QUOTE(FyChai @ Dec 29 2023, 08:52 AM)
The DB is ori set from developer, I just add on 3 MCB on left hand side for dry and wet kitchen. May I know is that call MCCB for my current 63A breaker? If I change to 100mA, do I need to upgrade or remain 63A?

As per pic above, do I need to place 1 RCB for every floor? Or just for the cable which use for water heater?
Sorry lots of questions, i need more knowledge before asking a electrician to visit again. Previous electrician came to check and never mention about the 300mA of breaker and RCB until I find it myself.
The quality of components used are questionable if they already installed C16 MCB.
As per pic above, do I need to place 1 RCB for every floor? Or just for the cable which use for water heater?
Sorry lots of questions, i need more knowledge before asking a electrician to visit again. Previous electrician came to check and never mention about the 300mA of breaker and RCB until I find it myself.
Your scope of work:
change the mains (entire house) RCD to 30mA.
install a new 10mA RCD for EACH WH (water heater) circuit.
You do not need a RCD for every floor.