views
     
SUSslimey
post Mar 6 2019, 04:44 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(faiz293 @ Mar 6 2019, 04:41 PM)
Just call another one and ask him to check that filter?
*
first step is to check gas pressure and compressor drawing amp. then only can make the conclusion.
if pressure high(higher than normal) and drawing too much amp then likely filter problem.
drawing too much amp will overload the compressor and give that error.

but if pressure low then need to check for leakage in the connection or indoor coil or outdoor compressor leak
fireballs
post Mar 6 2019, 04:45 PM

10101
*******
Senior Member
5,650 posts

Joined: Mar 2012
Overload of compressor . Or the compressor run kaokao also hard to reach the set temperature.

Try this

Power off 10min then on back. Not the remote But the switch to the AC
Set temperature to 26c. Turn on
Listen to compressor run.
If the compressor turn on then off then on again, then OK.
Look at the hose near the compressor and see if got see ice on the pipe. If got = just refill gas
If the compressor turn on and continue to run until the error come out then off, then possiBle change the relay at indoor unit. Should be a rm10 item

alfiejr
post Mar 6 2019, 04:48 PM

Gaming~
******
Senior Member
1,294 posts

Joined: Feb 2012
From: Taman Rasa Sayang, Cheras


Indoor unit is changeable. Pricing depends on the reseller if cut throat or not. 2nd hand air cond is also not bad. Used 1 hp including outdoor unit only around rm300~400 again u need to know the technician before buying it.

So the safest is just to get a brand new one. Lazada has some good deals if you're into that.
TSfaiz293
post Mar 6 2019, 05:34 PM

Working from Home
****
Senior Member
623 posts

Joined: Jul 2008


QUOTE(fireballs @ Mar 6 2019, 04:45 PM)
Overload of compressor . Or the compressor run kaokao also hard to reach the set temperature.

Try this

Power off 10min then on back. Not the remote But the switch to the AC
Set temperature to 26c. Turn on
Listen to compressor run.
If the compressor turn on then off then on again, then OK.
Look at the hose near the compressor and see if got see ice on the pipe. If got = just refill gas
If the compressor turn on and continue to run until the error come out then off, then possiBle change the relay at indoor unit.  Should be a rm10 item
*
Did exactly like u said. Set to 26, compressor still running after 15 minutes. Straight change to 31, it stops. Change back to 26, compressor run.
SUSslimey
post Mar 6 2019, 05:49 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(faiz293 @ Mar 6 2019, 05:34 PM)
Did exactly like u said. Set to 26, compressor still running after 15 minutes. Straight change to 31, it stops. Change back to 26, compressor run.
*
lel.......why change it to 31........sure stop la........

your indoor unit sensor working fine la
fireballs
post Mar 6 2019, 06:22 PM

10101
*******
Senior Member
5,650 posts

Joined: Mar 2012
And the relay works fine too. Means indoor unit is working fine. Outdoor uNit probably fine too.

Now.. do u see frosty pipe?
TSfaiz293
post Mar 7 2019, 09:12 AM

Working from Home
****
Senior Member
623 posts

Joined: Jul 2008


QUOTE(teamjoker @ Mar 6 2019, 05:45 PM)
Bro, after survey can let me know which brand u buy? I wanna change soon also. Thanks.
*
Cancel, now my unit is working fine. Hehehehe

QUOTE(fireballs @ Mar 6 2019, 06:22 PM)
And the relay works fine too.  Means indoor unit is working fine. Outdoor uNit probably fine too.

Now.. do u see frosty pipe?
*
Bro, thanks for your troubleshooting steps! After i turned off the switch for 10 minutes, n try again, the unit is now working fine! Not sure what was the problem. If happen again, i'll just change to a new one. Cheers!
harryfoo
post Mar 7 2019, 09:23 AM

Look at all my stars!!
*******
Senior Member
2,296 posts

Joined: Feb 2010


QUOTE(budakdegilz @ Mar 6 2019, 04:13 PM)
better change all set jer

less headache when problem arise

if outdoor unit(compressor) is in workable condition

u can sell it about rm50-100
*
Where to sell old compressor AC unit?
SUSbudakdegilz
post Mar 7 2019, 09:30 AM

Regular
******
Senior Member
1,138 posts

Joined: Dec 2006



QUOTE(harryfoo @ Mar 7 2019, 09:23 AM)
Where to sell old compressor AC unit?
*
i sell it to my technician installer actually

experience 2 times with a different installer

for shop..not sure

maybe can try those household electric equipment repair shop

smile.gif
galkelly
post Feb 12 2020, 04:05 AM

Enthusiast
*****
Junior Member
752 posts

Joined: Jun 2012
QUOTE(faiz293 @ Mar 6 2019, 04:36 PM)
14 times flash.

