My house all Eletrical on to max Test incoming Power only around 10A . Means i can change to 2Pole 32A MCB? Developer give now all 63A (1 x 2Pole MCB , 1x 100mA and 30mA) All 63A macam too much .

and after the 2 Pole 63A incoming MCB , the outgoing Cable is using 10mm not 16mm sad.gif .

This post has been edited by 13aby: Jul 25 2024, 07:06 PM
syaifau
post Jul 25 2024, 07:29 PM

New Member
*
Newbie
44 posts

Joined: Nov 2011


what?
TS13aby
post Jul 25 2024, 07:41 PM

Enthusiast
*****
Senior Member
975 posts

Joined: Jan 2009



QUOTE(syaifau @ Jul 25 2024, 07:29 PM)
what?
*
Dont la like this bro biggrin.gif

i not sure i clamp wrong or it really so low , 2 Airconds 2 WH this two is the biggest power eater i guess . Cuckoo , Air Fryer , Washine Machine and Fridge all On .

Or

i just follow back Developer 63A icon_question.gif because i planning to change all to HAGER . and mayb the 10mm to 16mm

Advice please rclxm9.gif
syaifau
post Jul 25 2024, 09:53 PM

New Member
*
Newbie
44 posts

Joined: Nov 2011


My knowledge in electrical is so vastly impaired, i cant even advise myself.

All the best with your investigation, @13aby
Momo33
post Jul 26 2024, 12:42 AM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(13aby @ Jul 25 2024, 08:41 PM)
Dont la like this bro  biggrin.gif

i not sure i clamp wrong or it really so low , 2 Airconds 2 WH this two is the biggest power eater i guess . Cuckoo , Air Fryer , Washine Machine and Fridge all On .

Or

i just follow back Developer 63A  icon_question.gif  because i planning to change all to HAGER . and mayb the 10mm to 16mm

Advice please  rclxm9.gif
*
2 AC , 2 WH on already is about 20 A .

Momo33
post Jul 26 2024, 01:14 AM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(13aby @ Jul 25 2024, 08:05 PM)
My house all Eletrical on to max Test incoming Power only around 10A . Means i can change to 2Pole 32A MCB? Developer give now all 63A (1 x 2Pole MCB , 1x 100mA and 30mA) All 63A macam too much .

and after the 2 Pole 63A incoming MCB , the outgoing Cable is using 10mm not 16mm  sad.gif  .
*
use MCB 20 A for AC, WH , 4 mm cable
MCB 6A for lightning. 1.5mm
MCB 16 A for 3 pin socket . 2.5mm

for RCCB 63A , 100mA for mains ,25mm cable
RCCB 63A , 30mA for the 3 pin sockets , 2.5mm cable
RCCB 63A , 10mA for WH , 4mm

post a pix of your DB box better to advise you.





TS13aby
post Jul 26 2024, 09:46 PM

Enthusiast
*****
Senior Member
975 posts

Joined: Jan 2009



QUOTE(Momo33 @ Jul 26 2024, 12:42 AM)
2 AC , 2 WH  on already is about  20  A .
*
ya thats why i feel weird also . mayb my clamp meter spoil sweat.gif
TS13aby
post Jul 26 2024, 09:48 PM

Enthusiast
*****
Senior Member
975 posts

Joined: Jan 2009



QUOTE(Momo33 @ Jul 26 2024, 01:14 AM)
use MCB 20 A    for AC,  WH  , 4 mm cable
MCB  6A   for lightning.         1.5mm
MCB 16 A   for  3 pin socket .   2.5mm

for RCCB   63A , 100mA  for mains   ,25mm  cable
RCCB  63A , 30mA    for  the 3 pin sockets  , 2.5mm cable
RCCB  63A , 10mA    for WH  ,    4mm

post a pix of your DB box  better to advise you.
*
Using 63A incoming 2 Pole MCB and others 2 Main RCCB 63A also no problem? both is 100mA and 30mA now . Cable to 100mA and 30mA Developer give 10mm but the incoming TNB is 16mm . for the cable size min is 16mm for 63A

My is High Rise Property

This post has been edited by 13aby: Jul 26 2024, 09:48 PM
TS13aby
post Jul 26 2024, 11:41 PM

