views
     
TSFyChai
post Aug 13 2024, 12:26 AM, updated 2y ago

New Member
*
Junior Member
34 posts

Joined: Nov 2016
Hi sir, I change the RCCB to ABB 30mA half year ago, but recently my RCCB keep trip, even I off the MCB, RCCB still unable to switch on, need to wait for 10 minutes only able to switch on the RCCB.

Sometimes it trip within 30 minutes, sometimes can last for half a day. I had try to off all small mcb, only on main MCB and RCCB, still trip after hours. May I know roughly what is the issue please? I have no idea to ask technician to check for which issue.

Please advise, appreciate.

This post has been edited by FyChai: Aug 13 2024, 01:25 AM
lj0000
post Aug 13 2024, 12:30 AM

Look at all my stars!!
*******
Senior Member
2,199 posts

Joined: Jan 2003
Neutral leak to earth
Mcb only control live.
TSFyChai
post Aug 13 2024, 12:39 AM

New Member
*
Junior Member
34 posts

Joined: Nov 2016
QUOTE(lj0000 @ Aug 13 2024, 12:30 AM)
Neutral leak to earth
Mcb only control live.
*
Do you mean its my neutral (black) wire issue?
lj0000
post Aug 13 2024, 07:55 AM

Look at all my stars!!
*******
Senior Member
2,199 posts

Joined: Jan 2003
QUOTE(FyChai @ Aug 13 2024, 12:39 AM)
Do you mean its my neutral (black) wire issue?
*
yes. remove all the neutral, check one by one which one got low ohm to earth
SUSRorschach85
post Aug 13 2024, 07:57 AM

Getting Started
**
Junior Member
109 posts

Joined: Jun 2016

Delay trip. sometimes can be caused by those fluorescent lightings.
dreamchaser88
post Aug 14 2024, 10:38 AM

New Member
*
Junior Member
24 posts

Joined: Nov 2010
Possible grounding broken, maybe check grounding cable as well.
TSFyChai
post Aug 15 2024, 02:22 AM

New Member
*
Junior Member
34 posts

Joined: Nov 2016
QUOTE(lj0000 @ Aug 13 2024, 07:55 AM)
yes. remove all the neutral, check one by one which one got low ohm to earth
*
Checked 1 neutral cable is low ohm to earth, wireman ask me to pull new cable since it fault. May I know do I just pull new neutral cable or pull live cable with it also?
lj0000
post Aug 15 2024, 08:10 AM

Look at all my stars!!
*******
Senior Member
2,199 posts

Joined: Jan 2003
QUOTE(FyChai @ Aug 15 2024, 02:22 AM)
Checked 1 neutral cable is low ohm to earth, wireman ask me to pull new cable since it fault. May I know do I just pull new neutral cable or pull live cable with it also?
*
check why low ohm first. could be something simple like the light socket busted.

ya if have the opportunity to lay new cable, do sekaligus live neutral earth.
TSFyChai
post Aug 15 2024, 10:50 AM

New Member
*
Junior Member
34 posts

Joined: Nov 2016
QUOTE(lj0000 @ Aug 15 2024, 08:10 AM)
check why low ohm first. could be something simple like the light socket busted.

ya if have the opportunity to lay new cable, do sekaligus live neutral earth.
*
Can I check myself and how to check please? The neutral with low ohm link light and fans, Wireman said need extra charge for the checking on light and fans and it cost a lot. Now we had disconnect the neutral, DB didnt trip again.
lj0000
post Aug 15 2024, 10:58 AM

Look at all my stars!!
*******
Senior Member
2,199 posts

Joined: Jan 2003
QUOTE(FyChai @ Aug 15 2024, 10:50 AM)
Can I check myself and how to check please? The neutral with low ohm link light and fans, Wireman said need extra charge for the checking on light and fans and it cost a lot. Now we had disconnect the neutral, DB didnt trip again.
*
the low ohmed neutral wire is removed, right?

check whole house, which socket or light does not work.

for socket, remove all plugged in devices, including extention socket

for light, remove if possible.


then use a multimeter to measure the ohm of the neutral to earth again.

TSFyChai
post Aug 15 2024, 11:16 AM

New Member
*
Junior Member
34 posts

Joined: Nov 2016
QUOTE(lj0000 @ Aug 15 2024, 10:58 AM)
the low ohmed neutral wire is removed, right?

check whole house, which socket or light does not work.

for socket, remove all plugged in devices, including extention socket

for light, remove if possible.
then use a multimeter to measure the ohm of the neutral to earth again.
*
Yes the Neutral removed, 10 lights and 1 fan doesn't work now. Its ceiling light and downlight, how to remove please? Just unplug the light bulb?
Momo33
post Aug 15 2024, 11:18 AM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(FyChai @ Aug 15 2024, 03:22 AM)
Checked 1 neutral cable is low ohm to earth, wireman ask me to pull new cable since it fault. May I know do I just pull new neutral cable or pull live cable with it also?
*
low ohm means what value ? should be below 1 ohm ,

possible the light,or fan or wire leakage .
disconnect the neutral of all lights and fan . neutral point just before the light .
connect back the neutral at the DB .
observe if trip

do inspection of the wires , connectors , see its secured good/ not broken / expose and not touchin light body .
check also the fan wire contacts secured and not touch fan body

you looking for any damage wire cover

takes time to DIY
isolate 1 by 1 of the circuit .


This post has been edited by Momo33: Aug 15 2024, 11:24 AM
lj0000
post Aug 15 2024, 11:21 AM

Look at all my stars!!
*******
Senior Member
2,199 posts

Joined: Jan 2003
QUOTE(FyChai @ Aug 15 2024, 11:16 AM)
Yes the Neutral removed, 10 lights and 1 fan doesn't work now. Its ceiling light and downlight, how to remove please? Just unplug the light bulb?
*
ok great
i think its the fan because light bulbs dont have ground.

some crazy electrician install downlight using the earth wire as a hook. it is also possible the ground wire strand touched neutral.
TSFyChai
post Aug 15 2024, 01:14 PM

New Member
*
Junior Member
34 posts

Joined: Nov 2016
QUOTE(Momo33 @ Aug 15 2024, 11:18 AM)
low ohm  means  what value ?   should be below  1 ohm , 

possible  the  light,or  fan or wire    leakage  .
disconnect the  neutral  of  all  lights  and fan .   neutral  point just before the light .
connect back the neutral at the DB .
observe if trip

do inspection  of the wires , connectors  ,  see its  secured  good/ not broken / expose   and not  touchin  light body .
check also the fan wire contacts  secured and not touch fan body

you looking for any damage wire cover

takes time  to DIY
isolate 1 by 1  of the circuit .
*
My house using 3 phase, saw wireman use the isolator checked 0.5 ohm at 500v.

May I know the name of isolator and roughly price? The wireman charge RM400 for checking, thinking to DIY or let him do it if the isolator expensive.

This post has been edited by FyChai: Aug 15 2024, 01:19 PM
TSFyChai
post Aug 15 2024, 01:23 PM

New Member
*
Junior Member
34 posts

Joined: Nov 2016
QUOTE(lj0000 @ Aug 15 2024, 11:21 AM)
ok great
i think its the fan because light bulbs dont have ground.

some crazy electrician install downlight using the earth wire as a hook. it is also possible the ground wire strand touched neutral.
*
Wireman charge RM400 for checking, May I know is it reasonable price or go buy isolator DIY? Its just 1 neutral connect those light and fans. At the end if wire issue need to pay another thousands for pulling new wire. Swt..
Momo33
post Aug 15 2024, 02:16 PM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(FyChai @ Aug 15 2024, 02:14 PM)
My house using 3 phase, saw wireman use the isolator checked 0.5 ohm at 500v.

May I know the name of isolator and roughly price? The wireman charge RM400 for checking, thinking to DIY or let him do it if the isolator expensive.
*
the tester is a insulation tester or megger . shopee have but not sure quality

since you know its the wire loop for lights and fan can try DIY . to find where the fault is.

so faults can be in the wiring , connections , fan and lights

disconnect the fan inputs . L N E
and all those easy lights
check if rccb trip.

if you disconnect all devices and still trip ..then wiring have issue.
ensure all wiring not touch any case , and not damage .

its time consuming but if you have the time just DIY as above first.
I am assuming you have a multimeter cos need to check resistance of wire if need . disconnect the L N E at DB box .


wiring seldom fail cos the lights circuit dont carry heavy current to melt it.




