QUOTE(Notconfused @ Jan 27 2022, 08:57 PM)
Hello folks
Need your input here...
Is it ok to remove 20a power socket and connect air contidioners directly to DB? I was told it’s optional but water heater must have a 20a power socket...
Thanks ya
It is common.Need your input here...
Is it ok to remove 20a power socket and connect air contidioners directly to DB? I was told it’s optional but water heater must have a 20a power socket...
Thanks ya
The 20A S/S/O normally comes with 2 poles A/C switch for on/off & is drawing the power from direct 20A MCB breaker from the DB.
Water heater should have the same connection like AC without the face plate, the only different for the water heater point would be the requirement for 10mA RCCB at the outgoing of the 20A MCB as per ST's regulation.