and after the 2 Pole 63A incoming MCB , the outgoing Cable is using 10mm not 16mm
This post has been edited by 13aby: Jul 25 2024, 07:06 PM
2 Poles MCB Incoming TNB Power
|
|
Jul 25 2024, 07:05 PM, updated 2y ago
Show posts by this member only | Post
#1
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
My house all Eletrical on to max Test incoming Power only around 10A . Means i can change to 2Pole 32A MCB? Developer give now all 63A (1 x 2Pole MCB , 1x 100mA and 30mA) All 63A macam too much .
and after the 2 Pole 63A incoming MCB , the outgoing Cable is using 10mm not 16mm This post has been edited by 13aby: Jul 25 2024, 07:06 PM |
|
|
|
|
|
Jul 25 2024, 07:29 PM
Show posts by this member only | Post
#2
|
![]()
Newbie
44 posts Joined: Nov 2011 |
what?
|
|
|
Jul 25 2024, 07:41 PM
Show posts by this member only | Post
#3
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
QUOTE(syaifau @ Jul 25 2024, 07:29 PM) Dont la like this bro i not sure i clamp wrong or it really so low , 2 Airconds 2 WH this two is the biggest power eater i guess . Cuckoo , Air Fryer , Washine Machine and Fridge all On . Or i just follow back Developer 63A Advice please |
|
|
Jul 25 2024, 09:53 PM
Show posts by this member only | Post
#4
|
![]()
Newbie
44 posts Joined: Nov 2011 |
My knowledge in electrical is so vastly impaired, i cant even advise myself.
All the best with your investigation, @13aby |
|
|
Jul 26 2024, 12:42 AM
Show posts by this member only | IPv6 | Post
#5
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,448 posts Joined: Oct 2019 |
QUOTE(13aby @ Jul 25 2024, 08:41 PM) Dont la like this bro 2 AC , 2 WH on already is about 20 A .i not sure i clamp wrong or it really so low , 2 Airconds 2 WH this two is the biggest power eater i guess . Cuckoo , Air Fryer , Washine Machine and Fridge all On . Or i just follow back Developer 63A Advice please |
|
|
Jul 26 2024, 01:14 AM
Show posts by this member only | IPv6 | Post
#6
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,448 posts Joined: Oct 2019 |
QUOTE(13aby @ Jul 25 2024, 08:05 PM) My house all Eletrical on to max Test incoming Power only around 10A . Means i can change to 2Pole 32A MCB? Developer give now all 63A (1 x 2Pole MCB , 1x 100mA and 30mA) All 63A macam too much . use MCB 20 A for AC, WH , 4 mm cable and after the 2 Pole 63A incoming MCB , the outgoing Cable is using 10mm not 16mm MCB 6A for lightning. 1.5mm MCB 16 A for 3 pin socket . 2.5mm for RCCB 63A , 100mA for mains ,25mm cable RCCB 63A , 30mA for the 3 pin sockets , 2.5mm cable RCCB 63A , 10mA for WH , 4mm post a pix of your DB box better to advise you. gobiomani liked this post
|
|
|
|
|
|
Jul 26 2024, 09:46 PM
Show posts by this member only | Post
#7
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
|
|
|
Jul 26 2024, 09:48 PM
Show posts by this member only | Post
#8
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
QUOTE(Momo33 @ Jul 26 2024, 01:14 AM) use MCB 20 A  for AC, WH , 4 mm cable Using 63A incoming 2 Pole MCB and others 2 Main RCCB 63A also no problem? both is 100mA and 30mA now . Cable to 100mA and 30mA Developer give 10mm but the incoming TNB is 16mm . for the cable size min is 16mm for 63AMCB 6A for lightning.    1.5mm MCB 16 A for 3 pin socket . 2.5mm for RCCB 63A , 100mA for mains ,25mm cable RCCB 63A , 30mA  for the 3 pin sockets , 2.5mm cable RCCB 63A , 10mA  for WH ,  4mm post a pix of your DB box better to advise you. My is High Rise Property This post has been edited by 13aby: Jul 26 2024, 09:48 PM |
|
|
Jul 26 2024, 11:41 PM
Show posts by this member only | Post
#9
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
|
|
|
Jul 27 2024, 12:26 AM
Show posts by this member only | IPv6 | Post
#10
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,448 posts Joined: Oct 2019 |
QUOTE(13aby @ Jul 26 2024, 10:48 PM) Using 63A incoming 2 Pole MCB and others 2 Main RCCB 63A also no problem? both is 100mA and 30mA now . Cable to 100mA and 30mA Developer give 10mm but the incoming TNB is 16mm . for the cable size min is 16mm for 63A looks fine . pix too. My is High Rise Property This post has been edited by Momo33: Jul 27 2024, 12:27 AM |
