 Electrical Wiring, Maximum Amp for 4mm cable

views
     
TSzzzhhhzzz
post Apr 18 2017, 07:39 AM, updated 9y ago

Regular
******
Senior Member
1,671 posts

Joined: Apr 2012
hi guys.. just wanted to ask some expert here.. what is the maximum amp that a 4mm cable with radial looping can take ? I read somewhere that a 2.5mm cable can take 20amp for radial circuit and 30amp for ring circuit... hope to get some help from some sifus here..
Zot
post Apr 18 2017, 08:09 AM

Look at all my stars!!
*******
Senior Member
7,938 posts

Joined: Mar 2014
This is not actually straight answer. Ability of wire to transfer current is different when transmitting over free air, inside concrete wall, how close two wire together, in trunking, etc. It also depends in ambient temperature.

In general, it is about 20A for 2.5mm cable. The ring circuit can carry more just because the current can be supplied in both direction from the Main Distributor Box. You can refer from this for Malaysia Guideline from Suruhanjaya Tenaga (ST)

http://www.st.gov.my/index.php/en/download...ntial-buildings

The 4mm can carry 26A under 30C ambient temperature. I'm no sifu blush.gif
cdspins
post Apr 18 2017, 08:10 AM

Look at all my stars!!
*******
Senior Member
2,714 posts

Joined: May 2008


I'm no sifus but was also interested to know... My understanding is that the length of cable also play a part. By the way, what you want to use it to power for? Home appliance rarely take more than 20A
billyboy
post Apr 18 2017, 08:16 AM

Look at all my stars!!
*******
Senior Member
2,220 posts

Joined: Apr 2006
copper or aluminium ?
made in malaysia or PRC ?
mega kabel or other brands ?
in the wall or outside ?

better put a decent margin
Zot
post Apr 18 2017, 08:18 AM

Look at all my stars!!
*******
Senior Member
7,938 posts

Joined: Mar 2014
QUOTE(cdspins @ Apr 18 2017, 08:10 AM)
I'm no sifus but was also interested to know... My understanding is that the length of cable also play a part. By the way, what you want to use it to power for? Home appliance rarely take more than 20A
*
Refer to the link I provided. I think it is easy to understand. Very good guide by ST
cdspins
post Apr 18 2017, 08:30 AM

Look at all my stars!!
*******
Senior Member
2,714 posts

Joined: May 2008


QUOTE(Zot @ Apr 18 2017, 08:18 AM)
Refer to the link I provided. I think it is easy to understand. Very good guide by ST
*
NICE rclxms.gif
TSzzzhhhzzz
post Apr 18 2017, 09:31 AM

Regular
******
Senior Member
1,671 posts

Joined: Apr 2012
thanks a lot guys biggrin.gif its actually conceal in concrete wall with pvc conduit....not using mega cable but made in malaysia cable with SIRIM
billyboy
post Apr 19 2017, 03:49 PM

Look at all my stars!!
*******
Senior Member
2,220 posts

Joined: Apr 2006
with JKR and ST chop is better quality
weikee
post Apr 19 2017, 04:30 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(zzzhhhzzz @ Apr 18 2017, 09:31 AM)
thanks a lot guys biggrin.gif its actually conceal in concrete wall with pvc conduit....not using mega cable but made in malaysia cable with SIRIM
*
Conceal cables will carry less load. 2.5mm in paper specification can go more than 20amps, but in real life use is better to be limit to 15amps. We cannot guarantee copper purity, bending issues that reduce the copper conductivity etc..

Here can give you some rought guide, always go lower than recommendation, don't go test threshold when life is at stake.

http://www.cable-ratings.co.uk/
Richard
post Apr 20 2017, 05:55 AM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(Zot @ Apr 18 2017, 08:09 AM)
This is not actually straight answer. Ability of wire to transfer current is different when transmitting over free air, inside concrete wall, how close two wire together, in trunking, etc. It also depends in ambient temperature.

In general, it is about 20A for 2.5mm cable. The ring circuit can carry more just because the current can be supplied in both direction from the Main Distributor Box. You can refer from this for Malaysia Guideline from Suruhanjaya Tenaga (ST)

http://www.st.gov.my/index.php/en/download...ntial-buildings

The 4mm can carry 26A under 30C ambient temperature. I'm no sifu  blush.gif
*
I would go with the Suruhanjaya Tenaga guidelines and progressively updated..


tangenttheta
post Apr 28 2017, 04:40 AM

Getting Started
**
Junior Member
62 posts

Joined: Dec 2013
Hi, i would like to ask is it safe for live wire for light and ceiling fan to be running at the floor?
And also is it safe for 2x1.5mm and 1x 1.5mm cable to supply 2 rooms and 1 bathroom, with heater, total of 7 sockets and 5lamps, 1 exhaust fan?
weikee
post Apr 28 2017, 08:21 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(tangenttheta @ Apr 28 2017, 04:40 AM)
Hi, i would like to ask is it safe for live wire for light and ceiling fan to be running at the floor?
And also is it safe for 2x1.5mm and 1x 1.5mm cable to supply 2 rooms and 1 bathroom, with heater, total of 7 sockets and 5lamps, 1 exhaust fan?
*
I assume you are running it on first floor for ground floor light if that is ok? You have to know where the wires are if not in future it you drill the floor will hit the wires. putting under the ground floor will be bad as moisture and underground termites may damage the cables.


1.5mm are way too thin, you need minimal 2.5mm, and each room minimal need one mcb, bath room seperate mcb.
tangenttheta
post Apr 28 2017, 11:06 AM

Getting Started
**
Junior Member
62 posts

Joined: Dec 2013
QUOTE(weikee @ Apr 28 2017, 08:21 AM)
I assume you are running it on first floor for ground floor light if that is ok? You have to know where the wires are if not in future it you drill the floor will hit the wires. putting under the ground floor will be bad as moisture and underground termites may damage the cables.   
1.5mm are way too thin, you need minimal 2.5mm, and each room minimal need one mcb, bath room seperate mcb.
*
It's in the ground floor living room, the wiring supplies fan and light, have 5 wires running in the ground but exposed like this..



This post has been edited by tangenttheta: Apr 28 2017, 11:08 AM


Attached thumbnail(s)
Attached Image
weikee
post Apr 28 2017, 11:26 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(tangenttheta @ Apr 28 2017, 11:06 AM)
It's in the ground floor living room, the wiring supplies fan and light, have 5 wires running in the ground but exposed like this..
*
This is really a lousy wiring man job. Furthermore without conduit. Good luck.
weikee
post Apr 28 2017, 11:28 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
All standard wiring have to come from top to bottom, not bottom up, water is bottom up.

Unless you have steel wall
tangenttheta
post Apr 28 2017, 11:51 AM

Getting Started
**
Junior Member
62 posts

Joined: Dec 2013
QUOTE(weikee @ Apr 28 2017, 11:28 AM)
All standard wiring have to come from top to bottom, not bottom up, water is bottom up.

Unless you have steel wall
*
I see.. so this is not the standard doing ya? Thanks thanks man..
heyamazingpeople
post May 3 2017, 12:17 AM

Casual
***
Junior Member
321 posts

Joined: Nov 2016
QUOTE(zzzhhhzzz @ Apr 18 2017, 07:39 AM)
hi guys.. just wanted to ask some expert here.. what is the maximum amp that a 4mm cable with radial looping can take ? I read somewhere that a 2.5mm cable can take 20amp for radial circuit and 30amp for ring circuit... hope to get some help from some sifus here..
*
where do u get to hear about ring and radial circuit?
Are you asking for your house renovation work? or Office, etc.?
TSzzzhhhzzz
post May 3 2017, 02:16 PM

Regular
******
Senior Member
1,671 posts

Joined: Apr 2012
QUOTE(heyamazingpeople @ May 3 2017, 12:17 AM)
where do u get to hear about ring and radial circuit?
Are you asking for your house renovation work? or Office, etc.?
*
House... wanted to loop further points... hence wanted to know the limitations...
fireballs
post May 3 2017, 02:19 PM

10101
*******
Senior Member
5,650 posts

Joined: Mar 2012
keep in mind the standards are referring to genuine copper cable.
many fakes out there ya
weikee
post May 3 2017, 03:06 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(zzzhhhzzz @ May 3 2017, 02:16 PM)
House... wanted to loop further points... hence wanted to know the limitations...
*
Ring circuit and looping are two different things.

2 Pages  1 2 >Top
 