Having way too many circuit is pointless if it does little to improve the safety and may even overwhelm the home owner. If you really had that much budget, using RCBOs with FE plus GI conduits & trunking will provide additional safety. S type RCD to protect the submain cables, phase sequence relay, SPD with 32A 4P MCB/MCCB.
At a quick glance, it is cut throat price. 1. Use only double socket outlets to reduce cutthroat. 2. 15A outlet at that price should use 4mm² instead of 2.5mm² cables. 3. Do you really need that many waterproof socket outlets? It better have it's own dedicated RCD or you will have RCCB trippings when the leakage got worse overtime. |
|
|