 [UPDATE] Tangki Air Overflow, even after changing pelampung set (pic)

views
     
TSone1002
post Oct 25 2015, 11:42 AM, updated 8y ago

On my way
****
Senior Member
617 posts

Joined: Jun 2009


Hi guys,

I'm having some kind of weird problem that I cannot figure out the source.....

My water tank is overflowing like waterfall dei...not sure if it's related, but it happened right after the maintenance by SYABAS in gombak area (batu caves).

Went to the bumbung to check, panjat here panjat there, found the tangki..opened the tangki, checked the pelampung, ok i think it's time to change the pelampung..damn hard to unscrew it..

So the process of changing the pelampung went well eventually. I thought I have solved it..but after a few hours, started overflowing again..... rclxub.gif rclxub.gif

Went back to the bumbung, suddenly tengok-tengok, the tangki full (above normal level).. Turned off main pipe, opened some taps to reduce the water level in the tangki..then checked the pelampung back again.. here are some pictures,


1) Checking the newly bought and installed pelampung set... Tangki is being filled..

Attached Image


2) Tried hand-stopping the pelampung, good, no water dripping...

Attached Image


3) Water automatically stopped, meaning no dripping. confirmed pelampung ok..

Attached Image


4) Now the water level still rising, until the pelampung also tenggelam....started overflowing again...

Attached Image


Now i really pening what could've caused the overflowing problem....I suspect it's the non-return valve.. But, well.. i don't know where it is, don't know what it looks like..and too many pipe connection...lol..

Can someone help me pleaseeee....tension gila!



------------------------- UPDATE ---------------------------------

Went back again to the roof, to take some pictures of the pipe connection just in case some one can help pinpoint the problem.

THIS IS THE FIRST TIME I WENT TO THE ROOF, SO VERY THE MESSY...NEVER KNEW SO MANY SAMPAH SARAP HERE LEFT BY THE OLD CONTRACTORS..ISH ISH ISH vmad.gif vmad.gif mad.gif mad.gif


1) Is the red circled the NON RETURN VALVE? The black pipe is the main pipe from outside into the tank.

Attached Image



2) Is this too?

Attached Image



If the non-return valve may be the cause, how much would it cost? can D.I.Y ke???? easy?? if can, I might do it myself... hujung bulan no gaji yet... rclxub.gif rclxub.gif rclxub.gif





The flow of the piping:

1) Attached Image

2) Attached Image

3) Attached Image

4) Attached Image

5)Attached Image






-----------------------------------------------------------------UPDATE 1ST NOVEMBER 2015-----------------------------------------------------------------


So I finally went to the hardware shop and bought two Check Valve (3/4") size..

Started to operation roof!! While going to the hardware, opened all taps to empty the water from the tank.. Then started opening the first suspected Check Valve.. It was soooo ketat to open had to use extra force.. I thought that was hard, but removing the previous pipe tape (the white tape) was even harder!!!!!

Here's the pic of the old check valve.. I THINK THE SPRING IS NOT WORKING ANYMORE. PUSHED EITHER SIDE, NOTHING MOVED. SO YEAH I GUESS THE SPRING IS NOT FUNCTIONING ANYMORE


Front

Attached Image



Back

Attached Image


And here's the pic of the new Check Valve.. The spring works wonderful..

Attached Image

Attached Image



Changed two suspected Check Valve to avoid double work.. I accidentally left one of the old check valved on the roof, malas nak ambil lagi.. later ambil lah..haha

Cost?? RM30 for one Check Valve (made in italy woi!!), and RM3 for the white tape..total with GST = RM67.30 (IINM)..

This is the first time my operation roof.. Hopefully with the lack of skills, I am able to solve my problem. Checked at the joints, alhamdulillah no leaking or evidence of water outside of the valve.. I hope the connection is tight and secure..

Tank is still filling though. I'll update if it still overflows....hopefully not!!!!! Touchwood!!

This post has been edited by one1002: Nov 1 2015, 02:29 PM
isildur88
post Oct 25 2015, 11:45 AM

Lord of Winterfell
*****
Senior Member
774 posts

Joined: May 2006
From: Winterfell


chane to new set. the one in the picture looks old
lucifah
post Oct 25 2015, 11:50 AM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


easiest n cheapest way?

bend the arm downward

and tie some empty mineral water bottle at the end

problem solved

zero cost
momusu
post Oct 25 2015, 12:00 PM

~morning musume fanboy~
*****
Senior Member
812 posts

Joined: Jan 2003
From: FantasyLand
put small bucket under the outlet, then wait n see if any leaks at the water outlet.

is that the only piping into the tank?
TSone1002
post Oct 25 2015, 12:14 PM

On my way
****
Senior Member
617 posts

Joined: Jun 2009


QUOTE(isildur88 @ Oct 25 2015, 11:45 AM)
chane to new set. the one in the picture looks old
*
change what to new set? If the arm set, it is new set. Just bought and installed yesterday... if the bola, still useable, tried rendam in water, no holes no bubbles, so still can use.. =D

QUOTE(lucifah @ Oct 25 2015, 11:50 AM)
easiest n cheapest way?

bend the arm downward

and tie some empty mineral water bottle at the end

problem solved

zero cost
*
Ya, if you see in the picture, the arm is already bent twice.. I bent it before installing.. However, even I bend it further down, it still will overflow, double triple check the pelampung, no water leak from the main pipe to the tangki, ceiling is not wet, no water dripping from the pelampung.. anyway, i tried your suggestion, same thing haha..


QUOTE(momusu @ Oct 25 2015, 12:00 PM)
put small bucket under the outlet, then wait n see if any leaks at the water outlet.

is that the only piping into the tank?
*
Hi, thanks for the reply, unfortunately, there are no water leaks. I went around the tangki, bend downwards to check for any water residue on the floor (ceiling), nope..nothing..no leaks confirmed!

For the connection, I have updated the photos in my first post.

