views
     
Eng_Tat
post Mar 20 2012, 03:53 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


i know 3 phase wiring is 3 16mm live wire + 25mm N wire into one db 3phase elcb. can we actually do this instead using 3+1 we do 1+1 16mm L+ 16mm n wire into 3 diffrrent db from the meter (each phase get each db (house got 3 db)) means we pull 6 wires instead of normal 4. ?
Eng_Tat
post Mar 20 2012, 11:18 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


sorry i dont really know how to draw cry.gif

Current set up single phase
Meter --- L 16mm+ N 16mm--- DB1 ---loop to ---DB2

Normally 3 Phases if I am not mistaken
Meter --- L 3x 16mm+ N 25mm (not sure is the correct size for N, read some where else)---DB1 ---loop to DB2

Can I just add 4 new 16mm wires (Examples)
Meter --- Phase 1 --- L 16mm+ N16mm to DB1 ---loop to DB2 (dont need to hack or disturb current wiring) (1x1.5hp ac + 1wh+ all lightings)
Meter --- Phase 2 --- L 16mm+ N16mm to DB3 (3x1.5hp ac + 1 Wh + Kitchen appliances + 10 13A Socket)
Meter --- Phase 3 --- L 16mm+ N16mm to DB4 (3x1.5hp ac + 2 Wh + 10 13A Socket)

QUOTE(ozak @ Mar 20 2012, 04:05 PM)
Don't understand. Can you draw out?
*
Eng_Tat
post Mar 21 2012, 09:35 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


wei kee, small house only 22*75 5room+4bathroom. so house need 4wh. 7-8 ac. i wont pasang straight all the ac, except their piping and wiring.
ori wiring only got 1wh + 1ac point sad.gif so really need to do wiring.
Eng_Tat
post Mar 22 2012, 10:46 AM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


I plan to use intant wh one. i think its alot cheaper. wh with pump is around 450-550. so total will be around rm1800-2200. if used solar one need to do piping which would cost alot of money. now i would only need to do wiring for 3 toilet, which is only around 350 additional.

*when i move in i will only install 2unit first...budget problems

QUOTE(weikee @ Mar 21 2012, 09:51 PM)
You plan to use instant or storage WH? If storage maybe you can consider solar since you have 4 unit. You save the money from 3 phase and use  it on Solar. Maybe top up 1 to 2k
*
Eng_Tat
post Mar 22 2012, 03:55 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


wei kee, those diagram is for one db with 3 rows?
Eng_Tat
post Mar 22 2012, 04:18 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


just starting to survey for products... hager 20A mcb is rm7.80 each. is the correct price? while eps/maxguard or amber is just rm4. hager can be used in sg but eps brand is not approve in sg.
Eng_Tat
post Mar 22 2012, 04:31 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


erm, this one based on the boss is ori and sirim approve, selling at dealer pricing. usually the price is hw much? maybe later i snap some photo and see.

QUOTE(ozak @ Mar 22 2012, 04:26 PM)
Copy 1? So cheap. Better compare price and check.
*
Eng_Tat
post Mar 22 2012, 05:01 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


honestly i got no idea, its 1pole 20A mcb. what is the normal pricing? later abit i take photo of it.

QUOTE(weikee @ Mar 22 2012, 04:38 PM)
Did he put the decimal point wrong? 7.80 for hager is dirt cheap.
*
Eng_Tat
post Mar 22 2012, 09:28 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


this is the picture of the mcb, any way to know is clone?


Attached thumbnail(s)
Attached Image Attached Image
Eng_Tat
post Mar 23 2012, 08:38 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


have no idea where is that hager made from, not written any where on the mcb, accept written made by hager. btw one inch white pipe can insert how many 4mm wires ideally. i know can the pipe sure can fit up to 12-15 wires. what is the different with grey pvc pipes?
Eng_Tat
post Jun 18 2012, 10:01 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


anyone knows is three phase tariff is same as single face?
Eng_Tat
post Jul 14 2012, 09:11 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


sorry.

This post has been edited by Eng_Tat: Jul 14 2012, 09:12 PM
Eng_Tat
post Aug 17 2014, 09:43 AM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


Your double poll switch is 63A, but the elcb is 40A. You should used 63A elcb as well normally. Do you used water heater as well, if yes, you should used separate Elcb for the heater, sensitivity rated 0.03.

QUOTE(S'aimer @ Aug 16 2014, 12:34 PM)
Took a look at my DB and It appears that I have 63A for my main fuse.

But realised that I don't see any fiber ready connection in storeroom or a telephone port at the back?
*
Eng_Tat
post Aug 17 2014, 11:56 AM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


Double pole is to cut off incoming from meter both N & L before going to the ELCB.

QUOTE(S'aimer @ Aug 17 2014, 11:15 AM)
Yes I have 1 water heater.

I also have a vitroceramic hob besides a built in oven.

What does a 63A double pole switch do?
*
Eng_Tat
post Aug 17 2014, 01:32 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


if your load is more then 40A, then you should change the the main ELCB, also i would recommend to put in another ELCB for heater.

QUOTE(S'aimer @ Aug 17 2014, 12:23 PM)
Hmm so what should I do then?
*
Eng_Tat
post Aug 17 2014, 04:13 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


yes, but many Malaysian i notice don't really know's about putting additional safety for their WH...

QUOTE(weikee @ Aug 17 2014, 03:32 PM)
Rccb will be better. It have to wired on the output to the water heater. Not in the distribution box.
*
Eng_Tat
post Aug 17 2014, 10:28 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


yes that's true that most wh comes with elcb, but we do still hear ppl get electrocuted. a proper stand alone elcb/rccb cost more than rm100, and we are not sure about the quality that comes with wh units as well. also a proper 13A socket is suppose to be paired with .03A sensitivity RCCB instead .1A sensitivity RCCB which is common practice in MY.

QUOTE(jimmylim85 @ Aug 17 2014, 08:29 PM)
The reason is simple, all Water Heater comes with ELCB built in. So electrician just provide one 20A isolator switch. Adding a RCCB will be too bulky and customer complains about it.

Anyway to learn more about the electrical safety circuit breakers. Refer here :

http://electrical-engineering-portal.com/w...b-elcb-and-rccb
*
Eng_Tat
post Sep 15 2014, 03:01 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


You can used armoured 4 core 16mm size. Or even better 25mm cables.

QUOTE(bengang13 @ Sep 15 2014, 09:48 AM)
Yeah will update here. But waht the spec for the main cable?
*
Eng_Tat
post Sep 15 2014, 09:27 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


Yes. 16mm is actually standard size to be used for 3 phased. if we don't really exceed 60A i don't see the need of 3 phased. can just used single phase with 25mm 2 core to cut cost.

QUOTE(weikee @ Sep 15 2014, 03:22 PM)
16mm2 is the standard use right? Now I see many only use 10mm2.

25mm2 will be superb smile.gif Can take up 80Amps per phase load no problem smile.gif
*
Eng_Tat
post Sep 15 2014, 09:40 PM

Look at all my stars!!
*******
Senior Member
2,215 posts

Joined: Nov 2007
From: Cheras, KL.


Do you really need 3 phase? single phase (60A incoming) can run 6 X 1.5HP AC (5Ax6) simultaneously with a lot of spares. Last time my house i did rewires for 3 phases ready (originally came with 2 core 16mm and i added another 2 core 25mm from incoming to the db to make it 3 phase ready, but i ended using single phase for nearly 3 yrs now nvr had an issue or tripping. can check what i did at my tread.

QUOTE(bengang13 @ Sep 15 2014, 03:02 PM)
ok..let me ask my electrician..but I belive its 16mm
*