Enthusiast
*****
Senior Member
975 posts

Joined: Jan 2009



user posted image

here is the photo of the incoming (Bottom Left) to two RCCB
Momo33
post Jul 27 2024, 12:26 AM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(13aby @ Jul 26 2024, 10:48 PM)
Using 63A incoming 2 Pole MCB and others 2 Main RCCB 63A also no problem? both is 100mA and 30mA now . Cable to 100mA and 30mA Developer give 10mm but the incoming TNB is 16mm . for the cable size min is 16mm for 63A

My is High Rise Property
*
looks fine . pix too. nod.gif


This post has been edited by Momo33: Jul 27 2024, 12:27 AM
TS13aby
post Jul 27 2024, 06:32 PM

Enthusiast
*****
Senior Member
975 posts

Joined: Jan 2009



QUOTE(Momo33 @ Jul 27 2024, 12:26 AM)
looks fine .  pix too.  nod.gif
*
so means i can continue use all 63A ya cox i planning to change all to Hager .
Momo33
post Jul 27 2024, 08:01 PM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(13aby @ Jul 27 2024, 07:32 PM)
so means i can continue use all 63A ya cox i planning to change all to Hager .
*
change over to Hager is better cos hager products good quality hence bit price higher.

the items your developer use i also never see this brand before.... maybe unknown china product no sirim too .


TS13aby
post Jul 30 2024, 12:04 PM

Enthusiast
*****
Senior Member
975 posts

Joined: Jan 2009



user posted image

Bought from two different place , why color different?
rphoen1x
post Jul 30 2024, 01:37 PM

Getting Started
**
Junior Member
128 posts

Joined: Jun 2011
I think you can check the authenticity at https://hager.com/_en/check
mushigen
post Aug 10 2024, 01:52 PM

Look at all my stars!!
*******
Senior Member
4,949 posts

Joined: Jul 2010


QUOTE(Momo33 @ Jul 26 2024, 01:14 AM)
use MCB 20 A    for AC,  WH  , 4 mm cable
MCB  6A  for lightning.        1.5mm
MCB 16 A  for  3 pin socket .  2.5mm

for RCCB  63A , 100mA  for mains  ,25mm  cable
RCCB  63A , 30mA    for  the 3 pin sockets  , 2.5mm cable
RCCB  63A , 10mA    for WH  ,    4mm

post a pix of your DB box  better to advise you.
*
May I know why you use 63A RCCB instead of 25A RCCB for WH since there should be a 20A MCB for WH to protect the RCCB?
Momo33
post Aug 10 2024, 02:28 PM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(mushigen @ Aug 10 2024, 02:52 PM)
May I know why you use 63A RCCB instead of 25A RCCB for WH since there should be a 20A MCB for WH to protect the RCCB?
*
if you know your WH amp rating then chose accordingly .

yes can use rccb 25A, 10mA for those instant WH / 4kW type.

63A one can handle a heavy current
rccb do not trip on over current .





Momo33
post Aug 10 2024, 02:32 PM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(13aby @ Jul 30 2024, 01:04 PM)
user posted image

Bought from two different place , why color different?
*
check box manufacture which country
marking on item side s may tell

there is china , France or fake that i have seen .




SUSceo684
post Aug 12 2024, 02:01 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(13aby @ Jul 26 2024, 11:41 PM)
user posted image

here is the photo of the incoming (Bottom Left) to two RCCB
*
It’s already sized correctly. Don’t waste money

What I would suggest is to redo the pigtails as there is a minimum bend radius (don't hard turn 90 degrees), keep the cable curved gently. Nanti patah inside and create hotspot.

This post has been edited by ceo684: Aug 12 2024, 02:12 AM
SUSceo684
post Aug 12 2024, 02:02 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(13aby @ Jul 30 2024, 12:04 PM)
user posted image

Bought from two different place , why color different?
*
Make sure buy from proper seller. Many recon ABB and Hager from Singapore HIP refurbishing land in MY. Plus why don’t you get 6kA withstand model instead of the 4.5kA. ABB not expensive for 6kA

This post has been edited by ceo684: Aug 12 2024, 02:04 AM
SUSceo684
post Aug 12 2024, 02:06 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(13aby @ Jul 25 2024, 07:41 PM)
Dont la like this bro  biggrin.gif

i not sure i clamp wrong or it really so low , 2 Airconds 2 WH this two is the biggest power eater i guess . Cuckoo , Air Fryer , Washine Machine and Fridge all On .

Or

i just follow back Developer 63A  icon_question.gif  because i planning to change all to HAGER . and mayb the 10mm to 16mm

Advice please  rclxm9.gif
*
Your clamp meter not true RMS is it.
One unit WH running from cold already take 14-16A easily.

The 16mm one you can buy Mega Kabel meter loose cut in the correct colours (red and black) as necessary, but if your supply (from meter) is 10mm then no point lah.

Also, not much use for the 100mA RCD when the 30mA RCD is capable for whole house sockets and lights. There is little point in using the 100mA RCD in modern day without fluorescent tube lights.

This post has been edited by ceo684: Aug 12 2024, 02:09 AM
TS13aby
post Aug 12 2024, 04:24 PM

Enthusiast
*****
Senior Member
975 posts

Joined: Jan 2009



QUOTE(ceo684 @ Aug 12 2024, 02:01 AM)
It’s already sized correctly. Don’t waste money

What I would suggest is to redo the pigtails as there is a minimum bend radius (don't hard turn 90 degrees), keep the cable curved gently. Nanti patah inside and create hotspot.
*
I plan to change all to Hager , so i follow back all same 63a for the RCCB and 2 Pole MCB for incoming ya .


TS13aby
post Aug 12 2024, 04:33 PM

Enthusiast
*****
Senior Member
975 posts

Joined: Jan 2009



QUOTE(rphoen1x @ Jul 30 2024, 01:37 PM)
I think you can check the authenticity at https://hager.com/_en/check
*
Sent , but no reply from them since ever haha


QUOTE(ceo684 @ Aug 12 2024, 02:02 AM)
Make sure buy from proper seller. Many recon ABB and Hager from Singapore HIP refurbishing land in MY. Plus why don’t you get 6kA withstand model instead of the 4.5kA. ABB not expensive for 6kA
*
Yes i bought from Authorised Reseller / Distributor shop (Pentapower(M) Sdn Bhd (Puchong) & (CPE Electrical Supplier via Shopee). But they say use 4.5k is enough . Or should i change all to 6k as developer provide?

QUOTE(ceo684 @ Aug 12 2024, 02:06 AM)
Your clamp meter not true RMS is it.
One unit WH running from cold already take 14-16A easily.

The 16mm one you can buy Mega Kabel meter loose cut in the correct colours (red and black) as necessary, but if your supply (from meter) is 10mm then no point lah.

Also, not much use for the 100mA RCD when the 30mA RCD is capable for whole house sockets and lights. There is little point in using the 100mA RCD in modern day without fluorescent tube lights.
*
Ya i redo the reading correct already , 1 WH running around 14A .... Incoming is 16mm from meter but thn 10mm to both RCCB (100mA & 30mA)

For my WH , Developer no give RCCB / RCBO i added myself for safety .
SUSceo684
post Aug 12 2024, 08:11 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(13aby @ Aug 12 2024, 04:33 PM)
Sent , but no reply from them since ever haha
Yes i bought from Authorised Reseller / Distributor shop (Pentapower(M) Sdn Bhd (Puchong) & (CPE Electrical Supplier via Shopee). But they say use 4.5k is enough . Or should i change all to 6k as developer provide?
Ya i redo the reading correct already , 1 WH running around 14A .... Incoming is 16mm from meter but thn 10mm to both RCCB (100mA & 30mA)

For my WH , Developer no give RCCB / RCBO i added myself for safety .
*
Forget the 100mA RCD (buang), rerun with 16mm inside the DB. That 10mm is only good for ard 40A and can create a hotspot which is unprotected because it is supposed to be 16mm throughout.
TS13aby
post Aug 12 2024, 09:07 PM

Enthusiast
*****
Senior Member
975 posts

Joined: Jan 2009



QUOTE(ceo684 @ Aug 12 2024, 08:11 PM)
Forget the 100mA RCD (buang), rerun with 16mm inside the DB. That 10mm is only good for ard 40A and can create a hotspot which is unprotected because it is supposed to be 16mm throughout.
*
means only use 1nos 30mA whole whole house?

The empty space is 2 nos RCCB 0.01 .. not yet install when snap this

user posted image

This post has been edited by 13aby: Aug 12 2024, 09:08 PM
SUSceo684
post Aug 12 2024, 10:18 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(13aby @ Aug 12 2024, 09:07 PM)
means only use 1nos 30mA whole whole house?

The empty space is 2 nos RCCB 0.01 .. not yet install when snap this

user posted image
*
Yes. According to MS1979 COP it is allowed. And safer too for changing lights.
TS13aby
post Aug 12 2024, 10:41 PM

Enthusiast
*****
Senior Member
975 posts

Joined: Jan 2009



QUOTE(ceo684 @ Aug 12 2024, 10:18 PM)
Yes. According to MS1979 COP it is allowed. And safer too for changing lights.
*
My neutral bar is separated by two sides , can i connect both side by tapping a wire? or need to replace a longer bar
SUSceo684
post Aug 13 2024, 02:50 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(13aby @ Aug 12 2024, 10:41 PM)
My neutral bar is separated by two sides , can i connect both side by tapping a wire? or need to replace a longer bar
*
Common neutral, use a 16mm Mega Kabel pigtail.
TS13aby
post Aug 13 2024, 10:02 AM

Enthusiast
*****
Senior Member
975 posts

Joined: Jan 2009



QUOTE(ceo684 @ Aug 13 2024, 02:50 AM)
Common neutral, use a 16mm Mega Kabel pigtail.
*
U mean connect with a 16mm cable like photo ? 10mm boleh? Existing Neutral developer using 10mm for both side

user posted image

This post has been edited by 13aby: Aug 13 2024, 10:06 AM
SUSceo684
post Aug 13 2024, 10:07 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(13aby @ Aug 13 2024, 10:02 AM)
U mean connect with a 16mm cable like photo ? 10mm boleh?

user posted image
*
Beli lah one meter of 16mm. Less than 10 bucks per meter only. 10mm not good enough. https://s.lazada.com.my/s.PTisA
TS13aby
post Aug 13 2024, 11:22 AM

Enthusiast
*****
Senior Member
975 posts

Joined: Jan 2009



QUOTE(ceo684 @ Aug 13 2024, 10:07 AM)
Beli lah one meter of 16mm. Less than 10 bucks per meter only. 10mm not good enough. https://s.lazada.com.my/s.PTisA
*
16mm i got spare , so i just tap the wire to connect the both bar ya
anakkk
post Aug 13 2024, 11:24 AM

Look at all my stars!!
*******
Senior Member
2,111 posts

Joined: Apr 2013
i dono, but you using 3 phase or single phase?
TS13aby
post Aug 13 2024, 08:47 PM

Enthusiast
*****
Senior Member
975 posts

Joined: Jan 2009



QUOTE(anakkk @ Aug 13 2024, 11:24 AM)
i dono, but you using 3 phase or single phase?
*
satu phase
SUSceo684
post Aug 14 2024, 05:14 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(13aby @ Aug 13 2024, 11:22 AM)
16mm i got spare , so i just tap the wire to connect the both bar ya
*
Yes, do a smooth horseshoe shape
TS13aby
post Aug 14 2024, 05:52 PM

Enthusiast
*****
Senior Member
975 posts

Joined: Jan 2009



QUOTE(ceo684 @ Aug 14 2024, 05:14 AM)
Yes, do a smooth horseshoe shape
*
just notice i dont have cutter size to cut 16mm haha , any recommendations for the cutter?
SUSceo684
post Aug 15 2024, 09:27 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(13aby @ Aug 14 2024, 05:52 PM)
just notice i dont have cutter size to cut 16mm haha , any recommendations for the cutter?
*
MTC-45 or 47 cutters. (the biggest one)

This post has been edited by ceo684: Aug 15 2024, 09:28 AM
Kiding
post Aug 15 2024, 01:00 PM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


QUOTE(13aby @ Aug 12 2024, 10:41 PM)
My neutral bar is separated by two sides , can i connect both side by tapping a wire? or need to replace a longer bar
*
if you plan to use your spare 100mA RCCB, then you cant connect both neutral bars.
TS13aby
post Aug 17 2024, 02:31 PM

Enthusiast
*****
Senior Member
975 posts

Joined: Jan 2009



QUOTE(ceo684 @ Aug 12 2024, 08:11 PM)
Forget the 100mA RCD (buang), rerun with 16mm inside the DB. That 10mm is only good for ard 40A and can create a hotspot which is unprotected because it is supposed to be 16mm throughout.
*
100mA removed and all now using 30mA RCCB

user posted image
SUSceo684
post Aug 21 2024, 12:32 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(13aby @ Aug 17 2024, 02:31 PM)
100mA removed and all now using 30mA RCCB

user posted image
*
The MCBs should ideally use the same brand so they're the same height.


Attached thumbnail(s)
Attached Image
TS13aby
post Aug 22 2024, 09:19 AM

Enthusiast
*****
Senior Member
975 posts

Joined: Jan 2009



QUOTE(ceo684 @ Aug 21 2024, 12:32 PM)
The MCBs should ideally use the same brand so they're the same height.
*
ya will change all to hager , previously i test bought two mcb from 2 different seller . one of it when power off V test 7.xx 😢😢 suspect is fake .... the other one test V is 2.xx perfect ....
prophecus
post Aug 22 2024, 09:27 AM

Getting Started
**
Junior Member
157 posts

Joined: Nov 2004
From: Petaling Jayo


QUOTE(ceo684 @ Aug 12 2024, 02:06 AM)
Your clamp meter not true RMS is it.
One unit WH running from cold already take 14-16A easily.

The 16mm one you can buy Mega Kabel meter loose cut in the correct colours (red and black) as necessary, but if your supply (from meter) is 10mm then no point lah.

Also, not much use for the 100mA RCD when the 30mA RCD is capable for whole house sockets and lights. There is little point in using the 100mA RCD in modern day without fluorescent tube lights.
*
Developers have to comply to wiring regulation by Suruhanjaya Tenaga. 10 mA for water heater and wet area. 30 mA for sockets. 100mA for lighting and AC.

in the UK they have moved on to RCBO. No more RCCB as it is included in each circuit. So if there is leakage only individual circuit would trip not the whole house. In Malaysia RCBO is available for Water heater (20A, 10mA trip), the rest not widely available yet or price too expensive.
jio
post Aug 23 2024, 02:45 PM

Casual
***
Junior Member
383 posts

Joined: May 2005
QUOTE(13aby @ Aug 22 2024, 09:19 AM)
ya will change all to hager , previously i test bought two mcb from 2 different seller . one of it when power off V test 7.xx 😢😢 suspect is fake .... the other one test V is 2.xx perfect ....
*
Which retard teach you testing MCB in off position using voltmeter? If you learn this bullshit from local YouTuber moron then stop watching those crap misinformation. That reading will change due to the effect of capacitance/inductance.

Your MCB should have sirim serial sticker or printed on it.
SUSceo684
post Aug 23 2024, 08:14 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(prophecus @ Aug 22 2024, 09:27 AM)
Developers have to comply to wiring regulation by Suruhanjaya Tenaga. 10 mA for water heater and wet area. 30 mA for sockets. 100mA for lighting and AC.
*
Dei. Read back MS1979 COP on the RCDs and ER1994 regulation. Especially the highlighted word.

QUOTE(prophecus @ Aug 22 2024, 09:27 AM)
in the UK they have moved on to RCBO. No more RCCB as it is included in each circuit. So if there is leakage only individual circuit would trip not the whole house. In Malaysia RCBO is available for Water heater (20A, 10mA trip), the rest not widely available yet or price too expensive.
*
Not economical to use RCBO for every circuit. Even for WH they do not carry the correct size of 20A/10mA. Most of the common RCBO is still 25A/10mA which is incorrect for the 2.5mm cut corner cables commonly installed.

This post has been edited by ceo684: Aug 23 2024, 08:26 PM


Attached thumbnail(s)
Attached Image Attached Image Attached Image

Attached File(s)
Attached File  ms.1979.2007.pdf ( 1.25mb ) Number of downloads: 2
Attached File  SuruhanjayaTenagaGuidelinesForElectricalWiringInResidentialBuildings.pdf ( 427.2k ) Number of downloads: 3

 