Welcome Guest ( Log In | Register )

Outline · [ Standard ] · Linear+

 [WTA] Questions for adding new MCB to DB

views
     
excaliburcombo
post Oct 12 2020, 05:55 PM

Getting Started
**
Junior Member
222 posts

Joined: May 2016


QUOTE(WaCKy-Angel @ Oct 12 2020, 03:47 PM)
Btw side question, see the existing MCB some is C10, C16, C20, C32 i understand higher consumption stuffs should use higher amp right?
Short googling says C10 can support like 8 lightings so my question is should i just use the highest possible like C32 for everything?

I bought the place 2nd hand and did not re-do whole house wiring, just added alot points and lightings i actually did not want looping but after the job done only i found out many wiring are looping so should i change all the MCB to higher just to avoid tripping?
*

if not sure you better let the pro done for you. Safety first bro. C32 mostly use for ring wiring. C10 MCB should support much more than 8 light depend on load. Yes correct MCB depend on load but you should also look the wire itself. Ex 1.5mm wire but drive high load the wire will become hot then burn (litar pintas)

 

Change to:
| Lo-Fi Version
0.0143sec    0.21    7 queries    GZIP Disabled
Time is now: 23rd December 2025 - 11:33 AM