QUOTE(weikee @ Jul 12 2013, 09:26 PM)
I got two storage heater 6 Ac and 1fridge. I don't see any problem. Need to know the max running current each and the concurrent running equipments.
2 heater and 3 Ac assume Ac is 1.5hp is about 10000watt additional fridge (depend the size) maybe 1500watt so total about 11500watt unless he got 2000w light if not is not an issue. Of course all this will be issue if owner switch on all the time and equipments running max load all the time.
Proper cabling is critical. In coming 63amps it will able handle 63 for short period of time. Most important the cable need to handle the load.
12kW would be around 50+ amps which is way over what the protection device can handle at 32 amps.
Proper cabling is important, but you'll have to size your protection (be it circuit breaker or RCD correctly), also water heaters should always have an RCD instead of a standard SP/DP circuit breaker to prevent death by electrocution. The last thing I want to do is die naked.
One should also note the size of ground wiring and staking and resistance required for the load being used. If you supply cabling is 20 mil and can carry 150 amps oso no use if you neutral conductor is small and your neutral block is tiny.
Electricity isn't just about current.