 Nanoe-G Problem

views
     
TSerik8lyt
post Nov 16 2013, 02:19 PM, updated 12y ago

Enthusiast
*****
Senior Member
715 posts

Joined: Jan 2008


After I turn on my aircon for a while, the needle tip of Nanoe-G sparkles and makes buzzing sound. My aircon is Panasonic CS-S10NKH.
cedyy
post Nov 16 2013, 02:34 PM

Regular
******
Senior Member
1,404 posts

Joined: Jun 2009


sounds like electrical problem. better switch off the ioniser function and call Panasonic come to attend. i suppose ur aircond is still under warranty? my unit's nanoe G's led light spoilt within 3 months. the pcb found to have corroded. Panasonic quality going down the drain

This post has been edited by cedyy: Nov 16 2013, 02:35 PM
TSerik8lyt
post Nov 16 2013, 03:50 PM

Enthusiast
*****
Senior Member
715 posts

Joined: Jan 2008


QUOTE(cedyy @ Nov 16 2013, 02:34 PM)
sounds like electrical problem. better switch off the ioniser function and call Panasonic come to attend. i suppose ur aircond is still under warranty? my unit's nanoe G's led light spoilt within 3 months. the pcb found to have corroded. Panasonic quality going down the drain
*
Are you sure is the electrical problem? I called one of my technician from the Panasonic line before and he said the Nanoe-G was dirty. I asked whether can I solve it by myself or not and I tried to use cotton stick to clean the needle tip but useless.
cedyy
post Nov 17 2013, 03:25 PM

Regular
******
Senior Member
1,404 posts

Joined: Jun 2009


QUOTE(erik8lyt @ Nov 16 2013, 03:50 PM)
Are you sure is the electrical problem? I called one of my technician from the Panasonic line before and he said the Nanoe-G was dirty. I asked whether can I solve it by myself or not and I tried to use cotton stick to clean the needle tip but useless.
*
you may lodge a complaint by sending e-mail to their customer service. they'll call you back and fix appointment to attend to the problem. should not need to clean the needle because the new design is automatically retract the needle when it's deactivated. so it should in a way clean itself.
TSerik8lyt
post Nov 26 2013, 02:11 AM

Enthusiast
*****
Senior Member
715 posts

Joined: Jan 2008


What will happen if I'm not using Nanoe-G when air-con is operating every time?
TSerik8lyt
post Dec 6 2013, 02:11 AM

Enthusiast
*****
Senior Member
715 posts

Joined: Jan 2008


Anyone knows?
ozak
post Dec 6 2013, 08:42 AM

10k Club
********
All Stars
17,023 posts

Joined: Jan 2005


QUOTE(erik8lyt @ Dec 6 2013, 02:11 AM)
Anyone knows?
*
Nothing happen. It is just another gadget in the aircon. It is an ionizer.

Can turn it off anytime.
JinXXX
post Dec 6 2013, 10:04 PM

Look at all my stars!!
*******
Senior Member
2,516 posts

Joined: Feb 2007
From: Uarla Umpur



QUOTE(ozak @ Dec 6 2013, 08:42 AM)
Nothing happen. It is just another gadget in the aircon. It is an ionizer.

Can turn it off anytime.
*
basic aircond still the best.. no need all those additional things that you pay extra alot only to spoil, 1/2 way down the road
TSerik8lyt
post Dec 7 2013, 04:44 PM

Enthusiast
*****
Senior Member
715 posts

Joined: Jan 2008


QUOTE(JinXXX @ Dec 6 2013, 10:04 PM)
basic aircond still the best.. no need all those additional things that you pay extra alot only to spoil, 1/2 way down the road
*
So the features like ECONAVI and Nanoe-G are just marketing gimmicks by Panasonic? Is there any difference between inverter and normal air-con?
ozak
post Dec 7 2013, 05:24 PM

