Hmm how to tell if my main fuse is of higher rating?

Because the electrician change the old single row DB to a three row DB?

Do I need to take picture of it?

QUOTE(supersound @ Aug 12 2014, 10:27 PM)
If the main fuse are 60A or higher rating, for sure single phase also enough.
But once your house caught fire, insurance won't pay you.
*
This post has been edited by S'aimer: Aug 12 2014, 09:34 PM
SUSsupersound
post Aug 12 2014, 09:45 PM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(S'aimer @ Aug 12 2014, 09:34 PM)
Hmm how to tell if my main fuse is of higher rating?

Because the electrician change the old single row DB to a three row DB?

Do I need to take picture of it?
*
The fuse does have a rating, just have a check on it.
Even if the main fuse is rated high, does not means the wire rated to it. So you still need to lay new wire and their own 13A fuse for air conds.
S'aimer
post Aug 12 2014, 09:56 PM

On my way
****
Senior Member
637 posts

Joined: Jul 2010
From: West Malaysia
Problem is. The electrical work has been done already

Saw a new thick bunch of wires dangling at the storeroom side where the Main DB is before the electrical works were completed.

Comes in red, yellow, black and green? The aircon switches are all 15A and the electrician added 3 new aircon points too

QUOTE(supersound @ Aug 12 2014, 10:45 PM)
The fuse does have a rating, just have a check on it.
Even if the main fuse is rated high, does not means the wire rated to it. So you still need to lay new wire and their own 13A fuse for air conds.
*
SUSsupersound
post Aug 12 2014, 09:58 PM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(S'aimer @ Aug 12 2014, 09:56 PM)
Problem is. The electrical work has been done already

Saw a new thick bunch of wires dangling at the storeroom side where the Main DB is before the electrical works were completed.

Comes in red, yellow, black and green? The aircon switches are all 15A and the electrician added 3 new aircon points too
*
Then should be good already.
ozak
post Aug 12 2014, 10:07 PM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(S'aimer @ Aug 12 2014, 09:19 PM)
Hm let's say.

If I plan to install another 2 aircons in the house at a later time which will make it a total of 3 in the house. I would have to change to 3 phase?

But as far as I can see, a single bungalow has no problem running all 3 aircons on a single phase.
*
No problem with single phase. Given you have 2hp of 3 aircon and 2hp fridge running together, it draw 6kw.

You can run anything together total not more than 12kw.
weikee
post Aug 12 2014, 10:19 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(supersound @ Aug 12 2014, 09:27 PM)
If the main fuse are 60A or higher rating, for sure single phase also enough.
But once your house caught fire, insurance won't pay you.
*
I don't see any reason why insurance won't pay if it run within the limit, and with proper wiring. Unless House owner using wrong wire sizing maybe. A single phase max fuse is 63amps with the correct wire sizing. If you have come across such information from Insurance do share with us.
S'aimer
post Aug 12 2014, 10:24 PM

On my way
****
Senior Member
637 posts

Joined: Jul 2010
From: West Malaysia
Thank you bro supersound and bro ozak.

Was looking through my reno photos and realize I didn't take pics of the wires at storeroom! sweat.gif

Cross my fingers everything is good.
SUSsupersound
post Aug 13 2014, 01:43 AM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(weikee @ Aug 12 2014, 10:19 PM)
I don't see any reason why insurance won't pay if it run within the limit, and with proper wiring. Unless House owner using wrong wire sizing maybe.  A single phase max fuse is 63amps with the correct wire sizing.  If you have come across such information from Insurance do share with us.
*
Is on the TNB application form on the requirement.
And insurance company will use this form and fire department's report to decide pay or not pay in case of fire.
Also, I do know that with single phase I can run 5-6 air conds without problem but when something happens I don't want insurance company have an excuse to deny a claim.

This post has been edited by supersound: Aug 13 2014, 02:27 AM
weikee
post Aug 13 2014, 08:27 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(supersound @ Aug 13 2014, 01:43 AM)
Is on the TNB application form on the requirement.
And insurance company will use this form and fire department's report to decide pay or not pay in case of fire.
Also, I do know that with single phase I can run 5-6 air conds without problem but when something happens I don't want insurance company have an excuse to deny a claim.
*
Please tell me which line state not support of 3rd ac?

http://www.tnb.com.my/application/uploads/...cation_Form.pdf


I have also consult General insurance agent, nothing to do with AC quantity installed.
SUSsupersound
post Aug 13 2014, 09:49 AM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(weikee @ Aug 13 2014, 08:27 AM)
Please tell me which line state not support of 3rd ac?

http://www.tnb.com.my/application/uploads/...cation_Form.pdf
I have also consult General insurance agent, nothing to do with AC quantity installed.
*
http://www.tnb.com.my/residential/manage-y...upply-type.html
You can always ignore this and your agent never tells you the truth.
Again nothing happens everybody happy, something happens you enjoy it.
cherroy
post Aug 13 2014, 09:57 AM

20k VIP Club
Group Icon
Staff
25,802 posts

Joined: Jan 2003
From: Penang


QUOTE(supersound @ Aug 13 2014, 01:43 AM)
Is on the TNB application form on the requirement.
And insurance company will use this form and fire department's report to decide pay or not pay in case of fire.
Also, I do know that with single phase I can run 5-6 air conds without problem but when something happens I don't want insurance company have an excuse to deny a claim.
*
1HP = 0.75KW

750/240 = 3~4A,

Safety margin let say 25%, make it 5A per air cond

5 x 6 = 30A.

Still within the capability of a single phase that is 50A.

You cannot overload the single phase, but there is no rule said single phase house being equiped with 6 air-cond then may void the fire insurance coverage.


weikee
post Aug 13 2014, 10:10 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(cherroy @ Aug 13 2014, 09:57 AM)
1HP = 0.75KW

750/240 = 3~4A, 

Safety margin let say 25%, make it 5A per air cond

5 x 6 = 30A.

Still within the capability of a single phase that is 50A.

You cannot overload the single phase, but there is no rule said single phase house being equiped with 6 air-cond then may void the fire insurance coverage.
*
Single Phase are allow to go up to 63Amps, giving 25% safety margin is 47.25 Amps, and using 230v, is 10867 Watt. it can drive 10 HP in total.

Is still more than 3AC

The 50Amps is after the safety margin of 63Amps

This post has been edited by weikee: Aug 13 2014, 10:11 AM
SUSsupersound
post Aug 13 2014, 11:43 AM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(cherroy @ Aug 13 2014, 09:57 AM)
1HP = 0.75KW

750/240 = 3~4A, 

Safety margin let say 25%, make it 5A per air cond

5 x 6 = 30A.

Still within the capability of a single phase that is 50A.

You cannot overload the single phase, but there is no rule said single phase house being equiped with 6 air-cond then may void the fire insurance coverage.
*
You are right, but again TNB already stated the guideline we "should" upgrade to 3 phase once we exceeding 3 air conds.
Your calculation are assuming that it is good quality of copper wire being used. It not even taking in to account of the qaulity, length and efficiency of the wire. Where's the heat generated calculation?
In some sense indeed we can't overload a single phase, but we can overload the wire which later overload the main fuse.
For sure insurance company never stated the rule on this as they release the claim's payment based on official report by government. Have you ever claim insurance before? The company need 1 single word only to deny a claim.
cherroy
post Aug 13 2014, 11:47 AM

20k VIP Club
Group Icon
Staff
25,802 posts

Joined: Jan 2003
From: Penang


QUOTE(supersound @ Aug 13 2014, 11:43 AM)
You are right, but again TNB already stated the guideline we "should" upgrade to 3 phase once we exceeding 3 air conds.
Your calculation are assuming that it is good quality of copper wire being used. It not even taking in to account of the qaulity, length and efficiency of the wire. Where's the heat generated calculation?
In some sense indeed we can't overload a single phase, but we can overload the wire which later overload the main fuse.
For sure insurance company never stated the rule on this as they release the claim's payment based on official report by government. Have you ever claim insurance before? The company need 1 single word only to deny a claim.
*
I would like to see the guidelines/rules state in this. smile.gif
Ty.
SUSsupersound
post Aug 13 2014, 11:50 AM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(cherroy @ Aug 13 2014, 11:47 AM)
I would like to see the guidelines/rules state in this.  smile.gif
Ty.
*
I forgot where I posted that guideline, maybe a find using the search function will help you to get the answer fast. I just posted it recently.
S'aimer
post Aug 16 2014, 12:34 PM

On my way
****
Senior Member
637 posts

Joined: Jul 2010
From: West Malaysia
Took a look at my DB and It appears that I have 63A for my main fuse.

But realised that I don't see any fiber ready connection in storeroom or a telephone port at the back?


Attached thumbnail(s)
Attached Image
weikee
post Aug 16 2014, 12:53 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(S'aimer @ Aug 16 2014, 12:34 PM)
Took a look at my DB and It appears that I have 63A for my main fuse.

But realised that I don't see any fiber ready connection in storeroom or a telephone port at the back?
*
What is fiber/tel line got to do with electrical?
S'aimer
post Aug 16 2014, 02:07 PM

On my way
****
Senior Member
637 posts

Joined: Jul 2010
From: West Malaysia
Has nothing to do with electrical but seeing that the fiber point is supposed to be put in the storeroom with the DB, I reckon I will have to install the fiber point.

QUOTE(weikee @ Aug 16 2014, 01:53 PM)
What is fiber/tel line got to do with electrical?
*
weikee
post Aug 16 2014, 03:02 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(S'aimer @ Aug 16 2014, 02:07 PM)
Has nothing to do with electrical but seeing that the fiber point is supposed to be put in the storeroom with the DB, I reckon I will have to install the fiber point.
*
Depend where you want your equipment at. It usually at TV area because unifi come with TV subscription. Unless you have already prepare LAN point.
S'aimer
post Aug 16 2014, 03:37 PM

On my way
****
Senior Member
637 posts

Joined: Jul 2010
From: West Malaysia
Bro,

Mind if I PM you?

QUOTE(weikee @ Aug 16 2014, 04:02 PM)
Depend where you want your equipment at. It usually at TV area because unifi come with TV subscription. Unless you have already prepare LAN point.
*