 Electrical Wiring, Maximum Amp for 4mm cable

views
     
TSzzzhhhzzz
post Apr 18 2017, 07:39 AM, updated 9y ago

Regular
******
Senior Member
1,671 posts

Joined: Apr 2012
hi guys.. just wanted to ask some expert here.. what is the maximum amp that a 4mm cable with radial looping can take ? I read somewhere that a 2.5mm cable can take 20amp for radial circuit and 30amp for ring circuit... hope to get some help from some sifus here..
Zot
post Apr 18 2017, 08:09 AM

Look at all my stars!!
*******
Senior Member
7,938 posts

Joined: Mar 2014
This is not actually straight answer. Ability of wire to transfer current is different when transmitting over free air, inside concrete wall, how close two wire together, in trunking, etc. It also depends in ambient temperature.

In general, it is about 20A for 2.5mm cable. The ring circuit can carry more just because the current can be supplied in both direction from the Main Distributor Box. You can refer from this for Malaysia Guideline from Suruhanjaya Tenaga (ST)

http://www.st.gov.my/index.php/en/download...ntial-buildings

The 4mm can carry 26A under 30C ambient temperature. I'm no sifu blush.gif
cdspins
post Apr 18 2017, 08:10 AM

Look at all my stars!!
*******
Senior Member
2,714 posts

Joined: May 2008


I'm no sifus but was also interested to know... My understanding is that the length of cable also play a part. By the way, what you want to use it to power for? Home appliance rarely take more than 20A
billyboy
post Apr 18 2017, 08:16 AM

Look at all my stars!!
*******
Senior Member
2,220 posts

Joined: Apr 2006
copper or aluminium ?
made in malaysia or PRC ?
mega kabel or other brands ?
in the wall or outside ?

better put a decent margin
Zot
post Apr 18 2017, 08:18 AM

Look at all my stars!!
*******
Senior Member
7,938 posts

Joined: Mar 2014
QUOTE(cdspins @ Apr 18 2017, 08:10 AM)
I'm no sifus but was also interested to know... My understanding is that the length of cable also play a part. By the way, what you want to use it to power for? Home appliance rarely take more than 20A
*
Refer to the link I provided. I think it is easy to understand. Very good guide by ST
cdspins
post Apr 18 2017, 08:30 AM

Look at all my stars!!
*******
Senior Member
2,714 posts

Joined: May 2008


QUOTE(Zot @ Apr 18 2017, 08:18 AM)
Refer to the link I provided. I think it is easy to understand. Very good guide by ST
*
NICE rclxms.gif
TSzzzhhhzzz
post Apr 18 2017, 09:31 AM

Regular
******
Senior Member
1,671 posts

Joined: Apr 2012
thanks a lot guys biggrin.gif its actually conceal in concrete wall with pvc conduit....not using mega cable but made in malaysia cable with SIRIM
billyboy
post Apr 19 2017, 03:49 PM

Look at all my stars!!
*******
Senior Member
2,220 posts

Joined: Apr 2006
with JKR and ST chop is better quality
weikee
post Apr 19 2017, 04:30 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(zzzhhhzzz @ Apr 18 2017, 09:31 AM)
thanks a lot guys biggrin.gif its actually conceal in concrete wall with pvc conduit....not using mega cable but made in malaysia cable with SIRIM
*
Conceal cables will carry less load. 2.5mm in paper specification can go more than 20amps, but in real life use is better to be limit to 15amps. We cannot guarantee copper purity, bending issues that reduce the copper conductivity etc..

Here can give you some rought guide, always go lower than recommendation, don't go test threshold when life is at stake.

http://www.cable-ratings.co.uk/
Richard
post Apr 20 2017, 05:55 AM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(Zot @ Apr 18 2017, 08:09 AM)
This is not actually straight answer. Ability of wire to transfer current is different when transmitting over free air, inside concrete wall, how close two wire together, in trunking, etc. It also depends in ambient temperature.

In general, it is about 20A for 2.5mm cable. The ring circuit can carry more just because the current can be supplied in both direction from the Main Distributor Box. You can refer from this for Malaysia Guideline from Suruhanjaya Tenaga (ST)

http://www.st.gov.my/index.php/en/download...ntial-buildings

The 4mm can carry 26A under 30C ambient temperature. I'm no sifu  blush.gif
*
I would go with the Suruhanjaya Tenaga guidelines and progressively updated..


tangenttheta
post Apr 28 2017, 04:40 AM

Getting Started
**
Junior Member
62 posts

Joined: Dec 2013
Hi, i would like to ask is it safe for live wire for light and ceiling fan to be running at the floor?
And also is it safe for 2x1.5mm and 1x 1.5mm cable to supply 2 rooms and 1 bathroom, with heater, total of 7 sockets and 5lamps, 1 exhaust fan?
weikee
post Apr 28 2017, 08:21 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(tangenttheta @ Apr 28 2017, 04:40 AM)
Hi, i would like to ask is it safe for live wire for light and ceiling fan to be running at the floor?
And also is it safe for 2x1.5mm and 1x 1.5mm cable to supply 2 rooms and 1 bathroom, with heater, total of 7 sockets and 5lamps, 1 exhaust fan?
*
I assume you are running it on first floor for ground floor light if that is ok? You have to know where the wires are if not in future it you drill the floor will hit the wires. putting under the ground floor will be bad as moisture and underground termites may damage the cables.


1.5mm are way too thin, you need minimal 2.5mm, and each room minimal need one mcb, bath room seperate mcb.
tangenttheta
post Apr 28 2017, 11:06 AM

Getting Started
**
Junior Member
62 posts

Joined: Dec 2013
QUOTE(weikee @ Apr 28 2017, 08:21 AM)
I assume you are running it on first floor for ground floor light if that is ok? You have to know where the wires are if not in future it you drill the floor will hit the wires. putting under the ground floor will be bad as moisture and underground termites may damage the cables.   
1.5mm are way too thin, you need minimal 2.5mm, and each room minimal need one mcb, bath room seperate mcb.
*
It's in the ground floor living room, the wiring supplies fan and light, have 5 wires running in the ground but exposed like this..



This post has been edited by tangenttheta: Apr 28 2017, 11:08 AM


Attached thumbnail(s)
Attached Image
weikee
post Apr 28 2017, 11:26 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(tangenttheta @ Apr 28 2017, 11:06 AM)
It's in the ground floor living room, the wiring supplies fan and light, have 5 wires running in the ground but exposed like this..
*
This is really a lousy wiring man job. Furthermore without conduit. Good luck.
weikee
post Apr 28 2017, 11:28 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
All standard wiring have to come from top to bottom, not bottom up, water is bottom up.

Unless you have steel wall
tangenttheta
post Apr 28 2017, 11:51 AM

Getting Started
**
Junior Member
62 posts

Joined: Dec 2013
QUOTE(weikee @ Apr 28 2017, 11:28 AM)
All standard wiring have to come from top to bottom, not bottom up, water is bottom up.

Unless you have steel wall
*
I see.. so this is not the standard doing ya? Thanks thanks man..
heyamazingpeople
post May 3 2017, 12:17 AM

Casual
***
Junior Member
321 posts

Joined: Nov 2016
QUOTE(zzzhhhzzz @ Apr 18 2017, 07:39 AM)
hi guys.. just wanted to ask some expert here.. what is the maximum amp that a 4mm cable with radial looping can take ? I read somewhere that a 2.5mm cable can take 20amp for radial circuit and 30amp for ring circuit... hope to get some help from some sifus here..
*
where do u get to hear about ring and radial circuit?
Are you asking for your house renovation work? or Office, etc.?
TSzzzhhhzzz
post May 3 2017, 02:16 PM

Regular
******
Senior Member
1,671 posts

Joined: Apr 2012
QUOTE(heyamazingpeople @ May 3 2017, 12:17 AM)
where do u get to hear about ring and radial circuit?
Are you asking for your house renovation work? or Office, etc.?
*
House... wanted to loop further points... hence wanted to know the limitations...
fireballs
post May 3 2017, 02:19 PM

10101
*******
Senior Member
5,650 posts

Joined: Mar 2012
keep in mind the standards are referring to genuine copper cable.
many fakes out there ya
weikee
post May 3 2017, 03:06 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(zzzhhhzzz @ May 3 2017, 02:16 PM)
House... wanted to loop further points... hence wanted to know the limitations...
*
Ring circuit and looping are two different things.
heyamazingpeople
post May 3 2017, 04:14 PM

Casual
***
Junior Member
321 posts

Joined: Nov 2016
QUOTE(zzzhhhzzz @ May 3 2017, 02:16 PM)
House... wanted to loop further points... hence wanted to know the limitations...
*
usually people do radial only.
Ring is more to office.. Where there is redundancy if wiring been cut off. U can imagine?
Just wondering where u heard all these term.
TSzzzhhhzzz
post May 4 2017, 08:34 AM

Regular
******
Senior Member
1,671 posts

Joined: Apr 2012
QUOTE(heyamazingpeople @ May 3 2017, 04:14 PM)
usually people do radial only.
Ring is more to office.. Where there is redundancy if wiring been cut off. U can imagine?
Just wondering where u heard all these term.
*
Yeah i am aware that house all using radial circuit... im just stating what i read from some guidelines that if you have ring circuit your cable can take more amps... though not much people using ring.. even in offices =D
Richard
post May 4 2017, 09:15 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(zzzhhhzzz @ May 4 2017, 08:34 AM)
Yeah i am aware that house all using radial circuit... im just stating what i read from some guidelines that if you have ring circuit your cable can take more amps... though not much people using ring.. even in offices =D
*
The primary reason for using a ring circuit is to support more switch socket outlets over a wider area on a single breaker..

A ring circuit covers 100m2, using 2.5mm2 PVC copper conductor on a single 30 or 32A circuit breaker..

If covering a smaller area just run radial circuit,

- 2.5mm2 for 20m2 on a 20A circuit breaker or

- 4mm2 for 50m2 with a 32A breaker..



heyamazingpeople
post May 4 2017, 11:52 PM

Casual
***
Junior Member
321 posts

Joined: Nov 2016
QUOTE(zzzhhhzzz @ May 4 2017, 08:34 AM)
Yeah i am aware that house all using radial circuit... im just stating what i read from some guidelines that if you have ring circuit your cable can take more amps... though not much people using ring.. even in offices =D
*
I have not really come across people talking about ring circuit so there will be cost saving when this ring circuit is able to loop up more power point. (Maybe i have not seen that much)
We usually talk about ring circuit is the redundancy when some wiring somehow breaks and the power point still can work, as the way they are wired is different.

can refer to page 17 in pdf below
Guidelines For Electrical Wiring In Residential - Suruhanjaya Tenaga
(search and download from google)

Not exactly sure what is your application / reason to do so (just want to save money as looping is cheaper? My thinking is costing can be subjective from contractor to contractor anyway. ). But u just have to understand wiring is designed to carry certain Amps, while MCB (circuit breaker) to ensure Amps flowing thru it will not exceed certain Amps.
Wiring can be oversized but MCB rating shall never be bigger than wiring.
Wiring burnt when carrying higher Amps than it is specified and MCB will not trip if it is not selected properly.

And if you compare the schematic from ST, radial circuit vs ring circuit.. isnt that ring circuit will just an additional looping / return wiring to the MCB.. so shouldnt it be costing more?
Well, up to ur contractor to advise.

This post has been edited by heyamazingpeople: May 5 2017, 12:27 AM
weikee
post May 5 2017, 08:12 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(heyamazingpeople @ May 4 2017, 11:52 PM)
I have not really come across people talking about ring circuit so there will be cost saving when this ring circuit is able to loop up more power point. (Maybe i have not seen that much)
We usually talk about ring circuit is the redundancy when some wiring somehow breaks and the power point still can work, as the way they are wired is different.

can refer to page 17 in pdf below
Guidelines For Electrical Wiring In Residential - Suruhanjaya Tenaga
(search and download from google)

Not exactly sure what is your application / reason to do so (just want to save money as looping is cheaper? My thinking is costing can be subjective from contractor to contractor anyway. ). But u just have to understand wiring is designed to carry certain Amps, while MCB (circuit breaker) to ensure Amps flowing thru it will not exceed certain Amps.
Wiring can be oversized but MCB rating shall never be bigger than wiring.
Wiring burnt when carrying higher Amps than it is specified and MCB will not trip if it is not selected properly.

And if you compare the schematic from ST, radial circuit vs ring circuit.. isnt that ring circuit will just an additional looping / return wiring to the MCB.. so shouldnt it be costing more?
Well, up to ur contractor to advise.
*
The "Malaysian" wireman will define looping as radial.

While actual looping technically can handle more load because the current are return back to mcb via 2 path. Ring will give redundant and more current. But will also give the danger of over load the wires if one of the path break and load are running high.
RickJames09
post Apr 18 2019, 12:18 PM

Getting Started
**
Junior Member
124 posts

Joined: Sep 2016
Hi Guys,

Can anyone explain to me whether my understanding is correct or not? For no 1-3, is that correct?

And what is no 4? it looks like RCD as well but i do not understand why there are so many RCD in this setup.

Thanks a bunch.

user posted image
Erza Scarlet
post Apr 18 2019, 12:33 PM

Getting Started
**
Junior Member
201 posts

Joined: Jul 2008
QUOTE(RickJames09 @ Apr 18 2019, 12:18 PM)
Hi Guys,

Can anyone explain to me whether my understanding is correct or not? For no 1-3, is that correct?

And what is no 4? it looks like RCD as well but i do not understand why there are so many RCD in this setup.

Thanks a bunch.

user posted image
*
No 3 come from no 4 in the left am i right?
SUSceo684
post Apr 18 2019, 10:44 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(RickJames09 @ Apr 18 2019, 12:18 PM)
Hi Guys,

Can anyone explain to me whether my understanding is correct or not? For no 1-3, is that correct?

And what is no 4? it looks like RCD as well but i do not understand why there are so many RCD in this setup.

Thanks a bunch.

user posted image
*
#4 Delixi CDB6VR is a electromagnetic RCCB.

Do note that "RCD" is a very broad term. Many different types of Residual Current Devices (RCD) exist.

For comparison sake:

RCCB. (Residual Current Operated Circuit Breaker without Integral Overcurrent Protection)
RCBO. (Residual Current Operated Circuit Breaker with Integral Overcurrent Protection)


RCCB is only an earth leakage protection device.
RCBO is Short circuit current protection device as well as earth leakage protection device.


The RCCB only measures the out of balance in current in the active and neutral wires. This is the current leaking to ground. It protects you against shock.
The RCBO does what the RCCB does, plus it has overload protection.

 

Change to: