QUOTE(lj0000 @ Jan 20 2024, 11:25 AM)
usually no need to brake tiles. just pull the wires through the pvc hose
should use 4mm2 cables. (my mistake. should not be 2.5)
https://www.st.gov.my/en/contents/publicati...r%20Systems.pdfyou may read the guide cover to cover.
some points
- use double pole 20A water heater switch
- as much as possible, the LN wires should not have joints.
- earth cable should not have joints.
- do not use 3pin plug to connect water heater
- leave a loop of wire before entering water heater (so water wont go inside)
QUOTE(ceo684 @ Jan 20 2024, 02:18 PM)
Must be same size as phase (live) conductor.
QUOTE(Selene Yeo @ Jan 20 2024, 02:57 PM)
That contractor is really endangering your parents' life by fixing underspec power cable. Water heaters with power rating below 5.711kW have to use 4mm2 cables, based on Suruhanjaya Tenaga's guidelines.

And the rest just follow lj0000's good advice.
Understood, thanks lj0000, ceo684 and Selene Yeo for the advice!! Sorry for late reply, was busy juggling work and renovation.
The contractor basically just pushed the blame on his staff. Excuse is 2.5mm finished, so his staff used 1.5mm. Quite BS la.
I warned him to be more careful and professional.
By the way, I've also decided to change completely new wiring for the common bathroom's water heater from DB too.
I bought Mega 4mm wire for the contractor to use this time.
The (instant) water heater I bought is Deka 4.5kW high power version.
For the RCBO, I bought Schneider Easy9 25A, 1P+N, 6kA, C Curve 10mA.
Schneider RCBO somehow doesn't have 20A version.
1) Should I buy EPS 20A 2P 10mA 6kA RCBO Type AC instead?
2) Why EPS RCBO has 2 poles, while Schneider RCBO only has 1 pole?
3) Is RCBO only good enough? Or should I use MCB + RCCB setup?
Thank you all again!!