QUOTE(cyberkoh88 @ Dec 20 2016, 10:47 AM)
thanks bro for your update. anyway yesterday night do testing, open 3 heater and open 3 aircon (total 3.5HP) on the same time. after 10-15 minutes, cutout fuse (next to Tenage Meter) blow. my whole house no electricity. no choice, ask that electrician to come to do troubleshooting. just found out that my cutout fuse only 30A, no wonder blow. So ask him to change the cutout fuse to 100A. On the same time, requested him to change the 40A RCD (maxguard) to 100A and the 60A DP Isolator (maxguard) to 100A as well. And also ask him to change one of the MCB (20A) to 40A (because one of my room aircon power use water heater point to do looping, worry if open aircon/water heater on the same time, will overload, so as precaution ask him to change to 40A). All together quote me RM400, no choice, need to take it coz already ask him to settle my cutout fuse blow.
I think you looking into burning your house.Like i comment before, changing fuse is simple, can even put in 200Amp if there is one available, but can your wire handle the load?
One heater Max load is 15Amps, you switch on 15amps x 3 = 45amps,
1HP ~ 4Amps, 3.5hp = 14 Amps
You do the math