QUOTE(stormer.lyn @ Sep 24 2022, 01:39 PM)
An RCCB does not trip on overcurrent. You should be running
Incoming power -> 16 A MCB -> This 25 A, 10 mA RCCB -> Water heater,
so that the MCB trips if more than 16 A flows, and the RCCB trips if there is a leakage approaching 10 mA.
Only an RCBO is like a combination of MCB + RCCB, and will trip if overcurrent
or leakage current.
Can't comment on the brand, sorry.
Appreciate it.
So should I change to RCBO, according to the electrician that our place does not provide a water heater point only normal power point and our electric point share with an a/c also.
QUOTE(ceo684 @ Sep 24 2022, 02:27 PM)
Can't find anything related to the brand hence "no comment". The trademark is super generic nothing shows up on a bing/google search for "safety SRA2 RCCB" :confused:
Follow stormer.lyn post above is correct.
Personally, if own house I'd spec in
only ABB/Hager because "you get what you pay for" also applies to components - you get VI type RCD; anything cheaper tend to be VD type RCD.
Most probably will ask to change to a better brand.
Any brand with 16A RCCD or RCBO with 0.01mA for WH and 63A/0.03mA.
Can provide model no. for the VI type RCCD. Appreciate