 [UPDATE] Tangki Air Overflow, even after changing pelampung set (pic)

views
     
TSone1002
post Oct 25 2015, 07:22 PM

On my way
****
Senior Member
617 posts

Joined: Jun 2009


QUOTE(magnesium @ Oct 25 2015, 02:21 PM)
I think 1st picture with red circle is the problem

It fails hence water back flow into your tank.
*
I think so too...but, in the third pic also have the non-return valve. The problem is I don't understand why outlet no. 3 going back to the main pipe into the tank..any idea?
TSone1002
post Oct 25 2015, 07:32 PM

On my way
****
Senior Member
617 posts

Joined: Jun 2009


QUOTE(Blindspot61 @ Oct 25 2015, 03:45 PM)
I think your problem is on the 1st 2 pic with the red circle. The steel pipe is suppose to be the outlet and the black pipe is suppose to be the inlet? (If i see it correctly)

How can inlet and outlet be connected. There should be only 1 inlet to your tangki that is the one connected to the float. If you need another inlet connection to your tangki, then it should end with another float.
if your outlet also connected to the inlet, for sure it will over flow becos no safety cut off.

Is that a new connection? The red circled joint.
*
Yup, the non-return valve? yes black pipe is the inlet (from SYABAS PIPE METER outside into tank).. You asked how can inlet and outlet be connected, this one I cannot help you haha..

This is not a new connection. More than 6-7 years already since the last contractor went up to the roof, so I can confirmed that the piping was OK, no problem. Only happened on Tuesday, right after SYABAS maintenance.. I suspect the high water pressure from the main intake (Syabas) caused the non-return valve to go kaput..

But the layout of piping makes me rclxub.gif rclxub.gif .

I don't know why, especially for the outlet no. 3, is going back to the mainpipe into the tank. This one really rclxub.gif . LOL.


QUOTE(asdasd @ Oct 25 2015, 04:25 PM)
TS,

you did 2 bypass for master bedroom and ground floor correct?

cheap solution is to reduce the water pressure from main intake outside the house (near syabas meter)

expensive solution is to change the non-return valve to a higher/better grade.

I suspect the problem is caused by increased water pressure from syabas main which affects the return valve..
*
Call me idiot, but I don't know about bypass... doh.gif doh.gif care to explain a bit?? haha...

Yea I have reduced the water pressure, closed the tap by half.. See if it makes any difference. But long term, gotta change the return valve... When you say expensive, how expensive?


QUOTE(lucifah @ Oct 25 2015, 05:29 PM)
you have two outlets which have the check valve

either one may caused the problem
this is a spring check valve

i always prefer a swing type check valve

the spring check valve got a plastic disc attached to the spring. like some forumer said, the backflow pressure is too strong that it pushed the valve open
*
Hey lucifah, thx man for the tip.. thumbup.gif thumbup.gif

What's the diff between swing and spring? what's the difference in cost pulak?? biggrin.gif biggrin.gif

By the way, in your previous posts, you said
QUOTE
"i see you have a bypass system. very clever thumbup.gif"
, why you said clever? Can explain abit? hehe sorry bro..i'm intrigued to know...
lucifah
post Oct 25 2015, 09:24 PM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(one1002 @ Oct 25 2015, 07:32 PM)
By the way, in your previous posts, you said  , why you said clever? Can explain abit? hehe sorry bro..i'm intrigued to know...
*
this setup usually means you are bypassing the water tank

the water in the tank only flows out if there is no water supply from SYABAS

so if there is water supply, you get the stronger water pressure from SYABAS pumps rather than gravity feed from your roof top water tank
lucifah
post Oct 25 2015, 09:26 PM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(zack85 @ Oct 25 2015, 06:21 PM)
pakai level sensor lah...abis crita...tongue.gif
*
this one is more complicated as you need a motorized valve to stop the water supply once the water level reaches certain level


HarDiE
post Oct 25 2015, 09:29 PM

Getting Started
**
Junior Member
208 posts

Joined: Apr 2009


once i kena like this. simple issue is tank cover bend inward pushing down the pelampung when its close so the inlet wont stop. i just bend down the pelampung arm inward.
TSone1002
post Oct 25 2015, 09:48 PM

On my way
****
Senior Member
617 posts

Joined: Jun 2009


QUOTE(lucifah @ Oct 25 2015, 09:24 PM)
this setup usually means you are bypassing the water tank

the water in the tank only flows out if there is no water supply from SYABAS

so if there is water supply, you get the stronger water pressure from SYABAS pumps rather than gravity feed from your roof top water tank
*
ahhh I see...i understand now...thanx!!


QUOTE(HarDiE @ Oct 25 2015, 09:29 PM)
once i kena like this. simple issue is tank cover bend inward pushing down the pelampung when its close so the inlet wont stop. i just bend down the pelampung arm inward.
*
Ya at first I thought the same too...I closed the cover, and placed my ear directly on the side of the tank.. I hear no water dripping..so this one can rule out already..

Anyway, I have to wait until weekend only can do DIY..no time la working.. sweat.gif sweat.gif

Will try to update how it goes!
Khalid21
post Oct 25 2015, 09:58 PM

Regular
******
Senior Member
1,138 posts

Joined: May 2010
clean inside the float valve.. maybe got debris inside

Aparaa
post Oct 26 2015, 10:58 AM

Getting Started
**
Junior Member
72 posts

Joined: Jul 2012
From: Eastern Kingdom
QUOTE(lucifah @ Oct 25 2015, 11:50 AM)
easiest n cheapest way?

bend the arm downward

and tie some empty mineral water bottle at the end

problem solved

zero cost
*
Pelampung not big enough. & try clean the stop valve. After a long period of time, they stainted and difficult to push in.

altan
post Oct 26 2015, 11:35 AM

Getting Started
**
Junior Member
188 posts

Joined: Sep 2009
From: Either PJ, JB or SG but not at your house!


QUOTE(one1002 @ Oct 25 2015, 07:22 PM)
I think so too...but, in the third pic also have the non-return valve. The problem is I don't understand why outlet no. 3 going back to the main pipe into the tank..any idea?
*
QUOTE(lucifah @ Oct 25 2015, 09:24 PM)
this setup usually means you are bypassing the water tank

the water in the tank only flows out if there is no water supply from SYABAS

so if there is water supply, you get the stronger water pressure from SYABAS pumps rather than gravity feed from your roof top water tank
*
As what lucifer mentioned, the issue lies with your one-way valve. Instead of visualizing the water flowing out of the tank and into the main pipe, you should visualize it backwards, say main pipe water flowing into the tank outlet pipes (stopped by the one-way valve).

Its a piping system that says in case no pressure from mains, tank water pressure will take over. If got main pressure, it will top up your tank and bypass the tank water usage for outlet 1 and 3. Since one of the one-way valve is faulty, then system fails and it will flow main water into the tank non-stop.

One of the two valves is faulty but my best advice is to replace both to save time from testing which valve is faulty. Just go to any hardware shop and ask for one-way valve with the correct size (measure your pipe diameter). Also, my advice on replacing both the valves is to sumbat outlet 1 and 3 from inside the tank (with a thick cloth and must be tight) and off main pipe tap. Drain the water in outlet 1 and 3 (Just open any tap to outlet 1 and 3). Do valve replacement with two pipe wrench. Don't forget to apply fresh Plumbing tape (white tape).

Too bad my house tanki piping system isn't like that and whenever water shortage, all the taps connected directly to the mains will run dry. sad.gif
mrcg
post Oct 26 2015, 12:03 PM

Getting Started
**
Junior Member
235 posts

Joined: Nov 2008
QUOTE(altan @ Oct 26 2015, 11:35 AM)
As what lucifer mentioned, the issue lies with your one-way valve. Instead of visualizing the water flowing out of the tank and into the main pipe, you should visualize it backwards, say main pipe water flowing into the tank outlet pipes (stopped by the one-way valve).

Its a piping system that says in case no pressure from mains, tank water pressure will take over. If got main pressure, it will top up your tank and bypass the tank water usage for outlet 1 and 3. Since one of the one-way valve is faulty, then system fails and it will flow main water into the tank non-stop.

One of the two valves is faulty but my best advice is to replace both to save time from testing which valve is faulty. Just go to any hardware shop and ask for one-way valve with the correct size (measure your pipe diameter). Also, my advice on replacing both the valves is to sumbat outlet 1 and 3 from inside the tank (with a thick cloth and must be tight) and off main pipe tap. Drain the water in outlet 1 and 3 (Just open any tap to outlet 1 and 3). Do valve replacement with two pipe wrench. Don't forget to apply fresh Plumbing tape (white tape).

Too bad my house tanki piping system isn't like that and whenever water shortage, all the taps connected directly to the mains will run dry.  sad.gif
*
maybe u can try tie some light rope or benang to tank outlet for outlet 1 and 3 inside the tank for simple visual inspection of water back flow due to failing valve..if any failed then better replace them both
altan
post Oct 26 2015, 12:34 PM

Getting Started
**
Junior Member
188 posts

Joined: Sep 2009
From: Either PJ, JB or SG but not at your house!


QUOTE(mrcg @ Oct 26 2015, 12:03 PM)
maybe u can try tie some light rope or benang to tank outlet for outlet 1 and 3 inside the tank for simple visual inspection of water back flow due to failing valve..if any failed then better replace them both
*
Its a good way to test but considering risking more overflowing water from the tank, might as well get it done before your water bill sky rockets. sweat.gif
zack85
post Oct 26 2015, 03:46 PM

New Member
*
Junior Member
24 posts

Joined: Feb 2008


QUOTE(lucifah @ Oct 25 2015, 09:26 PM)
this one is more complicated as you need a motorized valve to stop the water supply once the water level reaches certain level
*
saja je lah..u think level sensor cheap meh.. tongue.gif tongue.gif
lucifah
post Oct 26 2015, 05:47 PM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(zack85 @ Oct 26 2015, 03:46 PM)
saja je lah..u think level sensor cheap meh.. tongue.gif  tongue.gif
*
u can use float switch for slightly cheaper option. rm 100 nia mah flaotswitch tongue.gif
zack85
post Oct 26 2015, 06:07 PM

New Member
*
Junior Member
24 posts

Joined: Feb 2008


QUOTE(lucifah @ Oct 26 2015, 05:47 PM)
u can use float switch for slightly cheaper option. rm 100 nia mah flaotswitch  tongue.gif
*
advance tech maa.. tongue.gif
Zaryl
post Oct 27 2015, 09:24 AM

Hardcore Casual Gamer
******
Senior Member
1,709 posts

Joined: Jan 2003
From: Kedah Khap Khoun Khap (4K)



My problem was a bit different from yours.

Last time, my reservoir tank got leak, causing the water to FOREVER enter the tank and for 3 months, my water bill skyrocketed like crazy. Actually a very tiny crack at the bottom near the edge. Solution: put the silicon sealant (water proof) at it and problem solved.

But then again, it happened again. This time i suspected my water pump which i put near the main had caused the water pressure to hammer the tank and perhaps the check valve couldn't stand it. Some more, my water pump was faulty and in the end, i removed the water pump permanently.

Problem solved till today.

So yeah, i guess the water pressure being too strong is highly likely the main cuplrit.

You can go and saman SYABAS nao. laugh.gif
Haters_Gonna_H8
post Oct 27 2015, 11:44 PM

:hehe:
*******
Senior Member
2,663 posts

Joined: Aug 2012


QUOTE(lucifah @ Oct 26 2015, 05:47 PM)
u can use float switch for slightly cheaper option. rm 100 nia mah flaotswitch  tongue.gif
*
hi tauke. i think my house water tanks need servicing. u do house calls right? laugh.gif
lucifah
post Oct 27 2015, 11:45 PM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(Haters_Gonna_H8 @ Oct 27 2015, 11:44 PM)
hi tauke. i think my house water tanks need servicing. u do house calls right? laugh.gif
*
my charges are exorbitantly high

i charge by the hour

no gst though


laugh.gif
KageBunshi
post Oct 28 2015, 12:09 AM

Getting Started
**
Junior Member
158 posts

Joined: Jul 2007


QUOTE(lucifah @ Oct 25 2015, 09:24 PM)
this setup usually means you are bypassing the water tank

the water in the tank only flows out if there is no water supply from SYABAS

so if there is water supply, you get the stronger water pressure from SYABAS pumps rather than gravity feed from your roof top water tank
*
But if there is no water from SYABAS, the water would flow back to SYABAS main line?
of course i think SYABAS water meter is single way as well.

BTW the sketch of water flow i wrong i guess.
one way valve for master bedroom is wrongly indicated.
lucifah
post Oct 28 2015, 08:32 AM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(KageBunshi @ Oct 28 2015, 12:09 AM)
But if there is no water from SYABAS, the water would flow back to SYABAS main line?
of course i think SYABAS water meter is single way as well.

BTW the sketch of water flow i wrong i guess.
one way valve for master bedroom is wrongly indicated.
*
LOL. if it flows back to SYABAS main line, then the mter will run backwards, and SYABAS may end up owing you money tongue.gif
netmatrix
post Oct 28 2015, 08:02 PM

The machine... it sees everything.
*******
Senior Member
6,733 posts

Joined: Jan 2003
From: Zion


Its obvious the float ball has punctured and there is water inside.