

Joined: Oct 2007
From: broken heart land, single forever~
QUOTE(JohnLai @ Aug 14 2018, 01:13 PM)
I know I wrong lah..... sweat.gif

Didn't you guys read the rest of the post from first page till last page? blink.gif
*
K only read 1st post and short story
psyduck89
post Aug 14 2018, 02:50 PM

New Korean Member
*****
Senior Member
818 posts

Joined: Nov 2009
From: Not Your Business
QUOTE(acbc @ Aug 13 2018, 07:45 PM)
SIRIM bayar only. No need test also pass.
*
This..

Sirim = u pay money, we give sticker.

They sell sticker only..
ocphangaz
post Aug 14 2018, 02:54 PM

Midlife Crysis.
*****
Senior Member
768 posts

Joined: Nov 2004
QUOTE(JohnLai @ Aug 13 2018, 07:38 PM)
Recently, uncle bought one cheap surge protector powerstrip from MR DIY store at RM24 something? dry.gif

But, to uncle dismay, the MOV is installed at wrong place. As the result, only one socket is protected from possible surge while the other three are not.

Some pictures below (large image):

» Click to show Spoiler - click again to hide... «


Searching around the net for the MOV model returned:
user posted image
https://www.sunrom.com/p/10d471k-varistor-mov-for-220v-ac
Data from https://www.sunrom.com/get/559199 seem to indicate:
user posted image
Aside from the wrong MOV placement in the powerstrip, the MOV itself is fine for its intended purpose.
How in the world this thing qualify as surge protector when it only protect one socket out of four sockets? sweat.gif

SIRIM tengah tidur ke? dry.gif
*
uncle... if you see properly, the MOV is connected on LIVE and NEUTRAL common bus. meaning it's feeding ALL plugs.

eventhough it's cheaply made, it's correct according to your diagram.
lyc1982
post Aug 14 2018, 02:57 PM

ExpectNoMercy
*******
Senior Member
2,329 posts

Joined: Jun 2015
QUOTE(ocphangaz @ Aug 14 2018, 02:54 PM)
uncle... if you see properly, the MOV is connected on LIVE and NEUTRAL common bus. meaning it's feeding ALL plugs.

eventhough it's cheaply made, it's correct according to your diagram.
*
ts got burnt....

the sirim sticker there is not for fun afterall
shirohamada
post Aug 14 2018, 02:59 PM

Enthusiast
*****
Senior Member
944 posts

Joined: Jan 2007
QUOTE(Justin.Loong @ Aug 14 2018, 02:46 PM)
Do you mean flashlights using the magnetic charging method?
user posted image
Or the one that's using the USB plug in method?
user posted image
I'm curious to know.  hmm.gif
*
no.
from what i saw, it has 2 pin eu plug to connect to outlet. no other connector.
so it has a built in charger.
which is probably a crappy one, probably made out of a capacitor and rectifier chip. and the torch costs ~rm15. go figure

https://www.mrdiy.com.my/catalog/product/vi...1/category/197/

correction.
it's rm8.

This post has been edited by shirohamada: Aug 14 2018, 03:04 PM
Justin.Loong
post Aug 14 2018, 04:47 PM

Look at all my stars!!
*******
Senior Member
8,293 posts

Joined: Feb 2014


QUOTE(shirohamada @ Aug 14 2018, 02:59 PM)
no.
from what i saw, it has 2 pin eu plug to connect to outlet. no other connector.
so it has a built in charger.
which is probably a crappy one, probably made out of a capacitor and rectifier chip. and the torch costs ~rm15. go figure

https://www.mrdiy.com.my/catalog/product/vi...1/category/197/

correction.
it's rm8.
*
user posted image
Ahhh...this one ya.
I also wouldn't recommend it. dry.gif sad.gif shakehead.gif
Jay Chua CC
post Aug 14 2018, 04:51 PM

~Dont settle for good. Demand great~
*******
Senior Member
5,907 posts

Joined: Dec 2012
From: Taiping,Perak


I bought the mr. Diy yellow amd black ones. Using for 3 years+ d no problem wor.
zarakiken
post Aug 14 2018, 04:55 PM

Getting Started
**
Junior Member
58 posts

Joined: Jul 2009
From: Somewhere in Nendoroidian land...
QUOTE(mazannor81 @ Aug 13 2018, 07:59 PM)
wanna beter protection, better buy Cal Lab
*
Cal Lab exp bruh... used much for telecommunication and AV components...
doppatroll
post Aug 14 2018, 05:02 PM

Regular
******
Senior Member
1,123 posts

Joined: Sep 2013
user posted image
spider955
post Aug 14 2018, 05:20 PM

New Member
*
Newbie
4 posts

Joined: Jun 2015
report to sirim, pengguna, bomba, biro mca, ppim
wailam
post Aug 14 2018, 05:24 PM

Apa benda ini?
*****
Junior Member
976 posts

Joined: Nov 2014
From: Sandakan, Sabah


Nama pun Mr. DIY. TS pun DIY sendirilah.
Apelah TS. Itu pun tak tau kah doh.gif
sou12b810
post Aug 14 2018, 05:29 PM

Getting Started
**
Junior Member
147 posts

Joined: Sep 2014
clear marked only socket 3 is protected..


hcmalaya
post Aug 14 2018, 05:33 PM

Getting Started
**
Junior Member
61 posts

Joined: Oct 2015
Install a chicken after the surge protector
In case if surge happen
U get a BBQ chicken
Ohwai~~~
lee_lnh
post Aug 14 2018, 06:56 PM

Getting Started
**
Junior Member
115 posts

Joined: Oct 2008


ntg wrong.. common busbar..
but either way.. not much protection also..
those critical equipment I juz connect to AVR (with surge protection).
most of the time damage comes from undervoltage..
mazannor81
post Aug 16 2018, 06:19 PM

Getting Started
**
Junior Member
64 posts

Joined: May 2012
QUOTE(zarakiken @ Aug 14 2018, 04:55 PM)
Cal Lab exp bruh... used much for telecommunication and AV components...
*
well, when u have 10k worth of AV and others to protect the price is insignificant. It has saved my plasma, ht, laptop a couple time already. If Cal Lab isolator burnt, you just have to pay 25 to replace 1 to 1. So, you want buy a new laptop or jz spend a couple hundred, up to you.