If i turn off the main switch and wait for 30 seconds before turn on it will work again for 15-20 minutes before flashing.
*
Hi does ur mitsubishi mr slim still working ?
I am facing similar problem. On & off with blinking light.
Technician came & say could be thermostat faulty or relay swith. Yet cant determine the problem. Its been working fine for 20yrs. Now only got this problem. Its still blowing cold air.
Jus dunno why it on & off.
TSfaiz293
post Feb 12 2020, 07:15 AM

Working from Home
****
Senior Member
623 posts

Joined: Jul 2008


QUOTE(galkelly @ Feb 12 2020, 04:05 AM)
Hi does ur mitsubishi mr slim still working ?
I am facing similar problem. On & off with blinking light.
Technician came & say could be thermostat faulty or relay swith. Yet cant determine the problem. Its been working fine for 20yrs. Now only got this problem. Its still blowing cold air.
Jus dunno why it on & off.
*
Still working, but depending on its mood. If i turn on the ceiling fan along with the a/c, it will work fine. But see la, if no luck, it will turn off.
max_cavalera
post Feb 12 2020, 07:42 AM

rebirth
*******
Senior Member
5,614 posts

Joined: Jun 2006
From: Cyberjaya, Shah Alam, Ipoh



QUOTE(faiz293 @ Mar 6 2019, 05:13 PM)
You were saying to just change to a new unit?
He made a bypass i dont know what, and the ac works fine. So he suspect is the indoor unit. He quoted 480 for a recond unit.
*
My mistu mr the slim same problem after 5 years +... PCB board fried....my technician bypass the board. Can ON but cant control the temperature. Damn cold....

I just leave it be. But in ther future if ppl want to rent the place ill get it replaced with an inverter unit.
ivandj
post Oct 10 2020, 03:44 AM

On my way
****
Senior Member
578 posts

Joined: Jan 2005


Today mine had this problem .

When the compressor kicks in not more than a minute , Ac shuts down
and 14X blinking light

Model : ms-gh10vc

SUSceo684
post Oct 10 2020, 04:14 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(ivandj @ Oct 10 2020, 03:44 AM)
Today mine had this problem .

When the compressor kicks in not more than a minute , Ac shuts down
and 14X blinking light

Model : ms-gh10vc
*
Fan motor turning in IDU?
Sometimes fan motor failed will cause speed sensor to read 0, means epic fail so auto shut down
marukopi
post Oct 10 2020, 04:33 AM

Getting Started
**
Junior Member
174 posts

Joined: Feb 2019
Flash light and not cold ke? Then the aircond turn off itsef?

Last time me also got this issue, just change the outdoor unit. Now gooding.

This post has been edited by marukopi: Oct 10 2020, 04:34 AM
arc_archive
post Oct 10 2020, 05:00 AM

Casual
***
Junior Member
386 posts

Joined: Jun 2006
From: Luo Yang


Check the outdoor unit motor whether it produce any loud sound. My case a while ago, the blade motor was loud and suddenly at one point, it stop. Changed the motor and fill up the gas and it working fine till now.
ivandj
post Oct 10 2020, 05:02 AM

On my way
****
Senior Member
578 posts

Joined: Jan 2005


outdoor unit fine
ivandj
post Oct 10 2020, 05:05 AM

On my way
****
Senior Member
578 posts

Joined: Jan 2005


it will shut off when compressor is building up pressure
SUSdadah
post Oct 10 2020, 05:53 AM

Getting Started
**
Junior Member
161 posts

Joined: Apr 2019


lol ktard so kaya and straight say recond no good. My recond acson already 10 years still strong. I just change the kipas and it is still in good condition.

 

Change to: