 Please help if you have electrical knowledge, regarding 3 phase electric installation

views
     
TShendry91
post Mar 3 2021, 02:38 PM, updated 5y ago

Getting Started
**
Junior Member
110 posts

Joined: Jun 2015
I'm renovating my house and will change to 3 phase electric. Beside that, I would like to use smart switch in the future, so all the switch area has been pulled a neutral wire.
I want to ask whether my electric box is installed correctly and is it safe?
Because I saw the neutral wire all are connected together, but I do some research from online, it showing neutral return to own phase but the difference is that it uses MCCB, and mine is ELCB.
So i'm not sure if all the neutral connected like the image below, will have any cons?

My neutral wire image:
user posted image


Whole box:
user posted image


This is what I get from online:
user posted image


Between, ONE Live wire can connect to how many LED light? I saw my switch area only have one Live wire, and uses to control seven 18W downlight, and one wall Fan, will it overload?
COOLPINK
post Mar 3 2021, 02:53 PM

Look at all my stars!!
*******
Senior Member
3,665 posts

Joined: Oct 2010
looks fine to me.


18W X 7 = 126W
126W + 100W (normally) = 226W.

Normally one point should be a able to support at least 1000W or more so you should be fine.

i emphasis on normally bcs i have seen contractors cut cost and use cheapo wires mad.gif

This post has been edited by COOLPINK: Mar 3 2021, 02:54 PM
TShendry91
post Mar 3 2021, 02:59 PM

Getting Started
**
Junior Member
110 posts

Joined: Jun 2015
QUOTE(COOLPINK @ Mar 3 2021, 02:53 PM)
looks fine to me.
18W X 7  = 126W
126W + 100W (normally) = 226W.

Normally one point should be a able to support at least 1000W or more so you should be fine.

i emphasis on normally bcs i have seen contractors cut cost and use cheapo wires  mad.gif
*
No issue if neutral come from other phase?
Momo33
post Mar 3 2021, 03:12 PM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(hendry91 @ Mar 3 2021, 03:59 PM)
No issue if neutral come from other phase?
*
the return N to tenaga supply is 1 wire only .


COOLPINK
post Mar 3 2021, 03:13 PM

Look at all my stars!!
*******
Senior Member
3,665 posts

Joined: Oct 2010
QUOTE(hendry91 @ Mar 3 2021, 02:59 PM)
No issue if neutral come from other phase?
*
i see your concern here.
its no issue but the ampacity needs to be taken into account if shared neutral.

did you appoint a qualified electrician for your house work?
if so you could ask him to explain to you what the electrical plans are for a piece of mind.


SUSslimey
post Mar 3 2021, 04:50 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(hendry91 @ Mar 3 2021, 02:38 PM)
I'm renovating my house and will change to 3 phase electric. Beside that, I would like to use smart switch in the future, so all the switch area has been pulled a neutral wire.
I want to ask whether my electric box is installed correctly and is it safe?
Because I saw the neutral wire all are connected together, but I do some research from online,  it showing neutral return to own phase but the difference is that it uses MCCB, and mine is ELCB.
So i'm not sure if all the neutral connected like the image below, will have any cons?

My neutral wire image:
user posted image
Whole box:
user posted image
This is what I get from online:
user posted image
Between, ONE Live wire can connect to how many LED light? I saw my switch area only have one Live wire, and uses to control seven 18W downlight, and one wall Fan, will it overload?
*
Linking all neutral together is ok since only using one three phase rcd.

As for the lighting wire it depends on the wire size and the connected mcb.
7 downlight and a fan would be about 200 watt or about 1 amp.

Assuming it is 1.5mmsq wire connected to a 6 amp mcb. It still has plenty of safety factor.
SUSslimey
post Mar 3 2021, 04:53 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(COOLPINK @ Mar 3 2021, 03:13 PM)
i see your concern here.
its no issue but the ampacity needs to be taken into account if shared neutral.

did you appoint a qualified electrician for your house work?
if so you could ask him to explain to you what the electrical plans are for a piece of mind.
*
Assuming the load is balance accross the phases, the load on neutral would be zero.

But it is extremely important that the main neutral link to the supply is extremely well secured and tightened. Or else it might have unstable voltage ranging from 220 to 415 supplied to electrical equipment or you might hear a boom from the distribution box.


SUSceo684
post Mar 4 2021, 12:18 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(hendry91 @ Mar 3 2021, 02:38 PM)
I'm renovating my house and will change to 3 phase electric. Beside that, I would like to use smart switch in the future, so all the switch area has been pulled a neutral wire.
I want to ask whether my electric box is installed correctly and is it safe?
Because I saw the neutral wire all are connected together, but I do some research from online,  it showing neutral return to own phase but the difference is that it uses MCCB, and mine is ELCB.
So i'm not sure if all the neutral connected like the image below, will have any cons?

My neutral wire image:
user posted image
Whole box:
user posted image
This is what I get from online:
user posted image
Between, ONE Live wire can connect to how many LED light? I saw my switch area only have one Live wire, and uses to control seven 18W downlight, and one wall Fan, will it overload?
*
1. Better upload as attachment rather than use the upload images function (too low res to see)

2. Water Heater RCD (one each per WH unit) From the pic, no 10mA RCD for water heater was installed. This is statutory requirement. For old installation nvm but since you gonna redo, follow current standard.

Why 10mA RCD needed for water heater?
Because wet floor has very nice conductivity for fault current to flow through human = https://www.malaymail.com/news/malaysia/202...c-shock/1896447

ELCB is dinosaur technology
ELCB in WH cannot, will not, and certainly DID NOT protect against leakage for current flowing through human. It only protect L-PE leak (ie equipment protection only). L-N or L to other E (wet floor) leakage is not included in ELCB scope.

How much does this RCD (or RCBO) cost?
RCD ABB (Italy) or Hager (France) ~168 (online)
RCBO Schneider (PRC) ~100-105 (online)
other china brand also around 70 bucks but this is one thing not to skimp on.. treat it as a one off life insurance.. without yearly renewal. Maybe change once per 20-30 years.

Attached Image
It only takes 0.05A of 230V to kill a person.

Attached Image
It is very easy for an electrician to hook up a 10mA RCD per water heater circuit. Just need to identify the dedicated N for that circuit and connect to RCD 10mA. RCD 10mA line side L feed from 20A (C20) MCB load side; RCD line side N connect to common neutral. It is not rocket science. But it will definitely protect you so you can buy me a coffee.

3. All the N is common neutral when it return to TNB so basically it is correct. Common neutral and common PE (Earth).
Individual circuit (dedicated neutral) is required for special case like 10mA water heater circuit.

4.ELCB is old dino tech, you mean RCD/RCCB for mains protection right?
Only one mains (whole house) 30mA RCD needed to cover the whole house.

Use 30mA (0.03A) as whole house RCD (aka RCCD/RCCB) will give you best life protection (in general) against any fault current - be it 13A socket or light circuit. And it serves as a useful secondary line of defense even if the 10mA failed to trip on time (for WH RCD).

Note:
Anything else (100mA / 0.1A) or (300mA/0.3A) gives fire protection for building protection only. These do NOT protect human life.
Coz if there is a fault, the human dieded 2x or 6x over.


5. As for the 18W lamps.. you will need 100 pcs of them to be equivalent to a single electric kettle. One ceiling fan only takes about 85W. All in all they are low loads.
I doubt you will exceed a total of 6A (1380W) even if whole house LED and ceiling fans are turned on simultaneously.

The ones to look out for are the big loads such as water heaters (3000W typical storage heater) or (3300W-3800W typical instant heater); kettles ~1800W;; rice cooker slow cooker; oven be it microwave or conventional; electric stove/hob/induction cooker/air fryer, basically in short heavy heating appliances do not do looping shortcut but run a dedicated line to DB box with proper MS2113 cables (mega kabel, caramay, fajar cable).

6. Choice of 3 units of single phase (2P RCDs) per red/yellow/blue phase or 1 single unit of a three phase (4P RCD).
Both are not wrong, the 3x of 2P RCD is more for "business continuity" in case red phase has fault, you can still operate things on the yellow and blue uninterrupted.
Whereas in the case of using 1x of 4P RCD, any one phase has fault detected, entire house goes dark until the fault situation is rectified.
Cost wise, one 4P RCD is still cheaper relatively as compared to three units of 2P RCDs.

This post has been edited by ceo684: Mar 4 2021, 12:38 AM
SUSceo684
post Mar 4 2021, 12:32 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(slimey @ Mar 3 2021, 04:53 PM)
Assuming the load is balance accross the phases, the load on neutral would be zero.

But it is extremely important that the main neutral link to the supply is extremely well secured and tightened. Or else it might have unstable voltage ranging from 220 to 415 supplied to electrical equipment or you might hear a boom from the distribution box.
*
Yes, this is also important as phase-neutral is 230V
But phase to phase produces 415V fireworks show.
fireballs
post Mar 4 2021, 12:37 AM

10101
*******
Senior Member
5,650 posts

Joined: Mar 2012
Neutral looks ok
Your rcd is not

Since you reno, do it right

100ma for main or lamp
30ma for socket
10ma for water heater
Get reputable brand pls.
SUSceo684
post Mar 4 2021, 12:40 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(fireballs @ Mar 4 2021, 12:37 AM)
Neutral looks ok
Your rcd is not

Since you reno, do it right

100ma for main or lamp
30ma for socket
10ma for water heater
Get reputable brand pls.
*
Why buy 2 piece of mains RCD 100mA and 30mA when the requirement is "maximum of 100mA tolerance" - i.e. NOT "equal to 100mA" or "not less than 100mA tolerance"?

A single 30mA for whole house is cheaper TCO and provide better life protection whilst still fully compliant to the regulation of "maximum of 100mA tolerance".

