 Looping Wall Plug vs Extension Cords, Difference?

views
     
TSKahHoong
post Nov 24 2019, 09:27 PM, updated 7y ago

Getting Started
**
Junior Member
124 posts

Joined: Sep 2011
Hi guys, i would like to ask, what's the difference with looping wall plug and extensions? they both still come out from the same point rite? How high can each point tahan the wattage? Just recently realize, my old house have too many extension cords, every room and area only have 1 plug point.
fireballs
post Nov 24 2019, 09:31 PM

10101
*******
Senior Member
5,650 posts

Joined: Mar 2012
depend on the wire back to db
some old house even share he wire with two rooms.

typically, looping wall plug is better
extension use plug that can heat up at the pins. wall plug not so much if the wires done properly.

but in the end, is the cable back to db that matters.
TSKahHoong
post Nov 26 2019, 06:51 PM

Getting Started
**
Junior Member
124 posts

Joined: Sep 2011
QUOTE(fireballs @ Nov 24 2019, 09:31 PM)
depend on the wire back to db
some old house even share he wire with two rooms.

typically, looping wall plug is better
extension use plug that can heat up  at the pins. wall plug not so much if the wires done properly.

but in the end, is the cable back to db that matters.
*
I see, i have room that require 2 extension cords, plug on each other to extend the length and usage. I believe it is not safe to do so, hence i was thinking, if do looping will it be the same.
SUSceo684
post Nov 26 2019, 07:01 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(KahHoong @ Nov 26 2019, 06:51 PM)
I see, i have room that require 2 extension cords, plug on each other to extend the length and usage. I believe it is not safe to do so, hence i was thinking, if do looping will it be the same.
*
Depends on the extension cord, if its the old school one using 13A sockets it is better than the cheapo 4-gang ones (but actually all four is sharing a common metal rail which can loosen over time and cause bad connections).
TSKahHoong
post Nov 28 2019, 06:55 PM

Getting Started
**
Junior Member
124 posts

Joined: Sep 2011
QUOTE(ceo684 @ Nov 26 2019, 07:01 PM)
Depends on the extension cord, if its the old school one using 13A sockets it is better than the cheapo 4-gang ones (but actually all four is sharing a common metal rail which can loosen over time and cause bad connections).
*
im using a MR DIY 1.5m 5 gang ones hmm.gif Should i do looping? i also realize, the only socket in the room, they do looping on my 1hp inverter aircond. now i connect two 1.5m 5 gang socket thru the room, consist of all electrical appliances you can imagine in the room. sweat.gif
kimzee
post Nov 30 2019, 12:27 PM

Casual
***
Junior Member
411 posts

Joined: Jan 2018
QUOTE(KahHoong @ Nov 28 2019, 06:55 PM)
im using a MR DIY 1.5m 5 gang ones  hmm.gif  Should i do looping? i also realize, the only socket in the room, they do looping on my 1hp inverter aircond. now i connect two 1.5m 5 gang socket thru the room, consist of all electrical appliances you can imagine in the room.  sweat.gif
*
Regardless of looping or extension cord being used on a single point going to the db, just make sure the total current being consumed is less than 10A.

Layman example:

a) 1 A/c, 2 fans, few lights and 2 laptops should be fine

b) 1 a/c, 1 kettle, 1 iron, 2 fans, 1 mini toaster, 2 laptops esp if all used at the same time will be looking for trouble.


This is a safety margin you need to safeguard not too much on the mcb side but the wiring consideration as poor wiring (esp in the extension cords) can get overheated even before the 13A mcb trips.

 