Hi,
A cable stated as 40/0.16 what does it mean?
0.16 means 16mm?
Cable 40/0.16 - what does it mean?
Cable 40/0.16 - what does it mean?
|
|
Jun 25 2022, 03:55 PM, updated 3y ago
Show posts by this member only | Post
#1
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,512 posts Joined: Sep 2007 |
Hi,
A cable stated as 40/0.16 what does it mean? 0.16 means 16mm? |
|
|
|
|
|
Jun 25 2022, 04:00 PM
Show posts by this member only | Post
#2
|
![]() ![]()
Junior Member
89 posts Joined: Jun 2009 |
40 is length.. 0.16 is diameter... You nak buat apa? Wire lock? mactreouser liked this post
|
|
|
Jun 25 2022, 04:04 PM
Show posts by this member only | IPv6 | Post
#3
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,119 posts Joined: Jun 2006 From: Kuala Lumpur |
Its 0.75mm2 Assume you are asking about 3 core wires alfiejr and mactreouser liked this post
|
|
|
Jun 25 2022, 04:09 PM
Show posts by this member only | Post
#4
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,512 posts Joined: Sep 2007 |
Thanks guys for your prompt reply!
QUOTE(h4r8_kIlLeR @ Jun 25 2022, 04:00 PM) I see. Yg 0.16 diameter tu kira yg luar ke (3 wire dlm), atau pun yg dlm tu (1 wire 0.16 diameter)?Utk lampu sambungan biasa. Boleh kan? QUOTE(ncool15 @ Jun 25 2022, 04:04 PM) Oh 0.75mm², how do you translate?Yes. 3C wires! This post has been edited by mactreouser: Jun 25 2022, 04:10 PM |
|
|
Jun 25 2022, 04:17 PM
Show posts by this member only | IPv6 | Post
#5
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,132 posts Joined: Apr 2014 From: Shah Alam, Selangor |
The wire contains 40 strands with each strand maximum diameter of 0.16 mm.
Cross section calculation is = ((diameter/2)²) x Pi) x (number of strands) = ((0.16/2)² x 3.14159) x 40 = 0.8 mm² nominal |
|
|
Jun 25 2022, 04:44 PM
Show posts by this member only | Post
#6
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
5,650 posts Joined: Mar 2012 |
https://www.st.gov.my/en/contents/presentat...NCES%202015.pdf https://www.energy-solutions.co.uk/technical-information 40strand of 0.16mm2diameter = 0.73mm2 max can use 6ampere if its copper. good enough for small led lights alfiejr and mactreouser liked this post
|
|
|
|
|
|
Jun 25 2022, 05:59 PM
Show posts by this member only | IPv6 | Post
#7
|
![]() ![]()
Junior Member
214 posts Joined: Mar 2016 |
QUOTE(mactreouser @ Jun 25 2022, 03:55 PM) 016 is the size of individual copper straini think and theres 40 of this strains mactreouser liked this post
|
|
|
Jun 25 2022, 11:02 PM
Show posts by this member only | IPv6 | Post
#8
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,512 posts Joined: Sep 2007 |
QUOTE(stormer.lyn @ Jun 25 2022, 04:17 PM) The wire contains 40 strands with each strand maximum diameter of 0.16 mm. Wah... You are Expert 😜Cross section calculation is = ((diameter/2)²) x Pi) x (number of strands) = ((0.16/2)² x 3.14159) x 40 = 0.8 mm² nominal Could you "teach" a little bit of the format? Interesting & useful 👍🏻 QUOTE(fireballs @ Jun 25 2022, 04:44 PM) https://www.st.gov.my/en/contents/presentat...NCES%202015.pdf Thanks for confirming! 👏🏼https://www.energy-solutions.co.uk/technical-information 40strand of 0.16mm2diameter = 0.73mm2 max can use 6ampere if its copper. good enough for small led lights So the 40 is Strand! I see . And this format "0.16mm2diameter = 0.73mm2" is from the chart given above? QUOTE(Lada Putih @ Jun 25 2022, 05:59 PM) Which means 0.16x3 = 40? 😲 |
|
|
Jun 26 2022, 09:53 AM
Show posts by this member only | Post
#9
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
5,650 posts Joined: Mar 2012 |
0.16 is the diameter R is diameter bahagi2 To get area is pi r kuasa Dua remember? So 3.142 x 0.08 x0.08 alfiejr and mactreouser liked this post
|
|
|
Jun 26 2022, 05:17 PM
Show posts by this member only | IPv6 | Post
#10
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,512 posts Joined: Sep 2007 |
|
|
|
Jun 26 2022, 07:05 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
5,650 posts Joined: Mar 2012 |
QUOTE(mactreouser @ Jun 26 2022, 05:17 PM) In jagung field ya mactreouser liked this post
|
|
|
Jun 26 2022, 07:13 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
13,210 posts Joined: Jul 2006 |
mactreouser liked this post
|
|
|
Jun 30 2022, 10:28 PM
Show posts by this member only | IPv6 | Post
#13
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,512 posts Joined: Sep 2007 |
|
|
|
|
|
|
Jun 30 2022, 10:33 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
4,498 posts Joined: Jun 2011 |
What wiring work you doing? Please find the sizing over here. 1.5mm2 for lighting/fans, 2.5mm^2 for rings sockets (regular non high current sockets) 4mm^2 for higher loads / kitchen ![]() http://ocw.ump.edu.my/pluginfile.php/11228...al%20Wiring.pdf alfiejr and mactreouser liked this post
|
|
|
Jul 1 2022, 09:23 AM
Show posts by this member only | IPv6 | Post
#15
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
4,998 posts Joined: Dec 2010 |
40 strands wire is for power circuit or signal?
|
|
|
Jul 2 2022, 09:39 PM
Show posts by this member only | IPv6 | Post
#16
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,512 posts Joined: Sep 2007 |
QUOTE(iSean @ Jun 30 2022, 10:33 PM) What wiring work you doing? Thanks for the information! I'm not Pro , just love to DIY 😁Please find the sizing over here. 1.5mm2 for lighting/fans, 2.5mm^2 for rings sockets (regular non high current sockets) 4mm^2 for higher loads / kitchen ![]() http://ocw.ump.edu.my/pluginfile.php/11228...al%20Wiring.pdf Learned some ideas from Seller, 1.5mm for normal appliances, 2.5mm for Appliances like Microwave and Oven. The 4mm wires for Kitchen means? Sockets or Appliances? |
|
|
Jul 3 2022, 08:35 AM
Show posts by this member only | IPv6 | Post
#17
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
4,498 posts Joined: Jun 2011 |
QUOTE(mactreouser @ Jul 2 2022, 09:39 PM) Thanks for the information! I'm not Pro , just love to DIY 😁 Terminate to 3 pin socketLearned some ideas from Seller, 1.5mm for normal appliances, 2.5mm for Appliances like Microwave and Oven. The 4mm wires for Kitchen means? Sockets or Appliances? mactreouser liked this post
|
|
|
Jul 3 2022, 10:03 AM
Show posts by this member only | IPv6 | Post
#18
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
3,836 posts Joined: Aug 2016 |
ceo684 can advise. mactreouser liked this post
|
|
|
Jul 4 2022, 03:01 AM
Show posts by this member only | IPv6 | Post
#19
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
usually all these weird size like 40/0076 or 70/0076 don't meet ST requirement for electrical wiring. also, there are substandard cables (fake copper) around in the market. this is something that one should read up on as electrical safety is not to be trifled with mactreouser liked this post
|
|
|
Jul 4 2022, 05:47 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
4,547 posts Joined: Dec 2004 From: Metro Prima, Kuala Lumpur, Malaysia, Earth, Sol |
QUOTE(New Klang @ Jul 1 2022, 09:23 AM) should be power, signal dont need 40 strands. even so still missing the material, like copper or zinc, copper is alot better, but zinc is cheaper. mactreouser liked this post
|
|
|
Jul 4 2022, 08:02 AM
Show posts by this member only | IPv6 | Post
#21
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
4,998 posts Joined: Dec 2010 |
QUOTE(ceo684 @ Jul 4 2022, 03:01 AM) usually all these weird size like 40/0076 or 70/0076 don't meet ST requirement for electrical wiring. also, there are substandard cables (fake copper) around in the market. this is something that one should read up on as electrical safety is not to be trifled with QUOTE(narf03 @ Jul 4 2022, 05:47 AM) should be power, signal dont need 40 strands. even so still missing the material, like copper or zinc, copper is alot better, but zinc is cheaper. I don't see how 0.16mm diameter strands can have the strength to withstand cable pulling. Maybe this type don't get pulled over long distances.We usually use 7 strands cables with minimum 1.5 mm sq for power. Is there zinc cable? I know of copper and aluminum. mactreouser liked this post
|
|
|
Jul 4 2022, 08:46 AM
Show posts by this member only | IPv6 | Post
#22
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(New Klang @ Jul 4 2022, 08:02 AM) I don't see how 0.16mm diameter strands can have the strength to withstand cable pulling. Maybe this type don't get pulled over long distances. Those are substandard size.. not even 1.5mm² for light circuit.. u can google the sizingWe usually use 7 strands cables with minimum 1.5 mm sq for power. Is there zinc cable? I know of copper and aluminum. hence they are only used as device cord NOT permanent installation (which is the usual 1.5, 2.5, 4.0 kind of sizing) They make horrible device cords if ur stripping using pliers (not a jig) as its too easy to cut thru the hair thin metal (if u wired LED lights u will know how annoyingly smol) This post has been edited by ceo684: Jul 4 2022, 08:49 AM mactreouser liked this post
|
|
|
Jul 4 2022, 08:50 AM
Show posts by this member only | IPv6 | Post
#23
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
4,998 posts Joined: Dec 2010 |
QUOTE(ceo684 @ Jul 4 2022, 08:46 AM) Those are substandard size.. not even 1.5mm² for light circuit.. u can google the sizing In offshore projects, minimum power cable size is 2.5 mm sq though.hence they are only used as device cord NOT permanent installation (which is the usual 1.5, 2.5, 4.0 kind of sizing) They make horrible device cords if ur stripping using pliers (not a jig) as its too easy to cut thru the hair thin metal (if u wired LED lights u will know how annoyingly smol) 7 strands are due to withstanding termination crimping stress Yes, 40 strands are not suitable for insulation wire strippers. This post has been edited by New Klang: Jul 4 2022, 08:53 AM mactreouser and ceo684 liked this post
|
|
|
Jul 4 2022, 11:21 AM
Show posts by this member only | IPv6 | Post
#24
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,033 posts Joined: Jul 2005 |
Unless you are building another webb telescope, why need to be so particular about the wire spec. In Msia we use cross sectional area 1.5mm2, 2.5mm2 for wire size. mactreouser liked this post
|
|
|
Jul 4 2022, 12:55 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
4,547 posts Joined: Dec 2004 From: Metro Prima, Kuala Lumpur, Malaysia, Earth, Sol |
QUOTE(New Klang @ Jul 4 2022, 08:02 AM) I don't see how 0.16mm diameter strands can have the strength to withstand cable pulling. Maybe this type don't get pulled over long distances. got, my ups use big fat zinc cable, connecting the battery.We usually use 7 strands cables with minimum 1.5 mm sq for power. Is there zinc cable? I know of copper and aluminum. mactreouser liked this post
|
|
|
Jul 4 2022, 12:58 PM
Show posts by this member only | IPv6 | Post
#26
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
5,650 posts Joined: Mar 2012 |
Frankly this is obsolete standard from British era Now no one in the world use anymore lagenda110 and mactreouser liked this post
|
|
|
Jul 4 2022, 01:03 PM
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,791 posts Joined: Jul 2011 |
I always use 70/76 standard. mactreouser liked this post
|
|
|
Jul 4 2022, 02:17 PM
Show posts by this member only | IPv6 | Post
#28
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,033 posts Joined: Jul 2005 |
QUOTE(narf03 @ Jul 4 2022, 12:55 PM) There is only 2 type of material commonly used for cable construction, copper and aluminium. Zinc is just the coating. mactreouser liked this post
|
|
|
Jul 4 2022, 03:35 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
4,547 posts Joined: Dec 2004 From: Metro Prima, Kuala Lumpur, Malaysia, Earth, Sol |
QUOTE(Singh_Kalan @ Jul 4 2022, 02:17 PM) There is only 2 type of material commonly used for cable construction, copper and aluminium. Zinc is just the coating. oh then i might be wrong, saw the material, then do some google, found zinc, i tot its zinc. mactreouser liked this post
|
|
|
Jul 5 2022, 01:55 AM
Show posts by this member only | IPv6 | Post
#30
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,512 posts Joined: Sep 2007 |
QUOTE(ceo684 @ Jul 4 2022, 03:01 AM) usually all these weird size like 40/0076 or 70/0076 don't meet ST requirement for electrical wiring. I see! But we consumer, hard to differentiate, right? also, there are substandard cables (fake copper) around in the market. this is something that one should read up on as electrical safety is not to be trifled with QUOTE(narf03 @ Jul 4 2022, 05:47 AM) should be power, signal dont need 40 strands. even so still missing the material, like copper or zinc, copper is alot better, but zinc is cheaper. What does SIGNAL means. For example? |
|
|
Jul 5 2022, 02:01 AM
Show posts by this member only | IPv6 | Post
#31
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,512 posts Joined: Sep 2007 |
QUOTE(Singh_Kalan @ Jul 4 2022, 11:21 AM) Unless you are building another webb telescope, why need to be so particular about the wire spec. In Msia we use cross sectional area 1.5mm2, 2.5mm2 for wire size. Ya lo. When I asked options or suggestions from the store, they only mentions 1.5mm or 2.5mm. and most probably go for 2.5mm! |
|
|
Jul 5 2022, 02:06 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
4,547 posts Joined: Dec 2004 From: Metro Prima, Kuala Lumpur, Malaysia, Earth, Sol |
QUOTE(mactreouser @ Jul 5 2022, 01:55 AM) signal means data, like network cable, the cable that connect from switch to your autogate(send signal to open / close gate), ignore POE in this example.signal need very small amount of current, all it need to do is giving signal, not do work mactreouser liked this post
|
|
|
Jul 5 2022, 06:08 AM
Show posts by this member only | IPv6 | Post
#33
|
![]() ![]()
Junior Member
148 posts Joined: Jul 2022 |
Go for mega cable for the best quality.... Usually there are 3 sizes... 1.5mm 2.5mm 4mm Depend on your load... But imma recommend 2.5mm and 4mm mactreouser liked this post
|
|
|
Jul 5 2022, 09:20 AM
Show posts by this member only | IPv6 | Post
#34
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(New Klang @ Jul 4 2022, 08:50 AM) In offshore projects, minimum power cable size is 2.5 mm sq though. Yup, my power extension also made from 2.5mmsq7 strands are due to withstanding termination crimping stress Yes, 40 strands are not suitable for insulation wire strippers. Whatever I plug in to it will be comfortably cool QUOTE(Singh_Kalan @ Jul 4 2022, 11:21 AM) Unless you are building another webb telescope, why need to be so particular about the wire spec. In Msia we use cross sectional area 1.5mm2, 2.5mm2 for wire size. It becomes a technicality that insurance can and will use to deny claim if you use substandard cable in permanent installation.Weakest point is the ceiling for max current capacity of any cable. QUOTE(fireballs @ Jul 4 2022, 12:58 PM) Still got sell on spee. Its alright for low voltage battery experiments for school but certainly not for point wiring (permanent installation)QUOTE(pretty23 @ Jul 4 2022, 01:03 PM) Even power strips also use 1.25mmsq as minimum standard in SG. mactreouser liked this post
|
|
|
Jul 5 2022, 10:15 AM
Show posts by this member only | IPv6 | Post
#35
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,033 posts Joined: Jul 2005 |
For small cable/wire size < 6mm2, the manufacturer is more important. Some wire imported from China, the insulation will become brittle after few years, esp when exposed to UV. Pose a big risk for fire and electrocution. mactreouser liked this post
|
|
|
Jul 8 2022, 05:34 PM
Show posts by this member only | IPv6 | Post
#36
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
4,998 posts Joined: Dec 2010 |
|
|
|
Jul 18 2022, 03:52 PM
Show posts by this member only | IPv6 | Post
#37
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,512 posts Joined: Sep 2007 |