This post has been edited by Momo33: Aug 15 2024, 02:28 PM
lj0000
post Aug 15 2024, 07:29 PM

Look at all my stars!!
*******
Senior Member
2,199 posts

Joined: Jan 2003
QUOTE(FyChai @ Aug 15 2024, 01:23 PM)
Wireman charge RM400 for checking, May I know is it reasonable price or go buy isolator DIY? Its just 1 neutral connect those light and fans. At the end if wire issue need to pay another thousands for pulling new wire. Swt..
*
Go get yourself a multimeter. You can try diy first
If fail only get the pro.
It's simple enough.

If don't have multimeter just connect back the neutral wire to the screw block

If found the rosak device then won't trip
TSFyChai
post Aug 15 2024, 10:29 PM

New Member
*
Junior Member
34 posts

Joined: Nov 2016
QUOTE(Momo33 @ Aug 15 2024, 02:16 PM)
the    tester  is  a  insulation tester  or  megger  .  shopee have  but not sure  quality

since  you know its  the  wire loop  for lights  and fan  can try DIY . to find where the fault is.

so faults can be in the wiring ,  connections ,  fan  and  lights

disconnect the fan  inputs  .    L N E
and  all those easy  lights 
check if rccb  trip. 

if you disconnect all  devices  and still  trip  ..then  wiring have issue. 
ensure all wiring not touch any case ,  and not damage .

its time consuming  but if you have the time  just DIY  as above  first.
I am assuming you have a  multimeter  cos need to check  resistance of wire  if need  .  disconnect  the  L  N  E at DB  box .
wiring  seldom fail  cos    the  lights  circuit dont carry heavy current  to melt it.
*
QUOTE(lj0000 @ Aug 15 2024, 07:29 PM)
Go get yourself a multimeter. You can try diy first
If fail only get the pro.
It's simple enough.

If don't have multimeter just connect back the neutral wire to the screw block

If found the rosak device then won't trip
*
Ok, i try to disconnect light and fans wire one by one and connect back the neutral to test it. Btw, what is the multimeter you mentions please? Maybe i can buy from electrical shop for DIY
lj0000
post Aug 15 2024, 10:43 PM

Look at all my stars!!
*******
Senior Member
2,199 posts

Joined: Jan 2003
QUOTE(FyChai @ Aug 15 2024, 10:29 PM)
Ok, i try to disconnect light and fans wire one by one and connect back the neutral to test it. Btw, what is the multimeter you mentions please? Maybe i can buy from electrical shop for DIY
*
You can get uni-t digital meter
Or sunwah analog meter.
The analog meter will be easier to use for your case.
The digital meter is more versatile
Momo33
post Aug 15 2024, 11:23 PM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(FyChai @ Aug 15 2024, 11:29 PM)
Ok, i try to disconnect light and fans wire one by one and connect back the neutral to test it. Btw, what is the multimeter you mentions please? Maybe i can buy from electrical shop for DIY
*
https://shopee.com.my/PRO%F0%9F%8F%A0UNI-T-...93-0f5e4fd36720



specs.
Range UT123
Certifications RoHS
Category ratings CAT III 600V
DC voltage (V) 600V ±(0.5%+2)

AC voltage (V) 600V ±(1%+3)

DC Current (A) 10A

AC Current (A) 10A

Resistance (Ω) 20MΩ ±(0.8%+2)

40MΩ

Temperature -40~300°C ±(1%+5)

-40~572°F ±(2%+6)

Capacitance (F) 4000μF
TSFyChai
post Aug 16 2024, 01:40 AM

New Member
*
Junior Member
34 posts

Joined: Nov 2016
QUOTE(lj0000 @ Aug 15 2024, 10:43 PM)
You can get uni-t digital meter
Or sunwah analog meter.
The analog meter will be easier to use for your case.
The digital meter is more versatile
*
QUOTE(Momo33 @ Aug 15 2024, 11:23 PM)
https://shopee.com.my/PRO%F0%9F%8F%A0UNI-T-...93-0f5e4fd36720
specs.
Range                                             UT123               
Certifications          RoHS
Category ratings     CAT III 600V
DC voltage (V)         600V            ±(0.5%+2)        

AC voltage (V)         600V            ±(1%+3)           

DC Current (A)         10A                                         

AC Current (A)         10A                                         

Resistance (Ω)         20MΩ          ±(0.8%+2)

                                   40MΩ                                      

Temperature            -40~300°C  ±(1%+5)

                                   -40~572°F   ±(2%+6)

Capacitance (F)       4000μF
*
Appreciate, I disconnect lighting one by one and use the meter test neutral and earth on DB right?

This post has been edited by FyChai: Aug 16 2024, 01:42 AM
Momo33
post Aug 16 2024, 06:16 AM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(FyChai @ Aug 16 2024, 02:40 AM)
Appreciate, I disconnect lighting one by one and use the meter test neutral and earth on DB right?
*
to visualise better some questions.

how old your wiring
what type of lighting on this loop ? fluorescent 4 feet? LED downlights or the leds bulb screw on type,
the LED is it 1 driver for multiple leds or ?
how many switches on this loop , LEDs.

the rccb trip can happen when none /light, fan is ON , ?
is the fan ON at that time ?
tryin to understand situation when rccb trip timing

example fan have coils . when in use heats get hot and the coils leak .... then trip.
this is my main suspect .

you need a test pen .
and a rubber gloves too .

there are also multimeter about 100 RM more solid if budget allows . check only sanwa and uni T brands.


This post has been edited by Momo33: Aug 16 2024, 06:49 AM
TSFyChai
post Aug 16 2024, 06:34 PM

New Member
*
Junior Member
34 posts

Joined: Nov 2016
QUOTE(Momo33 @ Aug 16 2024, 06:16 AM)
to  visualise better  some questions.

how old your wiring
what type of lighting  on this loop ?  fluorescent 4 feet?  LED downlights or the leds  bulb screw  on type, 
the LED  is it 1 driver  for multiple leds or ?
how many switches  on this loop ,  LEDs.

the  rccb trip  can happen  when  none  /light, fan      is ON  , ?
is the fan ON  at that time ?
tryin to understand  situation  when rccb trip  timing

example  fan have coils  .  when in use  heats get hot  and the coils  leak .... then trip.
this is my main suspect .

you need  a test pen .
and  a  rubber gloves  too .

there are  also  multimeter  about 100 RM  more solid  if budget allows .  check only sanwa and  uni T  brands.
*
Wire around 15 years, but just use for 1 year. The house empty 10+ years.
2 round ceiling light, 3 normal light with bulb, 5 LED downlight.
2 switch for 2 round ceiling light, 3 switch for 3 light bulb, 2 switch for 5 LED downlight, 1 switch for 1 fan

I tried off all of them, and also off the MCB, RCCB still trip within 5 minutes to half a day. I try to switch on fan for hours, didnt trip, but the RCCB straight away trip when i off the fan, but only once.

The RCCB never trip after I disconnect the neutral cable from DB box.
Momo33
post Aug 16 2024, 09:22 PM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(FyChai @ Aug 16 2024, 07:34 PM)
Wire around 15 years, but just use for 1 year. The house empty 10+ years.
2 round ceiling light, 3 normal light with bulb, 5 LED downlight.
2 switch for 2 round ceiling light, 3 switch for 3 light bulb, 2 switch for 5 LED downlight, 1 switch for 1 fan

I tried off all of them, and also off the MCB, RCCB still trip within 5 minutes to half a day. I try to switch on fan for hours, didnt trip, but the RCCB straight away trip when i off the fan, but only once.

The RCCB never trip after I disconnect the neutral cable from DB box.
*
all the lights point is in the hall or go also outside car park or ? if outside check water leaks/ wet and all the power connect

all the lights neutral wire return to the DB on 1 wire ?

am thinkin how to check and if can break up the circuit . or know how the neutral wiring loop goes to the points.


the round ceiling light is fluorescent round ? if yes open check any loose/ bare contacts . try to disconnect both out from the loop at the power connect to the light . . check if rccb still trip

is any part of the wiring under a false ceiling ?

the neutral wire from DB goes point A and continues to point B and point C etc..
means at the power point connect / is a 3 point carrying L N E , you will see 2 wire connect together cos to continue the loop .

the idea is to break the neutral loop , by disconnecting them . mean 1 wire is connect , the other hang free. hence you break the neutral loop to exclude light further down the loop . for troubleshooting purpose .




TSFyChai
post Aug 23 2024, 01:58 AM

New Member
*
Junior Member
34 posts

Joined: Nov 2016
QUOTE(Momo33 @ Aug 16 2024, 09:22 PM)
all the lights point  is in the hall  or   go  also  outside  car park  or   ?    if outside  check  water leaks/ wet   and all  the power connect

all the lights  neutral wire    return  to the DB  on 1  wire  ? 

am thinkin   how to  check   and if can break up the circuit  .   or know  how the  neutral wiring  loop goes  to the  points.  
the round  ceiling  light is  fluorescent round ?    if yes  open  check any loose/ bare   contacts  . try to disconnect  both  out  from the loop  at the power connect to the light .   .   check if rccb  still trip

is   any part of  the wiring under  a false  ceiling ?

the neutral  wire  from  DB   goes   point A    and   continues to point B   and point C    etc..
means  at the  power point connect /  is a 3  point carrying L N E  ,        you will  see   2  wire  connect together  cos to continue the loop .

the idea is to break the  neutral  loop  , by  disconnecting   them  .  mean 1 wire is connect ,  the other  hang free.   hence  you break the neutral loop  to  exclude  light further down the loop   .   for troubleshooting purpose .
*
I tried to DIY but I found the cable looping and i unable to buy UniT multimeter, so I didnt touch it and ask wireman for troubleshooting.

Wireman found out there are 3 neutral cable looping at fan and one of it ohm lower than 0.1, so he disconnect the faulty neutral wire from the fan and ON RCCB and Main MCB. The RCCB works, but trip after couple of minutes, and he pull ON the RCCB again,.

Few of my applicants burned out with sound "boom" immediatrly when he ON the RCCB. Lots of socket surge after that, and the surge issue solved after he install back the neutral cable at fan and wireman said is it because of thunder, not his fault. Since its raining at that time...

Its that really? Need you guys advise please. Appreciate.

This post has been edited by FyChai: Aug 23 2024, 02:06 AM
Momo33
post Aug 23 2024, 09:30 AM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(FyChai @ Aug 23 2024, 02:58 AM)
I tried to DIY but I found the cable looping and i unable to buy UniT multimeter, so I didnt touch it and ask wireman for troubleshooting.

Wireman found out there are 3 neutral cable looping at fan and one of it ohm lower than 0.1, so he disconnect the faulty neutral wire from the fan and ON RCCB and Main MCB. The RCCB works, but trip after couple of minutes, and he pull ON the RCCB again,.

Few of my applicants burned out with sound "boom" immediatrly when he ON the RCCB. Lots of socket surge after that, and the surge issue solved after he install back the neutral cable at fan and wireman said is it because of thunder, not his fault. Since its raining at that time...

Its that really? Need you guys advise please. Appreciate.
*
Wireman found out there are 3 neutral cable looping at fan and one of it ohm lower than 0.1, so he disconnect the faulty neutral wire from the fan and ON RCCB and Main MCB. The RCCB works, but trip after couple of minutes, and he pull ON the RCCB again,.
>> its possible there are other wiring at higher that normal leakage . your rccb 30 mA too sensitive . house wiring is old and leak higher. Last time the standard "Old house" use 100mA .rccb.

Few of my applicants burned out with sound "boom" immediately when he ON the RCCB.
>> this i not sure why ..cos should not happen .
put ON rccb cause a small surge but appliances can handle this.

your appliance blowup IMMEDIATELY at rccb put ON or after some time ??

he install back the neutral cable at fan
>> the faulty N wire replace or ?







TSFyChai
post Aug 23 2024, 12:20 PM

New Member
*
Junior Member
34 posts

Joined: Nov 2016
QUOTE(Momo33 @ Aug 23 2024, 09:30 AM)
Wireman found out there are 3 neutral cable looping at fan and one of it ohm lower than 0.1, so he disconnect the faulty neutral wire from the fan and ON RCCB and Main MCB. The RCCB works, but trip after couple of minutes, and he pull ON the RCCB again,.
>>   its possible   there are  other  wiring   at higher that normal leakage .  your rccb 30 mA    too sensitive  .  house wiring is old and leak higher.    Last time the standard  "Old house"  use 100mA .rccb.

Few of my applicants burned out with sound "boom" immediately when he ON the RCCB.
>>   this i  not sure why ..cos   should not happen . 
put ON rccb  cause a small surge  but  appliances  can handle this. 

your  appliance  blowup  IMMEDIATELY  at  rccb put ON   or  after  some  time ??

he install back the neutral cable at fan
>>  the faulty N wire  replace  or ?
*
The RCCB trip is a sign , it mean there is leakage, it protect my appliance and cable, and I had use 30mA for year, no issue at all.
The appliances didnt burned out when RCCB first trip, its only burned when wireman push ON the RCCB after trip. Old house doesnt mean using old appliances, 30mA is definitely works. Singapore old house also use 30mA

I had checked with other PW4 wireman, if there is looping 3 cable on neutral, it mean more than 1 MCB sharing the neutral, simply disconnect neutral but didn't disconnect the live cable will cause short circuit and burn. Wireman should also check and disconnect the live cable.


I heard 3 sounds of explosion immediately when he ON the RCCB after trip.
The short circuit issue solved when he connect back the faulty neutral cable, didnt replace with new cable.

This post has been edited by FyChai: Aug 23 2024, 12:24 PM
Momo33
post Aug 23 2024, 01:23 PM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(FyChai @ Aug 23 2024, 01:20 PM)
The RCCB trip is a sign , it mean there is leakage, it protect my appliance and cable, and I had use 30mA for year, no issue at all.
The appliances didnt burned out when RCCB first trip, its only burned when wireman push ON the RCCB after trip. Old house doesnt mean using old appliances, 30mA is definitely works. Singapore old house also use 30mA

I had checked with other PW4 wireman, if there is looping 3 cable on neutral, it mean more than 1 MCB sharing the neutral, simply disconnect neutral but didn't disconnect the live cable will cause short circuit and burn. Wireman should also check and disconnect the live cable.
I heard 3 sounds of explosion immediately when he ON the RCCB after trip.
The short circuit issue solved when he connect back the faulty neutral cable, didnt replace with new cable.
*
the main purpose of rccb is to protect human . Not appliance .
rccb do not have over current protection . you have MCB for this.

The Malaysian Tenaga recommendation is 100mA for main DB , 30mA for sockets , 10mA for water heater.
new house developer will put 100mA .
yes can use 30mA but the risk is more trips when the wiring get old and degrade. this depend also if the wiring is first grade cable or cheap one.

""I had checked with other PW4 wireman, if there is looping 3 cable on neutral, it mean more than 1 MCB sharing the neutral, simply disconnect neutral but didn't disconnect the live cable will cause short circuit and burn. Wireman should also check and disconnect the live cable.""
this explain above i find no logic. . if remove 1 neutral wire that part circuit will not function/ cos the wire loop is not close complete and current cannot flow. means that bulb not work .
its shuld not trip rccb. or blow any
example if 1 wire for your bulb accident get loose/ or broke that light dont work , and rccb will not trip . right.

my guess is he not connect/ tight 1 connection cause sparking , cause trip rccb .
my guess .






TSFyChai
post Aug 23 2024, 05:08 PM

New Member
*
Junior Member
34 posts

Joined: Nov 2016
QUOTE(Momo33 @ Aug 23 2024, 01:23 PM)
the main purpose  of rccb  is to protect  human .  Not  appliance . 
rccb do not have over current protection .  you have MCB  for this.

The Malaysian  Tenaga recommendation  is 100mA  for  main DB , 30mA  for sockets ,  10mA for water heater.
new house  developer will put 100mA .
yes can use 30mA  but the risk is  more trips  when the wiring get old and degrade.  this depend  also if the  wiring is  first grade cable or cheap one. 

""I had checked with other PW4 wireman, if there is looping 3 cable on neutral, it mean more than 1 MCB sharing the neutral, simply disconnect neutral but didn't disconnect the live cable will cause short circuit and burn. Wireman should also check and disconnect the live cable.""
this explain above  i find no logic.  .  if remove  1 neutral wire  that part  circuit  will not function/ cos the wire  loop is not close complete  and current cannot flow. means that  bulb not work . 
its  shuld not  trip rccb. or blow  any
example if  1 wire for your  bulb  accident get loose/ or broke    that light dont work , and  rccb  will not trip .  right.

my guess  is he  not  connect/ tight  1 connection  cause sparking  , cause trip  rccb . 
my guess .
*
Erm, what is the point we discuss RCCB on this matter? Its really trip after the neutral cable disconnect, and I use it for year, never trip even thunderstorm, the only disadvantages is expensive.

I'm not proffesional on eletrical, but the facts is it trip after the faulty neutral cable disconnect, and whole house short circuit with few appliances, bulbs, adapter burned. Wireman take hours to troubleshoot, issue solve after he connect back the neutral cable.

Base on I check on chatgpt, the answer also meet what the PW4 wireman said :

ChatGPT
No, you should not disconnect the neutral wire while leaving the live and earth wires connected, especially with the current on. This is dangerous for several reasons:

Electrical Shock Hazard: Disconnecting the neutral while the live wire is still connected can create a dangerous situation where the exposed wires or connected devices may still carry live electricity. This increases the risk of electrical shock.

Potential Damage to Equipment: If the fan or any other electrical device is designed to use both the live and neutral wires, disconnecting the neutral can cause improper operation or even damage the equipment.

Fire Risk: Without a proper return path (neutral), the electrical system may behave unpredictably, potentially causing overheating, short circuits, or fires.




I'm not going to argue anything, just want to know the truth and prevent it happen again in future. Anyone with relevant knowledge or experience can share info with me please, Appreciate.
jio
post Aug 23 2024, 07:38 PM

Casual
***
Junior Member
383 posts

Joined: May 2005
QUOTE(FyChai @ Aug 23 2024, 12:20 PM)
The RCCB trip is a sign , it mean there is leakage, it protect my appliance and cable, and I had use 30mA for year, no issue at all.
The appliances didnt burned out when RCCB first trip, its only burned when wireman push ON the RCCB after trip. Old house doesnt mean using old appliances, 30mA is definitely works. Singapore old house also use 30mA

I had checked with other PW4 wireman, if there is looping 3 cable on neutral, it mean more than 1 MCB sharing the neutral, simply disconnect neutral but didn't disconnect the live cable will cause short circuit and burn. Wireman should also check and disconnect the live cable.
I heard 3 sounds of explosion immediately when he ON the RCCB after trip.
The short circuit issue solved when he connect back the faulty neutral cable, didnt replace with new cable.
*
1. The fact the 'electrician' quick to blame the lightning and reconnect back the faulty neutral cable shows he himself not sure what he was doing.

2. Is your electric supply 3 phase? If yes, then that explain the exploding appliances. There are circuits from different phase using the same neutral cable. If the appliances connected to that neutral cable (now disconnected) are left on, it will ended up the appliance being connected phase to phase 400V instead of 230V. Normally nobody will even think of shortcut share neutral in 3 phase, but occasionally there are daring idiots who think it is safe to do so as long as it is in the same phase. But that circuit might relocated to different phase later on causing this issue. You will have to untangle this shared neutral mess as the neutral cable might be overloaded without tripping the MCB.


SUSceo684
post Aug 23 2024, 08:32 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(FyChai @ Aug 23 2024, 05:08 PM)
Erm, what is the point we discuss RCCB on this matter? Its really trip after the neutral cable disconnect, and I use it for year, never trip even thunderstorm, the only disadvantages is expensive.

I'm not proffesional on eletrical, but the facts is it trip after the faulty neutral cable disconnect, and whole house short circuit with few appliances, bulbs, adapter burned. Wireman take hours to troubleshoot, issue solve after he connect back the neutral cable.

Base on I check on chatgpt, the answer also meet what the PW4 wireman said :

ChatGPT
No, you should not disconnect the neutral wire while leaving the live and earth wires connected, especially with the current on. This is dangerous for several reasons:

Electrical Shock Hazard: Disconnecting the neutral while the live wire is still connected can create a dangerous situation where the exposed wires or connected devices may still carry live electricity. This increases the risk of electrical shock.

Potential Damage to Equipment: If the fan or any other electrical device is designed to use both the live and neutral wires, disconnecting the neutral can cause improper operation or even damage the equipment.

Fire Risk: Without a proper return path (neutral), the electrical system may behave unpredictably, potentially causing overheating, short circuits, or fires.
I'm not going to argue anything, just want to know the truth and prevent it happen again in future. Anyone with relevant knowledge or experience can share info with me please, Appreciate.
*
Cannot disconnect neutral. Sure boom because of phase to phase is 415V.
Since the point of issue is too many neutrals tapping illegally into the fan neutral, what are those other two circuits powering? Does running a "patch cable" (exposed new cable) back to DB neutral busbar keep the power online steady?

Did wireman check that those 3 neutrals are actual neutrals and not swapped? (there is such possibility in hack wiring that the live and neutral are swapped)
SUSceo684
post Aug 23 2024, 08:34 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(Momo33 @ Aug 23 2024, 01:23 PM)
the main purpose  of rccb  is to protect  human .  Not  appliance . 
rccb do not have over current protection .  you have MCB  for this.

The Malaysian  Tenaga recommendation  is 100mA  for  main DB , 30mA  for sockets ,  10mA for water heater.
new house  developer will put 100mA .
yes can use 30mA  but the risk is  more trips  when the wiring get old and degrade.  this depend  also if the  wiring is  first grade cable or cheap one. 

""I had checked with other PW4 wireman, if there is looping 3 cable on neutral, it mean more than 1 MCB sharing the neutral, simply disconnect neutral but didn't disconnect the live cable will cause short circuit and burn. Wireman should also check and disconnect the live cable.""
this explain above  i find no logic.  .  if remove  1 neutral wire  that part  circuit  will not function/ cos the wire  loop is not close complete  and current cannot flow. means that  bulb not work . 
its  shuld not  trip rccb. or blow  any
example if  1 wire for your  bulb  accident get loose/ or broke    that light dont work , and  rccb  will not trip .  right.

my guess  is he  not  connect/ tight  1 connection  cause sparking  , cause trip  rccb . 
my guess .
*
My 1995 era house is on 3phase 30mA single RCD, seldom trip.

However, there is risk of brittle/loose contact in older wiring (if never move is ok) but once re-bent/reshaped to accommodate DB box replacement terus no power for that circuit - because the copper already patah inside.
TSFyChai
post Aug 23 2024, 09:31 PM

New Member
*
Junior Member
34 posts

Joined: Nov 2016
QUOTE(jio @ Aug 23 2024, 07:38 PM)
1. The fact the 'electrician' quick to blame the lightning and reconnect back the faulty neutral cable shows he himself not sure what he was doing.

2. Is your electric supply 3 phase? If yes, then that explain the exploding appliances. There are circuits from different phase using the same neutral cable. If the appliances connected to that neutral cable (now disconnected) are left on, it will ended up the appliance being connected phase to phase 400V instead of 230V. Normally nobody will even think of shortcut share neutral in 3 phase, but occasionally there are daring idiots who think it is safe to do so as long as it is in the same phase. But that circuit might relocated to different phase later on causing this issue. You will have to untangle this shared neutral mess as the neutral cable might be overloaded without tripping the MCB.
*
Yes, my house is 3 phase, and the 3 looping neutral cable is ori from developer, lol...

I am not sure did other phase using same neutral cable also, but upstair water heater, extension cable and light bulbs burned also. Losses thousands of ringgit, so pain..

This post has been edited by FyChai: Aug 23 2024, 09:46 PM
TSFyChai
post Aug 23 2024, 09:45 PM

New Member
*
Junior Member
34 posts

Joined: Nov 2016
QUOTE(ceo684 @ Aug 23 2024, 08:32 PM)
Cannot disconnect neutral. Sure boom because of phase to phase is 415V.
Since the point of issue is too many neutrals tapping illegally into the fan neutral, what are those other two circuits powering? Does running a "patch cable" (exposed new cable) back to DB neutral busbar keep the power online steady?

Did wireman check that those 3 neutrals are actual neutrals and not swapped? (there is such possibility in hack wiring that the live and neutral are swapped)
*
I am not sure is the neutral cables running patch cable back to DB.
Wireman has check other 2 neutral cable with multimeter with 500v, Ohm result show OL. The fan at living hall, faulty cable connect to other light at living hall, while another 2 functional neutral connect to yard and car porch lighting.

 

Change to: