QUOTE(ceo684 @ Mar 12 2021, 12:18 PM)
dear sifus..i have 2 DB fuse box in my house (DS) , wiring was done probably 8yrs ago
I remembered the technician did inform me each wall socket plug has no looping and direct to one MCB (not sure how true was his claim though)
but i checked and found out that it is still not following the safety spec mention in here
it is using a 100mA main rcd and all my water heaters are without the 10mA rcd as well
I need to do the following which involve no extra rewiring , please check and let me know if i miss out anything
1. replace each WH mcb with Schneider rcbo 25A 10mA. Should i change it to EPS 20A 10mA (i guess mine also just 2.5mm, i have no way to find out now)
Each WH heater wall switch is a single 20A neon light panel.
https://shopee.com.my/-EZ9D16625-Schneider-...0a-3491ef9d4a1d
2. replace the both rcd 100mA with the abb FH202 / Hager 63A 30mA , should i replace main DB 63A too (black color beside rcd), what would be the model i need to get if needed
https://shopee.com.my/ABB-FH202-63A-2P-30mA...78-cde7900452a8
https://shopee.com.my/hager-25A-40A-63A-2P-...8f-8c6a72adb7e9
DC box photo - 1st floor RCD same as below but MCB just have single tier
» Click to show Spoiler - click again to hide... «
thanks for the advice