I plan to buy a 3000watt built in oven for kitchen cabinet.
I need to know,
1. Cable size to use
2. MCB rating (C16, C20, C32)
3. Socket type to use
Any tips? Thanks.
Built in wall oven requirement.
Built in wall oven requirement.
|
|
Feb 4 2025, 10:56 PM, updated 10 months ago
Return to original view | IPv6 | Post
#1
|
![]() ![]()
Junior Member
199 posts Joined: Jan 2013 |
I plan to buy a 3000watt built in oven for kitchen cabinet.
I need to know, 1. Cable size to use 2. MCB rating (C16, C20, C32) 3. Socket type to use Any tips? Thanks. |
|
|
|
|
|
Feb 7 2025, 05:56 PM
Return to original view | IPv6 | Post
#2
|
![]() ![]()
Junior Member
199 posts Joined: Jan 2013 |
|
|
|
Feb 9 2025, 09:54 AM
Return to original view | IPv6 | Post
#3
|
![]() ![]()
Junior Member
199 posts Joined: Jan 2013 |
Is it a problem if neutral and live are 4mm but earth is 2.5mm?
|
|
|
Feb 9 2025, 10:19 AM
Return to original view | IPv6 | Post
#4
|
![]() ![]()
Junior Member
199 posts Joined: Jan 2013 |
QUOTE(stormer.lyn @ Feb 9 2025, 10:06 AM) This is not allowed by code in Malaysia. Only wiring larger than 16 mm² may use a Earth wire that is smaller than the power conductors. Oven itself looks like using 2.5mm cable (from oven manufacturer). I was told even 2.5mm is ok but for good measure use 4 mm (by electrician). Currently no 4 mm earth available so had to use 2.5 mm earth.(Disclaimer : this is off the top of my head, getting ready for something so reluctant to look for the actual size of wire but it is something like that. Maybe it's larger than 10 mm²?) You want to save money by using 2.5 mm² Earth wire then that's on you. |
|
|
Feb 14 2025, 08:45 PM
Return to original view | IPv6 | Post
#5
|
![]() ![]()
Junior Member
199 posts Joined: Jan 2013 |
QUOTE(stormer.lyn @ Feb 10 2025, 11:10 AM) Actually can use 2.5 mm² wires, as 3000 W will use under 14 Amp. 2.5 mm² wires are rated at 20 A so should be quite safe. Just ensure the wire is a branded that follows the proper specifications and the size is actually 2.5 mm². Make sure the MCB is C20 if using this size wire. I would use a maximum oven if using 2.5 mm² wires up to 4000 W. Already check my MCB and its C20. Thanks for the advice. |