The guy is probably right
fireballs
post Jan 12 2021, 10:26 PM

10101
*******
Senior Member
5,650 posts

Joined: Mar 2012
take a photo of your db panel

the buzzing is likely from loose contact. the loose contact will start causing heat, then burn the mcb. usually one mcb charring will trigger the rest if not fix immediately.

if u use those cap ayam one lagi facepalm

take the opportunity to review your protections against accidental touch/electrocution too
fireballs
post Jan 12 2021, 10:39 PM

10101
*******
Senior Member
5,650 posts

Joined: Mar 2012


sirim chop is good. but those with chop merely comply to bare minimum spec.
i dont trust those rm3 breakers. seriously.. the component also cost more than rm3

This post has been edited by fireballs: Jan 12 2021, 10:41 PM
fireballs
post Jan 12 2021, 10:57 PM

10101
*******
Senior Member
5,650 posts

Joined: Mar 2012
QUOTE(ceo684 @ Jan 12 2021, 10:42 PM)
I have seen all sorts of unknown no-SIRIM, questionable with SIRIM but China made barely passing brands to top tier LV equipment brands (ABB, Hager, Schneider, Siemens). Also in Msia mostly using C curve MCB which is very tolerant to overloading so if something really short out really is a big problem for sure laugh.gif
*
well..
mcb fail = fire. still have time to escape
leak = instant death


so for those who want to save money, go for cap ayam mcb, but please make sure rcd is branded.
fireballs
post Jan 12 2021, 11:11 PM

10101
*******
Senior Member
5,650 posts

Joined: Mar 2012
QUOTE(ceo684 @ Jan 12 2021, 11:06 PM)
Ideally all should be same brand.
In US the mfg dont cover if you use all rojak breakers.

Quality MCB only 7 bucks for 4.5kA or 8 bucks for 6kA
So even is boom also wont blow up whole place hahaha

What you said is true.. normally most of the top tier brand the cheap component MCB is made in china
But almost all the sensitive RCD (10ma/30mA) are still made in EU for better QC. Except S brand seems like everything in china one.
*
The s brand one...is using electronic tripping.
If voltage low, it may not trigger.
fireballs
post Jan 14 2021, 02:46 PM

10101
*******
Senior Member
5,650 posts

Joined: Mar 2012
QUOTE(MrGuGuZai @ Jan 14 2021, 12:36 PM)
user posted image
user posted image

13 years old mcb, whole house .
*
looks recent. no need to change all lah
just power off totally,
check/smell for burnt mark
retighten all all screws
the faulty mcb just replace it with same rating. if possible, get abb/hager/schneider brand MCB
just for the time being

when u have the budget, then consider to redo to proper rating





fireballs
post Jan 14 2021, 02:48 PM

10101
*******
Senior Member
5,650 posts

Joined: Mar 2012
QUOTE(clickNsnap @ Jan 14 2021, 02:27 PM)
Look like my house water heater (WH) is on 100mA... not for Life protection  sad.gif

Based on my MCB... cab I change the o.1A to 0.03A?

Thanks in advance!

user posted image

user posted image

user posted image
*
edited

the spd here is type1 for direct strike. i cant find the datasheet on this.
you may need to install a fuse to limit any current leak

you will need additional SPD type 2 to limit the voltage after a strike. most equipment wont survive a volt leak from a type 1 SPD


consider
type 1 = outdoor water filter. you wont drink from this tap
type 2 = clean filter. can shower
type 3 = cleanest can drink

This post has been edited by fireballs: Jan 14 2021, 02:57 PM
fireballs
post Jan 14 2021, 10:23 PM

10101
*******
Senior Member
5,650 posts

Joined: Mar 2012
QUOTE(clickNsnap @ Jan 14 2021, 09:14 PM)
What is the needs of additional SPD type 2? The current SPD setup serve well for now...before I install the SPD, my house gets tripped during heavy thunder storm/lighting.

Now, I am a bit of concern on my water heater... the previous post stated 100mA will not help to protect our life, change to 30mA is recommended.

Btw... what do you means...  hmm.gif  hmm.gif  hmm.gif
consider
type 1 = outdoor water filter. you wont drink from this tap
type 2 = clean filter. can shower
type 3 = cleanest can drink

*
spd is like water filter
type 1 handle the large direct strike current. thats why its written there as 10/350
however, the leakage also high. means if kena strike there will be some voltage pass through the filter

thus the need of type 2 spd for 8/20 wave


those belkins/mrdiy are type 3


for water heater you need 10mA
for socket outlet is 30mA
lamps can be 100mA

 

Change to: