It will be a mess to diagnose if there’s anything wrong with the electrical not to mention fire risk as the cable sizing will be different between light and sockets. The weak link will burn up in a short circuit and may not even trigger MCB to trip. Hence better not.
SUSceo684
post Mar 25 2023, 01:12 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(PowerGadget @ Mar 25 2023, 01:37 AM)
Thanks for the advise, ceo684. So does it mean it's better for me to pull neutral wire from db to each of the switch?

Is it possible to pull one neutral wire for one group of smart switch instead?

And what's the market rate to pull a neutral wire at the moment?
*
The neutral existence for lights, starts at the light point itself on the ceiling and back to DB.

Final circuit not supposed to be joined so to be code compliant by right have to pull all the way from DB to wherever the switch is.
Alternatively you can tap on the 13A SSO point "like looping socket" but have to upgrade all the wiring to 2.5mm to match the SSO MCB and existing SSO cable size.
SUSceo684
post Mar 30 2023, 10:20 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(PowerGadget @ Mar 30 2023, 04:20 PM)
Thanks for your reply epicure..

Wondering whether the method that you use was just adding a wire loop from socket or aircond to the light switch?

I plan to do it myself as it’s just adjacent switch but worry anything goes wrong.
*
In the correct flow the Live still fed from the light circuit and smaller MCB,
in the reversed flow "should anything go wrong on the socket neutral" - the socket MCB is 20A or higher because its cables are all 2.5mm or higher, light circuitry Live at 1.5mm will burn before the 20A MCB trip.

This is why it is not recommended to mix and match. It is a safety risk.

However if you mount the switch at the light point itself then you already have a L and N.