QUOTE(hottemper @ Aug 20 2022, 10:21 AM)
As per title, been using this for more than 10 years in my house, old house layout where the switch for heater is in my room
Recently it burnt, so it concerned me as is it ok to use 13a for this water heater, or it's best to change to the 20a on off switch, or the 15a round plug and socket? Thanks!


The instant water heater is normally at 3.3kW to 3.6kW power rating. So, current flow would beRecently it burnt, so it concerned me as is it ok to use 13a for this water heater, or it's best to change to the 20a on off switch, or the 15a round plug and socket? Thanks!


3600/250 = 14A (worse case). Even 3300/250 = 13.2 A
The current 13A socket is not suitable. It still works for long time because there is buffer to its rating normally not specified. Therefore it works near its max rating most of the time. The rating is related to contact resistance between socket and plug. So, if the current is high, the heat will also generated thus weaken the copper property over time. The clamping contact worsen over time until the point it get burnt.
The best would be using higher rated socket and the best available is 15A socket. I've been using for more than 15 years with no burning sign and my heater is 3.3kW rated. As for the wire from the socket to the heater, the 2.5mm² is fine. It should be able to carry even 25A (or at worse 20A) at 60ºC ambient temperature, according to calculator I have here. Anyway, it is short cable.
The water heater has internal RCCB or ELCB, but test it regularly to ensure functionality. Adding 10mA RCCB provides redundancy just in case the internal one fail. Well, I don;t have one also