 Rcbo tripping need advice

views
     
TSn0thing
post Sep 20 2022, 01:02 PM, updated 4y ago

Getting Started
**
Junior Member
127 posts

Joined: Jul 2005
So my water heater rcbo trips when I switch off the water heater on the wall switch. Called electrician, he changed rcbo after some testing but it still happened. Changed water heater, changed wall switch, still the same. Halppp.

1. Will only trip when turning off power on 20a wall switch.
2. Will not trip if 20a wall switch is left on 'ON' position and water heater is turned on/off on the water heater by turning on/off water or turning on/off by testing/resetting elcb.
3. Will not trip when letting water heater run for few minutes.
4. Changed 20a wall switch, still tripping when switch off on wall switch.
5. Changed water heater, still same issues
6. Replaced rcbo still same issues, so electrician put back the old one and didn't charge me.
7. Used to be using a 15A plug point for water heater but was changed to point specifically for water heater but still the same issue.
8. When it was using the 15A plug point, there's an on/off switch on it. Turning it on/off on the 15A plug point switch does not trip the rcbo.
9. Swapped wires on the fuse box to a 20A MCB does not cause it to trip


This post has been edited by n0thing: Sep 20 2022, 08:07 PM
stormer.lyn
post Sep 20 2022, 02:15 PM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(n0thing @ Sep 20 2022, 01:02 PM)
So my water heater rcbo trips when I switch off the water heater on the wall switch. Called electrician, he changed rcbo after some testing but it still happened. Changed water heater, changed wall switch, still the same. Halppp.

1. Will only trip when turning off power on 20a wall switch.
2. Will not trip if 20a wall switch is left on 'ON' position and water heater is turned on/off on the water heater by turning on/off water or turning on/off by testing/resetting elcb.
3. Will not trip when letting water heater run for few minutes.
4. Changed 20a wall switch, still tripping when switch off on wall switch.
5. Changed water heater, still same issues
6. Replaced rcbo still same issues, so electrician put back the old one and didn't charge me.
7. Used to be using a 15A plug point for water heater but was changed to  point specifically for water heater but still the same issue.
*
Run temporary wires from RCBO to 20 A switch to water heater to see if the problem persists.
TSn0thing
post Sep 20 2022, 02:44 PM

Getting Started
**
Junior Member
127 posts

Joined: Jul 2005
QUOTE(stormer.lyn @ Sep 20 2022, 02:15 PM)
Run temporary wires from RCBO to 20 A switch to water heater to see if the problem persists.
*
Technically already direct from rcbo to 20a wall switch to water heater.

Already removed the 15A wall point to this

https://s.lazada.com.my/s.4NRZl

stormer.lyn
post Sep 20 2022, 02:51 PM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(stormer.lyn @ Sep 20 2022, 02:15 PM)
Run temporary wires from RCBO to 20 A switch to water heater to see if the existing wire insulation has broken down and if the problem persists.
*
Or test the existing wires with an insulation tester

This post has been edited by stormer.lyn: Sep 20 2022, 02:52 PM
TSn0thing
post Sep 20 2022, 02:54 PM

Getting Started
**
Junior Member
127 posts

Joined: Jul 2005
QUOTE(stormer.lyn @ Sep 20 2022, 02:51 PM)
Or test the existing wires with an insulation tester
*
Ah, ok. Noted. Thanks.
TSn0thing
post Sep 20 2022, 02:57 PM

Getting Started
**
Junior Member
127 posts

Joined: Jul 2005
Another thing to add, electrician switched the wires on the fusebox from the rcbo to a 20a MCB and it didn't trip and worked fine.
TSn0thing
post Oct 3 2022, 07:43 PM

Getting Started
**
Junior Member
127 posts

Joined: Jul 2005
Just an update to close this topic, in the end, after changing so many things, it was the switch that was faulty. The new switch that was changed had issues too. Electrician said most likely due to the led light.

Changed to another switch and it has stopped tripping.
SUSceo684
post Oct 5 2022, 12:07 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(n0thing @ Oct 3 2022, 07:43 PM)
Just an update to close this topic, in the end, after changing so many things, it was the switch that was faulty. The new switch that was changed had issues too. Electrician said most likely due to the led light.

Changed to another switch and it has stopped tripping.
*
Use quality switches like MK should have no issue. Those caplang brands one.. whistling.gif
BrunoMalaya P
post Oct 6 2022, 02:16 AM

New Member
*
Probation
9 posts

Joined: Sep 2022


QUOTE(ceo684 @ Oct 5 2022, 12:07 AM)
Use quality switches like MK should have no issue. Those caplang brands one.. whistling.gif
*
Are SIEMENS switches ok? I think they are made in China.


Attached thumbnail(s)
Attached Image
mini orchard
post Oct 6 2022, 06:59 AM

10k Club
********
All Stars
14,511 posts

Joined: Sep 2017
QUOTE(BrunoMalaya @ Oct 6 2022, 02:16 AM)
Are SIEMENS switches ok? I think they are made in China.
*
Most of the world household products are now made in China, Ikea included

I believed they have proper QC and not made by those backyard factories.

If you want from origim country, if any, the price will be much more expensive.

This post has been edited by mini orchard: Oct 6 2022, 07:01 AM
TSn0thing
post Oct 6 2022, 11:52 AM

Getting Started
**
Junior Member
127 posts

Joined: Jul 2005
QUOTE(ceo684 @ Oct 5 2022, 12:07 AM)
Use quality switches like MK should have no issue. Those caplang brands one.. whistling.gif
*
My original switch was Hager. Lasted 7 years.
My replacement switch was Schneider avataron C from official store Lazada.
My current working switch is a Schneider Vivace. Haha.

 

Change to: