> Don't buy MR DIY Surge Protector powerstrip, The MOV is only protecting one socket.

views
     
ozak
post Aug 13 2018, 08:39 PM

10k Club
********
All Stars
17,013 posts

Joined: Jan 2005


QUOTE(JohnLai @ Aug 13 2018, 07:56 PM)
Yes, I know about those three lines protection.

In MR DIY powerstrip, if there is power surge and all four switches are turned on, only Green socket will be protected from surge while the Blue, Orange and Red sockets will be hit by surge.

In this case, the MOV should be installed as shown below in red line (Point of entry):
user posted image
This way, all four sockets will be protected from surge coming from Live wire by redirecting surge to Neutral wire out.
I have no idea why the MOV is installed that way protecting only one socket sweat.gif  and still pass SIRIM.
*
There is nothing wrong with the varistor placing. It did connect to live common and neutral common.

If you said it just protect the green, than the varistor should connect to the copper plate after the green switch.
Revamperz
post Aug 13 2018, 08:39 PM

im freaking IN! ™
*******
Senior Member
5,163 posts

Joined: Jan 2003


so i bought expensif belkin wan for over hundred rm ok o not?


Drian
post Aug 13 2018, 08:41 PM

Look at all my stars!!
*******
Senior Member
4,999 posts

Joined: Jan 2003


QUOTE(JohnLai @ Aug 13 2018, 07:56 PM)
Yes, I know about those three lines protection.

In MR DIY powerstrip, if there is power surge and all four switches are turned on, only Green socket will be protected from surge while the Blue, Orange and Red sockets will be hit by surge.

In this case, the MOV should be installed as shown below in red line (Point of entry):
user posted image
This way, all four sockets will be protected from surge coming from Live wire by redirecting surge to Neutral wire out.
I have no idea why the MOV is installed that way protecting only one socket sweat.gif  and still pass SIRIM.
*
It’s the same, they are all connected at the same line.
I doubt the parasitic inductance has any effect on it.

This post has been edited by Drian: Aug 13 2018, 08:42 PM
TSJohnLai
post Aug 13 2018, 08:43 PM

Skeptical Cat
*******
Senior Member
3,669 posts

Joined: Apr 2006
QUOTE(waterjunk @ Aug 13 2018, 08:28 PM)
Well the truth about surge protection is electrical surges are kinda unpredictable in terms of amplitude (peak to peak volt) or duration (surge time) so designing a perfect surge arrestor is close to impossible. Even industrial surge protector guys such as Emerson etc usually do not offer any sort of guarantee.

In fact some manufacturers put multiple MOVs across the same system in hopes that one of them 'catches' the strike. Theoretically installing a MOV at the 'entrance' is a good industry practice but there is no concrete proof that installing elsewhere along the PCC (Point of common coupling) affects the efficiency of the surge arrestor system.

If you have an expensive equipment, investing in a proper surge arrestor instead of Mr DIY is highly recommended  biggrin.gif
*
sad.gif I just read what those manufacturers product training brochure mentioned about MOV placement......it recommends the MOV to be installed at 'entrance' of power input.

Wouldn't installing MOV at 'entrance' mean that location is path of least resistance once the varistor start to conduct after encountering a surge?

user posted image


QUOTE(endau02 @ Aug 13 2018, 08:30 PM)
pls dont tell me u r an electrical engineer
*
I am not. laugh.gif


But seriously, I am not planning to use it for 1000v or lightning strike protection, just day to day small surge from high powered motors/heaters (Neighbours car cleaning/washing business) sweat.gif
waterjunk
post Aug 13 2018, 08:43 PM

New Member
*
Newbie
0 posts

Joined: Oct 2005



Mr DIY surge arrestor also can spark discussion LOL

SUSendau02
post Aug 13 2018, 08:43 PM

Look at all my stars!!
*******
Senior Member
3,180 posts

Joined: Jun 2009
From: Borlänge


QUOTE(ar188 @ Aug 13 2018, 08:38 PM)
betul la use 471
*
u wrote 275... the 275 is part number or volt?
ar188
post Aug 13 2018, 08:45 PM

Look at all my stars!!
*******
Senior Member
9,206 posts

Joined: Jun 2006
QUOTE(endau02 @ Aug 13 2018, 08:43 PM)
u wrote 275... the 275 is part number or volt?
*
where did i write? hmm.gif

in anycase if got one behind the part number, usually is multiplier la.
slaveone
post Aug 13 2018, 08:46 PM

Regular
******
Senior Member
1,229 posts

Joined: Jan 2003
QUOTE(mazannor81 @ Aug 13 2018, 07:59 PM)
wanna beter protection, better buy Cal Lab
*
still selling aaa..? last time bought one from them way back then. seller like cheebai but product is good
kurangak
post Aug 13 2018, 08:46 PM

certified /k addict
******
Senior Member
1,170 posts

Joined: Apr 2011
From: Deus Vult



wow.. i learned something new and useful in /k

what a rarity
slaveone
post Aug 13 2018, 08:46 PM

Regular
******
Senior Member
1,229 posts

Joined: Jan 2003
QUOTE(waterjunk @ Aug 13 2018, 08:43 PM)
Mr DIY surge arrestor also can spark discussion LOL
*
it's a crappy dump site for china products. some are ok but a lot of crap sold there
SUSendau02
post Aug 13 2018, 08:46 PM

Look at all my stars!!
*******
Senior Member
3,180 posts

Joined: Jun 2009
From: Borlänge


QUOTE(endau02 @ Aug 13 2018, 08:43 PM)
u wrote 275... the 275 is part number or volt?
*
OK

i saw the data sheet. it can be used.

the question here is can 275V damage ur load? if can, then hv to go 275V

sorry
QUOTE(ar188 @ Aug 13 2018, 08:45 PM)
where did i write? hmm.gif

in anycase if got one behind the part number, usually is multiplier la.
*
u did wrote 275 lol

This post has been edited by endau02: Aug 13 2018, 08:47 PM
KcX35
post Aug 13 2018, 08:52 PM

ㄨㄨ
*******
Senior Member
2,364 posts

Joined: Aug 2011
From: Between Heaven & Hell


want safety, want quality dont cheapskate, simple as that smile.gif
waterjunk
post Aug 13 2018, 08:52 PM

New Member
*
Newbie
0 posts

Joined: Oct 2005



QUOTE(JohnLai @ Aug 13 2018, 08:43 PM)
sad.gif  I just read what those manufacturers product training brochure mentioned about MOV placement......it recommends the MOV to be installed at 'entrance' of power input.

Wouldn't installing MOV at 'entrance' mean that location is path of least resistance once the varistor start to conduct after encountering a surge?

user posted image
I am not. laugh.gif
But seriously, I am not planning to use it for 1000v or lightning strike protection, just day to day small surge from high powered motors/heaters (Neighbours car cleaning/washing business) sweat.gif
*
Using back your diagram,

user posted image

If the impedance between the 2 points are negligible, then these 2 points are at the same electrical potential. I guess manufacturers don't know this value that's why they recommend putting at the 'entrance'? And Mr DIY probably installed it at whichever cheapest location
ar188
post Aug 13 2018, 08:54 PM

Look at all my stars!!
*******
Senior Member
9,206 posts

Joined: Jun 2006
QUOTE(endau02 @ Aug 13 2018, 08:46 PM)
OK

i saw the data sheet. it can be used.

the question here is can 275V damage ur load? if can, then hv to go 275V

sorry

u did wrote 275 lol
*
u got eye sight problem?

come i screen cap for you who wrote 275

Attached Image
nonnon
post Aug 13 2018, 08:57 PM

Getting Started
**
Junior Member
86 posts

Joined: Jul 2006
Must read fine print. How many sockets are protected.
TSJohnLai
post Aug 13 2018, 08:59 PM

Skeptical Cat
*******
Senior Member
3,669 posts

Joined: Apr 2006
QUOTE(waterjunk @ Aug 13 2018, 08:52 PM)
If the impedance between the 2 points are negligible, then these 2 points are at the same electrical potential. I guess manufacturers don't know this value that's why they recommend putting at the 'entrance'? And Mr DIY probably installed it at whichever cheapest location
*
Hmm, make sense. hmm.gif

So, sifu notworthy.gif ....Is it fine if I move current MOV location to entrance just to be safe? Or I just leave it as it is?
Since I don't even know the impedance between those two points and MR DIY probably installed it randomly.
SUSendau02
post Aug 13 2018, 09:00 PM

Look at all my stars!!
*******
Senior Member
3,180 posts

Joined: Jun 2009
From: Borlänge


QUOTE(ar188 @ Aug 13 2018, 08:54 PM)
u got eye sight problem?

come i screen cap for you who wrote 275

Attached Image
*
ok sorry

*okay.jpg*
ar188
post Aug 13 2018, 09:03 PM

Look at all my stars!!
*******
Senior Member
9,206 posts

Joined: Jun 2006
QUOTE(endau02 @ Aug 13 2018, 09:00 PM)
ok sorry

*okay.jpg*
*
sweat.gif alrite its all good.
waterjunk
post Aug 13 2018, 09:04 PM

New Member
*
Newbie
0 posts

Joined: Oct 2005



QUOTE(JohnLai @ Aug 13 2018, 08:59 PM)
Hmm, make sense. hmm.gif

So, sifu notworthy.gif  ....Is it fine if I move current MOV location to entrance just to be safe? Or I just leave it as it is?
Since I don't even know the impedance between those two points and MR DIY probably installed it randomly.
*
I not sifu la lol. If you paranoid then make a trip to Jln Pasar, buy another MOV with same part number and stick it to the entrance also can.

What makes u consider surge arrestors at the first place? If your lights dim while your neighbours wash their car it's better to check grounding instead icon_rolleyes.gif
TSJohnLai
post Aug 13 2018, 09:21 PM

Skeptical Cat
*******
Senior Member
3,669 posts

Joined: Apr 2006
QUOTE(waterjunk @ Aug 13 2018, 09:04 PM)
I not sifu la lol. If you paranoid then make a trip to Jln Pasar, buy another MOV with same part number and stick it to the entrance also can.

What makes u consider surge arrestors at the first place? If your lights dim while your neighbours wash their car it's better to check grounding instead  icon_rolleyes.gif
*
Aside from dimming, the light also become brighter suddenly for few seconds.

I can feel my table fan rotation suddenly speeds up a lot before returning to normal speed after my neighbours shut down their equipments.
sweat.gif