This post has been edited by one1002: Oct 25 2015, 12:20 PM
lucifah
post Oct 25 2015, 12:16 PM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(one1002 @ Oct 25 2015, 12:14 PM)
Ya, if you see in the picture, the arm is already bent twice.. I bent it before installing.. However, even I bend it further down, it still will overflow, double triple check the pelampung, no water leak from the main pipe to the tangki, ceiling is not wet, no water dripping from the pelampung.. anyway, i tried your suggestion, same thing haha..

*
bend it more like up to 60^ angle

since it doesn't have any adjusting screw, that's the only way to do it

or you can open up the valve and change the rubber diaphgram inside

that round rubber thing is only 50 sen at most maybe
lucifah
post Oct 25 2015, 12:18 PM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


ah, since you showed the 1-way check valve, i know your prob liao

the check valve got problem. u try to switch off the bypass

i see you have a bypass system. very clever thumbup.gif
SUS+ Blind Target +
post Oct 25 2015, 12:18 PM

Getting Started
**
Junior Member
133 posts

Joined: Oct 2014
From: Behind You !


did u change the bola pelampung or not, it looks used
lucifah
post Oct 25 2015, 12:19 PM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


the check valve is around rm 20. depending on size.

usually, this type of check valve, the spring inside corroded and not strong enough to push the plate to close the valve

thus water gets into the tank from the check valve itself

This post has been edited by lucifah: Oct 25 2015, 12:20 PM
magnesium
post Oct 25 2015, 12:22 PM

Regular
******
Senior Member
1,130 posts

Joined: May 2006


Could you please tell me while the water overflow, where is the water source into the tank?

That pelampung did you chage together the valve?
TSone1002
post Oct 25 2015, 12:24 PM

On my way
****
Senior Member
617 posts

Joined: Jun 2009


QUOTE(lucifah @ Oct 25 2015, 12:18 PM)
ah, since you showed the 1-way check valve, i know your prob liao

the check valve got problem. u try to switch off the bypass

i see you have a bypass system. very clever thumbup.gif
*
Lol, i no idea what you talking about hahaha..still learning... Check valve = Non-Return Valve = Red Circled in the picture??? Same thing? How do I switch off the bypass?

Sorry Lucifah for asking these, trying to learn few things before I call plumber...hahaha..

QUOTE(+ Blind Target + @ Oct 25 2015, 12:18 PM)
did u change the bola pelampung or not, it looks used
*
Nope, used back the bola.. Bola still useable..sudah rendam dalam air, bounced back like gila high..so still can use..check for holes or leaks, none found! =D

QUOTE(lucifah @ Oct 25 2015, 12:19 PM)
the check valve is around rm 20. depending on size.

usually, this type of check valve, the spring inside corroded and not strong enough to push the plate to close the valve

thus water gets into the tank from the check valve itself
*
This is what I suspect too...so I think better to change the whole set of valve right?

TSone1002
post Oct 25 2015, 12:29 PM

On my way
****
Senior Member
617 posts

Joined: Jun 2009


QUOTE(magnesium @ Oct 25 2015, 12:22 PM)
Could you please tell me while the water overflow, where is the water source into the tank?

That pelampung did you chage together the valve?
*
Hi, this is the reason I created this thread. biggrin.gif biggrin.gif Because I myself cannot figure out the water source into the tank (after the bola pelampung has stopped the water inlet). If you notice on my pictures in the first post, the pelampung set works wonderfully well. No dripping.. So I think, there must be some back-flow water coming back into the tank..hence it's overflowing.

Unfortunately, I have very very very limited knowledge in plumbing works..still learning..googling..etc.. =D

Bola pelampung is still usable, so I did not change it..just the arm.. In the first picture, the brass (tembaga) thing is new..made in England tau..haha
lucifah
post Oct 25 2015, 12:38 PM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(one1002 @ Oct 25 2015, 12:24 PM)
Lol, i no idea what you talking about hahaha..still learning... Check valve = Non-Return Valve = Red Circled in the picture??? Same thing? How do I switch off the bypass?

Sorry Lucifah for asking these, trying to learn few things before I call plumber...hahaha..
Nope, used back the bola.. Bola still useable..sudah rendam dalam air, bounced back like gila high..so still can use..check for holes or leaks, none found! =D
This is what I suspect too...so I think better to change the whole set of valve right?
*
i saw your pics got 2 check valve and 2 outlet pipes, so ayam confused why you have two

need to understand how your piping flow is baru can give idea
SUStlts
post Oct 25 2015, 12:58 PM

pee poo pee poo
******
Senior Member
1,891 posts

Joined: Apr 2008
From: Cheras
last time i got this problem to..in ma toilet...change pelampung also same ...problem is inside the 1st pic got 1 rubber part worn out aready
TSone1002
post Oct 25 2015, 01:27 PM

On my way
****
Senior Member
617 posts

Joined: Jun 2009


QUOTE(lucifah @ Oct 25 2015, 12:38 PM)
i saw your pics got 2 check valve and 2 outlet pipes, so ayam confused why you have two

need to understand how your piping flow is baru can give idea
*
OK Lucifah, I have prepared the piping flow for you..haha

1) Attached Image


2) Attached Image


3) Attached Image


4) Attached Image


5) The overall layout

Attached Image
magnesium
post Oct 25 2015, 02:21 PM

Regular
******
Senior Member
1,130 posts

Joined: May 2006


QUOTE(one1002 @ Oct 25 2015, 01:27 PM)
OK Lucifah, I have prepared the piping flow for you..haha

1) Attached Image
2) Attached Image
3) Attached Image
4) Attached Image
5) The overall layout

Attached Image
*
I think 1st picture with red circle is the problem

It fails hence water back flow into your tank.
Blindspot61
post Oct 25 2015, 03:45 PM

Getting Started
**
Junior Member
51 posts

Joined: Sep 2010


QUOTE(one1002 @ Oct 25 2015, 11:42 AM)
Hi guys,

I'm having some kind of weird problem that I cannot figure out the source.....

My water tank is overflowing like waterfall dei...not sure if it's related, but it happened right after the maintenance by SYABAS in gombak area (batu caves).

Went to the bumbung to check, panjat here panjat there, found the tangki..opened the tangki, checked the pelampung, ok i think it's time to change the pelampung..damn hard to unscrew it..

