Even the protection voltage also wrong.
Should be 275
Don't buy MR DIY Surge Protector powerstrip, The MOV is only protecting one socket.
Don't buy MR DIY Surge Protector powerstrip, The MOV is only protecting one socket.
|
|
Aug 13 2018, 08:20 PM
Return to original view | IPv6 | Post
#1
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
5,646 posts Joined: Mar 2012 |
Even the protection voltage also wrong.
Should be 275 |
|
|
Aug 13 2018, 11:10 PM
Return to original view | Post
#2
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
5,646 posts Joined: Mar 2012 |
in malaysia, our official voltage is
230V single phase, variation -6% +10% meaning from 216 to 253 most appliance can withstand +/- 10% of 230, meaning 207 to 253 thus the need of mov at 275V if you use a 400V mov... slightly higher voltage (non lightning) will burn your everything connected. equivalent to dont install. btw, you must have a fuse to disconnect the MOV once it got hit by lightning. else will bbq your house. |