QUOTE(ceo684 @ Aug 27 2021, 11:12 PM)
it has a stronger heater than the typical 3kW class. so if water pressure strong then this will be nice to use.

however as it takes 18.3A as per the rated power,
your wiring need to be up to code to support. using ciplak or fake wire will not have sufficient current carrying capacity to support well (undersized cable will heat up). Good quality 2.5mm² cable no problem.

any WH is just a fancy electric kettle. the most important life insurance is a properly fitted 10mA RCD at your DB box. one time payment saja no annual renewal premium.
*
Hi, because my condo is using the 3 phase electric power, so as per the DB box the current voltage for my unit is 415V. If I were to buy the Serene WH which consume up to 4.2KW.

4200/415=10.12A

So the 2.5mm cable can still cope with it right?



 