Hi,
I planned to install smart switch in almost all rooms. May I know if neutral wire normally available in the switch box for condo/service apartment in Malaysia?
Neutral wire in switch box
Neutral wire in switch box
|
|
Oct 3 2020, 12:50 AM, updated 6y ago
Show posts by this member only | Post
#1
|
![]() ![]()
Junior Member
94 posts Joined: Nov 2008 |
Hi,
I planned to install smart switch in almost all rooms. May I know if neutral wire normally available in the switch box for condo/service apartment in Malaysia? |
|
|
|
|
|
Oct 3 2020, 01:36 AM
Show posts by this member only | Post
#2
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
5,650 posts Joined: Mar 2012 |
no.
usually only live wire. you may borrow the nearest neutral or place your smart switch inside the lamp |
|
|
Oct 3 2020, 02:26 PM
Show posts by this member only | Post
#3
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,448 posts Joined: Oct 2019 |
QUOTE(UnrequitedC @ Oct 3 2020, 01:50 AM) Hi, switch box mean the 13 A socket in the room or ? I planned to install smart switch in almost all rooms. May I know if neutral wire normally available in the switch box for condo/service apartment in Malaysia? what type of smart switch , for what purpose ? where do you plan install the switch. . cos some location on the wiring system are OK some are not . |
|
|
Oct 4 2020, 08:38 AM
Show posts by this member only | Post
#4
|
![]() ![]() ![]() ![]() ![]()
Senior Member
852 posts Joined: Mar 2005 From: Penang |
|
|
|
Oct 4 2020, 10:56 PM
Show posts by this member only | Post
#5
|
![]() ![]()
Junior Member
94 posts Joined: Nov 2008 |
QUOTE(fireballs @ Oct 3 2020, 01:36 AM) no. Ya. But if neutral available it will be easier to install. usually only live wire. you may borrow the nearest neutral or place your smart switch inside the lamp QUOTE(Momo33 @ Oct 3 2020, 02:26 PM) switch box mean the 13 A socket in the room or ? In the socket. Target is to install in all bedroom and living room. what type of smart switch , for what purpose ? where do you plan install the switch. . cos some location on the wiring system are OK some are not . With smart switch, we can use alexa or google home to control the home appliances using voice or smartphone. QUOTE(yfyap69 @ Oct 4 2020, 08:38 AM) Yes. But it will be easier to install if neutral is readily available. |
|
|
Oct 4 2020, 10:58 PM
Show posts by this member only | Post
#6
|
![]() ![]()
Junior Member
94 posts Joined: Nov 2008 |
Thanks all.
I'm thinking to use other way to do it. There is xiaomi device that can control IR-controlled home appliances available in Malaysia. Maybe after tat will try the smart switch without neutral. |
|
|
|
|
|
Oct 5 2020, 01:00 AM
Show posts by this member only | IPv6 | Post
#7
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
3,356 posts Joined: Dec 2006 |
QUOTE(UnrequitedC @ Oct 4 2020, 10:56 PM) Ya. But if neutral available it will be easier to install. 13A socket have 3 wires, Live, Neutral & Earth.In the socket. Target is to install in all bedroom and living room. With smart switch, we can use alexa or google home to control the home appliances using voice or smartphone. Yes. But it will be easier to install if neutral is readily available. |
|
|
Oct 5 2020, 01:18 AM
Show posts by this member only | Post
#8
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,448 posts Joined: Oct 2019 |
QUOTE(UnrequitedC @ Oct 4 2020, 11:58 PM) Thanks all. in malaysia Neutral line, earth , Live is always available at the 13 amp 3 pins socket . that s the standard.I'm thinking to use other way to do it. There is xiaomi device that can control IR-controlled home appliances available in Malaysia. Maybe after tat will try the smart switch without neutral. |
|
|
Oct 5 2020, 08:53 AM
Show posts by this member only | Post
#9
|
![]() ![]() ![]() ![]() ![]()
Senior Member
852 posts Joined: Mar 2005 From: Penang |
QUOTE(UnrequitedC @ Oct 4 2020, 10:56 PM) Ya. But if neutral available it will be easier to install. Not that hard to install without neutral. Just extra 1 step to install capacitor at 1 of the light. It might be even harder to install with neutral especially those 3 or 4 gangs because so many wires with so little space to cram all the wires in. Trust me, I had install more than 20 wall switches.In the socket. Target is to install in all bedroom and living room. With smart switch, we can use alexa or google home to control the home appliances using voice or smartphone. Yes. But it will be easier to install if neutral is readily available. |
|
|
Oct 5 2020, 08:58 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
7,938 posts Joined: Mar 2014 |
QUOTE(yfyap69 @ Oct 5 2020, 08:53 AM) Not that hard to install without neutral. Just extra 1 step to install capacitor at 1 of the light. It might be even harder to install with neutral especially those 3 or 4 gangs because so many wires with so little space to cram all the wires in. Trust me, I had install more than 20 wall switches. It is even harder to pull N wire since you need to hack the wall to conceal it. Otherwise will need to lay on wall |
|
|
Oct 5 2020, 08:59 AM
Show posts by this member only | IPv6 | Post
#11
|
![]() ![]() ![]() ![]() ![]()
Senior Member
755 posts Joined: Oct 2008 From: Taiping, Perak |
I'm using smart switches... All without neutral wire... need to install capacitor at L1... no fuss..