10k Club
********
All Stars
17,023 posts

Joined: Jan 2005


QUOTE(JinXXX @ Dec 6 2013, 10:04 PM)
basic aircond still the best.. no need all those additional things that you pay extra alot only to spoil, 1/2 way down the road
*
Wasai, where're you been? Longtime no spam here. KL?


ozak
post Dec 7 2013, 05:29 PM

10k Club
********
All Stars
17,023 posts

Joined: Jan 2005


QUOTE(erik8lyt @ Dec 7 2013, 04:44 PM)
So the features like ECONAVI and Nanoe-G are just marketing gimmicks by Panasonic? Is there any difference between inverter and normal air-con?
*
It is not a marketing gimmicks. An add on extra function. Ionizer is 1 of the important function in air cleaner.
TSerik8lyt
post Dec 7 2013, 09:06 PM

Enthusiast
*****
Senior Member
715 posts

Joined: Jan 2008


QUOTE(ozak @ Dec 7 2013, 05:29 PM)
It is not a marketing gimmicks. An add on extra function. Ionizer is 1 of the important function in air cleaner.
*
Can I turn Nanoe-G off straight after turning on my air-con everytime? Because Nano-G makes little noise.
JinXXX
post Dec 8 2013, 12:39 AM

Look at all my stars!!
*******
Senior Member
2,516 posts

Joined: Feb 2007
From: Uarla Umpur



QUOTE(ozak @ Dec 7 2013, 05:24 PM)
Wasai, where're you been? Longtime no spam here. KL?
*
bz with work la boss.. no time to spam lyn sad.gif

QUOTE(erik8lyt @ Dec 7 2013, 09:06 PM)
Can I turn Nanoe-G off straight after turning on my air-con everytime? Because Nano-G makes little noise.
*
why not.. its just a function.. can't it stay off when u off it ?
TSerik8lyt
post Feb 12 2014, 12:29 PM

Enthusiast
*****
Senior Member
715 posts

Joined: Jan 2008


What if I change my current Nanoe-G to a new one? Will the noise gone?
TSerik8lyt
post Feb 14 2014, 03:08 PM

Enthusiast
*****
Senior Member
715 posts

Joined: Jan 2008


Anyone knows?
ozak
post Feb 14 2014, 03:31 PM

10k Club
********
All Stars
17,023 posts

Joined: Jan 2005


Just call the Panasonic service to check for you. Before decide what to do.
petlu28
post Feb 14 2014, 03:36 PM

Look at all my stars!!
*******
Senior Member
3,936 posts

Joined: Dec 2010
Can i just turn ON Nanoe-G only? When i ON aircond Nanoe-G will turn ON together.

QUOTE(ozak @ Feb 14 2014, 03:31 PM)
Just call the Panasonic service to check for you. Before decide what to do.
*
ozak
post Feb 14 2014, 04:05 PM

10k Club
********
All Stars
17,023 posts

Joined: Jan 2005


QUOTE(petlu28 @ Feb 14 2014, 03:36 PM)
Can i just turn ON Nanoe-G only? When i ON aircond Nanoe-G will turn ON together.
*
Without run the aircon? But just the blower and the nanoe G?

I never try before.
TSerik8lyt
post Feb 14 2014, 05:22 PM

Enthusiast
*****
Senior Member
715 posts

Joined: Jan 2008


QUOTE(petlu28 @ Feb 14 2014, 03:36 PM)
Can i just turn ON Nanoe-G only? When i ON aircond Nanoe-G will turn ON together.
*
I found that I can turn on my aircon by just turning on Nanoe-G and my remote control setting is configured to all auto. I can also turn off it by turning off Nanoe-G. Is this normal?
chilskater
post Feb 20 2014, 06:47 PM

Regular
******
Senior Member
1,124 posts

Joined: Oct 2004
yeahh...i hv samsung aircon with Nano G..cant use it coz it caused headache...so i switched it off..
katmai81
post Feb 20 2014, 07:13 PM

Getting Started
**
Junior Member
116 posts

Joined: Aug 2012
QUOTE(erik8lyt @ Nov 16 2013, 02:19 PM)
After I turn on my aircon for a while, the needle tip of Nanoe-G sparkles and makes buzzing sound. My aircon is Panasonic CS-S10NKH.
*
Mine also start having some buzzing sound and sparkle when using aircond with nanoe g on.....
I clean it using cotton bud like recommended in manual....
And now I don't hear any more noise....

I don't recall the needle retracting itself.....it stays there during on n off.
SUSkimsim
post Feb 20 2014, 07:18 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


Spakering sound may due to hard casing when changing to lower deg and created sound.

Please ask your installer to fit it nicely should be solved or open up front cover and paste some soft rubber piece to avoid on hard case too much gap.

This post has been edited by kimsim: Feb 20 2014, 07:20 PM
sovietmah
post Feb 21 2014, 11:58 AM

Look at all my stars!!
*******
Senior Member
2,243 posts

Joined: Nov 2005
So far i noticed I can turn ON Nanoe-G, acting like a air purfier without turning the aircon.
And i noticed the compressor fans also wont run, so less electricity used.

If turn ON aircon, also can turn on nanoe-g together.
I am using cs-s13pkh master bed room and cs-s24pkh for my living room.
But after used for 5 months, i noticed the cs-s13pkh seems like no longer cold, i report to hlk, so panasonic ppl will come tomorrow and have a look.

But sometimes turning on just nanoe-g acting as air purifier, i noticed the air even smelly than before.
anyone know why?

This post has been edited by sovietmah: Feb 21 2014, 11:59 AM
petlu28
post Feb 21 2014, 12:06 PM

Look at all my stars!!
*******
Senior Member
3,936 posts

Joined: Dec 2010
How you trun ON Nanoe-G without ON aircond? I can't turn ON Nanoe-G without ON aircond.


QUOTE(sovietmah @ Feb 21 2014, 11:58 AM)
So far i noticed I can turn ON Nanoe-G, acting like a air purfier without turning the aircon.
And i noticed the compressor fans also wont run, so less electricity used.

If turn ON aircon, also can turn on nanoe-g together.
I am using cs-s13pkh master bed room and cs-s24pkh for my living room.
But after used for 5 months, i noticed the cs-s13pkh seems like no longer cold, i report to hlk, so panasonic ppl will come tomorrow and have a look.

But sometimes turning on just nanoe-g acting as air purifier, i noticed the air even smelly than before.
anyone know why?
*
sovietmah
post Feb 21 2014, 12:09 PM

Look at all my stars!!
*******
Senior Member
2,243 posts

Joined: Nov 2005
QUOTE(petlu28 @ Feb 21 2014, 12:06 PM)
How you trun ON Nanoe-G without ON aircond? I can't turn ON Nanoe-G without ON aircond.
*
Just press the nanoe-g button when your aircon still OFF.
I think is green button if not mistaken.
petlu28
post Feb 21 2014, 12:14 PM

Look at all my stars!!
*******
Senior Member
3,936 posts

Joined: Dec 2010
I try before nothing function ON.

QUOTE(sovietmah @ Feb 21 2014, 12:09 PM)
Just press the nanoe-g button when your aircon still OFF.
I think is green button if not mistaken.
*
sovietmah
post Feb 21 2014, 01:43 PM

Look at all my stars!!
*******
Senior Member
2,243 posts

Joined: Nov 2005
QUOTE(petlu28 @ Feb 21 2014, 12:14 PM)
I try before nothing function ON.
*
Wat model? maybe no support only-nanoe-g?
petlu28
post Feb 21 2014, 01:53 PM

Look at all my stars!!
*******
Senior Member
3,936 posts

Joined: Dec 2010
If not support how come got Nanoe-G button? hmm.gif hmm.gif hmm.gif

QUOTE(sovietmah @ Feb 21 2014, 01:43 PM)
Wat model? maybe no support only-nanoe-g?
*
katmai81
post Feb 22 2014, 08:22 PM

Getting Started
**
Junior Member
116 posts

Joined: Aug 2012
QUOTE(kimsim @ Feb 20 2014, 07:18 PM)
Spakering sound may due to hard casing when changing to lower deg and created sound.

Please ask your installer to fit it nicely should be solved or open up front cover and paste some soft rubber piece to avoid on hard case too much gap.
*
Bro dont quite understand.
Care to explain bit more or even post pic?
Thanx
TSerik8lyt
post Feb 24 2014, 02:44 PM

Enthusiast
*****
Senior Member
715 posts

Joined: Jan 2008


Does anyone know why my technician pours water into my aircon internal part after removing my aircon external part?

This post has been edited by erik8lyt: Feb 24 2014, 02:44 PM
katmai81
post Feb 24 2014, 08:15 PM

Getting Started
**
Junior Member
116 posts

Joined: Aug 2012
QUOTE(erik8lyt @ Feb 24 2014, 02:44 PM)
Does anyone know why my technician pours water into my aircon internal part after removing my aircon external part?
*
U mean during service is it?
If yes...it's a form of cleaning chemical
TSerik8lyt
post Feb 24 2014, 08:26 PM

Enthusiast
*****
Senior Member
715 posts

Joined: Jan 2008


QUOTE(katmai81 @ Feb 24 2014, 08:15 PM)
U mean during service is it?
If yes...it's a form of cleaning chemical
*
Ya. I saw them remove many internal parts just to replace Nanoe-G to a new one.
SUSkimsim
post Feb 25 2014, 06:48 AM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(erik8lyt @ Feb 24 2014, 08:26 PM)
Ya. I saw them remove many internal parts just to replace Nanoe-G to a new one.
*
Seem like they know it kind of issue, but not to recalled
TSerik8lyt
post Feb 25 2014, 03:53 PM

Enthusiast
*****
Senior Member
715 posts

Joined: Jan 2008


Can I remove the Nanoe-G gadget and it won't be installed anymore from my aircon? Can my aircon operate?
TSerik8lyt
post Feb 25 2014, 10:10 PM

Enthusiast
*****
Senior Member
715 posts

Joined: Jan 2008


Anyone knows?
TSerik8lyt
post Mar 15 2014, 04:12 PM

Enthusiast
*****
Senior Member
715 posts

Joined: Jan 2008


I had changed to a new Nanoe-G. After a period, the thing starts to make noise. I have to press it and the noise is gone. The quality of Panasonic air-con is bad. I regret to have this air-con installed.
RidzOnes
post Jul 14 2016, 09:39 AM

New Member
*
Newbie
1 posts

Joined: Jul 2016
which one better?
Daikin or Panasonic? ( with inverter )
sidq
post Jul 14 2016, 12:02 PM

Getting Started
**
Junior Member
113 posts

Joined: Aug 2010


QUOTE(RidzOnes @ Jul 14 2016, 09:39 AM)
which one better?
Daikin or Panasonic? ( with inverter )
*
No one can say it for sure but you can refer here: https://forum.lowyat.net/topic/3602667

You can find lot of discussions/opinions about many brands.
zeefri
post Dec 6 2017, 09:55 PM

New Member
*
Junior Member
45 posts

Joined: Mar 2015
For those who have cleaned the nanoe-g generator in their AC manually, can you explain how you open the louver manually to access the nanoe-g? do we need to open the front panel as well?

This post has been edited by zeefri: Dec 6 2017, 09:56 PM
hanyeang
post Aug 1 2021, 10:56 AM

New Member
*
Newbie
4 posts

Joined: Jul 2013


QUOTE(erik8lyt @ Nov 16 2013, 02:19 PM)
After I turn on my aircon for a while, the needle tip of Nanoe-G sparkles and makes buzzing sound. My aircon is Panasonic CS-S10NKH.
*
Mine settled just clean tip and the side with cotton swap... No more sounds.

 

Change to: