QUOTE(cfc @ May 21 2022, 11:01 PM)
1. replace each WH mcb with Schneider rcbo 25A 10mA. Should i change it to EPS 20A 10mA (i guess mine also just 2.5mm, i have no way to find out now)
Each WH heater wall switch is a single 20A neon light panel.
If your cables are 2.5 mm², then you must use the 20 A RCBO. Only if your cables are 4 mm² (or larger) can you install the 25 A RCBO. You can see the size of the wires from the slack that is in the DB.Each WH heater wall switch is a single 20A neon light panel.
Alternately, if your water heater is below 4500 W, then you can go ahead and install the 20 A RCBO, no matter the size of the wires (as long as it is 2.5 mm² or larger) This will ensure the RCBO trips on an overcurrent, before the wires overheat.
QUOTE
2. replace the both rcd 100mA with the abb FH202 / Hager 63A 30mA , should i replace main DB 63A too (black color beside rcd), what would be the model i need to get if needed
Either brand is acceptable, as long as they are at 30 mA sensitivity (The ABB FH202 RCCB you have listed in the sh*pee link has a 100 mA option)It is not necessary to replace the incoming fused isolator EPS SFU-63 at position 24, 25, 26 in your DB
Edit : add information
This post has been edited by stormer.lyn: May 22 2022, 10:26 AM