 Inverter aircon using non-inverter piping?

views
     
ozak
post May 16 2012, 11:55 AM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(coconutzz @ May 16 2012, 11:38 AM)
This is just my personal experience and opinion..

I m going to install concealed NORMAL Piping for my renovation. This has been decided after I have asked a few questions to myself and also consulted some friends in the AC industry.

1) Are you installing Inverter ACs? Do you need Inverters?

2) Budget - Inverter piping is more expensive by about RM4-5 /
ft....might end up RM1-2k more ure paying depending on units and distance of piping

3) Inverter ACs maintenance - R410 is more expensive. Cleaning and chemical washing..we're looking at RM200-RM300 or more for 1HP AC

4) WHen is R22 phasing out...my friend told me approx. 10 years ..assuming he is correct...i think 10 yrs...is more than enuff

5) Inverter will only reduce power usage if it's continuously on for maybe about 8 hours or more

-------------------------------------

My Conclusion:

1) Inverter only suitable for my rooms cos I will on more than 8 hours...so for my rooms I m going to use Daikin Inverter that runs on R22 and normal piping

2) The rest are all using normal AC
Hope that helps smile.gif
*
Either 8hr use or less, overtime the inverter will payback the cost. Compare non inverter. The cost of the pipe and the aircon won't different alot.

I m using 1.5hp inverter with about 20ft of pipe. The cost + install is RM2200. With everyday usage of 8hr, monthly save is about rm40-45. 1yrs save me rm540. Service 1x peryear is rm100. It take me 2yrs to get back my money save compare non inverter even include service. The amount save is I compare with my last time non inverter unit.

So either 2hr or 8hr use, I still will go for inverter. Payback either long or short. Just my experience.

R410 and R22 gas is depend how enviroment friendly you are. If you care and want to contribute a bit to the enviroment, than change it. It doesn't cost you much. You don't need to top up every year.
Lara~
post May 16 2012, 04:07 PM

Getting Started
**
Junior Member
80 posts

Joined: Oct 2007
QUOTE(ozak @ May 16 2012, 11:55 AM)
Either 8hr use or less, overtime the inverter will payback the cost. Compare non inverter. The cost of the pipe and the aircon won't different alot.

I m using 1.5hp inverter with about 20ft of pipe. The cost + install is RM2200. With everyday usage of 8hr, monthly save is about rm40-45. 1yrs save me rm540. Service 1x peryear is rm100. It take me 2yrs to get back my money save compare non inverter even include service. The amount save is I compare with my last time non inverter unit.

So either 2hr or 8hr use, I still will go for inverter. Payback either long or short. Just my experience.

R410 and R22 gas is depend how enviroment friendly you are. If you care and want to contribute a bit to the enviroment, than change it. It doesn't cost you much. You don't need to top up every year.
*
Ozak wat brand of inverter a/c r u using? Service is only RM100/yr?
ozak
post May 16 2012, 04:24 PM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(Lara~ @ May 16 2012, 04:07 PM)
Ozak wat brand of inverter a/c r u using? Service is only RM100/yr?
*
Panasonic. Actually only cost rm75 the last I service back last year. The service is just takedown flush and clean the condenser and rotor. And outdoor unit clean. The cheap cost is not related to the aircon brand.
weikee
post May 16 2012, 07:21 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(lingleeyen @ May 16 2012, 11:40 AM)
Please note, there is no soldering involved in the installation of Room Air-Cond. It will involves only flaring.


Added on May 16, 2012, 11:46 am
Check it from the label on unit.


Added on May 16, 2012, 11:49 am
Use "venier" clipper, measure and match it against the standard piping thickness in the market. I am not sure if the "venier" is spell as "venier", but it sounded like that.


Added on May 16, 2012, 11:55 am
Inverter start saving after the room condition has stabilised and the compressor RPM tunes down and slows down without needing to  start stopping, hence saves energy. To achieve stable room condition, you need approximately 3 hours or less (not 8 hours or more), unless you open and close your door very frequest through put the time. Maintenance of Inverter AC is more expensive because of the refrigerant. Chemical used to wash the coil will be the same. Piping is also more expensive. Depending how is your ussage, inverter can be a good or bad choice. My view is that there is no point getting an inverter AC for living room which only uses AC for 1 hour. Can't save energy.
*
copper pipe can be solder, my previous unit in my mom house have to be solder because the indoor unit was twisted. So far no problem with leaking.

This post has been edited by weikee: May 16 2012, 07:23 PM
lingleeyen
post May 16 2012, 08:03 PM

Regular
******
Senior Member
1,376 posts

Joined: Jan 2011
QUOTE(weikee @ May 16 2012, 07:21 PM)
copper pipe can be solder, my previous unit in my mom house have to be solder because the indoor unit was twisted. So far no problem with leaking.
*
Copper tubes of course can be welded. What I mean is that under normal circumstances and normal installation, room air conds are just simple plug and play. Also, welding of copper pipes then operates without pre-testing does not really garuantee the quality of the weld.

BTW, please enlighten me on how is the indoor unit twisted?
weikee
post May 16 2012, 11:33 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(lingleeyen @ May 16 2012, 08:03 PM)
Copper tubes of course can be welded. What I mean is that under normal circumstances and normal installation, room air conds are just simple plug and play. Also, welding of copper pipes then operates without pre-testing does not really garuantee the quality of the weld.

BTW, please enlighten me on how is the indoor unit twisted?
*
Twisted because it was taken out for cleaning the worker must have accidentally bend the copper. Boss cut the affected, and re solder. I think the correct word for copper joining is solder, not weld.
skng03
post May 16 2012, 11:40 PM

Regular
******
Senior Member
1,450 posts

Joined: Oct 2008


Not just solder, flared then solder nod.gif
lingleeyen
post May 17 2012, 12:34 PM

Regular
******
Senior Member
1,376 posts

Joined: Jan 2011
QUOTE(weikee @ May 16 2012, 11:33 PM)
Twisted because it was taken out for cleaning the worker must have accidentally bend the copper. Boss cut the affected, and re solder.  I think the correct word for copper joining is solder, not weld.
*
The correct term in joining 2 Copper pipes is weld. Solder is when you do KH projects, soldering the IC or capacitor
kelvyn
post May 17 2012, 01:52 PM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
The correct terminology would be soldering the copper tubing. A propane torch is the primary tool used to solder copper tubing.
As the copper tubing is soft, the heat from welding process would melt the copper piping...

ozak
post May 17 2012, 02:03 PM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(kelvyn @ May 17 2012, 01:52 PM)
The correct terminology would be soldering the copper tubing. A propane torch is the primary tool used to solder copper tubing.
As the copper tubing is soft, the heat from welding process would melt the copper piping...
*
Eh... I thing it is not the correct way. It did need a propane torch to heat up the 2 copper pipe joint. But not melt it. A solder wire lead is need to melt and joint up the copper pipe. And you need a flux to clean up the joint side.
aeiou228
post May 17 2012, 02:43 PM

Look at all my stars!!
*******
Senior Member
5,867 posts

Joined: Feb 2006
I paid RM300 for standard installation fee for my new 1.5hp inverter aircon. If the installer cheat on the copper piping thickness, how can I spot the difference ?
weikee
post May 18 2012, 08:43 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(ozak @ May 17 2012, 02:03 PM)
Eh... I thing it is not the correct way. It did need a propane torch to heat up the 2 copper pipe joint. But not melt it. A solder wire lead is need to melt and joint up the copper pipe. And you need a flux to clean up the joint side.
*
Yes. Anyway some use the term welding, but in actual copper you can't weld well unless we have a ultrasonic welder which make me wonder which a/c installer want to invest such machine.
ozak
post May 18 2012, 10:45 PM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(weikee @ May 18 2012, 08:43 PM)
Yes. Anyway some use the term welding, but in actual copper you can't weld well unless we have a ultrasonic welder which make me wonder which a/c installer want to invest such machine.
*
Never see ppl using ultrasonic before. For copper welding, the old type is using something like copper lead. Blaze the copper joint till red and melt the copper lead to the joint. I can't remember the name as quite sometime I never done it.

New way just heat it up and use solder lead. Both need flux and sandpaper to be clean well.
weikee
post May 18 2012, 10:55 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(ozak @ May 18 2012, 10:45 PM)
Never see ppl using ultrasonic before.  For copper welding, the old type is using something like copper lead. Blaze the copper joint till red and melt the copper lead to the joint. I can't remember the name as quite sometime I never done it.

New way just heat it up and use solder lead. Both need flux and sandpaper to be clean well.
*
Ultrasonic is use in high tech electronic industry. That is called welding. Even for plastic too.
ozak
post May 18 2012, 11:14 PM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(weikee @ May 18 2012, 10:55 PM)
Ultrasonic is use in high tech electronic industry. That is called welding. Even for plastic too.
*
Yup. My working place have a lot of this ultrasonic welding. Kena burn by it too.
Lara~
post May 22 2012, 03:06 PM

Getting Started
**
Junior Member
80 posts

Joined: Oct 2007
I suppose its not a problem to use non-inverter aircons with inverter type piping, rite?
Coz my house comes wif all inverter type piping..
PJusa
post May 22 2012, 03:55 PM

Look at all my stars!!
*******
Senior Member
2,027 posts

Joined: Jan 2003
From: PJ
if the pipes connect it should be no problem. it's just that the pipe needs to be able to withstand the refridgerant's pressure. since non-inverter pressure is lower i dont see any problem.
YJYYEE
post Jun 10 2012, 01:59 AM

Getting Started
**
Junior Member
145 posts

Joined: Feb 2011
From: Selangor


QUOTE(lingleeyen @ May 16 2012, 11:32 AM)
Dear All,

The below will be my experience speaking.