|
|
Jul 27 2024, 06:32 PM
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
|
|
|
Jul 27 2024, 08:01 PM
Show posts by this member only | IPv6 | Post
#12
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,448 posts Joined: Oct 2019 |
QUOTE(13aby @ Jul 27 2024, 07:32 PM) change over to Hager is better cos hager products good quality hence bit price higher. the items your developer use i also never see this brand before.... maybe unknown china product no sirim too . gobiomani liked this post
|
|
|
Jul 30 2024, 12:04 PM
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
|
|
|
|
|
|
Jul 30 2024, 01:37 PM
|
![]() ![]()
Junior Member
128 posts Joined: Jun 2011 |
I think you can check the authenticity at https://hager.com/_en/check
|
|
|
Aug 10 2024, 01:52 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
4,949 posts Joined: Jul 2010 |
QUOTE(Momo33 @ Jul 26 2024, 01:14 AM) use MCB 20 A for AC, WH , 4 mm cable May I know why you use 63A RCCB instead of 25A RCCB for WH since there should be a 20A MCB for WH to protect the RCCB?MCB 6A for lightning. 1.5mm MCB 16 A for 3 pin socket . 2.5mm for RCCB 63A , 100mA for mains ,25mm cable RCCB 63A , 30mA for the 3 pin sockets , 2.5mm cable RCCB 63A , 10mA for WH , 4mm post a pix of your DB box better to advise you. |
|
|
Aug 10 2024, 02:28 PM
Show posts by this member only | IPv6 | Post
#16
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,448 posts Joined: Oct 2019 |
QUOTE(mushigen @ Aug 10 2024, 02:52 PM) May I know why you use 63A RCCB instead of 25A RCCB for WH since there should be a 20A MCB for WH to protect the RCCB? if you know your WH amp rating then chose accordingly .yes can use rccb 25A, 10mA for those instant WH / 4kW type. 63A one can handle a heavy current rccb do not trip on over current . mushigen liked this post
|
|
|
Aug 10 2024, 02:32 PM
Show posts by this member only | IPv6 | Post
#17
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,448 posts Joined: Oct 2019 |
|
|
|
Aug 12 2024, 02:01 AM
Show posts by this member only | IPv6 | Post
#18
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(13aby @ Jul 26 2024, 11:41 PM) It’s already sized correctly. Don’t waste moneyWhat I would suggest is to redo the pigtails as there is a minimum bend radius (don't hard turn 90 degrees), keep the cable curved gently. Nanti patah inside and create hotspot. This post has been edited by ceo684: Aug 12 2024, 02:12 AM |
|
|
Aug 12 2024, 02:02 AM
Show posts by this member only | IPv6 | Post
#19
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(13aby @ Jul 30 2024, 12:04 PM) Make sure buy from proper seller. Many recon ABB and Hager from Singapore HIP refurbishing land in MY. Plus why don’t you get 6kA withstand model instead of the 4.5kA. ABB not expensive for 6kAThis post has been edited by ceo684: Aug 12 2024, 02:04 AM |
|
|
Aug 12 2024, 02:06 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(13aby @ Jul 25 2024, 07:41 PM) Dont la like this bro Your clamp meter not true RMS is it.i not sure i clamp wrong or it really so low , 2 Airconds 2 WH this two is the biggest power eater i guess . Cuckoo , Air Fryer , Washine Machine and Fridge all On . Or i just follow back Developer 63A Advice please One unit WH running from cold already take 14-16A easily. The 16mm one you can buy Mega Kabel meter loose cut in the correct colours (red and black) as necessary, but if your supply (from meter) is 10mm then no point lah. Also, not much use for the 100mA RCD when the 30mA RCD is capable for whole house sockets and lights. There is little point in using the 100mA RCD in modern day without fluorescent tube lights. This post has been edited by ceo684: Aug 12 2024, 02:09 AM |
|
|
Aug 12 2024, 04:24 PM
Show posts by this member only | IPv6 | Post
#21
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
QUOTE(ceo684 @ Aug 12 2024, 02:01 AM) It’s already sized correctly. Don’t waste money I plan to change all to Hager , so i follow back all same 63a for the RCCB and 2 Pole MCB for incoming ya . What I would suggest is to redo the pigtails as there is a minimum bend radius (don't hard turn 90 degrees), keep the cable curved gently. Nanti patah inside and create hotspot. |
|
|
Aug 12 2024, 04:33 PM
Show posts by this member only | IPv6 | Post
#22
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
QUOTE(rphoen1x @ Jul 30 2024, 01:37 PM) Sent , but no reply from them since ever hahaQUOTE(ceo684 @ Aug 12 2024, 02:02 AM) Make sure buy from proper seller. Many recon ABB and Hager from Singapore HIP refurbishing land in MY. Plus why don’t you get 6kA withstand model instead of the 4.5kA. ABB not expensive for 6kA Yes i bought from Authorised Reseller / Distributor shop (Pentapower(M) Sdn Bhd (Puchong) & (CPE Electrical Supplier via Shopee). But they say use 4.5k is enough . Or should i change all to 6k as developer provide? QUOTE(ceo684 @ Aug 12 2024, 02:06 AM) Your clamp meter not true RMS is it. Ya i redo the reading correct already , 1 WH running around 14A .... Incoming is 16mm from meter but thn 10mm to both RCCB (100mA & 30mA)One unit WH running from cold already take 14-16A easily. The 16mm one you can buy Mega Kabel meter loose cut in the correct colours (red and black) as necessary, but if your supply (from meter) is 10mm then no point lah. Also, not much use for the 100mA RCD when the 30mA RCD is capable for whole house sockets and lights. There is little point in using the 100mA RCD in modern day without fluorescent tube lights. For my WH , Developer no give RCCB / RCBO i added myself for safety . |
|
|
Aug 12 2024, 08:11 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(13aby @ Aug 12 2024, 04:33 PM) Sent , but no reply from them since ever haha Forget the 100mA RCD (buang), rerun with 16mm inside the DB. That 10mm is only good for ard 40A and can create a hotspot which is unprotected because it is supposed to be 16mm throughout.Yes i bought from Authorised Reseller / Distributor shop (Pentapower(M) Sdn Bhd (Puchong) & (CPE Electrical Supplier via Shopee). But they say use 4.5k is enough . Or should i change all to 6k as developer provide? Ya i redo the reading correct already , 1 WH running around 14A .... Incoming is 16mm from meter but thn 10mm to both RCCB (100mA & 30mA) For my WH , Developer no give RCCB / RCBO i added myself for safety . |
|
|
Aug 12 2024, 09:07 PM
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
QUOTE(ceo684 @ Aug 12 2024, 08:11 PM) Forget the 100mA RCD (buang), rerun with 16mm inside the DB. That 10mm is only good for ard 40A and can create a hotspot which is unprotected because it is supposed to be 16mm throughout. means only use 1nos 30mA whole whole house? The empty space is 2 nos RCCB 0.01 .. not yet install when snap this ![]() This post has been edited by 13aby: Aug 12 2024, 09:08 PM |
|
|
Aug 12 2024, 10:18 PM
Show posts by this member only | IPv6 | Post
#25
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
|
|
|
Aug 12 2024, 10:41 PM
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
|
|
|
Aug 13 2024, 02:50 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
|
|
|
Aug 13 2024, 10:02 AM
Show posts by this member only | IPv6 | Post
#28
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
|
|
|
Aug 13 2024, 10:07 AM
Show posts by this member only | IPv6 | Post
#29
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(13aby @ Aug 13 2024, 10:02 AM) Beli lah one meter of 16mm. Less than 10 bucks per meter only. 10mm not good enough. https://s.lazada.com.my/s.PTisA |
|
|
Aug 13 2024, 11:22 AM
Show posts by this member only | IPv6 | Post
#30
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
QUOTE(ceo684 @ Aug 13 2024, 10:07 AM) Beli lah one meter of 16mm. Less than 10 bucks per meter only. 10mm not good enough. https://s.lazada.com.my/s.PTisA 16mm i got spare , so i just tap the wire to connect the both bar ya jio liked this post
|
|
|
Aug 13 2024, 11:24 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,111 posts Joined: Apr 2013 |
i dono, but you using 3 phase or single phase?
|
|
|
Aug 13 2024, 08:47 PM
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
|
|
|
Aug 14 2024, 05:14 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(13aby @ Aug 13 2024, 11:22 AM) Yes, do a smooth horseshoe shape 13aby liked this post
|
|
|
Aug 14 2024, 05:52 PM
Show posts by this member only | IPv6 | Post
#34
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
|
|
|
Aug 15 2024, 09:27 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
|
|
|
Aug 15 2024, 01:00 PM
Show posts by this member only | IPv6 | Post
#36
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,135 posts Joined: Jan 2003 From: Seri Kembangan |
|
|
|
Aug 17 2024, 02:31 PM
Show posts by this member only | IPv6 | Post
#37
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
|
|
|
Aug 21 2024, 12:32 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
|
|
|
Aug 22 2024, 09:19 AM
Show posts by this member only | IPv6 | Post
#39
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
QUOTE(ceo684 @ Aug 21 2024, 12:32 PM) ya will change all to hager , previously i test bought two mcb from 2 different seller . one of it when power off V test 7.xx 😢😢 suspect is fake .... the other one test V is 2.xx perfect .... |
|
|
Aug 22 2024, 09:27 AM
|
![]() ![]()
Junior Member
157 posts Joined: Nov 2004 From: Petaling Jayo |
QUOTE(ceo684 @ Aug 12 2024, 02:06 AM) Your clamp meter not true RMS is it. Developers have to comply to wiring regulation by Suruhanjaya Tenaga. 10 mA for water heater and wet area. 30 mA for sockets. 100mA for lighting and AC.One unit WH running from cold already take 14-16A easily. The 16mm one you can buy Mega Kabel meter loose cut in the correct colours (red and black) as necessary, but if your supply (from meter) is 10mm then no point lah. Also, not much use for the 100mA RCD when the 30mA RCD is capable for whole house sockets and lights. There is little point in using the 100mA RCD in modern day without fluorescent tube lights. in the UK they have moved on to RCBO. No more RCCB as it is included in each circuit. So if there is leakage only individual circuit would trip not the whole house. In Malaysia RCBO is available for Water heater (20A, 10mA trip), the rest not widely available yet or price too expensive. |
|
|
Aug 23 2024, 02:45 PM
|
![]() ![]() ![]()
Junior Member
383 posts Joined: May 2005 |
QUOTE(13aby @ Aug 22 2024, 09:19 AM) ya will change all to hager , previously i test bought two mcb from 2 different seller . one of it when power off V test 7.xx 😢😢 suspect is fake .... the other one test V is 2.xx perfect .... Which retard teach you testing MCB in off position using voltmeter? If you learn this bullshit from local YouTuber moron then stop watching those crap misinformation. That reading will change due to the effect of capacitance/inductance.Your MCB should have sirim serial sticker or printed on it. |
|
|
Aug 23 2024, 08:14 PM
Show posts by this member only | IPv6 | Post
#42
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(prophecus @ Aug 22 2024, 09:27 AM) Developers have to comply to wiring regulation by Suruhanjaya Tenaga. 10 mA for water heater and wet area. 30 mA for sockets. 100mA for lighting and AC. Dei. Read back MS1979 COP on the RCDs and ER1994 regulation. Especially the highlighted word.QUOTE(prophecus @ Aug 22 2024, 09:27 AM) in the UK they have moved on to RCBO. No more RCCB as it is included in each circuit. So if there is leakage only individual circuit would trip not the whole house. In Malaysia RCBO is available for Water heater (20A, 10mA trip), the rest not widely available yet or price too expensive. Not economical to use RCBO for every circuit. Even for WH they do not carry the correct size of 20A/10mA. Most of the common RCBO is still 25A/10mA which is incorrect for the 2.5mm cut corner cables commonly installed.This post has been edited by ceo684: Aug 23 2024, 08:26 PM Attached thumbnail(s) Attached File(s)
ms.1979.2007.pdf ( 1.25mb )
Number of downloads: 2
SuruhanjayaTenagaGuidelinesForElectricalWiringInResidentialBuildings.pdf ( 427.2k )
Number of downloads: 3 |