QUOTE(kimsim @ Sep 29 2015, 05:56 PM)
Someone said, if 1hp still able to used, but at the bending portion will be broken and gas leaking is depend on times.
You need to check with Aircon man n see how they tell u the correct answer, maybe last time copper price are cheaper and they used the thickness one for you.
I have Thermoline (copper tubing) catalogue with me. The safe working pressure claimed under Australian Standard AS1571-1985, for 6.4x0.58mm is 981psi, for 9.5x0.58mm is 639psi, for 12.7x0.58mm is 470psi.You need to check with Aircon man n see how they tell u the correct answer, maybe last time copper price are cheaper and they used the thickness one for you.
When I check with MHI engineer their recommended test pressure for their R410a system is 400psi. Daikin told me 400 to 450 psi.
If you check the R410a properties at 34 deg C the gas or liquid pressure is only around 290psi. In order for the system to fail, unless someone heat the gas up to 54 deg C then the pressure shall reach 470psi.
That means if you use back R22 copper tubing for R410a up to 1.5hp you still have around 60% safety factor. Of course 60% might not be comfortable if you consider others factors.
That's why I said 1hp should be ok and 1.5hp is risky.