R22 (HCFC) gas/ Freon/ refrigerant is what you use in most of the non-inverter models, regardless of brands. The R22 has lower operating pressure, hence it states that you need thinner gas tubes. Top up on this kind of is possible.

R410A (HFC) is the “new” gas where the operating pressure is approimately 1.6 to 1.8 times higher than R22, hence some of the manufacturer is recommending thicker tubes. However, these thicker tubes is not easily available in the market according to market spec, hence the price for these tubes will be high and not lots of installer carries stock. Top up on this kind of refrigerant is also possible, as the boiling point for all the refrigerant mixture is almost the same.

CFC is no longer available in the market. Banned long ago because of the effect to the environment. Production of R22 has been stopped in early this year, and what you get in the market now is recycled R22. Manufacturer assume that the price of R22 will go up as short of supply.

R410A is environmental friendly refrigerant as it does not deplete ozone/ zero ozone depletion potential (zero ODP). However, it still has certain level of Global Warming Potential (GWP). R22 on the other has a very low ODP, and relatively lower GWP compared to R410A

Installer will tell you the below 3 things about inverter pipings:-

1) Nothing will happen if you use thinner tubes, all my customer did not complain
2) Thick tubes I don’t have
3) I buy the tubes for you but it will be bloody expensive

I will say, if you already have new set of tubes installed in the wall, I will say go for it. Some of the manufacturer over-spec-ed their pipe thickness to cover their ass just in case things happened. My experience is the 0.33mm tube thickness (1/4”), 0.56mm tube thickness (1/2”) can with stand 600pascal testing pressure (approximately 450pascal operating pressure). The worst thing that will happen is that the tube will crack and gas will leak. No big deal actually. Since you have already concealed the wall, it is the matter of hacking it now or later. What if the tube did not crack? I am using inverter units with standard piping. Nothing happens…yet. If you are installing new, just get a thick pipe, so that there is no worry.

Tips for new installation of Inverter AC.

1) Make sure that they use the correct tool. For inverter AC, they will have a special gauge for inverter units
2) If you are recharging/ top up your R410A, make sure that the colour of the refrigerant tong is in pink, not other colour. R410A refrigerant only has one packaging. If they tell you can be used, chase them away. Don’t let them charge. Please note also brand new ACs do not need to add gas unless you exceeded their standard pipe length. If your installer says need to add gas, evaluate the piping length. If the piping does not exceed the standard length, and your installer says you need to add, he is conning you.
3) Just in case in any circumstance you are releasing all and re-charging the refrigerant to full, make sure that you know what is the initial amount of refrigerant (before 1st start up), so that you can put a weighing machine below the tong to ensure the real amount of refrigerant goes in. Installer in Malaysia uses only the gauge to measure. This is not wrong, but not really accurate. The pressure goes up by certain level, does not mean that the gas has go in at a certain weight.
4) Make sure that the refrigerant tong is at the right position (standing or reverse standing for certain tong model), to ensure gas form refrigerant is charged SLOWLY into the AC, not liquid. Liquid form of refrigerant will damage compressor at start up.
5) Make sure that the flaring of piping is done properly, no crack, no uneven, etc and please read the manual
6) Make sure your installer vacuum the system (standard procedure) at least for 20 minutes (not Malaysia standard procedure) to take out any residue in the piping before releasing the refrigerant from outdoor to the system. Imagine copper pipe cutting debris goes into your compressor.
7) If you have compressor burnt out and you wish to change AC, I will say dump the existing piping. If there is no choice, get your installer to vacuum the system kao kao kao kao before starting up. This is because burnt out compressor will have lots of “burn dirt” from compressor, sticking on to the pipes, and affecting the performance. Even if the performance is not your concern, the debris which still sticks to the pipe might come out one day and goes to your compressor. Compressor dies fast.
8) After the unit has been start up, the installer will run AC with full blast and lowest set temperature. This is standard procedure, but the important thing is to make sure the refrigerant runs to all indoor unit’s piping, to make sure that there is no clogging. How to do it? Only by touching every portion of fins to feel if it is cold and to see if all the parts has condensation water formed on it. Please differentiate between dripped condensation water and formed condensation water. If everything is OK, you are good to go.
*
Hi, could you recommend any contractor that match all the above criteria?...and if got price also better..coz i see before those useless contractor that didn't vacuum the pipes which cause the compressor to burn even thought its a new ac...smile.gif

Eng_Tat
post Jun 10 2012, 07:36 AM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


for ppl who want to do conceal, just to share the price of copper pipe 1/4+1/2" .71mm cooper tubing 15meter long is around rm243 for korean smartco pipe, if china pipe is around rm190.
lingleeyen
post Jun 10 2012, 10:39 AM

Regular
******
Senior Member
1,376 posts

Joined: Jan 2011
QUOTE(weikee @ May 18 2012, 08:43 PM)
Yes. Anyway some use the term welding, but in actual copper you can't weld well unless we have a ultrasonic welder which make me wonder which a/c installer want to invest such machine.
*
Oh. My mistake. The correct terminology is brazing. Not welding, not soldering definitely.