 My house voltage fluctuates.. Help

views
     
TSsamjet
post Sep 17 2017, 12:23 AM, updated 9y ago

Getting Started
**
Junior Member
190 posts

Joined: May 2012
From: Kuala Lumpur
My landed type house using single phase system
All the lamps will flicker suddenly. Sometimes very frequent sometimes not at all
Today suddenly the lamp and fan became very bright and spin very fast, last for few seconds before went back to normal.

On my right side the house is vacant, I asked my neighbor on the left and he said he didn't experience all that, which I doubt very much

When all these things happens, I never switch on/off anything. Nothing.
The only thing I turn on all the time is the fridge. I switched off and flickers still happen.

Should I just call tnb? These happen for a week already.
Anyone of you have this kind of experience?
SUSempatTan
post Sep 17 2017, 06:01 AM

Regular
******
Senior Member
1,678 posts

Joined: Mar 2016


New housing area?...
CKKwan
post Sep 17 2017, 06:07 AM

Enthusiast
*****
Senior Member
886 posts

Joined: Dec 2004
Call TNB and ask them to check their sub-station.

It happened to me once and blown some of my appliances (including my neighbors).

Rempit stolen some metal parts inside the sub-station.
enduser
post Sep 17 2017, 08:55 AM

Regular
******
Senior Member
1,280 posts

Joined: Jan 2003
Borrow ur friend clamp meter and measure the voltage .
It should be +10 -6% variance from the 230v.
ozak
post Sep 17 2017, 09:49 AM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


Just call the TNB.
TSsamjet
post Sep 17 2017, 10:58 AM

Getting Started
**
Junior Member
190 posts

Joined: May 2012
From: Kuala Lumpur
QUOTE(empatTan @ Sep 17 2017, 06:01 AM)
New housing area?...
*
10 year ++

QUOTE(CKKwan @ Sep 17 2017, 06:07 AM)
Call TNB and ask them to check their sub-station.

It happened to me once and blown some of my appliances (including my neighbors).

Rempit stolen some metal parts inside the sub-station.
*
Only me kena.. Asked my next two units neighbor. They don't have these problem too

QUOTE(enduser @ Sep 17 2017, 08:55 AM)
Borrow ur friend clamp meter and measure the voltage .
It should be +10 -6% variance from the 230v.
*
I measured and it is normal
But i can't see the peak voltage coming so I didn't measure at that particular moment

QUOTE(ozak @ Sep 17 2017, 09:49 AM)
Just call the TNB.
*
Will do. Is it something to do with my meter and the two fuses around the meter?
TheMrBinary
post Sep 17 2017, 11:15 AM

63 72 69 70 70 6c 69 6e 67 20 64 65 70 72 65 73 73 69 6f 6e
*******
Senior Member
2,449 posts

Joined: Dec 2011
From: 27.132481, 73.086548


If you have PC better plug it off until the fluctuation problem is fixed.
It can damage your PC especially hardisk.
fireballs
post Sep 17 2017, 11:18 AM

10101
*******
Senior Member
5,648 posts

Joined: Mar 2012
Someone stealing neutral bar at the substation.
Report to tnb

In the mean time, be ready to kill the switches.
Else install a overvoltage relay to trip the main breaker
ozak
post Sep 17 2017, 12:49 PM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(samjet @ Sep 17 2017, 10:58 AM)
Will do. Is it something to do with my meter and the two fuses around the meter?
*
Nope. Mostly from TNB.

Either like CKKwan explain or voltage coming not stable.

Your neighbour might not have the same problem because his line is another line.


TSsamjet
post Sep 17 2017, 01:41 PM

Getting Started
**
Junior Member
190 posts

Joined: May 2012
From: Kuala Lumpur
QUOTE(TheMrBinary @ Sep 17 2017, 11:15 AM)
If you have PC better plug it off until the fluctuation problem is fixed.
It can damage your PC especially hardisk.
*
Thanks for the reminder

QUOTE(fireballs @ Sep 17 2017, 11:18 AM)
Someone stealing neutral bar at the substation.
Report to tnb

In the mean time, be ready to kill the switches.
Else install a overvoltage relay to trip the main breaker
*
Bracing myself

QUOTE(ozak @ Sep 17 2017, 12:49 PM)
Nope. Mostly from TNB.

Either like CKKwan explain or voltage coming not stable.

Your neighbour might not have the same problem because his line is another line.
*
I already called tnb. I stay in double storey Terrance house. Actually how they distribute the three phase wire?
ozak
post Sep 17 2017, 02:01 PM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(samjet @ Sep 17 2017, 01:41 PM)
Thanks for the reminder
Bracing myself
I already called tnb. I stay in double storey Terrance house. Actually how they distribute the three phase wire?
*
1phase to you. 2nd phase your Neighbour. 3rd next next Neighbour. And repeat again.

Sometime tnb trip only 1phase, but your Neighbour got power.
fireballs
post Sep 17 2017, 02:17 PM

10101
*******
Senior Member
5,648 posts

Joined: Mar 2012
it could also be one of your neighbour doing renovation.
the live wire shorted to neutral causing the voltage increase.

really recommended to get a voltage stabilizer for all your equipment. not very expensive
http://www.lazada.com.my/neuro-power-np-av...0.0.xeiVch&ff=1
weikee
post Sep 17 2017, 02:27 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(fireballs @ Sep 17 2017, 02:17 PM)
it could also be one of your neighbour doing renovation.
the live wire shorted to neutral causing the voltage increase.

really recommended to get a voltage stabilizer for all your equipment. not very expensive
http://www.lazada.com.my/neuro-power-np-av...0.0.xeiVch&ff=1
*
Short already, will have voltage drop. Won't have Voltage increase.
fireballs
post Sep 17 2017, 02:54 PM

10101
*******
Senior Member
5,648 posts

Joined: Mar 2012
QUOTE(weikee @ Sep 17 2017, 02:27 PM)
Short already, will have voltage drop. Won't have Voltage increase.
*
assuming ts pakai Red,

neighbour short Blue to neutral


ts will kena 415V red to neutral
lvloo
post Sep 17 2017, 02:58 PM

New Member
*
Junior Member
13 posts

Joined: Mar 2006


Ghost ?

Richard
post Sep 17 2017, 11:55 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(weikee @ Sep 17 2017, 02:27 PM)
Short already, will have voltage drop. Won't have Voltage increase.
*
A fluctuating voltage is usually a problem with the Phase/Neutral connection..

Get a competent to check the consumer side distribution network then if good then make complain to the supply authority..
kimirockz
post Sep 18 2017, 11:09 PM

On my way
****
Senior Member
638 posts

Joined: May 2009
call TNB for checking
Lynxx
post Sep 19 2017, 01:02 AM

New Member
*
Newbie
2 posts

Joined: Sep 2017
Voltage fluctuation likely caused by broken or missing Neutral connection at TNB substation.
For single phase residential houses, TNB will distribute the 3 phases evenly among the houses to achieve a statistically balanced loading. When loading on the 3 phases are balanced, a missing Neutral will not cause a voltage spike or a voltage dip. However, when the loading is unbalanced, the phase having a lighter load will see a increase in voltage and the phase having a heavier load will see a voltage dip.
Contact TNB to rectify the problem.

 