QUOTE(ceo684 @ Dec 2 2021, 01:23 AM)
60A is not that hard to achieve with your usage
4 1hpaircons on @ 6A each = 24A
1 water heater 3kW class = 16A
Kettle = 9A
this is already 49A/60A. haven't counted your other stuff or 2nd water heater running..
It is better to replace with a proper MCB. Specify either ABB or Hager. If it trips, you just reset (push up).
[attachmentid=11052442]
this is MCB ^
ABB store sell pretty cheap for the
63A 2P MCB then you get the electrician to come and install. It might be worthwhile to refresh whole DB box if its just as dinosaur.
Current fuse holder, if fuse blow at night, it is almost impossible to find a fuse

Agree with you. like you said, didn't even factor in other stuffs like TV, fridges, computers etc.
And yesterday was a hot day. i guess the aircons were working at 100% all at once.
thanks for the ABB or Hager brand recommendations. I completely have no experience in this. Called a local electrician recommended by some shop, and hopefully the chap can come today or tomorrow to take a look and make necessary changes.
Luckily today weather is cooler, and the temperature on the MCB is hovering at 70 degrees. but scary to have it at 100 degrees. can cook meat already.