|
|
|
Oct 5 2020, 10:14 AM
Show posts by this member only | IPv6 | Post
#12
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
3,356 posts Joined: Dec 2006 |
QUOTE(yfyap69 @ Oct 5 2020, 08:53 AM) Not that hard to install without neutral. Just extra 1 step to install capacitor at 1 of the light. It might be even harder to install with neutral especially those 3 or 4 gangs because so many wires with so little space to cram all the wires in. Trust me, I had install more than 20 wall switches. He is saying appliances not lightings, so not an issue. 13A plugpoints have neutral+live+earth. |
|
|
Oct 5 2020, 11:11 PM
|
![]() ![]()
Junior Member
222 posts Joined: May 2016 |
13A socket got neutral line. All smart switch at my home using neutral type coz very easy to pull from 13A socket (At my home switch concealed box at top share line/piping with 13A socket at bottom so no need to spiderman at ceiling roof).
This post has been edited by excaliburcombo: Oct 5 2020, 11:11 PM |
|
|
|
|
|
Oct 8 2020, 09:10 PM
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,152 posts Joined: Jul 2011 |
How come no neutral wire in light wall sockets?
All houses nowadays got mar.... Is it because 3-phase don't have? |
|
|
Jan 19 2021, 08:55 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
14,037 posts Joined: Nov 2004 |
QUOTE(excaliburcombo @ Oct 5 2020, 11:11 PM) 13A socket got neutral line. All smart switch at my home using neutral type coz very easy to pull from 13A socket (At my home switch concealed box at top share line/piping with 13A socket at bottom so no need to spiderman at ceiling roof). Does the neutral wire need to be in the same phase or even circuit for it to work?Eg. lights on R1 while the switch I'm taking from is on Y5 for example. or I need to grab from R1 lights from R1 13A switches? |
|
|
Jan 19 2021, 01:47 PM
Show posts by this member only | IPv6 | Post
#16
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(lyt25_1234 @ Oct 8 2020, 09:10 PM) How come no neutral wire in light wall sockets? Err boss..dont confuse LIGHT n 13A SSO socket pleaseAll houses nowadays got mar.... Is it because 3-phase don't have? 13A SSO = need full LNE (3 cables) from DB to the 13A socket. Light L = L (from DB)----LIGHT SWITCH only operate on L --- light bulb holder (load) Light N = N from DB ----------------------------------------------- light bulb holder (load) as return path from load. N no need switching, unless its 2-pole (water heater switch to cut both L and N flow) Light E = E from DB ----------------------------------------------- light bulb holder (load) as safety backup return path from load This post has been edited by ceo684: Jan 19 2021, 01:47 PM |
|
|
Jan 19 2021, 01:49 PM
Show posts by this member only | IPv6 | Post
#17
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(celciuz @ Jan 19 2021, 08:55 AM) Does the neutral wire need to be in the same phase or even circuit for it to work? Neutral is common even if you have 3ph wiring.Eg. lights on R1 while the switch I'm taking from is on Y5 for example. or I need to grab from R1 lights from R1 13A switches? Generally neutral is shared but you need to keep certain special purpose neutral as dedicated virgin, do not connect anything to them (special purpose = i.e. the Water Heater or wet floor SSO) which are connected to 10mA RCD. 10mA RCD is very sensitive and it will not be able to operate if there is imbalance caused by the injected return path (it is more sensitive than your finance department when you submit fake claims using next door workers' receipts - when you are only entitled for own-expenses claims) This post has been edited by ceo684: Jan 19 2021, 01:53 PM |
|
|
Jan 19 2021, 02:25 PM
Show posts by this member only | IPv6 | Post
#18
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
14,037 posts Joined: Nov 2004 |
QUOTE(ceo684 @ Jan 19 2021, 01:49 PM) Neutral is common even if you have 3ph wiring. RCD is it the 25A 0.01A? As long I don't take from heater switch then right? Generally neutral is shared but you need to keep certain special purpose neutral as dedicated virgin, do not connect anything to them (special purpose = i.e. the Water Heater or wet floor SSO) which are connected to 10mA RCD. 10mA RCD is very sensitive and it will not be able to operate if there is imbalance caused by the injected return path (it is more sensitive than your finance department when you submit fake claims using next door workers' receipts - when you are only entitled for own-expenses claims) ![]() This post has been edited by celciuz: Jan 19 2021, 02:29 PM |
|
|
Jan 19 2021, 02:32 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
5,650 posts Joined: Mar 2012 |
ts, have u explored batteryless smart switch like the zigbee kinetik?
then basically just stick and run. no wiring needed energy is generated from the motion of switch. |
|
|