QUOTE
No. Installation Type Residual Current Device Sensitivity (Maximum) Requirement

1.
Overall Wiring (Single Phase or Three Phase)
100mA (0.1A)
Mandatory
2.
Final Circuit for Power (13A socket outlets)
30mA (0.03A)
Mandatory
3.
Wet places (toilets and wet kitchens) / Water heater circuits
10mA (0.01A)
Mandatory
Requirements for the Use of Residual Current Devices – RCDs (Sensitivity) Based on Regulation 36, Electricity Regulations 1994.
QUOTE
MS 1979:2015
Malaysia Standard MS 1979:2015 – Electrical installations of buildings – Code of Practice (First revision) also stated:
4.8.6 COP 51, RCDs for single phase installations
RCDs for single phase installations shall have a rated residual operating current not exceeding 100mA.
4.8.7 COP 52, RCDs for three-phase installations
RCDs for three-phase installations shall have a rated residual operating current not exceeding 100mA. Provided there are no threephase loads in the installation, it is recommended to install three (3) single phase RCDs instead of a single three-phase RCD. This practice will reduce the extent of power disruption in the installation in case there is an earth fault in one phase.
4.8.8 COP 53, RCDs for hand-held and fixed apparatus
RCDs with a rated residual operating current not exceeding 30mA shall be installed in installations where portable or fixed apparatus such as electric power tools, hair-dryers, electric kettles and washing machines, are used. RCDs with rated residual operating current not exceeding 30mA can be installed to protect an individual final power circuit or to protect a group of final power circuits.
4.8.9 COP 54, RCDs for special places
RCDs with a rated residual operating current not exceeding 10mA shall be installed in the following instances:
Where the floor is likely to be wet such as in water fountains, bathrooms, kitchens and swimming pools;
For the protection of equipment and apparatus, such as electric water heaters, booster pumps and other similar types; and
(Recommended) Where supply apparatus is used by children, the elderly, uninformed consumers who are sick, or other similar categories.
4.8.10 COP 55, Location of RCDs in single RCD-protected installation
If an installation is protected by a single RCD, it shall be located at the origin of the installation, that is, immediately after the main incoming isolator at the consumer unit or main switchboard.
This post has been edited by ceo684: Mar 4 2021, 12:48 AM
fireballs
post Mar 4 2021, 12:51 AM

10101
*******
Senior Member
5,650 posts

Joined: Mar 2012
QUOTE(ceo684 @ Mar 4 2021, 12:40 AM)
Why buy 2 piece of mains RCD 100mA and 30mA when the requirement is "maximum of 100mA tolerance" - i.e. NOT "equal to 100mA" or "not less than 100mA tolerance"?

A single 30mA for whole house is cheaper TCO and provide better life protection whilst still fully compliant to the regulation of "maximum of 100mA tolerance".
*
Yes is correct
In practice is better to use 3 units of 30ma single phase
So when trip won't bring down the whole house power.

It's not only about compliance but rather safety and convinience

Ts if have money pls add spd too
SUSceo684
post Mar 4 2021, 01:01 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(fireballs @ Mar 4 2021, 12:51 AM)
Yes is correct
In practice is better to use 3 units of 30ma single phase
So when trip won't bring down the whole house power.

It's not only about compliance but rather safety and convinience

Ts if have money pls add spd too
*
Yeah the ideal is to use 3x 2P 30mA but only two concerns:
1. Cost-wise it is also OK to use 1x 4P 30mA if budget constraint cannot stretch. Protection wise, TS, is the same as long as all are 30mA.
-- The only diff is any fault will trip whole house, rather than just that one phase.

2. Physical limitation of DB box space. It looks kinda full at the moment.
-- 1x 4P use 4 module, vs 3x 2P use 6 module space.

3. 3-phase (4P SPD) for lightning protection
individual module replaceable type thumbup.gif
-- CHNT (china brand) 40kA 4P ~423 shakehead.gif
-- ABB OVR-T2-3N-40-275PQS SURGE PROTECTIVE DEVICE [2CTB803973R1100] 40kA 4P ~480
-- SCHNEIDER A9L40600 iPRD40 MODULAR SURGE ARRESTER A9L40600 ~379

monobloc (use and throw as whole unit) devil.gif
-- Hager SPD SPM440E 40KA 4P ~502
-- Schneider SPD A9L15688 40KA 4P ~490

useless toys: rclxub.gif
those 30 dollar china SPD

This post has been edited by ceo684: Mar 4 2021, 01:10 AM
TShendry91
post Mar 4 2021, 10:22 AM

Getting Started
**
Junior Member
110 posts

Joined: Jun 2015
QUOTE(ceo684 @ Mar 4 2021, 12:18 AM)
1. Better upload as attachment rather than use the upload images function (too low res to see)

2. Water Heater RCD (one each per WH unit) From the pic, no 10mA RCD for water heater was installed. This is statutory requirement. For old installation nvm but since you gonna redo, follow current standard.

Why 10mA RCD needed for water heater?
Because wet floor has very nice conductivity for fault current to flow through human = https://www.malaymail.com/news/malaysia/202...c-shock/1896447

ELCB is dinosaur technology
ELCB in WH cannot, will not, and certainly DID NOT protect against leakage for current flowing through human. It only protect L-PE leak (ie equipment protection only). L-N or L to other E (wet floor) leakage is not included in ELCB scope.

How much does this RCD (or RCBO) cost?
RCD ABB (Italy) or Hager (France) ~168 (online)
RCBO Schneider (PRC) ~100-105 (online)
other china brand also around 70 bucks but this is one thing not to skimp on.. treat it as a one off life insurance.. without yearly renewal. Maybe change once per 20-30 years.

Attached Image
It only takes 0.05A of 230V to kill a person.

Attached Image
It is very easy for an electrician to hook up a 10mA RCD per water heater circuit. Just need to identify the dedicated N for that circuit and connect to RCD 10mA. RCD 10mA line side L feed from 20A (C20) MCB load side; RCD line side N connect to common neutral. It is not rocket science. But it will definitely protect you so you can buy me a coffee.

3. All the N is common neutral when it return to TNB so basically it is correct. Common neutral and common PE (Earth).
Individual circuit (dedicated neutral) is required for special case like 10mA water heater circuit.

4.ELCB is old dino tech, you mean RCD/RCCB for mains protection right?
Only one mains (whole house) 30mA RCD needed to cover the whole house.

Use 30mA (0.03A) as whole house RCD (aka RCCD/RCCB) will give you best life protection (in general) against any fault current - be it 13A socket or light circuit. And it serves as a useful secondary line of defense even if the 10mA failed to trip on time (for WH RCD).

Note:
Anything else (100mA / 0.1A) or (300mA/0.3A) gives fire protection for building protection only. These do NOT protect human life.
Coz if there is a fault, the human dieded 2x or 6x over.


5. As for the 18W lamps.. you will need 100 pcs of them to be equivalent to a single electric kettle. One ceiling fan only takes about 85W. All in all they are low loads.
I doubt you will exceed a total of 6A (1380W) even if whole house LED and ceiling fans are turned on simultaneously.

The ones to look out for are the big loads such as water heaters (3000W typical storage heater) or (3300W-3800W typical instant heater); kettles ~1800W;; rice cooker slow cooker; oven be it microwave or conventional; electric stove/hob/induction cooker/air fryer, basically in short heavy heating appliances do not do looping shortcut but run a dedicated line to DB box with proper MS2113 cables (mega kabel, caramay, fajar cable).

6. Choice of 3 units of single phase (2P RCDs) per red/yellow/blue phase or 1 single unit of a three phase (4P RCD).
Both are not wrong, the 3x of 2P RCD is more for "business continuity" in case red phase has fault, you can still operate things on the yellow and blue uninterrupted.
Whereas in the case of using 1x of 4P RCD, any one phase has fault detected, entire house goes dark until the fault situation is rectified.
Cost wise, one 4P RCD is still cheaper relatively as compared to three units of 2P RCDs.
*
Thanks man.
1. What is the "MCB C20 WH"? is it different type of other MCB?
2. if I have 4 header, which mean I will need FOUR 10mA RCD?
3. The purpose of 10mA RCD is to trip when the heater leaking to our body? my current installation if leaking it won't trip?
4. In short, I only need to have 10mA RCD in between the MCB and Header individually? Any other wiring need to be change/improve?
5. between I'm quite confusing are ELCB & RCCB the same? can you correct me if the naming in the image below wrong?
6. Appreciate if you can share the image of "MCB C20 WH" and 10mA RCD

user posted image

besides that, there are 2 type of MCB in the box, C10 and C20, click the link to see high res image:
image 1
image 2
image 3


This post has been edited by hendry91: Mar 4 2021, 10:40 AM
SUSslimey
post Mar 4 2021, 11:49 AM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(hendry91 @ Mar 4 2021, 10:22 AM)
Thanks man.
1. What is the "MCB C20 WH"? is it different type of other MCB?

that would refer to a unit of RCBO or a RCD+MCB wired together to act as a single unit
2. if I have 4 header, which mean I will need FOUR 10mA RCD?

yes. 10ma for each water heater. because each water heater consumes a lot of electricity and would require their own wiring. also, RCBO dont come in super big amp rating anyway.[/B

3. The purpose of 10mA RCD is to trip when the heater leaking to our body? my current installation if leaking it won't trip?
[B]usually water heater have built in 10ma rcd. that should trip first before the mains trip. but, it is safer to have additional safety such as a dedicated RCBO with 10ma trip characteristic wired to the water heater. if the leakage to body is 50ma, in the absence of the RCBO that trips with a lower threshold and assuming the water heater built in RCD failed, you have have shock and the mains RCD which is rated at 300ma in your case will not trip as it didnt reach the threshold of tripping


4. In short, I only need to have 10mA RCD in between the MCB and Header individually? Any other wiring need to be change/improve?
look at 1.


5. between I'm quite confusing are ELCB & RCCB the same? can you correct me if the naming in the image below wrong?
aint nobody produces ELCB nowadays. that's RCD

6. Appreciate if you can share the image of "MCB C20 WH" and 10mA RCD

user posted image

besides that, there are 2 type of MCB in the box, C10 and C20, click the link to see high res image:
image 1
image 2
image 3

C refers to the trip curvature characteristic. the 10 or 20 refers to the rated amp. i dont like how the electrician didnt label the live phases properly........those thick black wires which are phase should have a different color or at least marking to show that they are different phase.

*
This post has been edited by slimey: Mar 4 2021, 11:54 AM
SUSceo684
post Mar 4 2021, 01:45 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(hendry91 @ Mar 4 2021, 10:22 AM)
Thanks man.
1. What is the "MCB C20 WH"? is it different type of other MCB?
2. if I have 4 header, which mean I will need FOUR 10mA RCD?
3. The purpose of 10mA RCD is to trip when the heater leaking to our body? my current installation if leaking it won't trip?
4. In short, I only need to have 10mA RCD in between the MCB and Header individually? Any other wiring need to be change/improve?
5. between I'm quite confusing are ELCB & RCCB the same? can you correct me if the naming in the image below wrong?
6. Appreciate if you can share the image of "MCB C20 WH" and 10mA RCD

user posted image

besides that, there are 2 type of MCB in the box, C10 and C20, click the link to see high res image:
image 1
image 2
image 3
*
Sis actually. bruce.gif

1. What is the "MCB C20 WH"? is it different type of other MCB?
Standard C20 MCB.
WH denotes the one for WH circuit.

2. if I have 4 header, which mean I will need FOUR 10mA RCD?
Yes correct. WH 10mA RCD is per unit of WH. Each WH should be on its own dedicated circuit as one WH enough to use 15-17A nominal (WH is heavy appliance). Your 2.5mm cable only support 21A. And the 10mA RCD, only come (from branded mfg) up to 25A max current. In short, the standard cable sizing, the RCD current capacity (max 25A) all only suited for single unit WH as it is sensitive device (0.01A /10mA).
Whilst there are champions from china making 10mA RCD that can handle 40A laugh.gif I also dare not use.

3. The purpose of 10mA RCD is to trip when the heater leaking to our body? my current installation if leaking it won't trip?
Your current installation only trips at 300mA - by then, the human dieded 6 times over.
As the mains is 300mA, it allow 300mA leakage before it trip.
A human RIP at 50mA.
Attached Image

4. In short, I only need to have 10mA RCD in between the MCB and Header individually? Any other wiring need to be change/improve?
Yes, correct.
RCD is comparing input and output current difference. Input and output must = equal the same +/- RCD tolerance of say 10mA (0.01A).

Meaning, if WH input is 16A on L, at least 15.99A must return on WH output (N) else it has deemed to be lost somewhere.

Lost somewhere mean could be leaking through human.
So when the return not enough (<15.99) say only 11A return. The 4.99A cannot be lost, it mean it leak. As 4.99A far exceed the 0.01A allowed by 10mA RCD it will immediately trip.

MCB only consider single wire (L) amount of current passing through (short circuit prevention).
For a C20, meaning the speed limit is 20A.
Slight overload at 23A will trip the SLOW thermal overload after say 20 min.
Major overload at 100A will immediately trip the magnetic overload.

5. between I'm quite confusing are ELCB & RCCB the same? can you correct me if the naming in the image below wrong?
The difference is how and where they measure.
ELCB only detect earth current rise >0 leak (L to PE) leak on that appliance's earth. If it leak via anywhere else (L-N, or L-other PE eg wet floor, L-human) it will not bother. Hence in short I just say it protect that appliance only.

RCD because it constantly compare L input =N output + allowed tolerance (like 10.00A in on L, >9.99A must return as allowed tolerance is 0.01A for normal operation things like wire resistance that do NOT constitute a fault condition). It does not care where it leak through, RCD always compare in and out current so if it leak through any method (L-N, L-PE, L-other PE, L-human) it always trip.

Note: There is something called RCBO which do both function of MCB+RCD in one.


6. Appreciate if you can share the image of "MCB C20 WH" and 10mA RCD
MCB C20 is any usual C20 (20A MCB). WH is just designation for the WH circuit.

10mA RCD (must be used in conjunction together with C20 MCB) ie. add this along with MCB C20
ABB= https://www.lazada.com.my/products/abb-f202...i2IABn&search=1
Hager= https://www.lazada.com.my/products/hager-cc...l5n2dU&search=1
Schneider = https://www.lazada.com.my/products/schneide...8t5PsK&search=1

10mA RCBO = RCD+MCB in one package pao kah liao 2 function in one
Schneider RCBO https://www.lazada.com.my/products/schneide...PVCaV4&search=1
The drawback is, officially, their MCB is a C25 equivalent so you need to use with 4mm cable. As 2.5mm cable only good up to 21A rating.

user posted image
First one from left is MCB 3P (3 pole) C63 (63A)
Second one is 4P RCD but this is 300mA. Only used in commercial/industrial where they use heavy motors. Not safe for residential and its against regulation, as the human has dieded 6x before this trips. (RCD/RCCB/RCCD = same function with diff name like zebra crossing=pedestrian crossing)
Third one is MCB 1P C10 (10A)

You will then ask, why do people still put the 300mA in residential?
Just to save the few bucks for more profit/lower tender cost whistling.gif

This post has been edited by ceo684: Mar 4 2021, 01:59 PM
COOLPINK
post Mar 4 2021, 02:11 PM

Look at all my stars!!
*******
Senior Member
3,665 posts

Joined: Oct 2010
wah lau eh you guys can see the wordings on all the CB from the first pic.

i cant see shit man. laugh.gif
TShendry91
post Mar 4 2021, 02:53 PM

Getting Started
**
Junior Member
110 posts

Joined: Jun 2015
QUOTE(slimey @ Mar 4 2021, 11:49 AM)

*
Thanks slimey.
Ya, I feel you. I don't like their cincai style, I hope they organize the color of the cables according to the regulations, but it doesn't seem to be.
Kampung area all kampung style, maybe they don't even have a cert, but worked for a long time and followed the old method.

When I request the technician to pull the neutral cable to each switch area for smart switch, but he totally can't get it and need my long explanation.
and also ask him to hack the wall to put an empty pipe for Unifi fiber, but he told me can pull Cat cable, it's the same. I know he was outdated.

So I must do some research, and study by myself to make sure everything is correct.
TShendry91
post Mar 4 2021, 02:59 PM

Getting Started
**
Junior Member
110 posts

Joined: Jun 2015
QUOTE(ceo684 @ Mar 4 2021, 01:45 PM)
Sis actually.  bruce.gif

1. What is the "MCB C20 WH"? is it different type of other MCB?
Standard C20 MCB.
WH denotes the one for WH circuit.

2. if I have 4 header, which mean I will need FOUR 10mA RCD?
Yes correct. WH 10mA RCD is per unit of WH. Each WH should be on its own dedicated circuit as one WH enough to use 15-17A nominal (WH is heavy appliance). Your 2.5mm cable only support 21A. And the 10mA RCD, only come (from branded mfg) up to 25A max current. In short, the standard cable sizing, the RCD current capacity (max 25A) all only suited for single unit WH as it is sensitive device (0.01A /10mA).
Whilst there are champions from china making 10mA RCD that can handle 40A laugh.gif I also dare not use.

3. The purpose of 10mA RCD is to trip when the heater leaking to our body? my current installation if leaking it won't trip?
Your current installation only trips at 300mA - by then, the human dieded 6 times over.
As the mains is 300mA, it allow 300mA leakage before it trip.
A human RIP at 50mA.
Attached Image

4. In short, I only need to have 10mA RCD in between the MCB and Header individually? Any other wiring need to be change/improve?
Yes, correct.
RCD is comparing input and output current difference. Input and output must = equal the same +/- RCD tolerance of say 10mA (0.01A).

Meaning, if WH input is 16A on L, at least 15.99A must return on WH output (N) else it has deemed to be lost somewhere.

Lost somewhere mean could be leaking through human.
So when the return not enough (<15.99) say only 11A return. The 4.99A cannot be lost, it mean it leak. As 4.99A far exceed the 0.01A allowed by 10mA RCD it will immediately trip.

MCB only consider single wire (L) amount of current passing through (short circuit prevention).
For a C20, meaning the speed limit is 20A.
Slight overload at 23A will trip the SLOW thermal overload after say 20 min.
Major overload at 100A will immediately trip the magnetic overload.

5. between I'm quite confusing are ELCB & RCCB the same? can you correct me if the naming in the image below wrong?
The difference is how and where they measure.
ELCB only detect earth current rise >0 leak (L to PE) leak on that appliance's earth. If it leak via anywhere else (L-N, or L-other PE eg wet floor, L-human) it will not bother. Hence in short I just say it protect that appliance only.

RCD because it constantly compare L input =N output + allowed tolerance (like 10.00A in on L, >9.99A must return as allowed tolerance is 0.01A for normal operation things like wire resistance that do NOT constitute a fault condition). It does not care where it leak through, RCD always compare in and out current so if it leak through any method (L-N, L-PE, L-other PE, L-human) it always trip.

Note: There is something called RCBO which do both function of MCB+RCD in one.
6. Appreciate if you can share the image of "MCB C20 WH" and 10mA RCD
MCB C20 is any usual C20 (20A MCB). WH is just designation for the WH circuit.

10mA RCD (must be used in conjunction together with C20 MCB) ie. add this along with MCB C20
ABB= https://www.lazada.com.my/products/abb-f202...i2IABn&search=1
Hager= https://www.lazada.com.my/products/hager-cc...l5n2dU&search=1
Schneider = https://www.lazada.com.my/products/schneide...8t5PsK&search=1

10mA RCBO = RCD+MCB in one package pao kah liao 2 function in one
Schneider RCBO https://www.lazada.com.my/products/schneide...PVCaV4&search=1
The drawback is, officially, their MCB is a C25 equivalent so you need to use with 4mm cable. As 2.5mm cable only good up to 21A rating.

user posted image
First one from left  is MCB 3P (3 pole) C63 (63A)
Second one is 4P RCD but this is 300mA. Only used in commercial/industrial where they use heavy motors. Not safe for residential and its against regulation, as the human has dieded 6x before this trips. (RCD/RCCB/RCCD = same function with diff name like zebra crossing=pedestrian crossing)
Third one is MCB 1P C10 (10A)

You will then ask, why do people still put the 300mA in residential?
Just to save the few bucks for more profit/lower tender cost whistling.gif
*
Ops, Thanks Sis. haha

if 300mA RCD is for commercial/industrial, then what should be used for residential? RCD with lower mA?

Let's say la, I take a fork cucuk the 13A socket and kena shock, my MCB / RCD which one will trip and what's the cause(theory) to make it trip?

This post has been edited by hendry91: Mar 4 2021, 03:06 PM
SUSslimey
post Mar 4 2021, 03:14 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(hendry91 @ Mar 4 2021, 02:59 PM)
Ops, Thanks Sis. haha

if 300mA RCD is for commercial/industrial, then what should be used for residential? RCD with lower mA?

Let's say la, I take a fork cucuk the 13A socket and kena shock, my MCB / RCD which one will trip and what's the cause(theory) to make it trip?
*
Ideally all 13 amp socket is protected by 30ma trip characteristic rcd/rcbo.

And as for the cucuk 13a socket. It depends on how you cucuk lo.
If you cucuk live only and you kena shock. It depends on how grounded are you lo. Normally it will be a ouchie only and you quickly retract your hand lo. If rcd is rated at 300ma or 100ma it will not trip lo. If you are very grounded ..... let’s say you touch a metal ground of an appliance and you also touch live, it will be extreme ouchie or you die.

If you cucuk live only with one metal, cucuk neutral with another metal, and you hold the metal one in each hand, you will die regardless of rcd or mcb. Because to the circuit, you act like an appliance.

If you cucuk with a folk with both the neutral and live going in at the same time, the mcb will trip lo.

This post has been edited by slimey: Mar 4 2021, 03:16 PM
SUSceo684
post Mar 4 2021, 03:57 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(hendry91 @ Mar 4 2021, 02:59 PM)
Ops, Thanks Sis. haha

if 300mA RCD is for commercial/industrial, then what should be used for residential? RCD with lower mA?

Let's say la, I take a fork cucuk the 13A socket and kena shock, my MCB / RCD which one will trip and what's the cause(theory) to make it trip?
*
1 size fit all, 30mA whole house for residential.
Lower mA is tighter tolerance/more sensitive for life protection.

I personally use one piece RCD for 3phase supply. In pic is 30mA 4P 40A (the incoming to the unit is only 10mm cable so 40A each phase). Yours is newer place on 16mm then the TNB is 63A, so you need a 63A 4P 30ma RCD.

Generally top tier RCD for MY market easily ibtainable are from these 3, ABB Hager Schneider.

This post has been edited by ceo684: Mar 4 2021, 03:58 PM


Attached thumbnail(s)
Attached Image
TShendry91
post Mar 9 2021, 12:41 PM

Getting Started
**
Junior Member
110 posts

Joined: Jun 2015
QUOTE(ceo684 @ Mar 4 2021, 01:45 PM)
Sis actually.  bruce.gif

1. What is the "MCB C20 WH"? is it different type of other MCB?
Standard C20 MCB.
WH denotes the one for WH circuit.

2. if I have 4 header, which mean I will need FOUR 10mA RCD?
Yes correct. WH 10mA RCD is per unit of WH. Each WH should be on its own dedicated circuit as one WH enough to use 15-17A nominal (WH is heavy appliance). Your 2.5mm cable only support 21A. And the 10mA RCD, only come (from branded mfg) up to 25A max current. In short, the standard cable sizing, the RCD current capacity (max 25A) all only suited for single unit WH as it is sensitive device (0.01A /10mA).
Whilst there are champions from china making 10mA RCD that can handle 40A laugh.gif I also dare not use.

3. The purpose of 10mA RCD is to trip when the heater leaking to our body? my current installation if leaking it won't trip?
Your current installation only trips at 300mA - by then, the human dieded 6 times over.
As the mains is 300mA, it allow 300mA leakage before it trip.
A human RIP at 50mA.
Attached Image

4. In short, I only need to have 10mA RCD in between the MCB and Header individually? Any other wiring need to be change/improve?
Yes, correct.
RCD is comparing input and output current difference. Input and output must = equal the same +/- RCD tolerance of say 10mA (0.01A).

Meaning, if WH input is 16A on L, at least 15.99A must return on WH output (N) else it has deemed to be lost somewhere.

Lost somewhere mean could be leaking through human.
So when the return not enough (<15.99) say only 11A return. The 4.99A cannot be lost, it mean it leak. As 4.99A far exceed the 0.01A allowed by 10mA RCD it will immediately trip.

MCB only consider single wire (L) amount of current passing through (short circuit prevention).
For a C20, meaning the speed limit is 20A.
Slight overload at 23A will trip the SLOW thermal overload after say 20 min.
Major overload at 100A will immediately trip the magnetic overload.

5. between I'm quite confusing are ELCB & RCCB the same? can you correct me if the naming in the image below wrong?
The difference is how and where they measure.
ELCB only detect earth current rise >0 leak (L to PE) leak on that appliance's earth. If it leak via anywhere else (L-N, or L-other PE eg wet floor, L-human) it will not bother. Hence in short I just say it protect that appliance only.

RCD because it constantly compare L input =N output + allowed tolerance (like 10.00A in on L, >9.99A must return as allowed tolerance is 0.01A for normal operation things like wire resistance that do NOT constitute a fault condition). It does not care where it leak through, RCD always compare in and out current so if it leak through any method (L-N, L-PE, L-other PE, L-human) it always trip.

Note: There is something called RCBO which do both function of MCB+RCD in one.
6. Appreciate if you can share the image of "MCB C20 WH" and 10mA RCD
MCB C20 is any usual C20 (20A MCB). WH is just designation for the WH circuit.

10mA RCD (must be used in conjunction together with C20 MCB) ie. add this along with MCB C20
ABB= https://www.lazada.com.my/products/abb-f202...i2IABn&search=1
Hager= https://www.lazada.com.my/products/hager-cc...l5n2dU&search=1
Schneider = https://www.lazada.com.my/products/schneide...8t5PsK&search=1

10mA RCBO = RCD+MCB in one package pao kah liao 2 function in one
Schneider RCBO https://www.lazada.com.my/products/schneide...PVCaV4&search=1
The drawback is, officially, their MCB is a C25 equivalent so you need to use with 4mm cable. As 2.5mm cable only good up to 21A rating.

user posted image
First one from left  is MCB 3P (3 pole) C63 (63A)
Second one is 4P RCD but this is 300mA. Only used in commercial/industrial where they use heavy motors. Not safe for residential and its against regulation, as the human has dieded 6x before this trips. (RCD/RCCB/RCCD = same function with diff name like zebra crossing=pedestrian crossing)
Third one is MCB 1P C10 (10A)

You will then ask, why do people still put the 300mA in residential?
Just to save the few bucks for more profit/lower tender cost whistling.gif
*
Hi Sis,
my DB box out of slot, so might need to use RCBO. but the 4mm cable u mentioned is for out going from RCBO to water heater or incoming to RCBO?
My wireman told me like the image below, between can I use 2.5mm cable(To WH) with RCBO?
Can you demonstrate how to connect?
Thanks
user posted image

This post has been edited by hendry91: Mar 9 2021, 12:46 PM
SUSceo684
post Mar 9 2021, 01:12 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(hendry91 @ Mar 9 2021, 12:41 PM)
Hi Sis,
my DB box out of slot, so might need to use RCBO. but the 4mm cable u mentioned is for out going from RCBO to water heater or incoming to RCBO?
My wireman told me like the image below, between can I use 2.5mm cable(To WH) with RCBO?
Can you demonstrate how to connect?
Thanks
user posted image
*
Ideally, per ST WH Guidelines page 14, the RCBO (25A 10mA) is connected after the mains RCD 30mA as well. So you will have the 30mA (whole house) as second level RCD protection.

As RCBO = MCB and RCD in one.
The RCBO unit can be installed like an MCB (replace the existing MCB with the RCBO in-situ).

QUOTE
but the 4mm cable u mentioned is for out going from RCBO to water heater or incoming to RCBO?


The chain is only as strong as weakest link. All the way should be 4mm as the min cable size per ST guideline is 4mm for 3300-3800W WH.
Because typical load is around 15-17A.
Still can get away with 2.5mm if the 2.5mm cable is good quality (full copper and SIRIM and MS2113 certified) as the 2.5mm cable can take a 21A max load, but it is recommended to use 4mm if possible.

This post has been edited by ceo684: Mar 9 2021, 01:27 PM


Attached thumbnail(s)
Attached Image Attached Image

Attached File(s)
Attached File  Guideline_for_The_Design_Installation_Inspection_Testing_Operation_and_Maintenance_of_Water_Heater_Systems__1_.pdf ( 4.49mb ) Number of downloads: 30
TShendry91
post Mar 9 2021, 02:42 PM

Getting Started
**
Junior Member
110 posts

Joined: Jun 2015
QUOTE(ceo684 @ Mar 9 2021, 01:12 PM)
Ideally, per ST WH Guidelines page 14, the RCBO (25A 10mA) is connected after the mains RCD 30mA as well. So you will have the 30mA (whole house) as second level RCD protection.

As RCBO = MCB and RCD in one.
The RCBO unit can be installed like an MCB (replace the existing MCB with the RCBO in-situ).
The chain is only as strong as weakest link. All the way should be 4mm as the min cable size per ST guideline is 4mm for 3300-3800W WH.
Because typical load is around 15-17A.
Still can get away with 2.5mm if the 2.5mm cable is good quality (full copper and SIRIM and MS2113 certified) as the 2.5mm cable can take a 21A max load, but it is recommended to use 4mm if possible.
*
If I understand correctly, all the Water Heater are recommended to use 4mm cable, no matter use RCD/RCBO correct?
But no choice, already pulled 2.5mm cable, if the cable quality good enough shouldn't have problem right?

RCBO 25A 10mA & 20A 10mA, which one should I use?

This post has been edited by hendry91: Mar 9 2021, 03:27 PM
SUSslimey
post Mar 9 2021, 03:36 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(hendry91 @ Mar 9 2021, 02:42 PM)
If I understand correctly, all the Water Heater are recommended to use 4mm cable, no matter use RCD/RCBO correct?
But no choice, already pulled 2.5mm cable, if the cable quality good enough shouldn't have problem right?

RCBO 25A 10mA & 20A 10mA, which one should I use?
*
If use 2.5 mmsq cable, then 20a 10ma trip rcbo.

What’s the water heater rated wattage?
Ideally pull the wire again though.

Most older houses still using 2.5mmsq wire. Running water heater or 3600 watt. Not ideal. But real world usage hardly use 50 percent of the water heater power and usually usage only a few minutes.

But for peace of mind, 4mmsq is better

This post has been edited by slimey: Mar 9 2021, 03:39 PM
TShendry91
post Mar 9 2021, 03:38 PM

Getting Started
**
Junior Member
110 posts

Joined: Jun 2015
QUOTE(slimey @ Mar 9 2021, 03:36 PM)
If use 2.5 mmsq cable, then 20a 10ma trip rcbo.

What’s the water heater rated wattage?
*
Haven't bought a water heater yet.
20A support up to 4800 watts? which mean if I use 20A, then I need to buy the water heater below <4600 watts?

This post has been edited by hendry91: Mar 9 2021, 03:44 PM
SUSceo684
post Mar 9 2021, 03:45 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(hendry91 @ Mar 9 2021, 02:42 PM)
If I understand correctly, all the Water Heater are recommended to use 4mm cable, no matter use RCD/RCBO correct?
But no choice, already pulled 2.5mm cable, if the cable quality good enough shouldn't have problem right?

RCBO 25A 10mA & 20A 10mA, which one should I use?
*
Yes correct recommended 4mm per ST spec. Regardless RCBO or RCD.

Per cable mfg spec 2.5mm is safe up to 24A single phase max load - http://www.megakabel.com.my/A-1.pdf
Attached Image

If cable is from proper mfg (u see there is MS2112-3, SIRIM QAS certified, and mfg name on the cable) then OK.
Attached Image

Between RCBO 25A 10mA & 20A 10mA, for safest choice 20A 10mA when using 2.5mm cable.
Whilst going 1A extra may not be much difference above the cable mfg spec but for insurance claim (in case fire occur) this kind of technicality can and will void the claim validity, so if on 2.5mm cable pls use a RCBO 20A 10mA,
or pair RCBO/RCD in conjunction with a 20A MCB (DB box space limitation).

This post has been edited by ceo684: Mar 9 2021, 03:48 PM
SUSslimey
post Mar 9 2021, 03:46 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(hendry91 @ Mar 9 2021, 03:38 PM)
Haven't bought a water heater yet.
20A support up to 4800 watts? which mean if I use 20A, then I need to buy the water heater below <4600 watts?
*

I won’t recommend anything higher than 3600 watt although in ideal scenario, a perfect 2.5 mmsq can handle 24 amp
SUSceo684
post Mar 9 2021, 03:54 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(hendry91 @ Mar 9 2021, 03:38 PM)
Haven't bought a water heater yet.
20A support up to 4800 watts? which mean if I use 20A, then I need to buy the water heater below <4600 watts?
*
Hello, cannot use 4800W.

4800/230=20.8695652173913 A (21A for easy calculation)
by 80% derating factor (same as you don't redline your car every time) you should use cable that can support 26.25A ie minimum 4mm cable.

the minimum (as per ST spec) recommended is 4mm cable to use a 4800W heater (highlands model, usually from Pana or Hitachi).

In the market usually 3kw class is 3000W for storage, and 3300-3800W for instant WH. These are the recommended type (max power) for the 2.5mm cables typically installed.
Next step is 4800W.
Normally rare to find anything in between 3800 and 4800W.

QUOTE(slimey @ Mar 9 2021, 03:46 PM)
I won’t recommend anything higher than 3600 watt although in ideal scenario, a perfect 2.5 mmsq can handle 24 amp
*
If quality cable used.
If unknown/substandard cable.. insulation very thick, copper all substandard or adulterated so only 3kW class is safe option.

This post has been edited by ceo684: Mar 9 2021, 03:55 PM
SUSslimey
post Mar 9 2021, 03:55 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(ceo684 @ Mar 9 2021, 03:54 PM)
Hello, cannot use 4800W.

4800/230=20.8695652173913 A (21A for easy calculation)
by 80% derating factor (same as you don't redline your car every time) you should use cable that can support 26.25A ie minimum 4mm cable.

the minimum (as per ST spec) recommended is 4mm cable to use a 4800W heater (highlands model, usually from Pana or Hitachi).

In the market usually 3kw class is 3000W for storage, and 3300-3800W for instant WH.
Next step is 4800W.
Normally rare to find anything in between 3800 and 4800W.
If quality cable used.
If unknown/substandard cable.. insulation very thick, copper all substandard or adulterated so only 3kW class is safe option.
*
I haven’t seen before a instant water heater of 3kw class
SUSceo684
post Mar 9 2021, 03:57 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(slimey @ Mar 9 2021, 03:55 PM)
I haven’t seen before a instant water heater of 3kw class
*
Storage heater Rated Power : 3000W - Centon current series (QNQ RNQ SNQ)

Instant WH 3kw class = 3xxx W (typically 3300-3800W)
Older National/Pana is 3300W
Current series Pana 3600W
Current Toshiba 3800W

This post has been edited by ceo684: Mar 9 2021, 03:58 PM
TShendry91
post Mar 12 2021, 11:22 AM

Getting Started
**
Junior Member
110 posts

Joined: Jun 2015
QUOTE(slimey @ Mar 9 2021, 03:46 PM)
I won’t recommend anything higher than 3600 watt although in ideal scenario, a perfect 2.5 mmsq can handle 24 amp
*
https://shopee.com.my/EPS-20A-25A-2P-10mA-6...0848.2764232010
I would like to buy this(20A), am I getting the correct item?

This post has been edited by hendry91: Mar 12 2021, 11:23 AM
SUSslimey
post Mar 12 2021, 11:40 AM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(hendry91 @ Mar 12 2021, 11:22 AM)
https://shopee.com.my/EPS-20A-25A-2P-10mA-6...0848.2764232010
I would like to buy this(20A), am I getting the correct item?
*
Looks correct to me
SUSceo684
post Mar 12 2021, 12:18 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(hendry91 @ Mar 12 2021, 11:22 AM)
https://shopee.com.my/EPS-20A-25A-2P-10mA-6...0848.2764232010
I would like to buy this(20A), am I getting the correct item?
*
Yes, correct, RCBO 20A 10ma.
TShendry91
post Mar 13 2021, 10:54 AM

Getting Started
**
Junior Member
110 posts

Joined: Jun 2015
QUOTE(ceo684 @ Mar 12 2021, 12:18 PM)
Yes, correct, RCBO 20A 10ma.
*
Received the item, this one correct? 0.01A=10mA?
user posted image
SUSslimey
post Mar 13 2021, 01:05 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(hendry91 @ Mar 13 2021, 10:54 AM)
Received the item, this one correct? 0.01A=10mA?
user posted image
*
looks right to me
SUSceo684
post Mar 13 2021, 03:07 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(hendry91 @ Mar 13 2021, 10:54 AM)
Received the item, this one correct? 0.01A=10mA?
user posted image
*
Correct. Note that this RCBO is single direction connection to LINE/LOAD as top LINE/bottom LOAD ya.
TShendry91
post Mar 13 2021, 11:19 PM

Getting Started
**
Junior Member
110 posts

Joined: Jun 2015
Thanks ceo684 & slimey :-)

This post has been edited by hendry91: Mar 13 2021, 11:20 PM
TShendry91
post Apr 21 2021, 11:11 PM

Getting Started
**
Junior Member
110 posts

Joined: Jun 2015
QUOTE(ceo684 @ Mar 9 2021, 03:54 PM)
Hello, cannot use 4800W.

4800/230=20.8695652173913 A (21A for easy calculation)
by 80% derating factor (same as you don't redline your car every time) you should use cable that can support 26.25A ie minimum 4mm cable.

the minimum (as per ST spec) recommended is 4mm cable to use a 4800W heater (highlands model, usually from Pana or Hitachi).

In the market usually 3kw class is 3000W for storage, and 3300-3800W for instant WH. These are the recommended type (max power) for the 2.5mm cables typically installed.
Next step is 4800W.
Normally rare to find anything in between 3800 and 4800W.
If quality cable used.
If unknown/substandard cable.. insulation very thick, copper all substandard or adulterated so only 3kW class is safe option.
*
Hi, need your advice, can I use this heater? The electrical rating is 4.2kW, your mentioned the 3.6kW is fine for 2.5mm cable, but how about this?

user posted image
SUSceo684
post Apr 21 2021, 11:37 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(hendry91 @ Apr 21 2021, 11:11 PM)
Hi, need your advice, can I use this heater? The electrical rating is 4.2kW, your mentioned the 3.6kW is fine for 2.5mm cable, but how about this?

user posted image
*
Hi,
4200W / 230V = 18.26A


https://www.electrical-installation.org/enw...a_of_conductors
Per reference method B1 (single circuit, solid stranded cable enclosed in conduit) able to handle up to 21A with 2.5mm² cable.

This 21A is assuming that quality cable (eg Mega Kabel, Caramay, or any of the MCMA cartel members) is being used.. biggrin.gif
If elcheapo or fake cables - you might be running a risk that it is undersized for the load devil.gif

Also the length should be kept to reasonable length.. if the cables are too long then voltage drop will be a problem as well
Because if effective voltage drops, the amps go up
e.g. 4200W / 200V = 21A.
So there is about a 10% reserve capacity of the cable current capacity with 2.5mm² cables.. insofar as ST regulations go, officially they recommend minimum of 4mm² so that no need to worry or calculate so deeply.

This post has been edited by ceo684: Apr 21 2021, 11:40 PM
TShendry91
post Apr 22 2021, 05:35 AM

Getting Started
**
Junior Member
110 posts

Joined: Jun 2015
QUOTE(ceo684 @ Apr 21 2021, 11:37 PM)
Hi,
4200W / 230V = 18.26A
https://www.electrical-installation.org/enw...a_of_conductors
Per reference method B1 (single circuit, solid stranded cable enclosed in conduit) able to handle up to 21A with 2.5mm² cable.

This 21A is assuming that quality cable (eg Mega Kabel, Caramay, or any of the MCMA cartel members) is being used..  biggrin.gif
If elcheapo or fake cables - you might be running a risk that it is undersized for the load devil.gif

Also the length should be kept to reasonable length.. if the cables are too long then voltage drop will be a problem as well
Because if effective voltage drops, the amps go up
e.g. 4200W / 200V = 21A.
So there is about a 10% reserve capacity of the cable current capacity with 2.5mm² cables.. insofar as ST regulations go, officially they recommend minimum of 4mm² so that no need to worry or calculate so deeply.
*
What about this? Is this good enough?
user posted image
SUSceo684
post Apr 22 2021, 11:18 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(hendry91 @ Apr 22 2021, 05:35 AM)
What about this? Is this good enough?
user posted image
*
Should be OK, they print their name and spec on the cable, there's an older SIRIM cert issued for MPC cable and it is not in the news for fake SIRIM certs icon_rolleyes.gif
There are cases before - https://www.sirim-qas.com.my/forgery-on-license-no-pc000218/

How to identify a sub-standard cable (per https://www.st.gov.my/en/contents/files/dow...ble_testing.pdf )
1) Check and verify MARKINGS on Cable – shall be as per standard requirement
2) Check and verify APPROVAL / CERTIFICATION Mark/Label
3) Measure conductor resistance ( need to have a proper meter)
4) Measure size(s) • conductor • each strand ( and no of strands)
5) Check and verify copper content • normally by conductor resistance • weight the sample • Sometimes –by weighing the sample, with some experience, we can identify if the samples / weight of sample due to copper content or sheath of insulation

On the other hand w.r.t point no. 4 - there are also complaints on shopee that the cables are not as thick as they claim to be laugh.gif
https://shopee.com.my/MPC-2.5MM²-PVC-CABLE...2276.3417950523


This post has been edited by ceo684: Apr 22 2021, 11:24 PM
TShendry91
post Apr 27 2021, 12:56 PM

Getting Started
**
Junior Member
110 posts

Joined: Jun 2015
QUOTE(ceo684 @ Apr 22 2021, 11:18 PM)
Should be OK, they print their name and spec on the cable, there's an older SIRIM cert issued for MPC cable and it is not in the news for fake SIRIM certs   icon_rolleyes.gif
There are cases before - https://www.sirim-qas.com.my/forgery-on-license-no-pc000218/

How to identify a sub-standard cable (per https://www.st.gov.my/en/contents/files/dow...ble_testing.pdf )
1) Check and verify MARKINGS on Cable – shall be as per standard requirement
2) Check and verify APPROVAL / CERTIFICATION Mark/Label
3) Measure conductor resistance ( need to have a proper meter)
4)  Measure size(s) • conductor • each strand ( and no of strands)
5) Check and verify copper content • normally by conductor resistance • weight the sample • Sometimes –by weighing the sample, with some experience, we can identify if the samples / weight of sample due to copper content or sheath of insulation

On the other hand w.r.t point no. 4 - there are also complaints on shopee that the cables are not as thick as they claim to be  laugh.gif
https://shopee.com.my/MPC-2.5MM²-PVC-CABLE...2276.3417950523
*
Let's say, touch wood, when the cable overheat, will the MCB/RCD trip? I scare it won't trip and cause fire. lol

Actually I did check the cable marking last time, but I found that, when I rub the cable the marking will get erased, is that normal? Will quality cable be erased too?

This post has been edited by hendry91: Apr 27 2021, 01:03 PM
SUSceo684
post Apr 27 2021, 02:22 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(hendry91 @ Apr 27 2021, 12:56 PM)
Let's say, touch wood, when the cable overheat, will the MCB/RCD trip? I scare it won't trip and cause fire. lol

Actually I did check the cable marking last time, but I found that, when I rub the cable the marking will get erased, is that normal? Will quality cable be erased too?
*
That really depends on the max current capacity of the cable vs MCB.
For good cable lets say its 2.5mm² max safe load 24A. Meaning when it overload it will get warmer and warmer (it will not instantly kaboom at 26A).
When fitted with C20 MCB, rated 20A.
Mini overload say 21A on C20 maybe take 20min to trip the thermal overload characteristic of MCB.
More overload say 22A on C20 maybe take 6min to trip thermal.
Add more overload say 25A on C20 maybe take 2 min to trip.
More serious overload say 30A on C20 maybe 10 sec to trip thermal.
Times are just pluck from the air.

Its just to illustrate the slow blow characteristic of MCB. It will trip before the cables get insanely hot. As its not a huge overload (that will trip magnetic) all these small overload are thermal trip based, the higher the degree of overload the faster it will trip. MCB close 1 eye for minor overloads, where 20.1A on C20 will also probably take forever to trip. Like overloading a lorry by 20kg..JPJ close one eye lah.

Risk of substandard cable..

What happens in the use of cheapo cables that are underspec, where a small overload like 26A (supposedly safe upto 24A, but cable actually only safe up to 15A) is that even in normal operation it is running warm and if it gets to 26A may be very hot but MCB thinks OK je..but normal timing of slow blow of MCB only work if good cable is used..for substandard cable the cable itself may run a risk of overheating and melting BEFORE the slow blow trips. As we also cannot tell how lousy a substandard cable is (obviously it will proclaim the best) this is a gamble that most of us dont want to take, hence we always spec quality cables, but customers some dont understand and want cheapest possible prices..it is very easy to buy cheap shit junk at half price, that we all know..but this is something we want to sleep peacefully at night.

In event of short circuit aka HUGE overload many tens or hundreds of amp pass thru suddenly, ie way way over 5 to 10 times the 20A C curve rating it will trip the magnetic part of MCB instantly.
If the lorry overloaded at 200% of course cannot close one eye..JPJ kasi saman and impound it!

To digress on the C curve of C20 tongue.gif
MCB B curve instant magnetic trip between 3 to 5 times of rated full load current.meaning (3 to 5x) of 20A for a B20.
MCB C curve instant magnetic trip between 5 to 10 times of rated full load current. Meaning (5 to 10x) of 20A for a C20.

Malaysia is one of the funny places where B curve MCB is not common and C is plentiful. B curve already good enough for home use not to false/nuisance trip because..how many big motor or lathe machine or welding machine does one have AT HOME laugh.gif

In AU..B is commonly used for residential, i think same goes for UK.

https://www.se.com/au/en/faqs/FA290880/

QUOTE
B Curve means the MCB trips between 3-5 times full load current. It is mainly used in residential applications where loads are resistive e.g. lighting fixtures, domestic appliances with low surge Levels.
C Curve means the MCB trips between 5-10 times full load current. It is used  in commercial?industrial applications where there is greater chances of higher short circuit currents e.g. mainly inductive loads , fluorescent lighting.


This post has been edited by ceo684: Apr 27 2021, 02:32 PM
SUSslimey
post Apr 27 2021, 02:38 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(hendry91 @ Apr 27 2021, 12:56 PM)
Let's say, touch wood, when the cable overheat, will the MCB/RCD trip? I scare it won't trip and cause fire. lol

Actually I did check the cable marking last time, but I found that, when I rub the cable the marking will get erased, is that normal? Will quality cable be erased too?
*
Rcd does not trip due to heat.
Mcb yes, but must make sure mcb rating lower than cable rating.
The way mcb thermally trip is due to a thermal strip in the mcb that sense it’s own temperature, not the temp of the cable.
SUSceo684
post Apr 27 2021, 02:40 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(hendry91 @ Apr 27 2021, 12:56 PM)
Let's say, touch wood, when the cable overheat, will the MCB/RCD trip? I scare it won't trip and cause fire. lol

Actually I did check the cable marking last time, but I found that, when I rub the cable the marking will get erased, is that normal? Will quality cable be erased too?
*
To answer the question..in diff POV
For upto spec cable, yes when fitted w appropriate MCB yes MCB will trip if the cable overloaded. Slow blow or instant trip depending on overload size. But anyhow this will work regardless slow blow or instant trip

For substandard cable..in the reverse scenario..if MCB sized accordingly to actual true max safe capacity of cable lousy spec then will protect as per above case.
QUOTE
Challenge is how do we know the actual true max safe of fake cables


If MCB was sized to untrue claimed spec per the fake labelling (which is normal procedure)..there is such a risk the cable melted before MCB slow blow happens (if the cable is really substandard aka fake shit).

This post has been edited by ceo684: Apr 27 2021, 02:55 PM


Attached thumbnail(s)
Attached Image
TShendry91
post Apr 29 2021, 09:20 AM

Getting Started
**
Junior Member
110 posts

Joined: Jun 2015
QUOTE(ceo684 @ Apr 27 2021, 02:40 PM)
To answer the question..in diff POV
For upto spec cable, yes when fitted w appropriate MCB yes MCB will trip if the cable overloaded. Slow blow or instant trip depending on overload size. But anyhow this will work regardless slow blow or instant trip

For substandard cable..in the reverse scenario..if MCB sized accordingly to actual true max safe capacity of cable lousy spec then will protect as per above case.
If MCB was sized to untrue claimed spec per the fake labelling (which is normal procedure)..there is such a risk the cable melted before MCB slow blow happens (if the cable is really substandard aka fake shit).
*
Thanks.
I've another issue, I noticed that, when I switch on the light, my Fan Live cable will have minor current, the test pen light up, but not strong. Do you know what might be causing it? That wireman told me earth cable not deep enough, but I don't believe. lol
bobowyc
post Apr 29 2021, 09:33 AM

You are who you are.
******
Senior Member
1,921 posts

Joined: Apr 2013
From: Petaling Jaya


QUOTE(ceo684 @ Mar 4 2021, 01:45 PM)
Sis actually.  bruce.gif

1. What is the "MCB C20 WH"? is it different type of other MCB?
Standard C20 MCB.
WH denotes the one for WH circuit.

2. if I have 4 header, which mean I will need FOUR 10mA RCD?
Yes correct. WH 10mA RCD is per unit of WH. Each WH should be on its own dedicated circuit as one WH enough to use 15-17A nominal (WH is heavy appliance). Your 2.5mm cable only support 21A. And the 10mA RCD, only come (from branded mfg) up to 25A max current. In short, the standard cable sizing, the RCD current capacity (max 25A) all only suited for single unit WH as it is sensitive device (0.01A /10mA).
Whilst there are champions from china making 10mA RCD that can handle 40A laugh.gif I also dare not use.

3. The purpose of 10mA RCD is to trip when the heater leaking to our body? my current installation if leaking it won't trip?
Your current installation only trips at 300mA - by then, the human dieded 6 times over.
As the mains is 300mA, it allow 300mA leakage before it trip.
A human RIP at 50mA.
Attached Image

4. In short, I only need to have 10mA RCD in between the MCB and Header individually? Any other wiring need to be change/improve?
Yes, correct.
RCD is comparing input and output current difference. Input and output must = equal the same +/- RCD tolerance of say 10mA (0.01A).

Meaning, if WH input is 16A on L, at least 15.99A must return on WH output (N) else it has deemed to be lost somewhere.

Lost somewhere mean could be leaking through human.
So when the return not enough (<15.99) say only 11A return. The 4.99A cannot be lost, it mean it leak. As 4.99A far exceed the 0.01A allowed by 10mA RCD it will immediately trip.

MCB only consider single wire (L) amount of current passing through (short circuit prevention).
For a C20, meaning the speed limit is 20A.
Slight overload at 23A will trip the SLOW thermal overload after say 20 min.
Major overload at 100A will immediately trip the magnetic overload.

5. between I'm quite confusing are ELCB & RCCB the same? can you correct me if the naming in the image below wrong?
The difference is how and where they measure.
ELCB only detect earth current rise >0 leak (L to PE) leak on that appliance's earth. If it leak via anywhere else (L-N, or L-other PE eg wet floor, L-human) it will not bother. Hence in short I just say it protect that appliance only.

RCD because it constantly compare L input =N output + allowed tolerance (like 10.00A in on L, >9.99A must return as allowed tolerance is 0.01A for normal operation things like wire resistance that do NOT constitute a fault condition). It does not care where it leak through, RCD always compare in and out current so if it leak through any method (L-N, L-PE, L-other PE, L-human) it always trip.

Note: There is something called RCBO which do both function of MCB+RCD in one.
6. Appreciate if you can share the image of "MCB C20 WH" and 10mA RCD
MCB C20 is any usual C20 (20A MCB). WH is just designation for the WH circuit.

10mA RCD (must be used in conjunction together with C20 MCB) ie. add this along with MCB C20
ABB= https://www.lazada.com.my/products/abb-f202...i2IABn&search=1
Hager= https://www.lazada.com.my/products/hager-cc...l5n2dU&search=1
Schneider = https://www.lazada.com.my/products/schneide...8t5PsK&search=1

10mA RCBO = RCD+MCB in one package pao kah liao 2 function in one
Schneider RCBO https://www.lazada.com.my/products/schneide...PVCaV4&search=1
The drawback is, officially, their MCB is a C25 equivalent so you need to use with 4mm cable. As 2.5mm cable only good up to 21A rating.

user posted image
First one from left  is MCB 3P (3 pole) C63 (63A)
Second one is 4P RCD but this is 300mA. Only used in commercial/industrial where they use heavy motors. Not safe for residential and its against regulation, as the human has dieded 6x before this trips. (RCD/RCCB/RCCD = same function with diff name like zebra crossing=pedestrian crossing)
Third one is MCB 1P C10 (10A)

You will then ask, why do people still put the 300mA in residential?
Just to save the few bucks for more profit/lower tender cost whistling.gif
*
Holy.. I just bought a 3phase rccb and the seller gave me Hager 63A 4 pole 300ma RCCB. Should i tell them i want the smaller amp one? I already installed it in my client house just 2 days ago. -___- Why even the sellers dont know or they dont care? lol.
SUSceo684
post Apr 29 2021, 10:52 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(bobowyc @ Apr 29 2021, 09:33 AM)
Holy.. I just bought a 3phase rccb and the seller gave me Hager 63A 4 pole 300ma RCCB. Should i tell them i want the smaller amp one? I already installed it in my client house just 2 days ago. -___- Why even the sellers dont know or they dont care? lol.
*
For 4P, 300mA cheap ma coz insensitive.
They sell the 300mA because still valid use for industry.
Not all RCD created equal ohmy.gif

Should use the 30mA then up to par with current residential standard. 4P 30mA 63A usually cost almost double of the 4P 300ma.

Personally I'd still try to swap out to 30mA, safety first.

This post has been edited by ceo684: Apr 29 2021, 10:56 AM
SUSslimey
post Apr 29 2021, 11:06 AM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(hendry91 @ Apr 29 2021, 09:20 AM)
Thanks.
I've another issue, I noticed that, when I switch on the light, my Fan Live cable will have minor current, the test pen light up, but not strong. Do you know what might be causing it? That wireman told me earth cable not deep enough, but I don't believe. lol
*
wires run together in the same trunking.

it can induce a potential in nearby wires.

so there is voltage in them even without the switch is on. but if you test the current by putting the voltage to some or any work the voltage would immediately drop to zero.

pretty much normal and not a concern. nothing to do with earth or neutral
IMF2025
post Apr 29 2021, 11:08 AM

Getting Started
**
Junior Member
202 posts

Joined: Mar 2020


QUOTE(ceo684 @ Apr 29 2021, 10:52 AM)
For 4P, 300mA cheap ma coz insensitive.
They sell the 300mA because still valid use for industry.
Not all RCD created equal ohmy.gif

Should use the 30mA then up to par with current residential standard. 4P 30mA 63A usually cost almost double of the 4P 300ma.

Personally I'd still try to swap out to 30mA, safety first.
*
Aiyooo my hse too also using 300ma. Looks like these so called certified electriciant don’t know what they are doing.
lawrencesha
post Apr 29 2021, 11:12 AM

Enthusiast
*****
Junior Member
882 posts

Joined: Nov 2004


Nice.

This post has been edited by lawrencesha: Apr 29 2021, 03:28 PM
SUSceo684
post Apr 29 2021, 01:15 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(IMF2025 @ Apr 29 2021, 11:08 AM)
Aiyooo my hse too also using 300ma. Looks like these  so called certified electriciant don’t know what they are doing.
*
Can consider changing to 30mA whole house RCD.
It is actually not expensive for the RCD itself especially if you are on single phase - RCD 30mA 63A 2P - [ABB / Hager within RM130; Schneider within RM110].

Attached Image
Whilst ST regulations say maximum of 100mA whole house and 30mA for 13A sockets.. this entails fitting TWO RCDs moneyflies.gif moneyflies.gif moneyflies.gif
Note the maximum.. it is not "exactly/identical" but "up to" meaning.
Meaning to save cost + fully compliant with the law, a 30mA whole house RCD will protect everything with one single RCD unit.

Actually all these are covered in the ST guidelines but then again from business perspective the end user may not be aware of the risks or just want cheapest solution that lights up so corners will have to be cut somewhere whistling.gif
Attached File  ST_Guidelines_For_Electrical_Wiring_2008_Edition.pdf ( 427.2k ) Number of downloads: 13


QUOTE(lawrencesha @ Apr 29 2021, 11:12 AM)
Your wires looks so thin. What size you buy? I use minimum 2mm. I'm sure you loop the wires.

Looks scary.. like gonna melt at any time...
*
According to TS pic above TS is using 2.5mm² cables which should be fine for general sockets.
Also (presumably) looking at the nos. of MCBs in the whole DB box there should be enough individual circuits for the house not to exceed the 20A radial circuit floor area coverage of 20m² - if TS stay in 10 acre built-up home then that will be insufficient lah biggrin.gif

Attached Image
bobowyc
post Apr 29 2021, 01:26 PM

You are who you are.
******
Senior Member
1,921 posts

Joined: Apr 2013
From: Petaling Jaya


QUOTE(ceo684 @ Apr 29 2021, 10:52 AM)
For 4P, 300mA cheap ma coz insensitive.
They sell the 300mA because still valid use for industry.
Not all RCD created equal ohmy.gif

Should use the 30mA then up to par with current residential standard. 4P 30mA 63A usually cost almost double of the 4P 300ma.

Personally I'd still try to swap out to 30mA, safety first.
*
Whoa. Double the price? 😱 whoaaa. Expensive oh.. need check with my supplier see how much.
SUSceo684
post Apr 29 2021, 01:49 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(bobowyc @ Apr 29 2021, 01:26 PM)
Whoa. Double the price? 😱 whoaaa. Expensive oh.. need check with my supplier see how much.
*
Attached Image

Can get by with 300mA if the building is not a house but a factory/commercial building without 13A sockets laugh.gif
Ultimately still need at least one unit 30mA RCD to comply with mandatory requirements for residential.

Well.. once you go three phase it is one "increased cost factor" price element.. (over single phase)
Low amp (40A) three phase still cheap ..marginal increase from 63A single phase component
once you go higher amp (63A and above) on three phase .. another "increased cost factor" price element
high sensitivity component (w.r.t three phase) another "increased cost factor" price element laugh.gif

Hager
40A 4P the difference is RM127-145-166 between 300-100-30mA - for this case not much price difference, might as well go 30mA full
63A 4P the difference is RM153-199-250 between 300-100-30mA - for this case 60% diff hmm.gif

ABB FH204
40A 4P the difference is RM126-138-138 between 300-100-30mA - for this case not much price difference, might as well go 30mA full
63A 4P the difference is RM138-179-289 between 300-100-30mA - for this case it looks like double lah laugh.gif

This post has been edited by ceo684: Apr 29 2021, 01:51 PM
TShendry91
post Apr 29 2021, 02:47 PM

Getting Started
**
Junior Member
110 posts

Joined: Jun 2015
QUOTE(slimey @ Apr 29 2021, 11:06 AM)
wires run together in the same trunking.

it can induce a potential in nearby wires.

so there is voltage in them even without the switch is on. but if you test the current by putting the voltage to some or any work the voltage would immediately drop to zero.

pretty much normal and not a concern. nothing to do with earth or neutral
*
Sorry, I don't understand what u said. x faham what's the voltage & current in ur sentence. Haha
But can u tell me, when i switch on the light, the test pen have a very weak light(fan Live cable on the ceiling) is that normal or something wrong with the installation?
lyt25_1234
post Apr 29 2021, 03:12 PM

Regular
******
Senior Member
1,152 posts

Joined: Jul 2011
Is this smart meter that I can use myTNB app to monitor my house energy usage?

user posted image
SUSceo684
post Apr 29 2021, 04:21 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(hendry91 @ Apr 29 2021, 02:47 PM)
Sorry, I don't understand what u said. x faham what's the voltage & current in ur sentence. Haha
But can u tell me, when i switch on the light, the test pen have a very weak light(fan Live cable on the ceiling) is that normal or something wrong with the installation?
*
INDUCTIVE COUPLING
It is very normal (inductive coupling/voltage by inductance) as all the cables are run straight and in parallel over long distances (several meters) in close proximity (all stuffed into same conduit).
https://www.smar.com/en/technical-article/i...l-installations

WHY YOUR VOLTAGE INDICATOR LIGHTS UP ON NEARBY CABLES
Coz when the light cable is energised it will also have inductive coupling effect on nearby cables (ie fan cable).
The same effect also happens if you run the fan and test on the light cable.

This is partly why nobody install LAN cable in the same conduit next to power cables as the power cables will disturb the data transmission in unshielded UTP LAN cable.

INDUCTIVE COUPLING EFFECT USED IN NCV (Non Contact Voltage) DETECTION
The 230V AC voltage can be detected in non-contact voltage tester (as you can see even 8cm airgap here, the NCV detector lighted up)
Attached Image

QUOTE(lyt25_1234 @ Apr 29 2021, 03:12 PM)
Is this smart meter that I can use myTNB app to monitor my house energy usage?

user posted image
*
Its made by Smart meter company laugh.gif
Not sure bout the app, but on mytnb web, click around there will be an Other Resources or similar link for smart meter portal

This post has been edited by ceo684: Apr 29 2021, 05:27 PM
SUSslimey
post Apr 29 2021, 06:00 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(hendry91 @ Apr 29 2021, 02:47 PM)
Sorry, I don't understand what u said. x faham what's the voltage & current in ur sentence. Haha
But can u tell me, when i switch on the light, the test pen have a very weak light(fan Live cable on the ceiling) is that normal or something wrong with the installation?
*
normal.
cfc
post May 21 2022, 11:01 PM

Casual
***
Junior Member
440 posts

Joined: Apr 2005
QUOTE(ceo684 @ Mar 12 2021, 12:18 PM)
Yes, correct, RCBO 20A 10ma.
*
dear sifus..

i have 2 DB fuse box in my house (DS) , wiring was done probably 8yrs ago
I remembered the technician did inform me each wall socket plug has no looping and direct to one MCB (not sure how true was his claim though)

but i checked and found out that it is still not following the safety spec mention in here
it is using a 100mA main rcd and all my water heaters are without the 10mA rcd as well

I need to do the following which involve no extra rewiring , please check and let me know if i miss out anything

1. replace each WH mcb with Schneider rcbo 25A 10mA. Should i change it to EPS 20A 10mA (i guess mine also just 2.5mm, i have no way to find out now)
Each WH heater wall switch is a single 20A neon light panel.
https://shopee.com.my/-EZ9D16625-Schneider-...0a-3491ef9d4a1d

2. replace the both rcd 100mA with the abb FH202 / Hager 63A 30mA , should i replace main DB 63A too (black color beside rcd), what would be the model i need to get if needed
https://shopee.com.my/ABB-FH202-63A-2P-30mA...78-cde7900452a8
https://shopee.com.my/hager-25A-40A-63A-2P-...8f-8c6a72adb7e9

DC box photo - 1st floor RCD same as below but MCB just have single tier
» Click to show Spoiler - click again to hide... «


thanks for the advice

This post has been edited by cfc: May 21 2022, 11:10 PM
stormer.lyn
post May 22 2022, 10:13 AM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
dear sifus..
QUOTE(cfc @ May 21 2022, 11:01 PM)
1. replace each WH mcb with Schneider rcbo 25A 10mA. Should i change it to EPS 20A 10mA (i guess mine also just 2.5mm, i have no way to find out now)
Each WH heater wall switch is a single 20A neon light panel.
If your cables are 2.5 mm², then you must use the 20 A RCBO. Only if your cables are 4 mm² (or larger) can you install the 25 A RCBO. You can see the size of the wires from the slack that is in the DB.
Alternately, if your water heater is below 4500 W, then you can go ahead and install the 20 A RCBO, no matter the size of the wires (as long as it is 2.5 mm² or larger) This will ensure the RCBO trips on an overcurrent, before the wires overheat.

QUOTE
2. replace the both rcd 100mA with the abb FH202 / Hager 63A 30mA , should i replace main DB 63A too (black color beside rcd), what would be the model i need to get if needed
*
Either brand is acceptable, as long as they are at 30 mA sensitivity (The ABB FH202 RCCB you have listed in the sh*pee link has a 100 mA option)
It is not necessary to replace the incoming fused isolator EPS SFU-63 at position 24, 25, 26 in your DB

Edit : add information

This post has been edited by stormer.lyn: May 22 2022, 10:26 AM
cfc
post May 22 2022, 08:37 PM

Casual
***
Junior Member
440 posts

Joined: Apr 2005
Thanks for replying. Just checked , all is 2.5mm2 for those with 20A mcb.
Lazada/shopee only have eps or maxguard with 20A 10ma rcbo available , will get the eps brand then ..
Want to use a better quality part also cannot d

LESSON LEARNT :Equip with right adequate knowledge and get a qualified certified technician is important during renovation to avoid all the hassle in future


JasonTheGreat
post May 30 2022, 01:36 PM

Enthusiast
*****
Junior Member
832 posts

Joined: Jul 2016
Hi all sifus,
I just bought a built in oven with 3300W rating but find the cable 2 meters too short. The cable doesn't come with a plug.

As for my socket, the contractor built a 15A socket outlet to the MCB.

My questions is, is it safe to use a 20A connector block (white with screw) to connect to wire and then to a 15A socket?

stormer.lyn
post May 30 2022, 08:30 PM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(JasonTheGreat @ May 30 2022, 01:36 PM)
Hi all sifus,
I just  bought a built in oven with 3300W rating but find the cable 2 meters too short. The cable doesn't come with a plug.

As for my socket, the contractor built a 15A socket outlet to the MCB.

My questions is, is it safe to use a 20A connector block (white with screw) to connect to wire and then to a 15A socket?
*
While it is technically safe to use a 20 A terminal block, I prefer to use the NASA way for joining or also called the Western Union lineman's splice. Do once and I am sure that it will last forever.

If I need a water proof joint, I would add on the marine method for insulation, which is Self-amalgamating tape and and a layer of PVC insulating tape as the final external layer.

 