TSTheBladeRunner
post Feb 4 2025, 10:56 PM, updated 10 months ago

Getting Started
**
Junior Member
199 posts

Joined: Jan 2013
I plan to buy a 3000watt built in oven for kitchen cabinet.

I need to know,

1. Cable size to use
2. MCB rating (C16, C20, C32)
3. Socket type to use

Any tips? Thanks.
TSTheBladeRunner
post Feb 7 2025, 05:56 PM

Getting Started
**
Junior Member
199 posts

Joined: Jan 2013
QUOTE(stormer.lyn @ Feb 5 2025, 02:35 PM)
1. 4 mm² for each of the 3 wires
2. C25 or C20
3. Direct wiring with disconnect switch, commando plug or round pin 15A socket + plug
*
Thanks for the recommendation. Will make sure electrician will follow it.
TSTheBladeRunner
post Feb 9 2025, 09:54 AM

Getting Started
**
Junior Member
199 posts

Joined: Jan 2013
Is it a problem if neutral and live are 4mm but earth is 2.5mm?
TSTheBladeRunner
post Feb 9 2025, 10:19 AM

Getting Started
**
Junior Member
199 posts

Joined: Jan 2013
QUOTE(stormer.lyn @ Feb 9 2025, 10:06 AM)
This is not allowed by code in Malaysia. Only wiring larger than 16 mm² may use a Earth wire that is smaller than the power conductors.
(Disclaimer : this is off the top of my head, getting ready for something so reluctant to look for the actual size of wire but it is something like that. Maybe it's larger than 10 mm²?)

You want to save money by using 2.5 mm² Earth wire then that's on you.
*
Oven itself looks like using 2.5mm cable (from oven manufacturer). I was told even 2.5mm is ok but for good measure use 4 mm (by electrician). Currently no 4 mm earth available so had to use 2.5 mm earth.


TSTheBladeRunner
post Feb 14 2025, 08:45 PM

Getting Started
**
Junior Member
199 posts

Joined: Jan 2013
QUOTE(stormer.lyn @ Feb 10 2025, 11:10 AM)
Actually can use 2.5 mm² wires, as 3000 W will use under 14 Amp. 2.5 mm² wires are rated at 20 A so should be quite safe. Just ensure the wire is a branded that follows the proper specifications and the size is actually 2.5 mm². Make sure the MCB is C20 if using this size wire. I would use a maximum oven if using 2.5 mm² wires up to 4000 W.
*
Already check my MCB and its C20. Thanks for the advice.

 