QUOTE(FyChai @ Aug 23 2024, 01:20 PM)
The RCCB trip is a sign , it mean there is leakage, it protect my appliance and cable, and I had use 30mA for year, no issue at all.
The appliances didnt burned out when RCCB first trip, its only burned when wireman push ON the RCCB after trip. Old house doesnt mean using old appliances, 30mA is definitely works. Singapore old house also use 30mA
I had checked with other PW4 wireman, if there is looping 3 cable on neutral, it mean more than 1 MCB sharing the neutral, simply disconnect neutral but didn't disconnect the live cable will cause short circuit and burn. Wireman should also check and disconnect the live cable.
I heard 3 sounds of explosion immediately when he ON the RCCB after trip.
The short circuit issue solved when he connect back the faulty neutral cable, didnt replace with new cable.
the main purpose of rccb is to protect human . Not appliance .
rccb do not have over current protection . you have MCB for this.
The Malaysian Tenaga recommendation is 100mA for main DB , 30mA for sockets , 10mA for water heater.
new house developer will put 100mA .
yes can use 30mA but the risk is more trips when the wiring get old and degrade. this depend also if the wiring is first grade cable or cheap one.
""I had checked with other PW4 wireman, if there is looping 3 cable on neutral, it mean more than 1 MCB sharing the neutral, simply disconnect neutral but didn't disconnect the live cable will cause short circuit and burn. Wireman should also check and disconnect the live cable.""
this explain above i find no logic. . if remove 1 neutral wire that part circuit will not function/ cos the wire loop is not close complete and current cannot flow. means that bulb not work .
its shuld not trip rccb. or blow any
example if 1 wire for your bulb accident get loose/ or broke that light dont work , and rccb will not trip . right.
my guess is he not connect/ tight 1 connection cause sparking , cause trip rccb .
my guess .