change to 3 phase from 1 phase, can we do it outself?
|
TStrust4you
|
Sep 15 2018, 03:45 PM, updated 8y ago
|
|
Hi! would like to seek for expert opinion,
If we change residential title 1 phase to 3 phase, how much does it cost usually?
contractor got quote need at least 5k. really that expensive?
I ask TNB they just say caj sambungan RM250 and then deposit for residential is RM700 ( if u have deposit RM500 for one phase, then you just neef to top up RM200)
Please advise accordingly thank you!
Regards.
|
|
|
|
|
|
TStrust4you
|
Sep 18 2018, 08:24 PM
|
|
QUOTE(Richard @ Sep 17 2018, 05:20 PM) You need to redo your home DB (distribution box) wiring from one phase to three phase This includes add in rcd,mcb,busbars and a new box, the new three phase cables from the kwh meter to the board, testing and commissioning. Then liasing for the kwh meter installation Get a second or third party quotation to make the best decision boss usually how much does that cost? for the add in rcd,mcb,busbars and a new box, the new three phase cables from the kwh meter to the board, testing and commissioning?
|
|
|
|
|
|
TStrust4you
|
Sep 18 2018, 08:25 PM
|
|
QUOTE(BaRT @ Sep 17 2018, 08:51 PM) may i know why u wanna convert to 3 phase? if u dont mind, can share what electrical appliance in your house. boss convert 3 phase because i have 7 air cond, possible on 5 at the same time, one of it is 2 horsepower. if 1 phase can support ah boss
|
|
|
|
|
|
TStrust4you
|
Sep 19 2018, 11:29 PM
|
|
QUOTE(Richard @ Sep 19 2018, 04:57 PM) For five one HP aircon running at the same time, the possibilities of all inductive loads being on simultaneously very high due to the auto temp sensors of the aircon. The standard running amps roughly 4.5Amps and starting amps 6x minimum thus adding other auxiliary loads will overload the standard 63amps rated protection devices and cabling connection. For such a situation it is recommended to split the loads to 50%of the rated protection device and cabling connection. Thus adding a three phase incomer supply for safety and peace of mind.For minimizing risk hazard of an electrical fire Thefor are situations where a very high quality material and installation where the 63Amp rated fuse and oversized cabling will not blow fuse but such situations are discounted from the average situation. Conclusion for single phase to three phase per standard TNB supply 63amp HRC fuse c/w 16mm2 PVC cable is correct recommended. Edit* residential internal wiring is only 40/63Amps with 16mm2 PVC copper conductors. O/H hard drawn aluminium conductors to be sized one level higher. bro thank you for the detailed explaination. so lansi the way "slimey" replied. Lazy for me to layan that kind of person though.. besides i also have 60 plug point which will be used many at one shot, therefore my load will be quite high as well
|
|
|
|
|