Double Pole Switch (40A) meant for heater, with int. leaking current protection
|
weikee
|
May 14 2015, 10:06 AM
|
|
QUOTE(Shingkyo @ May 12 2015, 06:33 PM)  This is the one that is on the vendor website. I asked my electrician if he can help install a junction box plus a RCD but he doesnt know anything about this thing... LoL... So may I ask if I were to get a junction box, is it that the top left is live, right is neutral, bottom goes to heater wiring? The heater earth and the earth from db box just connect to the same screw holes? Just like this video: https://www.youtube.com/watch?v=UIl9TXZm8SwIs it? I need to know more technically before I engage Safesense... If you look at the picture, top left, there is this water valve, and what happen if this water valve leak? water will go directly to the elcb. What a "Professional" installer. Behind the ELCB is water pipe, is also crazy.
|
|
|
|
|
|
weikee
|
May 14 2015, 10:42 AM
|
|
QUOTE(Shingkyo @ May 14 2015, 10:17 AM) So is it OK if it is installed above e water outlet? Only if the pipe not in the wall, and way above or away from water reachable area. Last time we had a maid when she clean the bathroom, she was till the top tiles that mean the ceiling also wet  can you imagine such maid wash this bathroom. Sure get electrocuted.
|
|
|
|
|