QUOTE(senscents @ Sep 24 2022, 01:29 PM)
Is this brand Reliable?
Just install 0.01mA for WH and 0.03mA for wall socket.
Wondering can I use the 25A for water heater ?
Previously was just 16A as the wire are 2.5mm.
An RCCB does not trip on overcurrent. You should be running Just install 0.01mA for WH and 0.03mA for wall socket.
Wondering can I use the 25A for water heater ?
Previously was just 16A as the wire are 2.5mm.
Incoming power -> 16 A MCB -> This 25 A, 10 mA RCCB -> Water heater,
so that the MCB trips if more than 16 A flows, and the RCCB trips if there is a leakage approaching 10 mA.
Only an RCBO is like a combination of MCB + RCCB, and will trip if overcurrent or leakage current.
Can't comment on the brand, sorry.