As for my water heater which was wired differently as my aircond explained earlier, but also using the same switch (Schneider KB31D20NE):
Connect the live wire which is from the dB (mine is 1 of the 2 white wires is live) to L1.
Connect the load wire which is from the heater (mine is the other remaining white wire) to L2.
Connect the neutral wire which is from the dB (mine is 1 of the 2 black wires) to N1.
Connect the neutral wire which is from the heater (mine is the other remaining black wire) to N2.
Disclaimer: If not sure, hire an electrician! While finding my way around, I mistakenly connect the wires in such a way that even if the switch is off, the load wire in the heater has electricity, enough to kill someone who thought there would be no electricity when the switch is in off position. Misled also by heater standby lights did not light up; because the circuit is not complete
I had a few testing tools at my disposal to 'figure out' any mistakes. (1) A multimeter to understand the continuity of the double pole switch. (2) A Fluke voltmeter or Test pen to determine the presence/absence of electricity on the heater when the switch is on/off, as well as to identify the live wire at the wall. I never trust the wiremen before me, nor the colours of the wires.