 Switch to 3 pin plug.

views
     
TSFusionXY
post Dec 31 2021, 09:13 PM, updated 4y ago

LAZZIE ON VACATION
*******
Senior Member
3,836 posts

Joined: Aug 2016

Hey, I plan to connect light switch to connect to 3 pin plug.
As my socket is under the wall TV cabinet. I have to squat down to switch off and on everytime. Like make off and on switch somewhere near the TV cabinet while the main switch remain on whole time.

I plan to use 3 pin plug then to switch then to 3 pin socket.

3 pin plug top - - Switch - - Socket.
I saw one hotel they put the switch outside connected to 3 pin plug to power up the mini bar.
SUSceo684
post Dec 31 2021, 09:21 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




Why not just extend the socket's L&N (two wires only) up to a more accessible position (using a WH 20A switch), so that the switch is more visible and no need to crawl around?

This post has been edited by ceo684: Dec 31 2021, 09:22 PM
TSFusionXY
post Dec 31 2021, 09:27 PM

LAZZIE ON VACATION
*******
Senior Member
3,836 posts

Joined: Aug 2016

QUOTE(ceo684 @ Dec 31 2021, 09:21 PM)
Why not just extend the switch (two wires only) up to a more accessible position, so that the switch is more visible and no need to crawl around?
*
Ya. My situation is that my socket is under the table.
Plan to use to switch on and off speaker while not in use.
Cause I have to open and close the cover everytime I want to turn off and on.
My TV and android box always switch on the whole time.

Meaning that I want to rewire switch to 3 pin plug. Like switch put above cabinet when using. Another thing is using extension.
Extension socket good idea but have to crawl under the cabinet.

Like switch to 3 pin. Do I have to use the water heater switch?
Seems like light switch no earth connection.
SUSceo684
post Dec 31 2021, 09:40 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(FusionXY @ Dec 31 2021, 09:27 PM)
Ya. My situation is that my socket is under the table.
Plan to use to switch on and off speaker while not in use.
Cause I have to open and close the cover everytime I want to turn off and on.
My TV and android box always switch on the whole time.

Meaning that I want to rewire switch to 3 pin plug. Like switch put above cabinet when using. Another thing is using extension.
Extension socket good idea but have to crawl under the cabinet.

Like switch to 3 pin. Do I have to use the water heater switch?
Seems like light switch no earth connection.
*
Normal switch is 10A rated.. ur socket rated for 13A..and it only cut L.

It is better to use WH 20A switch, rated for 20A > 13A socket, and cuts both L and N.

WH switch just earth to the earthing screw.

Cable use proper cable like Mega Kabel 2.5mm², shopee/lazada got sell loose cuts per meter, not expensive.

Connectors you will need 2x Wago 221-412 at the very minimum. Can get frm shopee LINK or element14 (bit more expensive but confirm legit LINK.

Alternatively can also use the usual connector blocks but quite mafan lah, as some are poorly made. Wago is screwless.

This post has been edited by ceo684: Dec 31 2021, 09:41 PM
TSFusionXY
post Dec 31 2021, 11:17 PM

LAZZIE ON VACATION
*******
Senior Member
3,836 posts

Joined: Aug 2016

QUOTE(ceo684 @ Dec 31 2021, 09:40 PM)
Normal switch is 10A rated.. ur socket rated for 13A..and it only cut L.

It is better to use WH 20A switch, rated for 20A > 13A socket, and cuts both L and N.

WH switch just earth to the earthing screw.

Cable use proper cable like Mega Kabel 2.5mm², shopee/lazada got sell loose cuts per meter, not expensive.

Connectors you will need 2x Wago 221-412 at the very minimum. Can get frm shopee LINK or element14 (bit more expensive but confirm legit LINK.

Alternatively can also use the usual connector blocks but quite mafan lah, as some are poorly made. Wago is screwless.
*
Thank you. Will try this.
SUSceo684
post Dec 31 2021, 11:43 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(FusionXY @ Dec 31 2021, 11:17 PM)
Thank you. Will try this.
*
Most welcome. I think the diagram didnt attach properly earlier.


Attached thumbnail(s)
Attached Image
TSFusionXY
post Jan 1 2022, 12:33 AM

LAZZIE ON VACATION
*******
Senior Member
3,836 posts

Joined: Aug 2016

QUOTE(ceo684 @ Dec 31 2021, 11:43 PM)
Most welcome. I think the diagram didnt attach properly earlier.
*
Exactly my setup.
Thumbs up.
TSFusionXY
post Jan 1 2022, 01:13 AM

LAZZIE ON VACATION
*******
Senior Member
3,836 posts

Joined: Aug 2016

The wire connector to connect which one?
Saw some water heater switch can connect 3 cables.
SUSceo684
post Jan 1 2022, 01:25 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(FusionXY @ Jan 1 2022, 01:13 AM)
The wire connector to connect which one?
Saw some water heater switch can connect 3 cables.
*
From the original socket (IN-WALL wiring) it is just few inches.. in order to connect the L and N UP to the WH switch line side, need to extend - use the Wago connector - and one length of the new mega kabel.
Then, from the WH switch load side, another length of new mega kabel come back DOWN to the original 13A socket.

You will basically need twice the distance for red and black mega kabel 2.5mm²
and a single distance for the green mega kabel 2.5mm²

Meaning, if the extension is like 130cm then buy 3m of red+black and 2m of the green. U can get loose cut 2.5mm (by meter) here in the correct colours: LINK

For the E, just run one length up from the original 13A socket E to the WH switch's E.

It should be possible to conceal in-wall if you have a rotary hammer can do the hacking chase, cables go in concealed PVC conduit then patch back afterwards with ready mix cement+a bit of putty.

This post has been edited by ceo684: Jan 1 2022, 01:28 AM
TSFusionXY
post Jan 1 2022, 03:50 AM

LAZZIE ON VACATION
*******
Senior Member
3,836 posts

Joined: Aug 2016

QUOTE(ceo684 @ Jan 1 2022, 01:25 AM)
From the original socket (IN-WALL wiring) it is just few inches.. in order to connect the L and N UP to the WH switch line side, need to extend - use the Wago connector - and one length of the new mega kabel.
Then, from the WH switch load side, another length of new mega kabel come back DOWN to the original 13A socket.

You will basically need twice the distance for red and black mega kabel 2.5mm²
and a single distance for the green mega kabel 2.5mm²

Meaning, if the extension is like 130cm then buy 3m of red+black and 2m of the green. U can get loose cut 2.5mm (by meter) here in the correct colours: LINK

For the E, just run one length up from the original 13A socket E to the WH switch's E.

It should be possible to conceal in-wall if you have a rotary hammer can do the hacking chase, cables go in concealed PVC conduit then patch back afterwards with ready mix cement+a bit of putty.
*
Oh. You mean disconnect the old socket.
Oh I rewire plug top then connect switch then socket?
SUSceo684
post Jan 1 2022, 04:44 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(FusionXY @ Jan 1 2022, 03:50 AM)
Oh. You mean disconnect the old socket.
Oh I rewire plug top then connect switch then socket?
*
Nope.. i mean add a 20A WH switch to control power feeding the existing socket. Then u can just use the 20A switch to on off the sockrt, which u can leave on permanently.
TSFusionXY
post Jan 1 2022, 05:05 AM

LAZZIE ON VACATION
*******
Senior Member
3,836 posts

Joined: Aug 2016

QUOTE(ceo684 @ Jan 1 2022, 04:44 AM)
Nope.. i mean add a 20A WH switch to control power feeding the existing socket. Then u can just use the 20A switch to on off the sockrt, which u can leave on permanently.
*
Okay.

My setup is like this below.
3 pin plug > WH Switch > Socket.
Can I connect more than socket with this setup?
TSFusionXY
post Jan 1 2022, 05:17 AM

LAZZIE ON VACATION
*******
Senior Member
3,836 posts

Joined: Aug 2016

If I plan to use the plug top. How much current plug top fuse should I get?
13A plug?
SUSceo684
post Jan 1 2022, 03:50 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(FusionXY @ Jan 1 2022, 05:17 AM)
If I plan to use the plug top. How much current plug top fuse should I get?
13A plug?
*
That depends on the equipment power rating. Up to 1kW can use 5A fuse. Up to 3kW use 13A fuse.

This post has been edited by ceo684: Jan 1 2022, 03:50 PM
TSFusionXY
post Jan 1 2022, 04:32 PM

LAZZIE ON VACATION
*******
Senior Member
3,836 posts

Joined: Aug 2016

QUOTE(ceo684 @ Jan 1 2022, 03:50 PM)
That depends on the equipment power rating. Up to 1kW can use 5A fuse. Up to 3kW use 13A fuse.
*
I'm using for speakers with subwoofer.
I think 13A Fuse plug better.
TSFusionXY
post Jan 2 2022, 02:25 AM

LAZZIE ON VACATION
*******
Senior Member
3,836 posts

Joined: Aug 2016

One more question.
ceo684
2.5mm is the best choice?
What's the difference between 1.5mm and 2.5mm?
SUSceo684
post Jan 2 2022, 04:04 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(FusionXY @ Jan 2 2022, 02:25 AM)
One more question.
ceo684
2.5mm is the best choice?
What's the difference between 1.5mm and 2.5mm?
*
2.5mm is the best choice?
Yes, you are not buying them by 100m rolls, it is because technically the in-wall wiring is also 2.5mm² to that existing socket.

What's the difference between 1.5mm and 2.5mm?
🔥🔥🔥 vs 🆗
One does not compromise the chain by introducing a weak point. By regulation, all 13A socket need to use a minimum of 2.5mm² cables for the IN-WALL part. Otherwise you need to derate the MCB instead of 20A you need to downgrade the MCB to 10A. Which means spending another 8 bucks for a MCB. Might as well just keep the whole chain 2.5mm².

This post has been edited by ceo684: Jan 2 2022, 04:05 AM
TSFusionXY
post Jan 2 2022, 03:48 PM

LAZZIE ON VACATION
*******
Senior Member
3,836 posts

Joined: Aug 2016

QUOTE(ceo684 @ Jan 2 2022, 04:04 AM)
2.5mm is the best choice?
Yes, you are not buying them by 100m rolls, it is because technically the in-wall wiring is also 2.5mm² to that existing socket.

What's the difference between 1.5mm and 2.5mm?
🔥🔥🔥 vs 🆗
One does not compromise the chain by introducing a weak point. By regulation, all 13A socket need to use a minimum of 2.5mm² cables for the IN-WALL part. Otherwise you need to derate the MCB instead of 20A you need to downgrade the MCB to 10A. Which means spending another 8 bucks for a MCB. Might as well just keep the whole chain 2.5mm².
*
1.5mm for lamp only right?
I checked the air conditioner wiring also use 2.5mm type.
TSFusionXY
post Jan 2 2022, 04:26 PM

LAZZIE ON VACATION
*******
Senior Member
3,836 posts

Joined: Aug 2016

ceo684
I checked in Shopee for the copper wire.
40/0076 is the correct one?
Or 70/0076? This one for high power?

Fajar 1.5mm or 2.5mm copper?
Notice one shop using 1.5mm for extension.
user posted image

1.5mm flexible cable equals to 2.5mm pvc cable?

Below are four options.
Which is the correct ones for which purposes?
user posted image

Mind to share what's the difference between 4 sizes.

This post has been edited by FusionXY: Jan 2 2022, 05:25 PM
N9484640
post Jan 2 2022, 09:05 PM

Chasing Electric
******
Senior Member
1,297 posts

Joined: Aug 2014
Just change to smart wall socket or smart plug
https://shopee.com.my/WPM-Home-Tuya-Wifi-Un...50-67b8b50f2b7f

https://shopee.com.my/WPM-Home-Tuya-Smart-W...de-5f4c0b827a6e

https://shopee.com.my/TP-Link-3-Outlets-Wif...b4-18385cb076e1

I connect my subwoofers power plug to these. Can on/off using voice command or using your smartphone app

This post has been edited by N9484640: Jan 2 2022, 09:06 PM
TSFusionXY
post Jan 2 2022, 09:18 PM

LAZZIE ON VACATION
*******
Senior Member
3,836 posts

Joined: Aug 2016

QUOTE(N9484640 @ Jan 2 2022, 09:05 PM)
Just change to smart wall socket or smart plug
https://shopee.com.my/WPM-Home-Tuya-Wifi-Un...50-67b8b50f2b7f

https://shopee.com.my/WPM-Home-Tuya-Smart-W...de-5f4c0b827a6e

https://shopee.com.my/TP-Link-3-Outlets-Wif...b4-18385cb076e1

I connect my subwoofers power plug to these. Can on/off using voice command or using your smartphone app
*
Great idea.

Will try setup.
SUSceo684
post Jan 3 2022, 12:58 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(FusionXY @ Jan 2 2022, 03:48 PM)
1.5mm for lamp only right?
I checked the air conditioner wiring also use 2.5mm type.
*
QUOTE(FusionXY @ Jan 2 2022, 04:26 PM)
ceo684
I checked in Shopee for the copper wire.
40/0076 is the correct one? HELL NO
Or 70/0076? This one for high power? OH NO

Fajar 1.5mm or 2.5mm copper? 2.5mm
Notice one shop using 1.5mm for extension. I use 2.5mm myself. If its smaller than your pinky finger there is not enough copper. Do not skimp and make a weak link.
user posted image

1.5mm flexible cable equals to 2.5mm pvc cable? No boss.. that 1.5mm is only rated for lights. It being a 13A socket has a 2.5mm legal requirement

Below are four options.
Which is the correct ones for which purposes?
user posted image

Mind to share what's the difference between 4 sizes.
*
All those elcheapo 0076 stuff is usually lamp cord of useless thickness.
Photo show 3Cx40 (0076). Notice HOW SMALL the wires are. The ones in the wall look humongous (but they're 2.5mm) - https://forum.lowyat.net/index.php?showtopi...post&p=98247271

Just get Mega Kabel 2.5mm since its gonna be concealed in conduit. This one JKR spec.

Or if you want to make an extension then spec it with 2.5mm Fajar Cable, add a cable gland 10mm and the 4-gang backbox.

 