QUOTE(narf03 @ Jul 5 2022, 02:06 AM) signal means data, like network cable, the cable that connect from switch to your autogate(send signal to open / close gate), ignore POE in this example. I see! So, switch for lamps/lights consider Signal Cable? signal need very small amount of current, all it need to do is giving signal, not do work QUOTE(lagenda110 @ Jul 5 2022, 06:08 AM) Go for mega cable for the best quality.... Mega Cable means the Brand? If that's the name, a lot of people recommended Fajar Cable. Usually there are 3 sizes... 1.5mm 2.5mm 4mm Depend on your load... But imma recommend 2.5mm and 4mm QUOTE(ceo684 @ Jul 5 2022, 09:20 AM) Yup, my power extension also made from 2.5mmsq You always provided very Pro & Useful informations! Learned something 😁Whatever I plug in to it will be comfortably cool It becomes a technicality that insurance can and will use to deny claim if you use substandard cable in permanent installation. Weakest point is the ceiling for max current capacity of any cable. Still got sell on spee. Its alright for low voltage battery experiments for school but certainly not for point wiring (permanent installation) Even power strips also use 1.25mmsq as minimum standard in SG. Does it mean, no matter what's the purpose for, you'll always go for 2.5mm? |
|
|
Jul 18 2022, 04:21 PM
Show posts by this member only | IPv6 | Post
#38
|
![]() ![]()
Junior Member
148 posts Joined: Jul 2022 |
QUOTE(mactreouser @ Jul 18 2022, 03:52 PM) I see! So, switch for lamps/lights consider Signal Cable? haha go for mega cable brand sir for best qualityMega Cable means the Brand? If that's the name, a lot of people recommended Fajar Cable. You always provided very Pro & Useful informations! Learned something 😁 Does it mean, no matter what's the purpose for, you'll always go for 2.5mm? |
|
|
Jul 19 2022, 11:25 PM
Show posts by this member only | IPv6 | Post
#39
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(mactreouser @ Jul 18 2022, 03:52 PM) I see! So, switch for lamps/lights consider Signal Cable? That depends on what u installing, if concealed in-wall circuits carrying 230V must follow 1.5mm minMega Cable means the Brand? If that's the name, a lot of people recommended Fajar Cable. You always provided very Pro & Useful informations! Learned something 😁 Does it mean, no matter what's the purpose for, you'll always go for 2.5mm? its super cheap even if u buy loose cut per meter don't even bother getting anything thinner because hard to strip if its those extra low voltage purposes like HDMI/ LAN cable then its not really a problem on cable thickness since those are only for data signal 2.5mm so peace of mind as this is way overspec, its the same stuff as in-wall so this extension can use macam a wall socket (use kettle or vacuum or rotohammers). Its heavy, and expensive, nobody will use 2.5mm except me 1.25mm SG standard for power strips because that CCA > 13A so anyhow fuse will blow before wire catch fire Using lousy wire for power strips just mean that the wire will overheat before 13A fuse blow all those 40/0076 70/0076 are substandard cable spec. good for kids to play with science experiments to light up 12V car bulb je This post has been edited by ceo684: Jul 19 2022, 11:34 PM mactreouser liked this post
|
|
|
Mar 9 2023, 10:03 AM
Show posts by this member only | IPv6 | Post
#40
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,512 posts Joined: Sep 2007 |
QUOTE(ceo684 @ Jul 19 2022, 11:25 PM) That depends on what u installing, if concealed in-wall circuits carrying 230V must follow 1.5mm min How abou wallt socket for Electric Stove (2500-3500w) ... Oven... Microwave? 2.5mm cable or 1.5mm is good enough?its super cheap even if u buy loose cut per meter don't even bother getting anything thinner because hard to strip if its those extra low voltage purposes like HDMI/ LAN cable then its not really a problem on cable thickness since those are only for data signal 2.5mm so peace of mind as this is way overspec, its the same stuff as in-wall so this extension can use macam a wall socket (use kettle or vacuum or rotohammers). Its heavy, and expensive, nobody will use 2.5mm except me 1.25mm SG standard for power strips because that CCA > 13A so anyhow fuse will blow before wire catch fire Using lousy wire for power strips just mean that the wire will overheat before 13A fuse blow all those 40/0076 70/0076 are substandard cable spec. good for kids to play with science experiments to light up 12V car bulb je |
|
|
Mar 9 2023, 08:17 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(mactreouser @ Mar 9 2023, 10:03 AM) How abou wallt socket for Electric Stove (2500-3500w) ... Oven... Microwave? 2.5mm cable or 1.5mm is good enough? 13A SSO must be 2.5mm minDouble socket use 4mm Electric stove >2990W need to be professionally installed, if it didn't come with a plug top from factory it is not supposed to be used on 13A socket. Either 20A isolator or CEE commando plug This post has been edited by ceo684: Mar 9 2023, 09:17 PM mactreouser liked this post
|
|
|
Mar 10 2023, 10:56 AM
Show posts by this member only | IPv6 | Post
#42
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,512 posts Joined: Sep 2007 |
QUOTE(ceo684 @ Mar 9 2023, 08:17 PM) 13A SSO must be 2.5mm min Appreciate your comments! You always awesome la 😁Double socket use 4mm Electric stove >2990W need to be professionally installed, if it didn't come with a plug top from factory it is not supposed to be used on 13A socket. Either 20A isolator or CEE commando plug Sorry, may I supposed to further describe! The Electric Stove means those "Portable" one, came with a Power Cord! Oh? Double Socket needs a 4mm Cable?! Alamak, I fixed with 2.5mm Cable! Btw, it's so hard to apply a 2.5mm cable into a Double Socket already, can't imagine go with 4mm 😅 So, 2.5mm definitely not recommended? |
|
|
Mar 11 2023, 10:08 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,791 posts Joined: May 2008 |
Another keyword to look when buying extension cable is 'pure copper" and "SIRIM" Some 'pure cooper' cable dont have SIRIM but it ok as long it 's real 'pure cooper' mactreouser liked this post
|
|
|
Mar 11 2023, 12:40 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,512 posts Joined: Sep 2007 |
QUOTE(JLA @ Mar 11 2023, 10:08 AM) Another keyword to look when buying extension cable is 'pure copper" and "SIRIM" Ya lo. But the problem is , a lot of people said that although it mentioned Pure Copper but it may be Not! So? How to ensure? 🤣Some 'pure cooper' cable dont have SIRIM but it ok as long it 's real 'pure cooper' |
|
|
Mar 13 2023, 04:52 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,220 posts Joined: Apr 2006 |
"40/0.16" refers to the construction of the cable's conductors. The first number (40) indicates the number of individual strands or wires that are twisted together to form the conductor. In this case, there are 40 strands. The second number (0.16) refers to the diameter of each individual strand, measured in millimeters. In this case, each strand has a diameter of 0.16mm. So, the full designation "40/0.16" means that the cable has 40 individual strands, each with a diameter of 0.16mm, twisted together to form a single conductor. This type of cable is commonly used for low voltage applications, such as in electronics and small appliances. mactreouser and ozak liked this post
|
|
|
Mar 13 2023, 04:53 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,220 posts Joined: Apr 2006 |
QUOTE(mactreouser @ Mar 11 2023, 12:40 PM) Ya lo. But the problem is , a lot of people said that although it mentioned Pure Copper but it may be Not! So? How to ensure? 🤣 There are a few methods you can use to verify if a copper cable is genuine copper:Look for a copper hallmark: If you have access to a magnifying glass, you can look for a hallmark on the surface of the copper cable. This hallmark will typically indicate that the cable is made of genuine copper. Check the color: Copper has a distinct reddish-brown color, so if the cable has a different color or appears to be painted, it may not be genuine copper. Check the weight: Copper is a dense metal, so a genuine copper cable should feel heavier than a similarly sized cable made from another material. You can compare the weight of the copper cable to a known copper sample of the same size. Conduct a magnet test: Copper is not magnetic, so if the cable is attracted to a magnet, it may not be genuine copper. Test the conductivity: Copper is an excellent conductor of electricity, so you can use a multimeter to test the cable's conductivity. Touch one end of the multimeter to the copper wire and the other end to a known conductor. If the meter reads a high level of conductivity, the cable is likely genuine copper. It's important to note that some copper cables may be coated with a layer of another material, such as tin or silver, so these tests may not always be conclusive. If you're unsure about the authenticity of a copper cable, you can consult a professional or take it to a testing facility for analysis. mactreouser liked this post
|
|
|
Apr 2 2023, 02:30 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,512 posts Joined: Sep 2007 |
QUOTE(billyboy @ Mar 13 2023, 04:52 PM) "40/0.16" refers to the construction of the cable's conductors. Cool! Thanks for the idea! I still get stuck in here lately, especially the following 0.16. as you mentioned, 0.16mm for "each" strand, that means the very little thin copper in every LNE? At first I thought it's the size of each LNE, means Live cable 0.16mm and so on. 😅The first number (40) indicates the number of individual strands or wires that are twisted together to form the conductor. In this case, there are 40 strands. The second number (0.16) refers to the diameter of each individual strand, measured in millimeters. In this case, each strand has a diameter of 0.16mm. So, the full designation "40/0.16" means that the cable has 40 individual strands, each with a diameter of 0.16mm, twisted together to form a single conductor. This type of cable is commonly used for low voltage applications, such as in electronics and small appliances. So, in Malaysia we always mention Cable size in 1.5mm, 2.5mm, 4mm , right? But in US they called that AWG/Guage? In "mm" seems better way to understand ya. QUOTE(billyboy @ Mar 13 2023, 04:53 PM) There are a few methods you can use to verify if a copper cable is genuine copper: Wow .. love it. Thanks for your efforts! Magnet seems the best way to check ya??Look for a copper hallmark: If you have access to a magnifying glass, you can look for a hallmark on the surface of the copper cable. This hallmark will typically indicate that the cable is made of genuine copper. Check the color: Copper has a distinct reddish-brown color, so if the cable has a different color or appears to be painted, it may not be genuine copper. Check the weight: Copper is a dense metal, so a genuine copper cable should feel heavier than a similarly sized cable made from another material. You can compare the weight of the copper cable to a known copper sample of the same size. Conduct a magnet test: Copper is not magnetic, so if the cable is attracted to a magnet, it may not be genuine copper. Test the conductivity: Copper is an excellent conductor of electricity, so you can use a multimeter to test the cable's conductivity. Touch one end of the multimeter to the copper wire and the other end to a known conductor. If the meter reads a high level of conductivity, the cable is likely genuine copper. It's important to note that some copper cables may be coated with a layer of another material, such as tin or silver, so these tests may not always be conclusive. If you're unsure about the authenticity of a copper cable, you can consult a professional or take it to a testing facility for analysis. |