You have two db box? Each 32amps two already 64amp
Single Phase wiring amp
Single Phase wiring amp
|
|
Jul 12 2013, 09:17 PM
Return to original view | Post
#1
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
12,019 posts Joined: Jan 2003 |
You have two db box? Each 32amps two already 64amp
|
|
|
|
|
|
Jul 12 2013, 09:26 PM
Return to original view | Post
#2
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
12,019 posts Joined: Jan 2003 |
QUOTE(empire23 @ Jul 12 2013, 09:18 PM) 3 air con, 2 fridges and 2 water heaters definitely will tarpau your supply and set your house on fire if you happened to run all of them at the same time lol. I don't even need the AS3000 standard to tell me that. I got two storage heater 6 Ac and 1fridge. I don't see any problem. Need to know the max running current each and the concurrent running equipments.Might I suggest going to 3 phase power instead? Split the phases and balance the load correctly. 2 heater and 3 Ac assume Ac is 1.5hp is about 10000watt additional fridge (depend the size) maybe 1500watt so total about 11500watt unless he got 2000w light if not is not an issue. Of course all this will be issue if owner switch on all the time and equipments running max load all the time. Proper cabling is critical. In coming 63amps it will able handle 63 for short period of time. Most important the cable need to handle the load. This post has been edited by weikee: Jul 12 2013, 09:27 PM |
|
|
Jul 12 2013, 09:34 PM
Return to original view | Post
#3
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
12,019 posts Joined: Jan 2003 |
|
|
|
Jul 12 2013, 10:19 PM
Return to original view | Post
#4
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
12,019 posts Joined: Jan 2003 |
QUOTE(mikicun @ Jul 12 2013, 09:41 PM) never assume when it come to electricity... Can use for 3 units of 13Amp face plate, but if 3 running at high current it will trip the MCB. Depend the load.2hp is only around 1.5kw and not 10kw.. and theres a "faktor pelbagai" (diversity factor) for electrical calculation... example: 1 unit of 20A MCB and be use for up to 3 unit of 13A S/S/O.. |
|
|
Jul 12 2013, 10:21 PM
Return to original view | Post
#5
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
12,019 posts Joined: Jan 2003 |
QUOTE(empire23 @ Jul 12 2013, 09:35 PM) 12kW would be around 50+ amps which is way over what the protection device can handle at 32 amps. Single 32 Amps will not go up to 12kw, but with two 32amp he can go up to 12kw without issue if load are properly distributed. Proper cabling is important, but you'll have to size your protection (be it circuit breaker or RCD correctly), also water heaters should always have an RCD instead of a standard SP/DP circuit breaker to prevent death by electrocution. The last thing I want to do is die naked. One should also note the size of ground wiring and staking and resistance required for the load being used. If you supply cabling is 20 mil and can carry 150 amps oso no use if you neutral conductor is small and your neutral block is tiny. Electricity isn't just about current. Std practice is having same wire thickness for Neutral and Live. Than again, if you notice incoming from TNB have 3 Live wires (RYB), and one Neutral wires. Every wonder why Neutral don't need the total thickness of 3 Live wires? This post has been edited by weikee: Jul 12 2013, 10:23 PM |
|
|
Jul 12 2013, 10:32 PM
Return to original view | Post
#6
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
12,019 posts Joined: Jan 2003 |
QUOTE(mikicun @ Jul 12 2013, 09:34 PM) i can only see the 32A fuse.. which is more than enough for a house.. In practice, we don't use 240v, is safer to use 230v because TNB do not guarantee supply to be at 240v constant. I know the industry use to have fluctuate and can be -6% to +10%, residential should be very far off.32A x 240V = 7680W maximum load your DB can handle.. ur total connected load is..? lighting, socket outlet, fridge, tv, a/c, w/htr and so on...? |
|
|
|
|
|
Jul 12 2013, 10:33 PM
Return to original view | Post
#7
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
12,019 posts Joined: Jan 2003 |
|
|
|
Jul 12 2013, 11:24 PM
Return to original view | Post
#8
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
12,019 posts Joined: Jan 2003 |
QUOTE(mikicun @ Jul 12 2013, 10:36 PM) correct... the neutral cable already been calculated for... so your point is... Just to make sure we are at same page what about the earthing? the earthing is always the smallest cable among all..? Earthing is usually no load and will trip even with small load. If earthing to carry load is acting like neutral. If you want to try can bypass the ELCB, try Live + Earth equipment still power up. Neutral and earth/ground are identical both go back to the earth, house just that house ground are nearer compare to neutral ground. Not sure if you understand what i mean. I see how some people do creative wiring to reduce the bill by playing around with earthing |
|
|
Jul 12 2013, 11:36 PM
Return to original view | Post
#9
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
12,019 posts Joined: Jan 2003 |
QUOTE(sapphirejohn @ Jul 12 2013, 10:42 PM) I don't think I have to 32A DB because the upper flr does not have the 32A circuit breaker. Than you need to check and I notice there are 2 diff color for the MCB? 01) Your master fused (beside the meter) is it 63amps or smaller. If smaller you also need to check the wires after the fused can it support up to 63 amps. 02) From the Master fused to the house MCB/circuit breaker you need to check if the wires are thick enough to support 63amps. If all can support 63amps than you can just change to bigger fused and bigger. Best ask your electrician to check If you don't understand what i mean. |
|
|
Jul 13 2013, 12:25 AM
Return to original view | Post
#10
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
12,019 posts Joined: Jan 2003 |
QUOTE(empire23 @ Jul 13 2013, 12:11 AM) He should survey what kind of power is coming in before shoving 2x 32 amp boxes in there. A little bit of homework saves a lot of issues in the long run. On many industrial 3 phase applications I've done, we sometimes keep the neutral skinny if we are connecting to a well balanced load to save costs as allowable by AS3000 or other relevant standards. My early post was assuming he have 2x 32amps, picture was not clear and seeing from a smart phone is not easy. If its only 32amp, TS need to properly check the incoming cables until the DB.You don't need the same size of neutral conductor for a 3 phase because Wye 3 phase systems are inherently balanced. Thus if you correctly balance a 3 phase system you'll never need more than the sum of 1 output conductor (actually you won't even need a neutral). That's why TS should get a proper electrician to survey everything. A good electrician will figure the best way to balance everything. You'll never get perfect balance, but getting close is best. Also an electrician can see if anyone has daisy chained the circuit which is very common in houses, whereby instead of wiring in new cables, people just daisy it off the nearest circuit. If you're daisying off an already heavily loaded circuit, add something like a fridge will create problems. 3 Phases equipments will have (should have) well balance. Problem will be house uses 3 phases incoming. I never like daisy chain (usually in china-man term is looping), still prefer direct. |
| Change to: | 0.0566sec
0.56
6 queries
GZIP Disabled
Time is now: 15th December 2025 - 03:25 PM |