QUOTE(watermonkey @ Jan 23 2010, 06:11 PM)
Do you think that it's wise to ask my electrician to reduce the sensitivity?
Unfortunately too much speculation has created conclusions. Some misinformation noted and corrected.One, earth ground has no relationship to how an ELCD, RDC works. That is completely about what safety ground does. Unfortunately some mistakenly call that earth ground. Safety ground means a fault to any equipment results in a tripped circuit breaker. So that humans are protected from shocks. That receptacle's safety ground cannot connect to earth ground. It must connect to a bus bar in the main breaker box. Otherwise it may not provide sufficient human protection. And so the two ground (even if interconnected elsewhere) are completely different - have different purposes.
Second, ELCD, etc detect when an incoming current is different from an outgoing current. That means some current must be going elsewhere; maybe harmfully through a human. So the ELCD/RCD cuts off electricity. It does not need any safety ground or earth ground to function / protect / be effective.
Third, ELCD/RCD is not tripped by a microseconds current from something like lightning. A fault current takes milliseconds. But that much longer current can be created by a 'follow-through' current. This is AC current s flowing because a microsecond transient has made other and temporary connections (ie plasma or arcs).
Tripping is not created by lightning. But what lightning created and must never create causes an ELCD/RCD to trip. Solution was always this simple. Do not give a lightning current any reason to be inside. Otherwise all appliances are at risk.
That current is inside because it found better paths to earth (sometimes destructively) via appliances. If that current connects to earth BEFORE entering, then nothing inside is conducting that microsecond current. No microsecond current creating a milliseconds follow-through current means no nuisance tripping.
Nuisance tripping is a misnomer. Since the problem is really crated by intentionally not earthing transients to earth ground (not safety ground) and BEFORE it can enter.
Four, an effective solution means every incoming wire must connect low impedance (ie less than 3 meters) to earth at the service entrance. TV cable and satellite dish would make that connection only with a hardwire. AC electric and phone wires must make that low impedance (ie less than 3 meter) connection via a 'whole house' protector.
If that current is not connected low impedance (ie hardwire has no sharp bends) to upgraded earth ground electrodes, then that current will be inside hunting for earth ground via interior appliances and wires. That can even cause nuisance tripping. Because a current that should not be inside is inside.
That one human mistake that creates nuisance tripping. Another can be electronics that are missing required line filters. Resulting high frequency noise can cause some ELCD/RCD circuits to become confused and to intermittently trip.
Do not cure symptoms. Sensitivity is not the problem. Currents that should not be anywhere inside are the problem and what must be addressed. Those currents must connect low impedance (ie hardwire has no splices) to earth ground electrodes BEFORE entering.