 Air cond copper piping cost issue

views
     
nihility
post Feb 24 2025, 03:51 PM

Regular
******
Senior Member
1,595 posts

Joined: Sep 2021


QUOTE(cop23 @ Feb 24 2025, 10:06 AM)
60 ft copper pipe, is the compressor efficient enought to support such a long distance. you should think how to move the compressor nearer to wall unit. I dont think this is a good idea.please consul expert.
*
60ft = 20m, it is at the limit of of performance for fully inverter unit. The option for non-inverter unit is totally out of consideration due to distance limitation.

Some Strata, they limit the location to place the outdoor unit but they will specify what type of AC to use ( inverter or non-inverter).

This is a common issue with the newly built unit, developer want to conceal the piping in the slab. But once the piping leaks, it is almost impossible to detect / repair. Ended up, the AC contractor usually will suggest to by-pass the old pipe & run the new pipes. Just like the old plumbing pipe in old house, if you ask the plumber go to detect & repair, the plumber will ask the owner to by-pass with the new piping.
dudester
post Feb 24 2025, 03:57 PM

Regular
******
Senior Member
1,226 posts

Joined: Nov 2017
last time had the same problem, but we did detect the leak.
instead, reinstall the ac back to back to balcony and put condenser there with short piping requirement.
marvinben
post Feb 24 2025, 04:17 PM

Getting Started
**
Junior Member
249 posts

Joined: Mar 2010
QUOTE(cop23 @ Feb 24 2025, 10:06 AM)
60 ft copper pipe, is the compressor efficient enought to support such a long distance. you should think how to move the compressor nearer to wall unit. I dont think this is a good idea.please consul expert.
*
Modern R32 system no problem. Example cheapest Daikin 1hp can go 25m~82ft. I've even done 30m installs (no elevation changes tho) with no issue.

Edit: Copper Pipe for 1hp-1.15hp would be RM12 for 2 feet. What cost a lot is the labor. (Open ceiling, run new pipes, close ceiling, seal wall, paint).

This post has been edited by marvinben: Feb 24 2025, 04:22 PM
cop23
post Feb 24 2025, 04:18 PM

Getting Started
**
Junior Member
78 posts

Joined: Jan 2009


QUOTE(nihility @ Feb 24 2025, 03:51 PM)
60ft = 20m, it is at the limit of of performance for fully inverter unit. The option for non-inverter unit is totally out of consideration due to distance limitation.

Some Strata, they limit the location to place the outdoor unit but they will specify what type of AC to use ( inverter or non-inverter).

This is a common issue with the newly built unit, developer want to conceal the piping in the slab. But once the piping leaks, it is almost impossible to detect / repair. Ended up, the AC contractor usually will suggest to by-pass the old pipe & run the new pipes. Just like the old plumbing pipe in old house, if you ask the plumber go to detect & repair, the plumber will ask the owner to by-pass with the new piping.
*
IC, if the compressor location is fixed you may have no choice but to repair the leaking.

Perhaps you can arrange for someone to inject pressurized water into the copper pipe to locate the leak, and then cut and replace the damaged section with a new piece.

but all this need try and error. or else change new copper hose.

hope you get best solution without spen big amount.
TShoonanoo
post Feb 24 2025, 05:13 PM

Regular
******
Senior Member
1,782 posts

Joined: Jul 2022
QUOTE(deejay_krish @ Feb 24 2025, 09:57 AM)
bollocks, they can cut where the leak is and fit a new extension with torch gas, thats how copper pipe works. Theres also many modern tools to find the leak nowadays. Clearly this guy is trying to rob you. Move away and find a better guy. Keep in mind what i said. And use it as reference.
*
yeah I have a hunch on that one.

that's why I am delaying to do so

This post has been edited by hoonanoo: Feb 24 2025, 05:14 PM
TShoonanoo
post Feb 24 2025, 05:15 PM

Regular
******
Senior Member
1,782 posts

Joined: Jul 2022
QUOTE(dudester @ Feb 24 2025, 03:57 PM)
last time had the same problem, but we did detect the leak.
instead, reinstall the ac back to back to balcony and put condenser there with short piping requirement.
*
friend...if I can do that, would have done it long ago lah.

But I live in Condo, and the management don't allow this
TShoonanoo
post Feb 24 2025, 05:16 PM

Regular
******
Senior Member
1,782 posts

Joined: Jul 2022
QUOTE(nihility @ Feb 24 2025, 03:51 PM)
60ft = 20m, it is at the limit of of performance for fully inverter unit. The option for non-inverter unit is totally out of consideration due to distance limitation.

Some Strata, they limit the location to place the outdoor unit but they will specify what type of AC to use ( inverter or non-inverter).

This is a common issue with the newly built unit, developer want to conceal the piping in the slab. But once the piping leaks, it is almost impossible to detect / repair. Ended up, the AC contractor usually will suggest to by-pass the old pipe & run the new pipes. Just like the old plumbing pipe in old house, if you ask the plumber go to detect & repair, the plumber will ask the owner to by-pass with the new piping.
*
bypass very ugly la

will make my house look like a space ship with black hose running through the ceiling.
homicidal85
post Feb 24 2025, 05:20 PM

Getting Started
**
Junior Member
295 posts

Joined: Jun 2006
From: JB


QUOTE(hoonanoo @ Feb 23 2025, 10:15 PM)
my condo air cond not strong, macam gas leaking.

called air cond guy to come, confirmed leaking but not from air cond, suspect from piping that goes from ceiling board through the concrete ceiling to outside the fan.

Air cond guy claimed its about 60 feet. And every 2 feet copper piping is RM 25. If costed together about 1,500.

Really that expensive?

I have 4 other air conds in my unit, if any of the copper piping koyak...wow it means 1,500 X 5.

Are there any alternative?
*
1. is your outdoor unit really that far away? who the fuk installed an outdoor unit through concrete 40-50' away from the indoor unit?
2. how did they route the drainage? if the drainage anywhere near as long as the copper piping, I would be surprised if it isnt leaking somewhere and causing damage or mold to your house.

as others have noted. just need to repair the part that is leaking. by right, you shouldnt need to replace the whole length of pipe.

This post has been edited by homicidal85: Feb 24 2025, 05:21 PM
dudester
post Feb 24 2025, 05:22 PM

Regular
******
Senior Member
1,226 posts

Joined: Nov 2017
QUOTE(hoonanoo @ Feb 24 2025, 05:15 PM)
friend...if I can do that, would have done it long ago lah.

But I live in Condo, and the management don't allow this
*
mine was condo. i asked management, why many can put in balcony. they say common problem and allow.
TShoonanoo
post Feb 24 2025, 05:28 PM

Regular
******
Senior Member
1,782 posts

Joined: Jul 2022
QUOTE(homicidal85 @ Feb 24 2025, 05:20 PM)
1. is your outdoor unit really that far away? who the fuk installed an outdoor unit through concrete 40-50' away from the indoor unit?
2. how did they route the drainage? if the drainage anywhere near as long as the copper piping, I would be surprised if it isnt leaking somewhere and causing damage or mold to your house.

as others have noted. just need to repair the part that is leaking. by right, you shouldnt need to replace the whole length of pipe.
*
yes it is at the other side of my condo, near the wet kitchen where they house the split unit fans which are hidden by a wall of decorative metal cladding.

you be surprised how fuked up developers are these days. All aesthetics, no proper plan for these eventualities.

The copper piping goes from my master bedroom through 2 other rooms then L-share bend and through the kitchen then through to the wet kitchen and to the fans.

Some of the piping goes through the plaster boards that have a small door open to view but 50% of it goes through the concrete ceiling....

it some ways the contractor say is logical
nihility
post Feb 24 2025, 05:56 PM

Regular
******
Senior Member
1,595 posts

Joined: Sep 2021


QUOTE(hoonanoo @ Feb 24 2025, 05:16 PM)
bypass very ugly la

will make my house look like a space ship with black hose running through the ceiling.
*
You put a proper PVC casing to conceal the insulated piping, run it at the edge of the walls. That would be the cheapest & reliable option.

If you want to conceal by hacking, it would be worse.

Ugly = temporary. Use this to motivate yourself that you are going to move out to bigger house in near future.
nihility
post Feb 24 2025, 06:03 PM

Regular
******
Senior Member
1,595 posts

Joined: Sep 2021


QUOTE(cop23 @ Feb 24 2025, 04:18 PM)
IC, if the compressor location is fixed you may have no choice but to repair the leaking.

Perhaps you can arrange for someone to inject pressurized water into the copper pipe to locate the leak, and then cut and replace the damaged section with a new piece.

but all this need try and error. or else change new copper hose.

hope you get best solution without spen big amount.
*
It was not the problem to be faced by me. It was other people's problem, actually.

I just got to know the issue & try to understand the scenario from the people who face the issue. At least I know how to deal with this issue for another application.

Anyway, thanks for your wishes.
urgrocer P
post Feb 24 2025, 07:29 PM

New Member
*
Probation
10 posts

Joined: Aug 2020
Is any part of the copper buried in concrete?
GamersFamilia
post Feb 24 2025, 10:17 PM

Proud to be Malaysian
********
All Stars
17,802 posts

Joined: Dec 2007
From: Bandar Baru Bangi , Malaysia




Previously my aircond copper pipe leak during service, they just welding it, until now perfect
yehlai
post Feb 25 2025, 12:57 AM

tree lover
*******
Senior Member
4,539 posts

Joined: Feb 2006
From: LocOmoT|oN.L0co|oti0N


QUOTE(hoonanoo @ Feb 24 2025, 08:33 AM)
the problem is that the piping goes through some concrete roofing as well as over the plaster board.

he says he is pumping high pressure gas to detect. If got sound or yellow stain on plaster board that is where the leakage is.

However, if the leakage is over the concreate ceiling, that's difficult to trace.

he suggested to replace the whole piping, he claims to be 60 feet. I don't think its that long.

Yes I am finding a second opinion.
*
If your pipings are concealed suggest to change whole copper piping
How old is your house?

Reason being there might be multiple leaking point
let's say if you hack your wall and found one leaking point
then you weld back
after few weeks if not cold then you need find other leaking spot
hacking + weld + conceal again
double work.. labor alone will be hefty

Not suggest to do half baked work
the technician also will tell you they will not guarantee.. after repair done
because if the pipe is old and started leaking, potentially other section have same issues or will have same issue soon (almost time)

This also depends on quality and thickness of the copper pipe used by your contractor

Even if you hack the whole pipe to inspect and weld back muitlple leaking spots
don't think the repair will be as good as brand new copper pipe

Just need to ensure your technician using good copper pipe
one time repair and you're good

yehlai
post Feb 25 2025, 01:03 AM

tree lover
*******
Senior Member
4,539 posts

Joined: Feb 2006
From: LocOmoT|oN.L0co|oti0N


QUOTE(boonwuilow @ Feb 24 2025, 12:02 AM)
You can provide your own copper piping, u go besi buruk ask around see got any or not, these are the kind of item where it is easily stolen by worker then sold to besi buruk for a quick buck. This kind of copper typically they are buying at RM30 / kilo. If u offer them at RM50 / kilo chances is they are more than willing to sell you.
*
Don't get yourself trouble
if change.. must be brand new pipe
yehlai
post Feb 25 2025, 01:06 AM

tree lover
*******
Senior Member
4,539 posts

Joined: Feb 2006
From: LocOmoT|oN.L0co|oti0N


QUOTE(giftfre @ Feb 24 2025, 08:55 AM)
Last time my aircon also leaking so i bought a new aircon from Shopee and call technician for installation.
then the technician dismantled old aircon together with old piping and reinstalled new aircon with new piping set.
Installation cost at around RM250 (10 feet copper only).
*
Got hacking, drilling and conceal?
from wht I know.. the installation fees not include those above

If all included, maybe TS can double confirm again before hiring them
because it's cheaper than change/repair old piping
boonwuilow
post Feb 25 2025, 01:55 AM

Diesel rocks
*******
Senior Member
3,836 posts

Joined: Oct 2009
From: Cheras, Selangor


QUOTE(yehlai @ Feb 25 2025, 01:03 AM)
Don't get yourself trouble
if change.. must be brand new pipe
*
is brand new
giftfre
post Feb 25 2025, 07:22 AM

Control Macho
****
Junior Member
682 posts

Joined: Jul 2010



QUOTE(yehlai @ Feb 25 2025, 01:06 AM)
Got hacking, drilling and conceal?
from wht I know.. the installation fees not include those above

If all included, maybe TS can double confirm again before hiring them
because it's cheaper than change/repair old piping
*
no wall hack. The job scope are replace old in & outdoor unit and piping.
homicidal85
post Feb 25 2025, 10:14 AM

Getting Started
**
Junior Member
295 posts

Joined: Jun 2006
From: JB


QUOTE(hoonanoo @ Feb 24 2025, 05:28 PM)
yes it is at the other side of my condo, near the wet kitchen where they house the split unit fans which are hidden by a wall of decorative metal cladding.

you be surprised how fuked up developers are these days. All aesthetics, no proper plan for these eventualities.

The copper piping goes from my master bedroom through 2 other rooms then L-share bend and through the kitchen then through to the wet kitchen and to the fans.

Some of the piping goes through the plaster boards that have a small door open to view but 50% of it goes through the concrete ceiling....

it some ways the contractor say is logical
*
thats crazy man. the developer might have been better off putting up more decorative metalwork on the other side.