 Double Pole Switch (40A) meant for heater, with int. leaking current protection

views
     
TSShingkyo
post May 12 2015, 05:15 PM, updated 11y ago

Getting Started
**
Junior Member
62 posts

Joined: May 2006
I was looking thru one of the vendor in Malaysia (S***Sense) providing solution for lightning surge and I do see that they have RCD installation for heater (which is to be installed near to the heater unit). I therefore asked for a concealed solution and they told me that they can install something at a switch socket (as my house toilet are all with 15A socket point).

This is what the vendor showed me (I got the image online and get the exact match since I saw the Chinese word)
user posted image
This is to replaced the normal socket outlet the center bottom is where the heater 3-core wiring goes in. This one triggers at 6ma at 0.025ms

As I later on did a search on the Chinese shopping website and find something nicer
user posted image

As this one replace the double pole switch 20a, however it only triggers at 30ma at 0.025ms. I am just wondering if these devices are reliable and anyone tried it yet? I believe the socket type is tried otherwise why it can be found in Malaysia.
lucifah
post May 12 2015, 05:28 PM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


i'd never use any china made / brand electrical switches eventhough how beautiful they are

its potential electrical hazard. i'd not even use it as normal 13a plug, let alone handle a water heater current.

go for reputable brands like hager or clipsal


TSShingkyo
post May 12 2015, 06:05 PM

Getting Started
**
Junior Member
62 posts

Joined: May 2006
couldnt find any similar one from hager/clipsal/schneider..
ozak
post May 12 2015, 06:15 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


https://forum.lowyat.net/topic/2954371/+80
https://forum.lowyat.net/index.php?showtopi...post&p=46859762
https://forum.lowyat.net/index.php?showtopi...post&p=71697676
TSShingkyo
post May 12 2015, 06:33 PM

Getting Started
**
Junior Member
62 posts

Joined: May 2006
user posted image

This is the one that is on the vendor website. I asked my electrician if he can help install a junction box plus a RCD but he doesnt know anything about this thing... LoL...

So may I ask if I were to get a junction box, is it that the top left is live, right is neutral, bottom goes to heater wiring? The heater earth and the earth from db box just connect to the same screw holes?

Just like this video: https://www.youtube.com/watch?v=UIl9TXZm8Sw

Is it? I need to know more technically before I engage Safesense...
TSShingkyo
post May 13 2015, 03:19 PM

Getting Started
**
Junior Member
62 posts

Joined: May 2006
Anyway, just found out that China standards are RCD only, no ELCB at all. Just wonder why Msia still sticks to it, should have forcefully by law change to RCD at 30ma.
ozak
post May 13 2015, 03:41 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Shingkyo @ May 12 2015, 06:33 PM)
user posted image

This is the one that is on the vendor website. I asked my electrician if he can help install a junction box plus a RCD but he doesnt know anything about this thing... LoL...

So may I ask if I were to get a junction box, is it that the top left is live, right is neutral, bottom goes to heater wiring? The heater earth and the earth from db box just connect to the same screw holes?

Just like this video: https://www.youtube.com/watch?v=UIl9TXZm8Sw

Is it? I need to know more technically before I engage Safesense...
*
This installation is very dangerous. The box elcb don't have water proof. It too near to the heater shower. Better don't install in this way.

Either fix it on top which water cannot spray on it. Or outside the bathroom.
ozak
post May 13 2015, 03:43 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Shingkyo @ May 13 2015, 03:19 PM)
Anyway, just found out that China standards are RCD only, no ELCB at all. Just wonder why Msia still sticks to it, should have forcefully by law change to RCD at 30ma.
*
Msia already have RCD long. Even internal heater is using RCD now.
noobiedonkey
post May 13 2015, 03:46 PM

Enthusiast
*****
Senior Member
810 posts

Joined: Oct 2006
QUOTE(Shingkyo @ May 12 2015, 06:33 PM)
user posted image

This is the one that is on the vendor website. I asked my electrician if he can help install a junction box plus a RCD but he doesnt know anything about this thing... LoL...

So may I ask if I were to get a junction box, is it that the top left is live, right is neutral, bottom goes to heater wiring? The heater earth and the earth from db box just connect to the same screw holes?

Just like this video: https://www.youtube.com/watch?v=UIl9TXZm8Sw

Is it? I need to know more technically before I engage Safesense...
*
This does look very dangerous. Potential electric shock.
enduser
post May 13 2015, 03:54 PM

Regular
******
Senior Member
1,280 posts

Joined: Jan 2003
1) can download and refer here about guideline for electrical wirings in residential building

http://www.st.gov.my/images/article/polisi...uildings%20.pdf

2) requirement of rcd

http://www.st.gov.my/images/article/polisi...ing_systems.pdf

3) Prohibitory Notice for the Use of Earth Leakage Circuit Breaker (ELCB) Voltage Stabilizer

http://www.st.gov.my/index.php/policies/ci...stabilizer.html

TSShingkyo
post May 13 2015, 06:26 PM

Getting Started
**
Junior Member
62 posts

Joined: May 2006
QUOTE(ozak @ May 13 2015, 03:43 PM)
Msia already have RCD long. Even internal heater is using RCD now.
*
Why is it that the developer is using ELCB?
TSShingkyo
post May 13 2015, 06:28 PM

Getting Started
**
Junior Member
62 posts

Joined: May 2006
QUOTE(noobiedonkey @ May 13 2015, 03:46 PM)
This does look very dangerous. Potential electric shock.
*
I do see waterproof case in a shop.. so it is better I use the case n get my electrician to install?
TSShingkyo
post May 13 2015, 06:29 PM

Getting Started
**
Junior Member
62 posts

Joined: May 2006
QUOTE(enduser @ May 13 2015, 03:54 PM)
1) can download and refer here about guideline for electrical wirings in residential building

http://www.st.gov.my/images/article/polisi...uildings%20.pdf

2) requirement of rcd

http://www.st.gov.my/images/article/polisi...ing_systems.pdf

3) Prohibitory Notice for the Use of Earth Leakage Circuit Breaker (ELCB) Voltage Stabilizer

http://www.st.gov.my/index.php/policies/ci...stabilizer.html
*
So the installer in it is certified? How much do they charge? Engaged before?

enduser
post May 13 2015, 07:01 PM

Regular
******
Senior Member
1,280 posts

Joined: Jan 2003
QUOTE(Shingkyo @ May 13 2015, 06:29 PM)
So the installer in it is certified? How much do they charge? Engaged before?
*
wireman / pendawai 1 fasa pw1 or pendawai 3 fasa pw3

Refer here http://www.st.gov.my/index.php/application...ns/wireman.html
ozak
post May 14 2015, 09:58 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Shingkyo @ May 13 2015, 06:26 PM)
Why is it that the developer is using ELCB?
*
Are you talking about the old house?
ozak
post May 14 2015, 10:00 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(noobiedonkey @ May 13 2015, 03:46 PM)
This does look very dangerous. Potential electric shock.
*
What kind of installer can comeout such an idea that put a non waterproof ELCB so near to the shower. Crazy.
TSShingkyo
post May 14 2015, 10:03 AM

Getting Started
**
Junior Member
62 posts

Joined: May 2006
QUOTE(ozak @ May 14 2015, 09:58 AM)
Are you talking about the old house?
*
New house... in Nusajaya, Johor.

ozak
post May 14 2015, 10:06 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Shingkyo @ May 14 2015, 10:03 AM)
New house... in Nusajaya, Johor.
*
Print out the website from Enduser and show it to the developer. That is the TNB new rules.

My house already using RCD for over 10yrs.
weikee
post May 14 2015, 10:06 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(Shingkyo @ May 12 2015, 06:33 PM)
user posted image

This is the one that is on the vendor website. I asked my electrician if he can help install a junction box plus a RCD but he doesnt know anything about this thing... LoL...

So may I ask if I were to get a junction box, is it that the top left is live, right is neutral, bottom goes to heater wiring? The heater earth and the earth from db box just connect to the same screw holes?

Just like this video: https://www.youtube.com/watch?v=UIl9TXZm8Sw

Is it? I need to know more technically before I engage Safesense...
*
If you look at the picture, top left, there is this water valve, and what happen if this water valve leak? water will go directly to the elcb. What a "Professional" installer. Behind the ELCB is water pipe, is also crazy.
noobiedonkey
post May 14 2015, 10:13 AM

Enthusiast
*****
Senior Member
810 posts

Joined: Oct 2006
QUOTE(ozak @ May 14 2015, 10:00 AM)
What kind of installer can comeout such an idea that put a non waterproof ELCB so near to the shower. Crazy.
*
Well, even if waterproof also, I don't think water and electric are meant to play together
TSShingkyo
post May 14 2015, 10:14 AM

Getting Started
**
Junior Member
62 posts

Joined: May 2006
Also, if let's say I install a waterproof case, it is OK to install a RCD there? My unit is all with 15A socket, so can this socket connect to RCD and this RCD connect to heater? I assume it is OK while outside the toilet, there is normal double pole switch.

Should I use normal 1P+N RCD or 2P RCD?
TSShingkyo
post May 14 2015, 10:16 AM

Getting Started
**
Junior Member
62 posts

Joined: May 2006
QUOTE(ozak @ May 14 2015, 10:06 AM)
Print out the website from Enduser and show it to the developer. That is the TNB new rules.

My house already using RCD for over 10yrs.
*



Meaning DB box should be fitted with a RCD?

TSShingkyo
post May 14 2015, 10:17 AM

Getting Started
**
Junior Member
62 posts

Joined: May 2006
QUOTE(weikee @ May 14 2015, 10:06 AM)
If you look at the picture, top left, there is this water valve, and what happen if this water valve leak? water will go directly to the elcb.  What a "Professional" installer. Behind the ELCB is water pipe, is also crazy.
*
So is it OK if it is installed above e water outlet?
ozak
post May 14 2015, 10:23 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Shingkyo @ May 14 2015, 10:14 AM)
Also, if let's say I install a waterproof case, it is OK to install a RCD there? My unit is all with 15A socket, so can this socket connect to RCD and this RCD connect to heater? I assume it is OK while outside the toilet, there is normal double pole switch.

Should I use normal 1P+N RCD or 2P RCD?
*
Ain't it ugly to install such protector there? beside not safe.

Try install ontop far away or outside the bathroom. Get a proper design RCD which look better. I already post some example above.

If have 2P, than get the 2P.


ozak
post May 14 2015, 10:23 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Shingkyo @ May 14 2015, 10:16 AM)
Meaning DB box should be fitted with a RCD?
*
Yes.
TSShingkyo
post May 14 2015, 10:25 AM

Getting Started
**
Junior Member
62 posts

Joined: May 2006
QUOTE(ozak @ May 14 2015, 10:23 AM)
Yes.
*
It means we are shortchanged? Anyway, replacement is to just replace this ELCB with a RCD right?

TSShingkyo
post May 14 2015, 10:32 AM

Getting Started
**
Junior Member
62 posts

Joined: May 2006
The model number is CE240B from Hager. Is this ELCB or RCD? Because I see this word Earth Fault Indicator...
ozak
post May 14 2015, 10:32 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Shingkyo @ May 14 2015, 10:25 AM)
It means we are shortchanged? Anyway, replacement is to just replace this ELCB with a RCD right?
*
Yup. Ask your developer if it is a new house.
ozak
post May 14 2015, 10:34 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Shingkyo @ May 14 2015, 10:32 AM)
The model number is CE240B from Hager. Is this ELCB or RCD? Because I see this word Earth Fault Indicator...
*
"A residual-current device (RCD), or residual-current circuit breaker (RCCB) is an electrical wiring device that disconnects a circuit whenever it detects that the electric current is not balanced between the energized (line) conductor(s) and the return (neutral) conductor"

Is is a RCD.
TSShingkyo
post May 14 2015, 10:41 AM

Getting Started
**
Junior Member
62 posts

Joined: May 2006
Oh. So it is my misunderstanding? SO even a RCD also displays e earth fault indicator?
weikee
post May 14 2015, 10:42 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(Shingkyo @ May 14 2015, 10:17 AM)
So is it OK if it is installed above e water outlet?
*
Only if the pipe not in the wall, and way above or away from water reachable area. Last time we had a maid when she clean the bathroom, she was till the top tiles that mean the ceiling also wet smile.gif can you imagine such maid wash this bathroom. Sure get electrocuted.

 