So the process of changing the pelampung went well eventually. I thought I have solved it..but after a few hours, started overflowing again.....  rclxub.gif  rclxub.gif

Went back to the bumbung, suddenly tengok-tengok, the tangki full (above normal level).. Turned off main pipe, opened some taps to reduce the water level in the tangki..then checked the pelampung back again.. here are some pictures,
1) Checking the newly bought and installed pelampung set... Tangki is being filled..

Attached Image
2) Tried hand-stopping the pelampung, good, no water dripping...

Attached Image
3) Water automatically stopped, meaning no dripping. confirmed pelampung ok..

Attached Image
4) Now the water level still rising, until the pelampung also tenggelam....started overflowing again...

Attached Image
Now i really pening what could've caused the overflowing problem....I suspect it's the non-return valve.. But, well.. i don't know where it is, don't know what it looks like..and too many pipe connection...lol..

Can someone help me pleaseeee....tension gila!
------------------------- UPDATE ---------------------------------

Went back again to the roof, to take some pictures of the pipe connection just in case some one can help pinpoint the problem.

THIS IS THE FIRST TIME I WENT TO THE ROOF, SO VERY THE MESSY...NEVER KNEW SO MANY SAMPAH SARAP HERE LEFT BY THE OLD CONTRACTORS..ISH ISH ISH  vmad.gif  vmad.gif  mad.gif  mad.gif
1) Is the red circled the NON RETURN VALVE? The black pipe is the main pipe from outside into the tank.

Attached Image
2) Is this too?

Attached Image
If the non-return valve may be the cause, how much would it cost? can D.I.Y ke???? easy?? if can, I might do it myself... hujung bulan no gaji yet...  rclxub.gif  rclxub.gif  rclxub.gif
The flow of the piping:

1) Attached Image

2) Attached Image

3) Attached Image

4) Attached Image

5)Attached Image
*
I think your problem is on the 1st 2 pic with the red circle. The steel pipe is suppose to be the outlet and the black pipe is suppose to be the inlet? (If i see it correctly)

How can inlet and outlet be connected. There should be only 1 inlet to your tangki that is the one connected to the float. If you need another inlet connection to your tangki, then it should end with another float.
if your outlet also connected to the inlet, for sure it will over flow becos no safety cut off.

Is that a new connection? The red circled joint.
asdasd
post Oct 25 2015, 04:25 PM

Casual
***
Junior Member
337 posts

Joined: Nov 2004


TS,

you did 2 bypass for master bedroom and ground floor correct?

cheap solution is to reduce the water pressure from main intake outside the house (near syabas meter)

expensive solution is to change the non-return valve to a higher/better grade.

I suspect the problem is caused by increased water pressure from syabas main which affects the return valve..
lucifah
post Oct 25 2015, 05:29 PM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(one1002 @ Oct 25 2015, 01:27 PM)
OK Lucifah, I have prepared the piping flow for you..haha

*
you have two outlets which have the check valve

either one may caused the problem


this is a spring check valve
user posted image


i always prefer a swing type check valve
user posted image


the spring check valve got a plastic disc attached to the spring. like some forumer said, the backflow pressure is too strong that it pushed the valve open

This post has been edited by lucifah: Oct 25 2015, 05:29 PM
zack85
post Oct 25 2015, 06:21 PM

New Member
*
Junior Member
24 posts

Joined: Feb 2008


pakai level sensor lah...abis crita...tongue.gif
TSone1002
post Oct 25 2015, 07:22 PM

On my way
****
Senior Member
617 posts

Joined: Jun 2009


QUOTE(magnesium @ Oct 25 2015, 02:21 PM)
I think 1st picture with red circle is the problem

It fails hence water back flow into your tank.
*
I think so too...but, in the third pic also have the non-return valve. The problem is I don't understand why outlet no. 3 going back to the main pipe into the tank..any idea?
TSone1002
post Oct 25 2015, 07:32 PM

On my way
****
Senior Member
617 posts

Joined: Jun 2009


QUOTE(Blindspot61 @ Oct 25 2015, 03:45 PM)
I think your problem is on the 1st 2 pic with the red circle. The steel pipe is suppose to be the outlet and the black pipe is suppose to be the inlet? (If i see it correctly)

How can inlet and outlet be connected. There should be only 1 inlet to your tangki that is the one connected to the float. If you need another inlet connection to your tangki, then it should end with another float.
if your outlet also connected to the inlet, for sure it will over flow becos no safety cut off.

Is that a new connection? The red circled joint.
*
Yup, the non-return valve? yes black pipe is the inlet (from SYABAS PIPE METER outside into tank).. You asked how can inlet and outlet be connected, this one I cannot help you haha..

This is not a new connection. More than 6-7 years already since the last contractor went up to the roof, so I can confirmed that the piping was OK, no problem. Only happened on Tuesday, right after SYABAS maintenance.. I suspect the high water pressure from the main intake (Syabas) caused the non-return valve to go kaput..

But the layout of piping makes me rclxub.gif rclxub.gif .

I don't know why, especially for the outlet no. 3, is going back to the mainpipe into the tank. This one really rclxub.gif . LOL.


QUOTE(asdasd @ Oct 25 2015, 04:25 PM)
TS,

you did 2 bypass for master bedroom and ground floor correct?

cheap solution is to reduce the water pressure from main intake outside the house (near syabas meter)

expensive solution is to change the non-return valve to a higher/better grade.

I suspect the problem is caused by increased water pressure from syabas main which affects the return valve..
*
Call me idiot, but I don't know about bypass... doh.gif doh.gif care to explain a bit?? haha...

Yea I have reduced the water pressure, closed the tap by half.. See if it makes any difference. But long term, gotta change the return valve... When you say expensive, how expensive?


QUOTE(lucifah @ Oct 25 2015, 05:29 PM)
you have two outlets which have the check valve

either one may caused the problem
this is a spring check valve

i always prefer a swing type check valve

the spring check valve got a plastic disc attached to the spring. like some forumer said, the backflow pressure is too strong that it pushed the valve open
*
Hey lucifah, thx man for the tip.. thumbup.gif thumbup.gif

What's the diff between swing and spring? what's the difference in cost pulak?? biggrin.gif biggrin.gif

By the way, in your previous posts, you said
QUOTE
"i see you have a bypass system. very clever thumbup.gif"
, why you said clever? Can explain abit? hehe sorry bro..i'm intrigued to know...
lucifah
post Oct 25 2015, 09:24 PM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(one1002 @ Oct 25 2015, 07:32 PM)
By the way, in your previous posts, you said  , why you said clever? Can explain abit? hehe sorry bro..i'm intrigued to know...
*
this setup usually means you are bypassing the water tank

the water in the tank only flows out if there is no water supply from SYABAS

so if there is water supply, you get the stronger water pressure from SYABAS pumps rather than gravity feed from your roof top water tank
lucifah
post Oct 25 2015, 09:26 PM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(zack85 @ Oct 25 2015, 06:21 PM)
pakai level sensor lah...abis crita...tongue.gif
*
this one is more complicated as you need a motorized valve to stop the water supply once the water level reaches certain level


HarDiE
post Oct 25 2015, 09:29 PM

Getting Started
**
Junior Member
208 posts

Joined: Apr 2009


once i kena like this. simple issue is tank cover bend inward pushing down the pelampung when its close so the inlet wont stop. i just bend down the pelampung arm inward.
TSone1002
post Oct 25 2015, 09:48 PM

On my way
****
Senior Member
617 posts

Joined: Jun 2009


QUOTE(lucifah @ Oct 25 2015, 09:24 PM)
this setup usually means you are bypassing the water tank

the water in the tank only flows out if there is no water supply from SYABAS

so if there is water supply, you get the stronger water pressure from SYABAS pumps rather than gravity feed from your roof top water tank
*
ahhh I see...i understand now...thanx!!


QUOTE(HarDiE @ Oct 25 2015, 09:29 PM)
once i kena like this. simple issue is tank cover bend inward pushing down the pelampung when its close so the inlet wont stop. i just bend down the pelampung arm inward.
*
Ya at first I thought the same too...I closed the cover, and placed my ear directly on the side of the tank.. I hear no water dripping..so this one can rule out already..

Anyway, I have to wait until weekend only can do DIY..no time la working.. sweat.gif sweat.gif

Will try to update how it goes!
Khalid21
post Oct 25 2015, 09:58 PM

Regular
******
Senior Member
1,138 posts

Joined: May 2010
clean inside the float valve.. maybe got debris inside

Aparaa
post Oct 26 2015, 10:58 AM

Getting Started
**
Junior Member
72 posts

Joined: Jul 2012
From: Eastern Kingdom
QUOTE(lucifah @ Oct 25 2015, 11:50 AM)
easiest n cheapest way?

bend the arm downward

and tie some empty mineral water bottle at the end

problem solved

zero cost
*
Pelampung not big enough. & try clean the stop valve. After a long period of time, they stainted and difficult to push in.

altan
post Oct 26 2015, 11:35 AM

Getting Started
**
Junior Member
188 posts

Joined: Sep 2009
From: Either PJ, JB or SG but not at your house!


QUOTE(one1002 @ Oct 25 2015, 07:22 PM)
I think so too...but, in the third pic also have the non-return valve. The problem is I don't understand why outlet no. 3 going back to the main pipe into the tank..any idea?
*
QUOTE(lucifah @ Oct 25 2015, 09:24 PM)
this setup usually means you are bypassing the water tank

the water in the tank only flows out if there is no water supply from SYABAS

so if there is water supply, you get the stronger water pressure from SYABAS pumps rather than gravity feed from your roof top water tank
*
As what lucifer mentioned, the issue lies with your one-way valve. Instead of visualizing the water flowing out of the tank and into the main pipe, you should visualize it backwards, say main pipe water flowing into the tank outlet pipes (stopped by the one-way valve).

Its a piping system that says in case no pressure from mains, tank water pressure will take over. If got main pressure, it will top up your tank and bypass the tank water usage for outlet 1 and 3. Since one of the one-way valve is faulty, then system fails and it will flow main water into the tank non-stop.

One of the two valves is faulty but my best advice is to replace both to save time from testing which valve is faulty. Just go to any hardware shop and ask for one-way valve with the correct size (measure your pipe diameter). Also, my advice on replacing both the valves is to sumbat outlet 1 and 3 from inside the tank (with a thick cloth and must be tight) and off main pipe tap. Drain the water in outlet 1 and 3 (Just open any tap to outlet 1 and 3). Do valve replacement with two pipe wrench. Don't forget to apply fresh Plumbing tape (white tape).

Too bad my house tanki piping system isn't like that and whenever water shortage, all the taps connected directly to the mains will run dry. sad.gif
mrcg
post Oct 26 2015, 12:03 PM

Getting Started
**
Junior Member
235 posts

Joined: Nov 2008
QUOTE(altan @ Oct 26 2015, 11:35 AM)
As what lucifer mentioned, the issue lies with your one-way valve. Instead of visualizing the water flowing out of the tank and into the main pipe, you should visualize it backwards, say main pipe water flowing into the tank outlet pipes (stopped by the one-way valve).

Its a piping system that says in case no pressure from mains, tank water pressure will take over. If got main pressure, it will top up your tank and bypass the tank water usage for outlet 1 and 3. Since one of the one-way valve is faulty, then system fails and it will flow main water into the tank non-stop.

One of the two valves is faulty but my best advice is to replace both to save time from testing which valve is faulty. Just go to any hardware shop and ask for one-way valve with the correct size (measure your pipe diameter). Also, my advice on replacing both the valves is to sumbat outlet 1 and 3 from inside the tank (with a thick cloth and must be tight) and off main pipe tap. Drain the water in outlet 1 and 3 (Just open any tap to outlet 1 and 3). Do valve replacement with two pipe wrench. Don't forget to apply fresh Plumbing tape (white tape).

Too bad my house tanki piping system isn't like that and whenever water shortage, all the taps connected directly to the mains will run dry.  sad.gif
*
maybe u can try tie some light rope or benang to tank outlet for outlet 1 and 3 inside the tank for simple visual inspection of water back flow due to failing valve..if any failed then better replace them both
altan
post Oct 26 2015, 12:34 PM

Getting Started
**
Junior Member
188 posts

Joined: Sep 2009
From: Either PJ, JB or SG but not at your house!


QUOTE(mrcg @ Oct 26 2015, 12:03 PM)
maybe u can try tie some light rope or benang to tank outlet for outlet 1 and 3 inside the tank for simple visual inspection of water back flow due to failing valve..if any failed then better replace them both
*
Its a good way to test but considering risking more overflowing water from the tank, might as well get it done before your water bill sky rockets. sweat.gif
zack85
post Oct 26 2015, 03:46 PM

New Member
*
Junior Member
24 posts

Joined: Feb 2008


QUOTE(lucifah @ Oct 25 2015, 09:26 PM)
this one is more complicated as you need a motorized valve to stop the water supply once the water level reaches certain level
*
saja je lah..u think level sensor cheap meh.. tongue.gif tongue.gif
lucifah
post Oct 26 2015, 05:47 PM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(zack85 @ Oct 26 2015, 03:46 PM)
saja je lah..u think level sensor cheap meh.. tongue.gif  tongue.gif
*
u can use float switch for slightly cheaper option. rm 100 nia mah flaotswitch tongue.gif
zack85
post Oct 26 2015, 06:07 PM

New Member
*
Junior Member
24 posts

Joined: Feb 2008


QUOTE(lucifah @ Oct 26 2015, 05:47 PM)
u can use float switch for slightly cheaper option. rm 100 nia mah flaotswitch  tongue.gif
*
advance tech maa.. tongue.gif
Zaryl
post Oct 27 2015, 09:24 AM

Hardcore Casual Gamer
******
Senior Member
1,709 posts

Joined: Jan 2003
From: Kedah Khap Khoun Khap (4K)



My problem was a bit different from yours.

Last time, my reservoir tank got leak, causing the water to FOREVER enter the tank and for 3 months, my water bill skyrocketed like crazy. Actually a very tiny crack at the bottom near the edge. Solution: put the silicon sealant (water proof) at it and problem solved.

But then again, it happened again. This time i suspected my water pump which i put near the main had caused the water pressure to hammer the tank and perhaps the check valve couldn't stand it. Some more, my water pump was faulty and in the end, i removed the water pump permanently.

Problem solved till today.

So yeah, i guess the water pressure being too strong is highly likely the main cuplrit.

You can go and saman SYABAS nao. laugh.gif
Haters_Gonna_H8
post Oct 27 2015, 11:44 PM

:hehe:
*******
Senior Member
2,663 posts

Joined: Aug 2012


QUOTE(lucifah @ Oct 26 2015, 05:47 PM)
u can use float switch for slightly cheaper option. rm 100 nia mah flaotswitch  tongue.gif
*
hi tauke. i think my house water tanks need servicing. u do house calls right? laugh.gif
lucifah
post Oct 27 2015, 11:45 PM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(Haters_Gonna_H8 @ Oct 27 2015, 11:44 PM)
hi tauke. i think my house water tanks need servicing. u do house calls right? laugh.gif
*
my charges are exorbitantly high

i charge by the hour

no gst though


laugh.gif
KageBunshi
post Oct 28 2015, 12:09 AM

Getting Started
**
Junior Member
158 posts

Joined: Jul 2007


QUOTE(lucifah @ Oct 25 2015, 09:24 PM)
this setup usually means you are bypassing the water tank

the water in the tank only flows out if there is no water supply from SYABAS

so if there is water supply, you get the stronger water pressure from SYABAS pumps rather than gravity feed from your roof top water tank
*
But if there is no water from SYABAS, the water would flow back to SYABAS main line?
of course i think SYABAS water meter is single way as well.

BTW the sketch of water flow i wrong i guess.
one way valve for master bedroom is wrongly indicated.
lucifah
post Oct 28 2015, 08:32 AM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(KageBunshi @ Oct 28 2015, 12:09 AM)
But if there is no water from SYABAS, the water would flow back to SYABAS main line?
of course i think SYABAS water meter is single way as well.

BTW the sketch of water flow i wrong i guess.
one way valve for master bedroom is wrongly indicated.
*
LOL. if it flows back to SYABAS main line, then the mter will run backwards, and SYABAS may end up owing you money tongue.gif
netmatrix
post Oct 28 2015, 08:02 PM

The machine... it sees everything.
*******
Senior Member
6,733 posts

Joined: Jan 2003
From: Zion


Its obvious the float ball has punctured and there is water inside.
SUSahter
post Oct 29 2015, 03:45 PM

Getting Started
**
Junior Member
266 posts

Joined: Jul 2008
Btw if the house is still under insurance protection, overflow & pipe burst is covered ... so better keep the receipt if u get someone to fix it
K.I.T.T
post Oct 30 2015, 03:31 PM

On my way
****
Junior Member
672 posts

Joined: Sep 2008
QUOTE(lucifah @ Oct 25 2015, 11:50 AM)
easiest n cheapest way?

bend the arm downward

and tie some empty mineral water bottle at the end

problem solved

zero cost
*
rumah TS ni air tank dia kat atas siling. kalau bocor .....habislah....no need 1 year .. air tangki can jatuh already
lucifah
post Oct 30 2015, 05:06 PM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(K.I.T.T @ Oct 30 2015, 03:31 PM)
rumah TS ni air tank dia kat atas siling. kalau bocor .....habislah....no need 1 year .. air tangki can jatuh already
*
almost all house tangki air is on the siling

baru lah tekanan air kuat kerana perbezaan tenaga upaya yang dihasilkan oleh beza ketinggian

chewahhh

teknikal sungguh aku petang ini
ihavenoidea
post Oct 31 2015, 10:16 AM

Regular
******
Senior Member
1,301 posts

Joined: Sep 2012
QUOTE(lucifah @ Oct 25 2015, 05:29 PM)
you have two outlets which have the check valve

either one may caused the problem
this is a spring check valve
user posted image
i always prefer a swing type check valve
user posted image
the spring check valve got a plastic disc attached to the spring. like some forumer said, the backflow pressure is too strong that it pushed the valve open
*
This valve might help for my dad's place.
Currently the pump is pushing water to the 2nd floor to the tank, then from tank flow back down.. but the pressure is super weak.
If i make a t before the tank with the outlet of the tank do you think this would help?
lucifah
post Oct 31 2015, 10:19 AM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(ihavenoidea @ Oct 31 2015, 10:16 AM)
This valve might help for my dad's place.
Currently the pump is pushing water to the 2nd floor to the tank, then from tank flow back down.. but the pressure is super weak.
If i make a t before the tank with the outlet of the tank do you think this would help?
*
can't promise that unless you really understand where to put the check valve and its position
SUS+ Blind Target +
post Oct 31 2015, 10:22 AM

Getting Started
**
Junior Member
133 posts

Joined: Oct 2014
From: Behind You !


still not solved? biggrin.gif
lemon5969
post Nov 1 2015, 02:34 PM

Casual
***
Junior Member
412 posts

Joined: May 2009



Banyak yang bijak pandai biggrin.gif
TSone1002
post Nov 1 2015, 02:38 PM

On my way
****
Senior Member
617 posts

Joined: Jun 2009


QUOTE(Khalid21 @ Oct 25 2015, 09:58 PM)
clean inside the float valve.. maybe got debris inside
*
Nah..I just changed the pelampung valve set and the Check valve.. hahaha


QUOTE(Aparaa @ Oct 26 2015, 10:58 AM)
Pelampung not big enough. & try clean the stop valve. After a long period of time, they stainted and difficult to push in.
*
Yeah, that's what I tried when replacing the check valve.. the first check valve (master bedroom) cannot even pushed in. It's stuck.. the second check valve can push in, but just a bit. Not like the new one.. So i just changed both.

QUOTE(altan @ Oct 26 2015, 11:35 AM)
As what lucifer mentioned, the issue lies with your one-way valve. Instead of visualizing the water flowing out of the tank and into the main pipe, you should visualize it backwards, say main pipe water flowing into the tank outlet pipes (stopped by the one-way valve).

Its a piping system that says in case no pressure from mains, tank water pressure will take over. If got main pressure, it will top up your tank and bypass the tank water usage for outlet 1 and 3. Since one of the one-way valve is faulty, then system fails and it will flow main water into the tank non-stop.

One of the two valves is faulty but my best advice is to replace both to save time from testing which valve is faulty. Just go to any hardware shop and ask for one-way valve with the correct size (measure your pipe diameter). Also, my advice on replacing both the valves is to sumbat outlet 1 and 3 from inside the tank (with a thick cloth and must be tight) and off main pipe tap. Drain the water in outlet 1 and 3 (Just open any tap to outlet 1 and 3). Do valve replacement with two pipe wrench. Don't forget to apply fresh Plumbing tape (white tape).

Too bad my house tanki piping system isn't like that and whenever water shortage, all the taps connected directly to the mains will run dry.  sad.gif
*
Yes sirrrrr!!! I finally figured out the two bypass systems (2 check valves).. It is like a direct flow from Syabas to the Master bedroom and other bedroom.. hehe.. So in outlet 3, it is not running back to main pipe..it is actually from the mainpipe, bypassing the tank and going straight to the other bathroom.


QUOTE(mrcg @ Oct 26 2015, 12:03 PM)
maybe u can try tie some light rope or benang to tank outlet for outlet 1 and 3 inside the tank for simple visual inspection of water back flow due to failing valve..if any failed then better replace them both
*
I takut oh to do that later got water inside tank, all overflow inside my house hahahahaa...


QUOTE(altan @ Oct 26 2015, 12:34 PM)
Its a good way to test but considering risking more overflowing water from the tank, might as well get it done before your water bill sky rockets.  sweat.gif
*
yeah, was pain in the A** to open and close main supply at 5.30am before mandi manda..lol..same at night..

QUOTE(Zaryl @ Oct 27 2015, 09:24 AM)
My problem was a bit different from yours.

Last time, my reservoir tank got leak, causing the water to FOREVER enter the tank and for 3 months, my water bill skyrocketed like crazy. Actually a very tiny crack at the bottom near the edge. Solution: put the silicon sealant (water proof) at it and problem solved.

But then again, it happened again. This time i suspected my water pump which i put near the main had caused the water pressure to hammer the tank and perhaps the check valve couldn't stand it. Some more, my water pump was faulty and in the end, i removed the water pump permanently.

Problem solved till today.

So yeah, i  guess the water pressure being too strong is highly likely the main cuplrit.

You can go and saman SYABAS nao.  laugh.gif
*
Yeah this actually happened after SYABAS Maintenance last week (20th Oct 2015)..after that, straight away overflow...I think the water pressure busted the check valve.. Lagipun, i think it's due time juga to change..



TSone1002
post Nov 1 2015, 02:38 PM

On my way
****
Senior Member
617 posts

Joined: Jun 2009


QUOTE(KageBunshi @ Oct 28 2015, 12:09 AM)
But if there is no water from SYABAS, the water would flow back to SYABAS main line?
of course i think SYABAS water meter is single way as well.

BTW the sketch of water flow i wrong i guess.
one way valve for master bedroom is wrongly indicated.
*
Correct sir.. sorry for the sketch..It is wrongly indicated..actually it is located at the straight pipe from tank going to the master bathroom..not between those two..haha

QUOTE(netmatrix @ Oct 28 2015, 08:02 PM)
Its obvious the float ball has punctured and there is water inside.
*
No sir, already checked the float ball...like i mentioned in a few posts before, I rendam inside water, no bubbles, and when i released it, the ball just pushed back out of the water very high woiii..haha

QUOTE(+ Blind Target + @ Oct 31 2015, 10:22 AM)
still not solved?  biggrin.gif
*
Hopefully solved lah...still waiting for the tank to fill up..will monitor again..

This post has been edited by one1002: Nov 1 2015, 02:39 PM
TSone1002
post Nov 1 2015, 02:53 PM

On my way
****
Senior Member
617 posts

Joined: Jun 2009


UPDATED ON THE 1ST POST, PAGE 1
altan
post Nov 1 2015, 03:31 PM

Getting Started
**
Junior Member
188 posts

Joined: Sep 2009
From: Either PJ, JB or SG but not at your house!


QUOTE(one1002 @ Nov 1 2015, 02:53 PM)
UPDATED ON THE 1ST POST, PAGE 1
*
Goodluck thumbup.gif
.E.T.
post May 11 2016, 01:07 AM

New Member
*
Newbie
1 posts

Joined: Jul 2007


Just for my information, how long does it usually fill up a water tank from empty?

clouds
post May 12 2016, 01:42 PM

Casual
***
Junior Member
318 posts

Joined: Jan 2009
From: Grave



QUOTE(.E.T. @ May 11 2016, 01:07 AM)
Just for my information, how long does it usually fill up a water tank from empty?
*
depends..berapa besar tangki..ts patut cuci tangki sekali..sudah banyak keladak air..u mandi x gatal badan ke?
sgpdsmss
post Nov 13 2017, 07:51 AM

Regular
******
Senior Member
1,704 posts

Joined: Jan 2005
QUOTE(one1002 @ Oct 25 2015, 11:42 AM)
Hi guys,

I'm having some kind of weird problem that I cannot figure out the source.....

My water tank is overflowing like waterfall dei...not sure if it's related, but it happened right after the maintenance by SYABAS in gombak area (batu caves).

Went to the bumbung to check, panjat here panjat there, found the tangki..opened the tangki, checked the pelampung, ok i think it's time to change the pelampung..damn hard to unscrew it..

So the process of changing the pelampung went well eventually. I thought I have solved it..but after a few hours, started overflowing again.....  rclxub.gif  rclxub.gif

Went back to the bumbung, suddenly tengok-tengok, the tangki full (above normal level).. Turned off main pipe, opened some taps to reduce the water level in the tangki..then checked the pelampung back again.. here are some pictures,
1) Checking the newly bought and installed pelampung set... Tangki is being filled..

Attached Image
2) Tried hand-stopping the pelampung, good, no water dripping...

Attached Image
3) Water automatically stopped, meaning no dripping. confirmed pelampung ok..

Attached Image
4) Now the water level still rising, until the pelampung also tenggelam....started overflowing again...

Attached Image
Now i really pening what could've caused the overflowing problem....I suspect it's the non-return valve.. But, well.. i don't know where it is, don't know what it looks like..and too many pipe connection...lol..

Can someone help me pleaseeee....tension gila!
------------------------- UPDATE ---------------------------------

Went back again to the roof, to take some pictures of the pipe connection just in case some one can help pinpoint the problem.

THIS IS THE FIRST TIME I WENT TO THE ROOF, SO VERY THE MESSY...NEVER KNEW SO MANY SAMPAH SARAP HERE LEFT BY THE OLD CONTRACTORS..ISH ISH ISH  vmad.gif  vmad.gif  mad.gif  mad.gif
1) Is the red circled the NON RETURN VALVE? The black pipe is the main pipe from outside into the tank.

Attached Image
2) Is this too?

Attached Image
If the non-return valve may be the cause, how much would it cost? can D.I.Y ke???? easy?? if can, I might do it myself... hujung bulan no gaji yet...  rclxub.gif  rclxub.gif  rclxub.gif
The flow of the piping:

1) Attached Image

2) Attached Image

3) Attached Image

4) Attached Image

5)Attached Image
-----------------------------------------------------------------UPDATE 1ST NOVEMBER 2015-----------------------------------------------------------------
So I finally went to the hardware shop and bought two Check Valve (3/4") size..

Started to operation roof!! While going to the hardware, opened all taps to empty the water from the tank.. Then started opening the first suspected Check Valve.. It was soooo ketat to open had to use extra force.. I thought that was hard, but removing the previous pipe tape (the white tape) was even harder!!!!!

Here's the pic of the old check valve.. I THINK THE SPRING IS NOT WORKING ANYMORE. PUSHED EITHER SIDE, NOTHING MOVED. SO YEAH I GUESS THE SPRING IS NOT FUNCTIONING ANYMORE
Front

Attached Image
Back

Attached Image
And here's the pic of the new Check Valve.. The spring works wonderful..

Attached Image

Attached Image
Changed two suspected Check Valve to avoid double work.. I accidentally left one of the old check valved on the roof, malas nak ambil lagi.. later ambil lah..haha

Cost?? RM30 for one Check Valve (made in italy woi!!), and RM3 for the white tape..total with GST = RM67.30 (IINM)..

This is the first time my operation roof.. Hopefully with the lack of skills, I am able to solve my problem. Checked at the joints, alhamdulillah no leaking or evidence of water outside of the valve.. I hope the connection is tight and secure..

Tank is still filling though. I'll update if it still overflows....hopefully not!!!!! Touchwood!!
*
after replaced the two Check Valve (3/4") size..
overflow problem solved?

thanks ..
TSone1002
post Nov 21 2017, 05:14 PM

On my way
****
Senior Member
617 posts

Joined: Jun 2009


QUOTE(sgpdsmss @ Nov 13 2017, 07:51 AM)
after replaced the two Check Valve (3/4") size..
overflow problem solved?

thanks ..
*
yes.. problem solved till now.. haha
netmatrix
post Nov 21 2017, 07:04 PM

The machine... it sees everything.
*******
Senior Member
6,733 posts

Joined: Jan 2003
From: Zion


Dude. Your plumber fcuked up the water inlet and outlet already. 2 pictures already exposed the problem. One of it is this,

user posted image

If you link the inlet and outlet, once the tank fills up and stops, the additional pressure will go to the second outler pipe. Assuming second pipe also stops due to normal faucet on/off, the water pressure has to go somewhere, it goes back to tank la. hahaha.
sgpdsmss
post Nov 21 2017, 09:17 PM

Regular
******
Senior Member
1,704 posts

Joined: Jan 2005
QUOTE(one1002 @ Nov 21 2017, 05:14 PM)
yes.. problem solved till now.. haha
*
thanks...i also replaced the valve to solved the overflow problem ...
lonerider
post Dec 22 2017, 08:44 PM

Getting Started
**
Junior Member
59 posts

Joined: Aug 2009
From: Cyberjaya



QUOTE(netmatrix @ Nov 21 2017, 07:04 PM)
Dude. Your plumber fcuked up the water inlet and outlet already. 2 pictures already exposed the problem. One of it is this,

user posted image

If you link the inlet and outlet, once the tank fills up and stops, the additional pressure will go to the second outler pipe. Assuming second pipe also stops due to normal faucet on/off, the water pressure has to go somewhere, it goes back to tank la. hahaha.
*
That is the purpose of installing check valve 😅 to prevent backflow....
TSone1002
post Dec 23 2017, 02:09 PM

On my way
****
Senior Member
617 posts

Joined: Jun 2009


Haha.. So far after changing those 2 valves, no more overflow as of now.. I considered it as fixed..
SUSslimey
post Dec 25 2017, 07:50 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
WTF...........

why don't install some stopcocks for isolation of certain parts so that can close off parts of the system in case of faults.

also, where is the overflow pipe of the tank? and the drainage pipe of the tank?

incomplete system
RioMeni
post Aug 3 2019, 07:31 PM

Getting Started
**
Junior Member
217 posts

Joined: Oct 2016
From: Ipoh


hi...what is the saiz of the pelampung of the main tangki?
ScooterBoi
post Aug 3 2019, 10:36 PM

Regular
******
Senior Member
1,372 posts

Joined: Mar 2013
QUOTE(RioMeni @ Aug 3 2019, 07:31 PM)
hi...what is the saiz of the pelampung of the main tangki?
*
What do you mean by 'pelampung'? Is it the float?

if you refer to the 3rd photo in 1st page, the black ball on the left is the float. The white gadget is the intake valve that can shut the water flow.

Both are sold separately. Normally, only the intake valve is replaced... only one standard size. To be sure, you measure the pipe diameter, and buy the intake valve to fit the pipe.

Note that the white one in the photo is plastic... you can get a better one made of brass - about RM 25.

The black ball or float, it is attached by turning the ball onto the end of the rod.


RioMeni
post Aug 4 2019, 01:53 AM

Getting Started
**
Junior Member
217 posts

Joined: Oct 2016
From: Ipoh


QUOTE(ScooterBoi @ Aug 3 2019, 10:36 PM)
What do you mean by 'pelampung'? Is it the float?

if you refer to the 3rd photo in 1st page, the black ball on the left is the float. The white gadget is the intake valve that can shut the water flow.

Both are sold separately. Normally, only the intake valve is replaced... only one standard size. To be sure, you measure the pipe diameter, and buy the intake valve to fit the pipe.

Note that the white one in the photo is plastic... you can get a better one made of brass - about RM 25.

The black ball or float, it is attached by turning the ball onto the end of the rod.
*
yes the float...now have to check out the tank for pipe diameter...brass valve is better? thanks for the recommendation
mushigen
post Aug 4 2019, 01:59 PM

Look at all my stars!!
*******
Senior Member
4,954 posts

Joined: Jul 2010


I am four years too late, lol. An easier way for TS to check is to
1. shut off water supply,
2.drain empty the tank,
3. open back the water supply
4. lift the float to simulate full tank level

if water comes in from the outlet line, it means the check valve is passing.

All check valves will fail at some point in time. The either fail open or stuck in closed position.
ScooterBoi
post Aug 4 2019, 02:53 PM

Regular
******
Senior Member
1,372 posts

Joined: Mar 2013
QUOTE(RioMeni @ Aug 4 2019, 01:53 AM)
yes the float...now have to check out the tank for pipe diameter...brass valve is better? thanks for the recommendation
*
Usually there's nothing wrong with the float, and the old one can be reused.

The brass valve is more 'heavy duty'. Worn out rubber rings/seals would caused slow leakage... but if the thin rod, which the float is attached to, broke...

If there's leakage and overflow, and you need to shut the main water supply because the intake valve is faulty, you can remove the valve and take it to the shop.

This way, you break the job into 2 sessions...

ScooterBoi
post Aug 4 2019, 03:36 PM

Regular
******
Senior Member
1,372 posts

Joined: Mar 2013
QUOTE(mushigen @ Aug 4 2019, 01:59 PM)
I am four years too late, lol. An easier way for TS to check is to
1. shut off water supply,
2.drain empty the tank,
3. open back the water supply
4. lift the float to simulate full tank level

if water comes in from the outlet line, it means the check valve is passing.

All check valves will fail at some point in time. The either fail open or stuck in closed position.
*
The pipe network could be simpler and fail-proof without using any check valves.

The water flow from the mains should branch at ground level, one going up to the tank, the other to the kitchen area at the back of the house.

The connection of the water from the mains to the outlet pipe from the tank is done so that the same tap can have water from either the mains or the tank? It doesn't make sense...



mushigen
post Aug 4 2019, 06:24 PM

Look at all my stars!!
*******
Senior Member
4,954 posts

Joined: Jul 2010


QUOTE(ScooterBoi @ Aug 4 2019, 03:36 PM)
The pipe network could be simpler and fail-proof without using any check valves.

The water flow from the mains should branch at ground level, one going up to the tank, the other to the kitchen area at the back of the house.

The connection of the water from the mains to the outlet pipe from the tank is done so that the same tap can have water from either the mains or the tank? It doesn't make sense...
*
This to me is a clever idea. When the mains pressure is higher than the pressure in the tank (which comes from the liquid height), it will supply water to the bathroom (or whichever tap that is taking water from the tank).
When the water pressure is low, or supply is cut, the water from the tank will flow to the bathroom tap. We all know the water from the tank can be rather low in pressure, which makes installing rain shower impossible.
A second check valve should be installed along the pipe supplying water to the tank so that the water in the tank does not drain down to your neighbour's house via the mains biggrin.gif

The disadvantages of such set up are:
1. Water in the tank is hardly replenished since our mains pressure is/should always be high (in an ideal world).
2. Usage of check valves as a form of safeguarding is never a good idea, especially in a area as inaccessible as the tank under the roof.

 

Change to: