PSA on electrical safety since you haven't started anything.

For water heater safety
WH circuit if you are redoing the wiring for it, use 4.0mm² cables per ST spec.
Good cables from Mega Kabel/Caramay/Fajar Cable cost more. But they are "cheng liu" with all the SIRIM legit certification.
There are elcheapo/fake cables at half price I also don't dare to install in customer premises. Safety first.

More importantly each WH circuit (basically each unit) need its own 10mA RCD/RCBO 0.01A (NOT 0.1A).
Check DB box to see if such thing exist.

For further reading Attached File  Guideline_for_The_Design_Installation_Inspection_Testing_Operation_and_Maintenance_of_Water_Heater_Systems__1_.pdf ( 4.49mb ) Number of downloads: 25


Having a 10mA RCD fitted will prevent the likelihood of becoming news material.
https://www.straitstimes.com/asia/se-asia/m...e-having-shower
https://www.malaymail.com/news/malaysia/202...c-shock/1896447


For whole house electrical safety
Per ST (Suruhanjaya Tenaga) regulations - to be fully compliant - you should use a 30mA whole house high sensitivity RCD (0.03A NOT 0.3A) for human life safety.

100mA & 300mA RCDs should only be used in commercial/industrial as they are NOT very useful to protect human life
They are commonly fitted in residential as they are indeed cheap coz less sensitive and they are only good for preventing building from catching fire.


Attached Image

Attached Image
SUSceo684
post May 8 2021, 09:41 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




PSA on your 1F yard extension wall design.

Remember kids can and will climb over anything when you are not watching for a moment.
Pls use ONLY either:
solid wall or VERTICAL elements if you are putting in metal rails.

HORIZONTAL elements have been outlawed in the US, UK for staircase railings and safety barriers.
However this is from a newly VPed high-rise project icon_question.gif see the danger?

Attached Image
SUSceo684
post May 8 2021, 09:48 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(jeffboon97 @ May 8 2021, 09:43 PM)
Thank you so much for the guidance! I'll keep this in mind, my brother is an electrician so I don't want to cheap out on electrical else my brother will nag me if I do!

Also, do you prefer AC or DC Water heat?
Based on my research it seems like DC pump is more long last and quieter, but not as powerful as AC?
*
Most welcome. Good to know you've got someone competent to handle the electrical works. thumbup.gif
DC pump WH is better than AC. AC pump always noisier than the DC pump.

However if water pressure is good enough (this one really need to bring a hose to test on site) i.e. using just your thumb [fingerprint, not stuffing the thumb inside the hose ] to cover the water flow, try to stop the water, then you may NOT need a pump model.

> If you can stop the water with your thumb = water pressure weak. Get WH pump model.

> If it is virtually impossible to stop the water with your thumb = water pressure good. WH pump optional.
SUSceo684
post May 8 2021, 10:20 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(joeblow @ May 8 2021, 10:09 PM)
.
2. According to sales person, 5 blade supposed to have more wind and quieter. Another guy selling 3 blades claim the same. Currently I am using Rubine 3 blades DC motor, very quiet and good. So I still thinking if I should try the Panasonic ones.
*
I have a Pana Bayu 4 windless wonder POS fan. It is essentially the biggest regret of my life. I have installed and uninstalled it in 3 rooms from living to MBR to finally stuffing in smallest room. Windless as in even at max speed u put tissue on the table the tissue stay there, will never blow off. Want to donate away to people also I heartache to transfer uselessness to other people.

For ceiling fan
On a budget: The regulator 60" is cheap and produces most wind (8122 cfm or 230m³/min) it just doesnt look pretty.

Remote fan 56" <300 bucks usually metal blade. KDK OK. Pana latest range are POS, 2018 model windless, 2014 one strong wind.

Remote fan 56" 400 bucks Vtouch Jr/515 bucks Sensa 4 ABS blade, there is some better tech in the blade angle and they are excellent cfm too (225m³/min). These all use the same blade, tried and true design.

To reiterate NEVER ever buy a Pana POS remote fan (Bayu 4). Many forumer also regret in ceiling fan threads. Get a KDK.

KDK and Pana made in same factory, but Pana factory can modify Pana design and cost cutting suka hati as they are the principal.
KDK model made under license, local Pana assembler cannot modify spec, design, or cost cut without principal approval.
That is the fundamental difference.

This post has been edited by ceo684: May 8 2021, 10:29 PM
SUSceo684
post May 8 2021, 11:15 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(Zwean @ May 8 2021, 10:37 PM)
I have the Bayu 4.. no issue with wind... how high is your ceiling
*
Rumaweep 9.5 feet. Brand new in box POS.
I made the mistake of buying in 2018. Installed in 2019, no warranty.
It make a lot of grok grok noise at slow speed 1-2 even if i stripped the "dinner plate" naked.

P.S. I installed many fans in my lifetime, this was my 2nd Bayu 4.

I have a 2014 variant which works beautifully.

QUOTE(joeblow @ May 8 2021, 10:42 PM)
Thanks for the heads up. May I know what is POS fan?

Can you comment on these two model? I almost bought the panasonic one during 5 5 promotion.

Rubine Celling Fan Gavia 56" DC Motor RCF-GAVIA56
https://www.lazada.com.my//products/i202954...YL&urlFlag=true

PANASONIC F-M15GWSQH/F-M15GWSRH 60" DC MOTOR CEILING FAN
https://www.lazada.com.my//products/i143931...YL&urlFlag=true

Or can you recommend a good DC KDK model? Energy saving, super quiet and with LED. Thanks.
*
POS = Piece of Shite. laugh.gif

Sensa 4 (around RM515), DC brushless. thumbup.gif
https://shopee.com.my/KDK-K14ZW-56-Sensa-4-...5032.5642458864

All AC motor are brushless.
DC motor can be brushed or brushless type so need to make sure its brushless for long life.

Attached Image

QUOTE
Generally fans are very low consumption (up to ~70W at max speed on AC fan) especially at slow/mid speeds, you can't really feel the TNB bill diff even with "inefficient AC fan" as compared to inefficient aircon, fridges.


Sensa 4 (DC) is using same blades as Vtouch Jr (AC) and the previous EOL model Sensa 4 (AC).
This 56" blade design makes about 225m3/min wind which is very plentiful.
ABS blade is very quiet. No funny sounds like the POS Bayu 4 scraping against the center core.
Also, the safety device for Vtouch Jr/Sensa is using metal hook to the center core chassis. biggrin.gif

The POS Bayu 4 design is using a "clothes peg wire" as the safety device to prevent blade from flying off. rclxub.gif

You can go up to the Sensa 5 (DC) current model as well. The more fancy Nikko, Kaze are more nice-to-haves and doesn't make more wind lol.

QUOTE
5 blade supposed to have more wind and quieter.


No noticeable difference, I have a whole mix of fans 3-4-5 blades as long as it is not a faulty unit.
Wind sound is silent.

There is some slight differences in power consumption and cfm between the 4- and 5- bladed variants but it is within a few % you won't notice in a blind test.
4-bladed balancing is easier to do. 5-bladed ones more tricky to balance.

This post has been edited by ceo684: May 8 2021, 11:28 PM
SUSceo684
post May 9 2021, 12:27 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(davidlow7 @ May 9 2021, 11:21 AM)
Sorry for hijacking.
Hey mate,

Thanks for this. I just received my house key and intend to ensure all my electrical stuff are really safe for use - do you have any professional contacts we can reach out to ensure this follows the standard?

My experience with wiremen outside is they will use their experience but unfounded theories to justify things around without conforming to standard.
*
Whilst I do my own home wiring and the likes (DB box refresh with like for like) I don't possess a Wirewoman cert (I used to sell and commission inverters and production line (automation) sensors for industry/SME). A definition of "competent persons" based on https://www.st.gov.my/en/web/application/details/7/17 will be PW1 (Single Phase Wireman) or PW3 (Three Phase Wireman) certified personnel. I'm sure there are such wiremen who follow standards but mostly from what I see a lot have cowed to price pressure (to survive and win jobs) and do not strictly follow the ST requirements for residential wiring.

Usually new homes' wiring will still be following ST guidelines somewhat, what we can do here (easily) is that you take a picture of your consumer unit ("DB box") and upload here as attachment (NOT the "Upload Images" imgur pic as its hard to zoom). Then we'll look at it and see if anything major needs rectification.

Attached Image

FOR BETTER LYN FORUMER COMMENTARY
What we would want to see in your DB box are all the green text portions, i.e.
1. Overview of the DB box components (just open the user accessible panel). NO NEED to open the service panel.
2. Close ups of all the bigger blocks inside. We need to see the markings clearly to be able to comment.

Attached Image


FOR TESTING 13A SOCKETS
Some people use their phone charger. Phones must be cheap nowadays to risk as test devices.
I recommend bringing along one cheap table lamp (using a 230V bulb) just to plug/unplug test out the sockets.
This will ensure your sockets have power + not expensive to replace test equipment + correct phase-neutral (=230V) wiring NOT phase-phase (=415V) connection

FOR TESTING LIGHT/FAN CIRCUITS
Need a ladder and an assistant. Usually just test out with test pen to see the switching works/ or to label/map out your switches control which item.

This post has been edited by ceo684: May 9 2021, 12:40 PM
SUSceo684
post May 9 2021, 02:28 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(jeffboon97 @ May 9 2021, 02:07 PM)
Mine will be half fencing height so need to extend the walls, thinking to do this kind of wall pattern. Not sure does this cost more or just the plain full wall will cost cheaper?
user posted image

May I know is it hard to maintain concrete table top?
*
FOR WALL WITH VENTILATION BLOCKS
This design is for relatively dry yard wall or is it gonna be exposed to rain always?
Coz if exposed to rain, you may wanna apply waterproofing (Sika 109) coating and paint over exterior sealer (eg Nippon 5400) and use weatherbond or equivalent (weatherproof paint). It will be easier to clean (blow with leafblower or brush out) dust only but if its all black and green with algae and moss, really good luck tongue.gif

What causes the algae and mold..basically boil down to the steps used, if just cincai paint over with elcheapo emulsion (those 18L 60 bucks white) paint only, no waterproofing, no proper sealer.. i have witnessed firsthand (on landed garden wall with old design ventilation blocks) it grows moss and algae and its tricky to clean out once the fungus set in. Didn't bother to repaint since we not on talking terms with that side neighbour laugh.gif

FOR CONCRETE TABLETOP
Constructed properly with necessary rebar and rebar is "jacked" up to settle inside at the midpoint thickness ie. Not lying on the bottom of poured cement, would be pretty bulletproof and strong.

Depending if youre finishing it with tiles or bare cement, if bare look can Sika waterproof it to be easier to clean..otherwise oil, sauce stain may soak inside (normal concrete molecule is like a sponge loves to absorb water)..by applying waterproofing it fills up the pores with polymer modifiers, basically its a full surface "stop leak".

This post has been edited by ceo684: May 9 2021, 02:36 PM
SUSceo684
post May 9 2021, 04:03 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(joeblow @ May 9 2021, 03:08 PM)
Just out of curiosity, as I am getting my keys soon too, what would you really do if your electrician tells you one thing and the developer says another. I am faced with this dilemma too. My area famously has tenants complaining about wiring short circuit before. Of course the developer will just give some excuses and not do the patch up work properly. For me I will just hand it over to my trusted electrician and make sure nothing's wrong especially with the high powered items like water heater, central pump etc. Hard to check the rest especially those wires concealed already inside the wall.
*
Generally this is the bane of concealed wiring.
In my block, i do small job add sockets from existing..I just started to open the socket only, wire edi popped loose. Not even screwed in properly!!

SELF CHECK SWITCHES & 13A SSO
If got time, test a hot/live terminal w test pen to make sure ur test pen is alive.
Turn off everything in DB box and tape it shut with masking tape. Open up each socket 1 by 1. Test w test pen on every contact, ALL wires incl earrh to make sure all wires are not energised. As idiotas can wire wrongly green cable to live.
Inspect the wires theyre not loose by tugging them gently.

Note: This may ruin the silicone seal some developers put on the switches n sockets - but without actual inspection you never know if wires are loose. Loose connections cause fires.

-------
W.R.T. DEVELOPER WIRING
Mostly light cables are on point 1.5mm² and 13A SSO cables 2.5mm².
This part usually never go far wrong (w.r.t cable sizing).
Common points of code violations include:
1. wrong colour code (cable colour doesnt reflect actual purpose, eg green is E but used as L);
2. swapped L and N (or other nonsense);
3. loose connections (not screwed properly)
4. idiota doing the job (screw on insulation rather than on the copper).
5. RCD selection
a) Usage of "useless for residential" whole house RCD 300mA (0.3A). as explained in PSA post above.
b) Lack of whole house RCD 30mA (0.03A) as explained in PSA post above.

The usual code violations for WH (water heaters); i.e. are:
1. Usage of barely passing cable of 2.5mm² (ST guideline 4.0mm²)
and/or
2. Lack of dedicated 10mA RCD or RCBO for WH circuits.

The 2.5mm² cable size will limit your WH selection to only 3kW class models. 4.8kW models not applicable to 2.5mm² wiring (FIRE RISK).

On a sidenote, generally the better brands for DB box components will be (top tier) ABB/Hager/Schneider, (midrange) local brands, (recommend to change) elcheapo China brands .. whilst all are also SIRIM certified.. but there are quality differences. Personally I use top tier stuff like ABB for my own home although I don't make much money to afford a nice landed, but peace of mind when sleeping is important.

My rumaweep came with some elcheapo China brand, I deleted whole DB box and installed a proper one with top tier components.

--------
TLDR FOR MOST IMPORTANT CHECKPOINTS
Mostly the area of high concern in your case are WH circuits and kitchen sockets (13A SSO) as this is where u use high powered appliances the most.
Water pump doesnt really consume that much power smile.gif

This post has been edited by ceo684: May 9 2021, 04:21 PM
SUSceo684
post May 10 2021, 07:32 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(celciuz @ May 10 2021, 03:40 PM)
Is MaxGuard one of the (midrange) local brands?
*
Yup. Boleh pakai lah.

QUOTE(jeffboon97 @ May 10 2021, 06:11 PM)
Hi first of all, thank you so much for the tips! I am afraid to engage with ID as their fees is quite high...
Perhaps if anyone here have reputable and recommended contractor contact that somewhat understand my design without the need of ID that would be great!

1. I am definitely aware of amount of plug point must be sufficient to cover many home appliances and based on what I discovered with 8 plug point on living room and another 8 plug point on kitchen should be alright.

2. I am blessed that my brother is an Electrician so he can guide me through the electrical part and quote me cheaper on that end.
4. Thanks, will do more research on 3 blade fan. *easier to maintain too! less 2 blade to clean*

7. Any recommended brands? I think Fotile is the leading brand in this industry?

Advise:
2. OK OK OK NO CHEAP OUT ON SOCKET!
*
Snipped out some.

POWER POINTS
Yup, the more the better, for kitchen can also use the 4mm² to run each cable-run to dual socket (double socket), it will be sufficient to run 2x heavy appliances.
This is where I will recommend using MK sockets, the internals are better built. Only 4.60-5 bucks/ea for single socket.
Socket got fat (frameless) and flush type (frame).. for the one with frame use MK or even not so famous brand like RANK they don't pop out so easily, Schneider frame one always pop out and is kinda nuisance.

Even for rooms also can consider to add few more or make everything convert to double socket in-situ without changing wires, it will be more than sufficient for lighter duty thins. More sockets around also greatly reduce the need for having a lot of extension plugs, especially for desktop or your computer room, all those chargers and other things can directly plug into wall.

-----
FANS

60" 3-blade regulator also work perfectly, even abused in school at max speed it manage to last awhile. The regulator box just need replacing after 6-10 years. Fan should last 15-20 years if not abused like school max speed everyday. The price/performance ratio is very good but just the aesthetic it doesn't look pretty lah. For <RM200 it produce the most airflow ~8100cfm.

Any 56" 4-blade remote from KDK will work perfectly.
Just no confidence in Pana remote fan since lately alot of lemon unit. For the size and from my OLD Pana 2014 it does produce a lot of wind already for a large master bedroom.
4-blade 56" even the KDK metal bladed <RM 300 also give about 7500cfm due to its size.
More canggih 400, 500 bucks basically will get you 4 blade with ABS blade and yuragi (natural breeze variable speed mode) /4 blade with ABS blade and yuragi and DC motor and room sensor (nice to have)

40" or similar smaller size fan the airflow will be lesser.

-----
HOOD & HOB (STOVE)
Hood wise there's a few types but the best one is the vented one (vent to outside). Check flow rate. The venting should be as vertical as possible (hot air goes up), long horizontal run may not work as well.
Recirculating hood not as good as vented, but still can-use-lah if venting is an issue..this was created more for high rise ppl coz not everyone can hack a CD-ROM hole in the wall (alot of stuctural wall=cannot hack issue).

We've also been using a recirc Fujioh hood from the previous owner (installed maybe around 1997), the hood still works well and reliable until today, only thing need to change after so many years is just the bulb. And occasional cleaning coz all the oil buildup still need to clean biggrin.gif

Hob wise.. usually look for cast iron pot holder for long lasting.. also in terms of burner power need to check -
as hobs are either two or three burners, squeezing three kancil into same space not the same power (per burner) as just two preve.
of coz, a standalone Scania lorry head (like the tabletop Rinnai RTL-35KS) will not be as pretty, since when lorry pretty la.. but wok hei on it alone (single stove) can be as good as turning on all the three kancils or two preves together.

This post has been edited by ceo684: May 10 2021, 07:37 PM
SUSceo684
post May 17 2021, 09:34 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(jeffboon97 @ May 17 2021, 03:44 PM)
Also, is power track system like Eubiq, Zenso is more cost effective than hacking and looping? Because my kitchen only have 3 sockets...
*
After 3 twist in sockets (estimated 110 each) can already buy a Bosch rotary hammer to dig the hole for more sockets if you do the traditional hacking and looping laugh.gif
Its still limited by your cable sizing from DB, as what those tracks alao doing are essentially high class looping.
SUSceo684
post May 19 2021, 02:34 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(jeffboon97 @ May 19 2021, 02:10 PM)
thanks for answering! If I would like to add more sockets to another location, Plaster Ceiling is a must right? Since the wiring must be conceal if pull from DB.
*
The cheap and dirty solution is looping points or douhle sockets. Minimal hacking required just to expand the hole in the wall at the socket location.
Assuming ur original wiring is 1 13A socket per 1 circuit. This will usually be on 2.5mm² cable and MCB 20A at the miminum spec. This 20A MCB is sized to protect the cable which can support 21A.

Two 13A sockets, i.e. replacing the single socket to double socket, between them the total load supported can be up to 20A. Whether 13+7 or 11+9 or 10+10A still wont trip the MCB (within limit) if 20A MCB is used for that 1 circuit. If max out both at 13+13=26 > 20 so will trip.
This assume ur original wiring is 1 circuit = 1 socket. If 1 circuit actually feed more than 1 socket originally then this will not work well for kitchen heavy appliances.

-----
There will still be hacking needed if you want to do new circuit direct from DB. Plaster ceiling hide the ceiling run.
From ceiling drop to socket, u still need a vertical hacking line on the wall.

This post has been edited by ceo684: May 19 2021, 02:37 PM
SUSceo684
post May 22 2021, 11:36 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(davidlow7 @ May 22 2021, 11:21 PM)
Thanks CEO
I finally able to access to my house and here's the image (attached)
*
Most welcome. Very clear picture thumbup.gif
Generally looks OK in terms of correct big blocks fitted and 10mA's for the WH too.

Once u have ceiling lights fitted,

test the 100mA "ELCB" (first one on bottom row, immediately NEXT to main switch) by pressing the test button.
The 100mA should trip to OFF. Maintain 100mA OFF.
Maintain the other 30mA ELCB ON..
All ceiling lights should be dead.
13A sockets (test table lamp) should be operational.

Then flip back the 100mA ELCB up to ON position.
Test the 30mA "ELCB" (middle of bottom row AWAY from main switch) with the test button.
The 30mA should trip to OFF. Maintain 30mA OFF.
Maintain the other 100mA ELCB ON.
All ceiling lights should be operational.
All 13A sockets (test table lamp) should be dead.

Lastly turn the 30mA ELCB on and resume normal operation.

If expected result follow above then all good.
Reversed result (i.e. 30mA ELCB is off but 13A socket still all operational) is swapped and needs corrective action.

This post has been edited by ceo684: May 22 2021, 11:42 PM
SUSceo684
post May 23 2021, 12:37 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(davidlow7 @ May 23 2021, 12:01 AM)
Very detailed explanation, really appreciate your patience and guidance and willing to spell them out for me.

I am just thinking if I should add another RCCB at each of the bathroom front for added safety or it would further complicate the safety setup?
*
For the additional RCD on water heater circuit, not required. Regulations say after leaving DB box no break in the circuit smile.gif

The 10mA RCD inside DB box for water heater protect whole WH circuit already ie from the DB box including WH unit. The WH circuits' RCD compare current in equals to current out operating on a very tight (strict) tolerance under normal operation (no current was "lost" like 2MDB funds), so a direct test for those 10mA's each using their respective test buttons will suffice (need to keep both the master 30mA and 100mA "ELCB" ON) as the individual WH circuits' 10mA's are connected as "subcon" to either one of the 30 or 100mA "main con".

The WH circuit itself (as subcon) is regulated to have a very sensitive 10mA (very low tolerance) RCD.
The main con regulation (master "ELCB" according to the not so accurate sticker label) feeding the WH circuit can be either the stricter 30mA "ELCB" or the "close one eye" 100mA.
Personally I prefer stricter 30mA as maincon for the WH 10mA subcon, but according to the regulations they can use up to "close one eye" tolerance level ie the 100mA as maincon.

To determine which maincon ELCB feeds the power to the WH, by turning OFF only the 30mA master "ELCB",
see if the WH unit still operational to give hot water.
If no power to WH unit when ONLY the 30mA master is OFF..meaning good, it is stricter secondary protection.

This post has been edited by ceo684: May 23 2021, 12:43 AM
SUSceo684
post Jun 30 2021, 03:10 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(jeffboon97 @ Jun 29 2021, 08:43 PM)
Hi guys, anyone can share some insight regarding debris bin? Is it compulsory to get 2 bins if our house sqft exceed 1000?

Question 2: How much is typical post renovation cleaning service?
*
Q1: it doesn't really tie to the house size. It tie to ur SoW. Depends on what will be hacked out. In my condo almost everyone here is 1200sf or bigger and they only use 1 bin. Unless you also plan to throw our bulky old sofas too. Anyhow bin tull already still can order a 2nd load. No issue.

Q2. Can be just the price of one vacuum cleaner if DIY. Sand and other big stones can sweep. Bur vac will condemn with the fine dust.

 