Wiring guide : 3 color wire (green, blue,black), Which one neutral, live and earth
|
SUSceo684
|
May 30 2021, 03:09 PM
|
|
QUOTE(jskhoo @ May 30 2021, 11:50 AM) Is it? What should be the power rating I need? Any suggestion of which Smart switch I would need for a storage water heater please? Thank you 3kw water heater need a 20A DP (double pole L+N); Else u need to wire up a contactor instead if you want to use original switch. A contactor allows a kancil to control the operation of a trailer load.
|
|
|
|
|
|
jskhoo
|
Jun 1 2021, 10:22 AM
|
New Member
|
QUOTE(ceo684 @ May 30 2021, 03:09 PM) 3kw water heater need a 20A DP (double pole L+N); Else u need to wire up a contactor instead if you want to use original switch. A contactor allows a kancil to control the operation of a trailer load. Thanks for the advice and guide.
|
|
|
|
|
|
jskhoo
|
Jun 1 2021, 08:43 PM
|
New Member
|
QUOTE(jskhoo @ May 30 2021, 11:27 AM) Hi, I am facing an issue of identifying which wire color label. I am attempting to upgrade my Storage Water Heater switch to to Sonoff tx wifi smart wall switch. There are three colors Red, Blue & Black.   Sonoff TX Switch Manual: https://sonoff.tech/wp-content/uploads/2021....2-20210305.pdfCan anyone help me match the wiring to the diagram please.  Forgot to ask, could anyone help me identify which wire is Live(IN), Live(OUT), Neutral?  Thank you
|
|
|
|
|
|
SUSceo684
|
Jun 1 2021, 08:58 PM
|
|
QUOTE(jskhoo @ Jun 1 2021, 08:43 PM) Forgot to ask, could anyone help me identify which wire is Live(IN), Live(OUT), Neutral?  Thank you Blue LINE (always ON regardless) and the black to its 3 o clock is N Red LOAD (switched ON/OFF) (based on LED). and the black to red 3 o cllck is N Confirm with test pen or multimeter because the previous installer is color blind.Never trust the colour. Bangla tarak wireman cert one. This post has been edited by ceo684: Jun 1 2021, 10:05 PM
|
|
|
|
|
|
jskhoo
|
Jun 2 2021, 08:35 PM
|
New Member
|
QUOTE(ceo684 @ Jun 1 2021, 08:58 PM) Blue LINE (always ON regardless) and the black to its 3 o clock is N Red LOAD (switched ON/OFF) (based on LED). and the black to red 3 o cllck is N Confirm with test pen or multimeter because the previous installer is color blind.Never trust the colour. Bangla tarak wireman cert one. Thanks so much for the clarification. Yeah I agree that the person who worked on it obviously didn't do a correct job on the wiring.
|
|
|
|
|
|
EvOliver
|
Jan 30 2022, 03:22 PM
|
Getting Started

|
Which one is Live line? Black or Blue? There's Black, Blue and Green here. Green should be earth.
|
|
|
|
|
|
ozak
|
Jan 30 2022, 03:29 PM
|
|
QUOTE(EvOliver @ Jan 30 2022, 03:22 PM) Which one is Live line? Black or Blue? There's Black, Blue and Green here. Green should be earth.  Usually is blue. If you want to confirm, take out the DB box cover. Check what color the wire that connect all together on the terminal. That is neutral.
|
|
|
|
|
|
IMF2025
|
Jan 30 2022, 03:55 PM
|
Getting Started

|
QUOTE(EvOliver @ Jan 30 2022, 03:22 PM) Which one is Live line? Black or Blue? There's Black, Blue and Green here. Green should be earth.  Black is usually live Blue is nuetral
|
|
|
|
|
|
EvOliver
|
Jan 30 2022, 04:00 PM
|
Getting Started

|
QUOTE(ozak @ Jan 30 2022, 03:29 PM) Usually is blue. If you want to confirm, take out the DB box cover. Check what color the wire that connect all together on the terminal. That is neutral. OK. Thanks for advice. I just tried to open up another wall socket to check. This one has yellow / black / green. So, I can assume black is common colour for neutral, and yellow is Live as it's connected to the live terminal of the socket. Black should be common colour for Neutral line then. Was confused because I always remember guideline for Brown / Blue / Green in the past which were Live / Neutral / Ground respectively. Blue was neutral. Probably colour scheme updates to accommodate 3-phase power supply network?
|
|
|
|
|
|
ozak
|
Jan 30 2022, 04:46 PM
|
|
QUOTE(EvOliver @ Jan 30 2022, 04:00 PM) OK. Thanks for advice. I just tried to open up another wall socket to check. This one has yellow / black / green. So, I can assume black is common colour for neutral, and yellow is Live as it's connected to the live terminal of the socket. Black should be common colour for Neutral line then. Was confused because I always remember guideline for Brown / Blue / Green in the past which were Live / Neutral / Ground respectively. Blue was neutral. Probably colour scheme updates to accommodate 3-phase power supply network?  Brown/ blue/green wire code is for electrical appliances. For house wiring, doesn’t follow this code. If 3phase incoming, red/blue/yellow is using and black is neutral. The only color that all what kind of code have to follow is the green for earth.
|
|
|
|
|
|
EvOliver
|
Jan 30 2022, 04:57 PM
|
Getting Started

|
QUOTE(ozak @ Jan 30 2022, 04:46 PM) Brown/ blue/green wire code is for electrical appliances. For house wiring, doesn’t follow this code. If 3phase incoming, red/blue/yellow is using and black is neutral. The only color that all what kind of code have to follow is the green for earth. Right. So in this case, can't really assume Black is usual Live. Have to really verify, either by reference connection, or by test pen, to be sure.
|
|
|
|
|
|
SUSceo684
|
Jan 30 2022, 05:14 PM
|
|
QUOTE(EvOliver @ Jan 30 2022, 04:57 PM) Right. So in this case, can't really assume Black is usual Live. Have to really verify, either by reference connection, or by test pen, to be sure. Generally in MY the code colours black is never L regardless flexicord or stiff (solid stranded) wire. However there's a lot of champion never follow proper colour code. Assume installer is colour blind and test to be sure. ⚠️ There is a possibility idiota installed L and N terbalik. Pls test to be sure. IN-WALL 230V wiring colour code typically L red yellow blue, sometimes even white 🤦♀️ N is black E is green This post has been edited by ceo684: Jan 30 2022, 06:49 PM
|
|
|
|
|
|
SUSceo684
|
Jan 30 2022, 05:17 PM
|
|
QUOTE(IMF2025 @ Jan 30 2022, 03:55 PM) Black is usually live Blue is nuetral Ini terbalik. Black is usually neutral in MY. Overseas code lain cerita.
|
|
|
|
|
|
ozak
|
Jan 30 2022, 05:27 PM
|
|
QUOTE(EvOliver @ Jan 30 2022, 04:57 PM) Right. So in this case, can't really assume Black is usual Live. Have to really verify, either by reference connection, or by test pen, to be sure. Follow as what I write on top how to verify. Take out the DB box front cover. You can see a bunch of wire connect together on the terminal. Earth and neutral. From here you can know what color wire for the neutral.
|
|
|
|
|
|
EvOliver
|
Jan 30 2022, 10:19 PM
|
Getting Started

|
Actually, I'm looking for a standardised spec for Malaysia power line colour code. Everyone should follow the same standard to avoid confusion nor misunderstanding.
|
|
|
|
|
|
EvOliver
|
Jan 30 2022, 10:37 PM
|
Getting Started

|
Yes, I've monitored a foreigner contractor installing LED ceiling lights before. One out of several lights, he actually tested one light and tripped the power. He happened to connect earth line to LEDs neutral terminal. 🤦♂️ Can't imagine how many connection mistakes could have been hidden from owners' view without knowing. Reversed Live and Neutral connection may be another hidden danger.
|
|
|
|
|
|
SUSceo684
|
Jan 31 2022, 12:42 AM
|
|
QUOTE(EvOliver @ Jan 30 2022, 10:19 PM) Actually, I'm looking for a standardised spec for Malaysia power line colour code. Everyone should follow the same standard to avoid confusion nor misunderstanding. It's in MS1979 spec and ST guidelines. Item 5.5 Attached File(s)
ST_Guidelines_For_Electrical_Wiring.pdf ( 427.2k )
Number of downloads: 79
|
|
|
|
|
|
EvOliver
|
Jan 31 2022, 02:45 AM
|
Getting Started

|
QUOTE(ceo684 @ Jan 31 2022, 12:42 AM) It's in MS1979 spec and ST guidelines. Item 5.5 Now we all can technically discuss with proper standard reference from Suruhanjaya Tenaga. It's supposed to be governed by law too. Thanks a lot for sharing and pointing out. I think everyone should have this MS doc handy.
|
|
|
|
|
|
louyeh
|
Jan 31 2022, 04:37 PM
|
|
Electrical wire colour code is only reliable if its practiced at the main DB first.
Test pen can't differentiate Earth vs Neutral.
Multimeter is the better tool.
E & L = 230VAC E & N = As close to 0VAC as possible, 1-2VAC is fine. Anything higher indicates improper wiring/installation L & N = 230VAC
Majority of electricians rely on test pen. The minorities don't bother to use one as they don't understand E & N difference.
|
|
|
|
|
|
SUSceo684
|
Jan 31 2022, 09:44 PM
|
|
QUOTE(louyeh @ Jan 31 2022, 04:37 PM) Electrical wire colour code is only reliable if its practiced at the main DB first.Test pen can't differentiate Earth vs Neutral. Multimeter is the better tool. E & L = 230VAC E & N = As close to 0VAC as possible, 1-2VAC is fine. Anything higher indicates improper wiring/installation L & N = 230VAC Majority of electricians rely on test pen. The minorities don't bother to use one as they don't understand E & N difference. Sometimes with champion faux electrician the code is only followed up to the first light.. then switch relocated + new lights added in same line due to plaster ceiling what you see at the switch and other lights will surprise you.
|
|
|
|
|